Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Kirk Herander
Yea, i suspected that. Me bad. been a while for sure.
On 6/25/2020 6:31:24 PM, William Miller  wrote:
Kirk:
If my memory is correct: What you describe below are port assignments if one is 
stacking FXR inverters for 120/240 with a Hub 10.3. It also requires changing 
DIP jumpers from factory defaults. This is not accurate for stacking Radians. 
With Radians I think secondary inverters can use any port but I have always 
used 2 through X for secondaries.
William
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org]] On Behalf Of Kirk Herander
Sent: Thursday, June 25, 2020 2:07 PM
To: re-wrenches@lists.re-wrenches.org [mailto:re-wrenches@lists.re-wrenches.org]
Subject: Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s
The master-slave config types and port assignments have always been confusing. 
The quick start guide lists a config where the master is port 1 and the slave 
is port 7. I believe port 7 is called the sub-master in this config. With only 
2 inverters it functions as the slave to the master in port 1. This config has 
always worked for me.
Hope this is accurate info.
On 6/25/2020 1:35:55 PM, Chris Schaefer mailto:ch...@solarandwindfx.com]> wrote:
G'Day All,
So I started up a system recently with two Radian 8048A's. The master is 
connected to port 1 and the slave connected to port 2 with the FlexNet at port 
3. There are no OB charge controllers in the system. When the hub is polling 
(led's scrolling) nothing shows up for the slave at port 2. It's like the slave 
inverter doesn't exist. So I moved the slave and flexnet down to port 3 and 4. 
No change in the polling. I swapped out comm (factory green) cables. Again no 
change. Looking at the control board of the slave there is only one green led 
on which is located at the upper right-hand side. Otherwise no led's are on. I 
have 57v at the buss bar terminals of the inverter. Of course since there is no 
polling at the hub there is no way to view port 2 to view the slave at the Mate.
Now the only thing that I didn't do was to try and use the manual on/off 
switch-jumper to start the slave. But in the past regardless of the inverter 
being on or off it would still show up on the hub. This is a new one and I'm 
looking for some direction here.
Thanks,
Christopher-
Chris Schaefer’s
Error! Filename not specified. [http://www.solarandwindfx.com]
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com [http://www.solarandwindfx.com] ~ E-mail: 
ch...@solarandwindfx.com [mailto:ch...@solarandwindfx.com]
Error! Filename not specified.
Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."
___ List sponsored by Redwood 
Alliance List Address: RE-wrenches@lists.re-wrenches.org 
[mailto:RE-wrenches@lists.re-wrenches.org] Change listserver email address & 
settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
[http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org] 
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
[http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html] 
List rules & etiquette: www.re-wrenches.org/etiquette.htm 
[http://www.re-wrenches.org/etiquette.htm] Check out or update participant 
bios: www.members.re-wrenches.org [http://www.members.re-wrenches.org]___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Kirk Herander
The master-slave config types and port assignments have always been confusing. 
The quick start guide lists a config where the master is port 1 and the slave 
is port 7. I believe port 7 is called the sub-master in this config. With only 
2 inverters it functions as the slave to the master in port 1. This config has 
always worked for me.

Hope this is accurate info.
On 6/25/2020 1:35:55 PM, Chris Schaefer  wrote:
G'Day All,

So I started up a system recently with two Radian 8048A's. The master is 
connected to port 1 and the slave connected to port 2 with the FlexNet at port 
3. There are no OB charge controllers in the system. When the hub is polling 
(led's scrolling) nothing shows up for the slave at port 2. It's like the slave 
inverter doesn't exist. So I moved the slave and flexnet down to port 3 and 4. 
No change in the polling. I swapped out comm (factory green) cables. Again no 
change. Looking at the control board of the slave there is only one green led 
on which is located at the upper right-hand side. Otherwise no led's are on. I 
have 57v at the buss bar terminals of the inverter. Of course since there is no 
polling at the hub there is no way to view port 2 to view the slave at the Mate.

