That's a different scenario, as a 100A genny would have a 100A OCPD. I
understand that the inverter output rating is limited, but what section of
code allows a 200A breaker to protect a #4 wire?







On Fri, Apr 15, 2022 at 9:26 PM Jerry Shafer via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> You must meet all expected source output potentials within the design and
> operating limits, as long as the distribution panel and connected wiring is
> rated for the max output of the protected source then you are good. A 200
> ATS connected to a 10 kW genny does not require 2/0 as it will never meet
> that rating. Just remember its whatever the max output can be plus your
> margin.
>
> On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Hi Jason,
>>
>> You bring up a valid point….in an off-grid scenario with the 15k do you
>> size the conductors to the continuous capacity, surge capacity or the OCPD
>> of the unit?
>>
>> -Chris
>>
>> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
>> re-wrenches@lists.re-wrenches.org> wrote:
>>
>>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>>
>>>
>>>
>>>
>>>
>>>
>>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>>> ja...@floridasolardesigngroup.com> wrote:
>>>
 I'm not following the wiring diagrams for this new inverter. It has
 200A pass-through capability with an integrated 200A load disconnect. But
 then it says the wire gauge for the load out wiring can be #4 to 2/0.

 In an off-grid scenario where there is no generator, the max continuous
 output is 62.5A, so I assume 80A circuit protection could be used with 80A
 rated wire (#4), but how is that circuit protection implemented if the 200A
 breaker is integrated? Do you have to run a short piece of 2/0 to an
 external 80A rated OCPD and then step down to #4?

 Jason Szumlanski





 ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> --
>> Chris Sparadeo
>>
>>
>> C_802-369-4458
>> H_802-728-3059
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jerry Shafer via RE-wrenches
You must meet all expected source output potentials within the design and
operating limits, as long as the distribution panel and connected wiring is
rated for the max output of the protected source then you are good. A 200
ATS connected to a 10 kW genny does not require 2/0 as it will never meet
that rating. Just remember its whatever the max output can be plus your
margin.

On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi Jason,
>
> You bring up a valid point….in an off-grid scenario with the 15k do you
> size the conductors to the continuous capacity, surge capacity or the OCPD
> of the unit?
>
> -Chris
>
> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>
>>
>>
>>
>>
>>
>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>>> I'm not following the wiring diagrams for this new inverter. It has 200A
>>> pass-through capability with an integrated 200A load disconnect. But then
>>> it says the wire gauge for the load out wiring can be #4 to 2/0.
>>>
>>> In an off-grid scenario where there is no generator, the max continuous
>>> output is 62.5A, so I assume 80A circuit protection could be used with 80A
>>> rated wire (#4), but how is that circuit protection implemented if the 200A
>>> breaker is integrated? Do you have to run a short piece of 2/0 to an
>>> external 80A rated OCPD and then step down to #4?
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>>
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Chris Sparadeo via RE-wrenches
Hi Jason,

You bring up a valid point….in an off-grid scenario with the 15k do you
size the conductors to the continuous capacity, surge capacity or the OCPD
of the unit?

-Chris

On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> P.S. ICYMI, this inverter has a massive combined AC coupled and DC coupled
> capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>
>
>
>
>
>
> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
> ja...@floridasolardesigngroup.com> wrote:
>
>> I'm not following the wiring diagrams for this new inverter. It has 200A
>> pass-through capability with an integrated 200A load disconnect. But then
>> it says the wire gauge for the load out wiring can be #4 to 2/0.
>>
>> In an off-grid scenario where there is no generator, the max continuous
>> output is 62.5A, so I assume 80A circuit protection could be used with 80A
>> rated wire (#4), but how is that circuit protection implemented if the 200A
>> breaker is integrated? Do you have to run a short piece of 2/0 to an
>> external 80A rated OCPD and then step down to #4?
>>
>> Jason Szumlanski
>>
>>
>>
>>
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Enphase

2022-04-15 Thread Jay via RE-wrenches
I’ve been following the enphase thread. 

I’ve used AP systems before and so far reliable and much less expensive. 

Their new DS3 inverters are much less expensive and larger capacity

But to the point of starting voltage MPPT range and watts 
DS3 voltage range:
DS3 S/L 16-60v,
DS3 26-60v

MPPT range: 
DS3 -S 22-48v   
DS3-L   25-55v
DS3.   32-55

Wattage
-S 640 va
-L  768 va
DS3  880 va

I’ve got a system for micros coming up and probably leaning this way. 
Curious what others think

Jay





___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Fronius primo grid settings

2022-04-15 Thread Jay via RE-wrenches
I wonder if anyone can tell me which is the correct setting for 240v 60hz 
w/neutral on a fronius primo. 
The manual doesn’t have the same options as the inverter. 