Now the only thing that I didn't do was to try and use the manual on/off 
switch-jumper to start the slave. But in the past regardless of the inverter 
being on or off it would still show up on the hub. This is a new one and I'm 
looking for some direction here.

Thanks,
Christopher-
Chris Schaefer’s
[http:www.solarandwindfx.com]
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com [http://www.solarandwindfx.com] ~ E-mail: 
ch...@solarandwindfx.com [mailto:ch...@solarandwindfx.com]

Thomas Jefferson, the author of our great Constitution, once said, "democracy" 
will cease to exist when you take away from those who are willing to work and 
give to those who would not."
___ List sponsored by Redwood 
Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver 
email address & settings: 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update 
participant bios: www.members.re-wrenches.org___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Chris Schaefer
Well after just a little over 2 hours on hold I did get through to a very
understanding tech support rep. I explained the issue and that the only LED
on the board that was on was the D21 (Remote Pwr). Today I learned that
this is powered by the Hub. Thus the PSB is indeed dead. I was given a
choice of either a replacement PSB or an entirely new inverter. Apparently
there has been an ongoing issue with the power supply boards lately and in
order to figure out why the engineering department would like to get the
entire unit returned for testing purposes. So for the sake of all of us out
in the field I agreed to replace the entire inverter in hopes that this
problem can be eliminated. Thanks for all your input and now we have yet
another tool in our "mental" toolbag.

Gratefully,
Christopher

On Thu, Jun 25, 2020 at 6:31 PM William Miller 
wrote:

> Kirk:
>
>
>
> If my memory is correct:  What you describe below are port assignments if
> one is stacking FXR inverters for 120/240 with a Hub 10.3.  It also
> requires changing DIP jumpers from factory defaults.  This is not accurate
> for stacking Radians.  With Radians I think secondary inverters can use any
> port but I have always used 2 through X for secondaries.
>
>
>
> William
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Kirk Herander
> *Sent:* Thursday, June 25, 2020 2:07 PM
> *To:* re-wrenches@lists.re-wrenches.org
> *Subject:* Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @
> Mate3s
>
>
>
> The master-slave config types and port assignments have always been
> confusing. The quick start guide lists a config where the master is port 1
> and the slave is port 7. I believe port 7 is called the sub-master in this
> config. With only 2 inverters it functions as the slave to the master in
> port 1. This config has always worked for me.
>
>
>
> Hope this is accurate info.
>
> On 6/25/2020 1:35:55 PM, Chris Schaefer  wrote:
>
> G'Day All,
>
>
>
> So I started up a system recently with two Radian 8048A's. The master is
> connected to port 1 and the slave connected to port 2 with the FlexNet at
> port 3. There are no OB charge controllers in the system. When the hub is
> polling (led's scrolling) nothing shows up for the slave at port 2. It's
> like the slave inverter doesn't exist. So I moved the slave and flexnet
> down to port 3 and 4. No change in the polling. I swapped out comm (factory
> green) cables. Again no change. Looking at the control board of the slave
> there is only one green led on which is located at the upper right-hand
> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
> the inverter. Of course since there is no polling at the hub there is no
> way to view port 2 to view the slave at the Mate.
>
>
>
> Now the only thing that I didn't do was to try and use the manual on/off
> switch-jumper to start the slave. But in the past regardless of the
> inverter being on or off it would still show up on the hub. This is  a new
> one and I'm looking for some direction here.
>
>
>
> Thanks,
>
> Christopher-
>
> Chris Schaefer’s
> *Error! Filename not specified.* 
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
>  ~ E-mail: **ch...@solarandwindfx.com
> *
>
> *Error! Filename not specified.*
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
>
> ___ List sponsored by Redwood
> Alliance List Address: RE-wrenches@lists.re-wrenches.org Change
> listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or
> update participant bios: www.members.re-wrenches.org
>
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
 ~ E-mail: ch...@solarandwindfx.com
*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
__

Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread William Miller
Kirk:



If my memory is correct:  What you describe below are port assignments if
one is stacking FXR inverters for 120/240 with a Hub 10.3.  It also
requires changing DIP jumpers from factory defaults.  This is not accurate
for stacking Radians.  With Radians I think secondary inverters can use any
port but I have always used 2 through X for secondaries.



William





*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Kirk Herander
*Sent:* Thursday, June 25, 2020 2:07 PM
*To:* re-wrenches@lists.re-wrenches.org
*Subject:* Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @
Mate3s



The master-slave config types and port assignments have always been
confusing. The quick start guide lists a config where the master is port 1
and the slave is port 7. I believe port 7 is called the sub-master in this
config. With only 2 inverters it functions as the slave to the master in
port 1. This config has always worked for me.



Hope this is accurate info.

On 6/25/2020 1:35:55 PM, Chris Schaefer  wrote:

G'Day All,



So I started up a system recently with two Radian 8048A's. The master is
connected to port 1 and the slave connected to port 2 with the FlexNet at
port 3. There are no OB charge controllers in the system. When the hub is
polling (led's scrolling) nothing shows up for the slave at port 2. It's
like the slave inverter doesn't exist. So I moved the slave and flexnet
down to port 3 and 4. No change in the polling. I swapped out comm (factory
green) cables. Again no change. Looking at the control board of the slave
there is only one green led on which is located at the upper right-hand
side. Otherwise no led's are on. I have 57v at the buss bar terminals of
the inverter. Of course since there is no polling at the hub there is no
way to view port 2 to view the slave at the Mate.



Now the only thing that I didn't do was to try and use the manual on/off
switch-jumper to start the slave. But in the past regardless of the
inverter being on or off it would still show up on the hub. This is  a new
one and I'm looking for some direction here.



Thanks,

Christopher-

Chris Schaefer’s
*Error! Filename not specified.* 

*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
 ~ E-mail: **ch...@solarandwindfx.com
*

*Error! Filename not specified.*

Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."

___ List sponsored by Redwood
Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver
email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or
update participant bios: www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Jerry Shafer
Ok back to outback defective board in the comms side of the inverter,
contact outback and what ever you do do NOT leave your number for a call
back as it will never come, call first thing, stay on hold and wait.
Jerry

On Thu, Jun 25, 2020, 2:00 PM Chris Schaefer 
wrote:

> Since the Flexnet on port 3 was active and could be seen on the Mate, thus
> I moved the slave on port 2 to port 3 and moved the FlexNet from port 3 to
> port 4. No change. I did try another OB factory green cable to no avail.
>
> Christopher
>
> On Thu, Jun 25, 2020 at 4:25 PM Jerry Shafer 
> wrote:
>
>> Chris
>> Did you skip over and plug in to port 3 with the slave, swap the cord,
>> Jerry
>>
>> On Thu, Jun 25, 2020, 12:54 PM Chris Schaefer 
>> wrote:
>>
>>> The system is critical to a farm watering operation so I wasn't able to
>>> shut it down to try and swap the port 1 inverter with the port 2 inverter.
>>> As for changing the power save settings, that is what alerted me to the
>>> issue. Under no circumstance can you see a port 2 via the Mate. That's what
>>> had me looking at the hub itself and that's when I noticed that the LED on
>>> port 2 wasn't lighting up as the hub scrolled/polled by.
>>>
>>> Christopher
>>>
>>> On Thu, Jun 25, 2020 at 3:37 PM William Miller 
>>> wrote:
>>>
 Christopher;



 Just spit-balling here:  is the secondary inverter asleep (hate the
 master/slave terminology…)?  Try changing power save settings to make sure
 the secondary is awake and see if that changes the situation.  Seems
 unlikely this will solve the problem, but it may provide some kind of clue.



 Also, did you try swapping primary and secondary?  Run with secondary
 alone as primary?



 William Miller



 *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
 Behalf Of *Chris Schaefer
 *Sent:* Thursday, June 25, 2020 10:35 AM
 *To:* RE-wrenches
 *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @
 Mate3s



 G'Day All,



 So I started up a system recently with two Radian 8048A's. The master
 is connected to port 1 and the slave connected to port 2 with the FlexNet
 at port 3. There are no OB charge controllers in the system. When the hub
 is polling (led's scrolling) nothing shows up for the slave at port 2. It's
 like the slave inverter doesn't exist. So I moved the slave and flexnet
 down to port 3 and 4. No change in the polling. I swapped out comm (factory
 green) cables. Again no change. Looking at the control board of the slave
 there is only one green led on which is located at the upper right-hand
 side. Otherwise no led's are on. I have 57v at the buss bar terminals of
 the inverter. Of course since there is no polling at the hub there is no
 way to view port 2 to view the slave at the Mate.



 Now the only thing that I didn't do was to try and use the manual
 on/off  switch-jumper to start the slave. But in the past regardless of the
 inverter being on or off it would still show up on the hub. This is  a new
 one and I'm looking for some direction here.



 Thanks,

 Christopher-

 Chris Schaefer’s
 

 *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
 *5115 South Hill Road ~ Canandaigua New York
 14424www.solarandwindfx.com  ~ E-mail: 
 **ch...@solarandwindfx.com
 *

 Thomas Jefferson, the author of our great Constitution, once said,
 "democracy" will cease to exist when you take away from those who are
 willing to work and give to those who would not."
 ___
 List sponsored by Redwood Alliance

 List Address: RE-wrenches@lists.re-wrenches.org

 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 List-Archive:
 http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

 List rules & etiquette:
 www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 www.members.re-wrenches.org


>>>
>>> --
>>>
>>> Chris Schaefer’s
>>> 
>>>
>>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>>>  ~ E-mail: ch...@solarandwindfx.com
>>> *
>>>
>>>
>>> Thomas Jefferson, the author of our great Constitution, once said,
>>> "democracy" will cease to exist when you take away from those who are
>>> willing to work and give to those who would not."
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wren

Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Chris Schaefer
Since the Flexnet on port 3 was active and could be seen on the Mate, thus
I moved the slave on port 2 to port 3 and moved the FlexNet from port 3 to
port 4. No change. I did try another OB factory green cable to no avail.

Christopher

On Thu, Jun 25, 2020 at 4:25 PM Jerry Shafer 
wrote:

> Chris
> Did you skip over and plug in to port 3 with the slave, swap the cord,
> Jerry
>
> On Thu, Jun 25, 2020, 12:54 PM Chris Schaefer 
> wrote:
>
>> The system is critical to a farm watering operation so I wasn't able to
>> shut it down to try and swap the port 1 inverter with the port 2 inverter.
>> As for changing the power save settings, that is what alerted me to the
>> issue. Under no circumstance can you see a port 2 via the Mate. That's what
>> had me looking at the hub itself and that's when I noticed that the LED on
>> port 2 wasn't lighting up as the hub scrolled/polled by.
>>
>> Christopher
>>
>> On Thu, Jun 25, 2020 at 3:37 PM William Miller 
>> wrote:
>>
>>> Christopher;
>>>
>>>
>>>
>>> Just spit-balling here:  is the secondary inverter asleep (hate the
>>> master/slave terminology…)?  Try changing power save settings to make sure
>>> the secondary is awake and see if that changes the situation.  Seems
>>> unlikely this will solve the problem, but it may provide some kind of clue.
>>>
>>>
>>>
>>> Also, did you try swapping primary and secondary?  Run with secondary
>>> alone as primary?
>>>
>>>
>>>
>>> William Miller
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>>> Behalf Of *Chris Schaefer
>>> *Sent:* Thursday, June 25, 2020 10:35 AM
>>> *To:* RE-wrenches
>>> *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @
>>> Mate3s
>>>
>>>
>>>
>>> G'Day All,
>>>
>>>
>>>
>>> So I started up a system recently with two Radian 8048A's. The master is
>>> connected to port 1 and the slave connected to port 2 with the FlexNet at
>>> port 3. There are no OB charge controllers in the system. When the hub is
>>> polling (led's scrolling) nothing shows up for the slave at port 2. It's
>>> like the slave inverter doesn't exist. So I moved the slave and flexnet
>>> down to port 3 and 4. No change in the polling. I swapped out comm (factory
>>> green) cables. Again no change. Looking at the control board of the slave
>>> there is only one green led on which is located at the upper right-hand
>>> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
>>> the inverter. Of course since there is no polling at the hub there is no
>>> way to view port 2 to view the slave at the Mate.
>>>
>>>
>>>
>>> Now the only thing that I didn't do was to try and use the manual
>>> on/off  switch-jumper to start the slave. But in the past regardless of the
>>> inverter being on or off it would still show up on the hub. This is  a new
>>> one and I'm looking for some direction here.
>>>
>>>
>>>
>>> Thanks,
>>>
>>> Christopher-
>>>
>>> Chris Schaefer’s
>>> 
>>>
>>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>>> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
>>>  ~ E-mail: **ch...@solarandwindfx.com
>>> *
>>>
>>> Thomas Jefferson, the author of our great Constitution, once said,
>>> "democracy" will cease to exist when you take away from those who are
>>> willing to work and give to those who would not."
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>
>> --
>>
>> Chris Schaefer’s
>> 
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>>  ~ E-mail: ch...@solarandwindfx.com
>> *
>>
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wr

Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Jerry Shafer
Chris
Did you skip over and plug in to port 3 with the slave, swap the cord,
Jerry

On Thu, Jun 25, 2020, 12:54 PM Chris Schaefer 
wrote:

> The system is critical to a farm watering operation so I wasn't able to
> shut it down to try and swap the port 1 inverter with the port 2 inverter.
> As for changing the power save settings, that is what alerted me to the
> issue. Under no circumstance can you see a port 2 via the Mate. That's what
> had me looking at the hub itself and that's when I noticed that the LED on
> port 2 wasn't lighting up as the hub scrolled/polled by.
>
> Christopher
>
> On Thu, Jun 25, 2020 at 3:37 PM William Miller 
> wrote:
>
>> Christopher;
>>
>>
>>
>> Just spit-balling here:  is the secondary inverter asleep (hate the
>> master/slave terminology…)?  Try changing power save settings to make sure
>> the secondary is awake and see if that changes the situation.  Seems
>> unlikely this will solve the problem, but it may provide some kind of clue.
>>
>>
>>
>> Also, did you try swapping primary and secondary?  Run with secondary
>> alone as primary?
>>
>>
>>
>> William Miller
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>> Behalf Of *Chris Schaefer
>> *Sent:* Thursday, June 25, 2020 10:35 AM
>> *To:* RE-wrenches
>> *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s
>>
>>
>>
>> G'Day All,
>>
>>
>>
>> So I started up a system recently with two Radian 8048A's. The master is
>> connected to port 1 and the slave connected to port 2 with the FlexNet at
>> port 3. There are no OB charge controllers in the system. When the hub is
>> polling (led's scrolling) nothing shows up for the slave at port 2. It's
>> like the slave inverter doesn't exist. So I moved the slave and flexnet
>> down to port 3 and 4. No change in the polling. I swapped out comm (factory
>> green) cables. Again no change. Looking at the control board of the slave
>> there is only one green led on which is located at the upper right-hand
>> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
>> the inverter. Of course since there is no polling at the hub there is no
>> way to view port 2 to view the slave at the Mate.
>>
>>
>>
>> Now the only thing that I didn't do was to try and use the manual on/off
>> switch-jumper to start the slave. But in the past regardless of the
>> inverter being on or off it would still show up on the hub. This is  a new
>> one and I'm looking for some direction here.
>>
>>
>>
>> Thanks,
>>
>> Christopher-
>>
>> Chris Schaefer’s
>> 
>>
>> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
>> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
>>  ~ E-mail: **ch...@solarandwindfx.com
>> *
>>
>> Thomas Jefferson, the author of our great Constitution, once said,
>> "democracy" will cease to exist when you take away from those who are
>> willing to work and give to those who would not."
>> ___
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>
> --
>
> Chris Schaefer’s
> 
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
>  ~ E-mail: ch...@solarandwindfx.com
> *
>
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Chris Schaefer
The system is critical to a farm watering operation so I wasn't able to
shut it down to try and swap the port 1 inverter with the port 2 inverter.
As for changing the power save settings, that is what alerted me to the
issue. Under no circumstance can you see a port 2 via the Mate. That's what
had me looking at the hub itself and that's when I noticed that the LED on
port 2 wasn't lighting up as the hub scrolled/polled by.

Christopher

On Thu, Jun 25, 2020 at 3:37 PM William Miller 
wrote:

> Christopher;
>
>
>
> Just spit-balling here:  is the secondary inverter asleep (hate the
> master/slave terminology…)?  Try changing power save settings to make sure
> the secondary is awake and see if that changes the situation.  Seems
> unlikely this will solve the problem, but it may provide some kind of clue.
>
>
>
> Also, did you try swapping primary and secondary?  Run with secondary
> alone as primary?
>
>
>
> William Miller
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Chris Schaefer
> *Sent:* Thursday, June 25, 2020 10:35 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s
>
>
>
> G'Day All,
>
>
>
> So I started up a system recently with two Radian 8048A's. The master is
> connected to port 1 and the slave connected to port 2 with the FlexNet at
> port 3. There are no OB charge controllers in the system. When the hub is
> polling (led's scrolling) nothing shows up for the slave at port 2. It's
> like the slave inverter doesn't exist. So I moved the slave and flexnet
> down to port 3 and 4. No change in the polling. I swapped out comm (factory
> green) cables. Again no change. Looking at the control board of the slave
> there is only one green led on which is located at the upper right-hand
> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
> the inverter. Of course since there is no polling at the hub there is no
> way to view port 2 to view the slave at the Mate.
>
>
>
> Now the only thing that I didn't do was to try and use the manual on/off
> switch-jumper to start the slave. But in the past regardless of the
> inverter being on or off it would still show up on the hub. This is  a new
> one and I'm looking for some direction here.
>
>
>
> Thanks,
>
> Christopher-
>
> Chris Schaefer’s
> 
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
>  ~ E-mail: **ch...@solarandwindfx.com
> *
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>

-- 

Chris Schaefer’s


*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
 ~ E-mail: ch...@solarandwindfx.com
*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Jerry Shafer
Wrenches
It sounds like a out of the box board failure, even if the slave is in
standby it is connected to the hub and you see it, if you swapped the
cable, port location, its time to talk to OB tech and get a board sent out,
Jerry

On Thu, Jun 25, 2020, 12:37 PM William Miller 
wrote:

> Christopher;
>
>
>
> Just spit-balling here:  is the secondary inverter asleep (hate the
> master/slave terminology…)?  Try changing power save settings to make sure
> the secondary is awake and see if that changes the situation.  Seems
> unlikely this will solve the problem, but it may provide some kind of clue.
>
>
>
> Also, did you try swapping primary and secondary?  Run with secondary
> alone as primary?
>
>
>
> William Miller
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Chris Schaefer
> *Sent:* Thursday, June 25, 2020 10:35 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s
>
>
>
> G'Day All,
>
>
>
> So I started up a system recently with two Radian 8048A's. The master is
> connected to port 1 and the slave connected to port 2 with the FlexNet at
> port 3. There are no OB charge controllers in the system. When the hub is
> polling (led's scrolling) nothing shows up for the slave at port 2. It's
> like the slave inverter doesn't exist. So I moved the slave and flexnet
> down to port 3 and 4. No change in the polling. I swapped out comm (factory
> green) cables. Again no change. Looking at the control board of the slave
> there is only one green led on which is located at the upper right-hand
> side. Otherwise no led's are on. I have 57v at the buss bar terminals of
> the inverter. Of course since there is no polling at the hub there is no
> way to view port 2 to view the slave at the Mate.
>
>
>
> Now the only thing that I didn't do was to try and use the manual on/off
> switch-jumper to start the slave. But in the past regardless of the
> inverter being on or off it would still show up on the hub. This is  a new
> one and I'm looking for some direction here.
>
>
>
> Thanks,
>
> Christopher-
>
> Chris Schaefer’s
> 
>
> *Tel/Fax 585-229-2083 or Cell 585-748-1870 *
> *5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
>  ~ E-mail: **ch...@solarandwindfx.com
> *
>
> Thomas Jefferson, the author of our great Constitution, once said,
> "democracy" will cease to exist when you take away from those who are
> willing to work and give to those who would not."
> ___
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Jay
Did you try putting the slave inverter to port 1?

Jay

> On Jun 25, 2020, at 10:35 AM, Chris Schaefer  wrote:
> 
> 
> G'Day All,
> 
> So I started up a system recently with two Radian 8048A's. The master is 
> connected to port 1 and the slave connected to port 2 with the FlexNet at 
> port 3. There are no OB charge controllers in the system. When the hub is 
> polling (led's scrolling) nothing shows up for the slave at port 2. It's like 
> the slave inverter doesn't exist. So I moved the slave and flexnet down to 
> port 3 and 4. No change in the polling. I swapped out comm (factory green) 
> cables. Again no change. Looking at the control board of the slave there is 
> only one green led on which is located at the upper right-hand side. 
> Otherwise no led's are on. I have 57v at the buss bar terminals of the 
> inverter. Of course since there is no polling at the hub there is no way to 
> view port 2 to view the slave at the Mate.
> 
> Now the only thing that I didn't do was to try and use the manual on/off  
> switch-jumper to start the slave. But in the past regardless of the inverter 
> being on or off it would still show up on the hub. This is  a new one and I'm 
> looking for some direction here.
> 
> Thanks,
> Christopher- 
> Chris Schaefer’s
> 
> Tel/Fax 585-229-2083 or Cell 585-748-1870 
> 5115 South Hill Road ~ Canandaigua New York 14424
> www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com
> 
> 
> 
> Thomas Jefferson, the author of our great Constitution, once said, 
> "democracy" will cease to exist when you take away from those who are willing 
> to work and give to those who would not."
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread William Miller
Christopher;



Just spit-balling here:  is the secondary inverter asleep (hate the
master/slave terminology…)?  Try changing power save settings to make sure
the secondary is awake and see if that changes the situation.  Seems
unlikely this will solve the problem, but it may provide some kind of clue.



Also, did you try swapping primary and secondary?  Run with secondary alone
as primary?



William Miller



*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Chris Schaefer
*Sent:* Thursday, June 25, 2020 10:35 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s



G'Day All,



So I started up a system recently with two Radian 8048A's. The master is
connected to port 1 and the slave connected to port 2 with the FlexNet at
port 3. There are no OB charge controllers in the system. When the hub is
polling (led's scrolling) nothing shows up for the slave at port 2. It's
like the slave inverter doesn't exist. So I moved the slave and flexnet
down to port 3 and 4. No change in the polling. I swapped out comm (factory
green) cables. Again no change. Looking at the control board of the slave
there is only one green led on which is located at the upper right-hand
side. Otherwise no led's are on. I have 57v at the buss bar terminals of
the inverter. Of course since there is no polling at the hub there is no
way to view port 2 to view the slave at the Mate.



Now the only thing that I didn't do was to try and use the manual on/off
switch-jumper to start the slave. But in the past regardless of the
inverter being on or off it would still show up on the hub. This is  a new
one and I'm looking for some direction here.



Thanks,

Christopher-

Chris Schaefer’s


*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424www.solarandwindfx.com
 ~ E-mail: **ch...@solarandwindfx.com
*

Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



Re: [RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Roland - RES
Hey Chris,

Sounds like a failed power supply board Outback part SPARE-215. If the unit is 
under warranty you should be able to get a replacement through OB tech support. 
 

> Sent from a IPhone, with touch screen keys on the fly. Please excuse 
> shortcuts and typos. 
> 
Roland Shackelford
NABCEP CERTIFIED PV INSTALLER
President 
Renewable Energy Services (RES), Inc. 
Mobile:  808-938-9239
www.renewablenergy.com

> On Jun 25, 2020, at 7:35 AM, Chris Schaefer  wrote:
> 
> 
> G'Day All,
> 
> So I started up a system recently with two Radian 8048A's. The master is 
> connected to port 1 and the slave connected to port 2 with the FlexNet at 
> port 3. There are no OB charge controllers in the system. When the hub is 
> polling (led's scrolling) nothing shows up for the slave at port 2. It's like 
> the slave inverter doesn't exist. So I moved the slave and flexnet down to 
> port 3 and 4. No change in the polling. I swapped out comm (factory green) 
> cables. Again no change. Looking at the control board of the slave there is 
> only one green led on which is located at the upper right-hand side. 
> Otherwise no led's are on. I have 57v at the buss bar terminals of the 
> inverter. Of course since there is no polling at the hub there is no way to 
> view port 2 to view the slave at the Mate.
> 
> Now the only thing that I didn't do was to try and use the manual on/off  
> switch-jumper to start the slave. But in the past regardless of the inverter 
> being on or off it would still show up on the hub. This is  a new one and I'm 
> looking for some direction here.
> 
> Thanks,
> Christopher- 
> Chris Schaefer’s
> 
> Tel/Fax 585-229-2083 or Cell 585-748-1870 
> 5115 South Hill Road ~ Canandaigua New York 14424
> www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com
> 
> 
> 
> Thomas Jefferson, the author of our great Constitution, once said, 
> "democracy" will cease to exist when you take away from those who are willing 
> to work and give to those who would not."
> 
> ___
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



[RE-wrenches] Slave Radian not showing up on Hub10 or @ Mate3s

2020-06-25 Thread Chris Schaefer
G'Day All,

So I started up a system recently with two Radian 8048A's. The master is
connected to port 1 and the slave connected to port 2 with the FlexNet at
port 3. There are no OB charge controllers in the system. When the hub is
polling (led's scrolling) nothing shows up for the slave at port 2. It's
like the slave inverter doesn't exist. So I moved the slave and flexnet
down to port 3 and 4. No change in the polling. I swapped out comm (factory
green) cables. Again no change. Looking at the control board of the slave
there is only one green led on which is located at the upper right-hand
side. Otherwise no led's are on. I have 57v at the buss bar terminals of
the inverter. Of course since there is no polling at the hub there is no
way to view port 2 to view the slave at the Mate.

Now the only thing that I didn't do was to try and use the manual on/off
switch-jumper to start the slave. But in the past regardless of the
inverter being on or off it would still show up on the hub. This is  a new
one and I'm looking for some direction here.

Thanks,
Christopher-

Chris Schaefer’s


*Tel/Fax 585-229-2083 or Cell 585-748-1870 *
*5115 South Hill Road ~ Canandaigua New York 14424**www.solarandwindfx.com
 ~ E-mail: ch...@solarandwindfx.com
*


Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
___
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org