I don’t need California or Hawaii settings. 

Thanks
Jay

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
P.S. ICYMI, this inverter has a massive combined AC coupled and DC coupled
capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.






On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
ja...@floridasolardesigngroup.com> wrote:

> I'm not following the wiring diagrams for this new inverter. It has 200A
> pass-through capability with an integrated 200A load disconnect. But then
> it says the wire gauge for the load out wiring can be #4 to 2/0.
>
> In an off-grid scenario where there is no generator, the max continuous
> output is 62.5A, so I assume 80A circuit protection could be used with 80A
> rated wire (#4), but how is that circuit protection implemented if the 200A
> breaker is integrated? Do you have to run a short piece of 2/0 to an
> external 80A rated OCPD and then step down to #4?
>
> Jason Szumlanski
>
>
>
>
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Razors & Removing paint from solar modules

2022-04-15 Thread Mark Downing via RE-wrenches
That would likely happen of the pressure spray were used on the back side of 
the modules.

From: RE-wrenches  On Behalf Of 
Solar Energy Solutions via RE-wrenches
Sent: Friday, April 15, 2022 3:12 PM
To: RE-wrenches 
Cc: Solar Energy Solutions 
Subject: Re: [RE-wrenches] Razors & Removing paint from solar modules

We have seen cells shattered…kind of cracked… yet still functioning, when we 
have heard of clients using pressure washers on panels.
Andrew Koyaanisqatsi
President
Solar Energy Solutions, Inc.
The BRIGHT CHOICE

Since 1987, helping you and your
Portland neighbors move towards an environmentally sustainable future.


503-238-4502
www.SolarEnergyOregon.com


On Apr 15, 2022, at 7:44 AM, Dana Orzel via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

If your use a razor only use a fresh razor blades. The moment you feel burrs 
stop & replace the razor as the burrs will scratch the glass. Also keep the 
surface always wet with a soapy solution [surfactant] to keep the surface slick 
& this extends the short life of a razors edge.
Use a razor handle to hold the blade & keep a first aid kit available. Soapy 
water & razor blades have interesting incidents.  I owned a window tint shop 40 
years ago & definitely had my share of razor cuts.


Dana Orzel  Great Solar Works, Inc.
C - 208.721.7003   
d...@solarwork.com
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136   
www.greatsolarworks.com
"Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email.


From: RE-wrenches 
mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Chris Mason via RE-wrenches
Sent: Friday, April 15, 2022 8:18 AM
To: RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Chris Mason 
mailto:cometenergysyst...@gmail.com>>
Subject: Re: [RE-wrenches] Removing paint from solar modules

Just a razor blade. I doubt you can take if off chemically.

On Fri, Apr 15, 2022 at 9:01 AM Mac Lewis via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:
Hi Wrenches,

We had some painters try to paint a house in 35 mph winds and (of course) the 
overspray got onto some recently installed solar modules.  They were using a 
latex water-based exterior paint.  Are there any mild solvents you might 
recommend to help clean this up?  Or just elbow grease?

Thanks!
--



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


--
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Razors & Removing paint from solar modules

2022-04-15 Thread Solar Energy Solutions via RE-wrenches
We have seen cells shattered…kind of cracked… yet still functioning, when we 
have heard of clients using pressure washers on panels.

Andrew Koyaanisqatsi
President
Solar Energy Solutions, Inc.
The BRIGHT CHOICE

Since 1987, helping you and your 
Portland neighbors move towards an environmentally sustainable future.

503-238-4502
www.SolarEnergyOregon.com

> On Apr 15, 2022, at 7:44 AM, Dana Orzel via RE-wrenches 
>  wrote:
> 
> 
> If your use a razor only use a fresh razor blades. The moment you feel burrs 
> stop & replace the razor as the burrs will scratch the glass. Also keep the 
> surface always wet with a soapy solution [surfactant] to keep the surface 
> slick & this extends the short life of a razors edge.
> Use a razor handle to hold the blade & keep a first aid kit available. Soapy 
> water & razor blades have interesting incidents.  I owned a window tint shop 
> 40 years ago & definitely had my share of razor cuts.
>  
>  
> Dana Orzel  Great Solar Works, Inc.
> C - 208.721.7003   d...@solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com
> "Responsible Technologies for Responsible People since 1988" 
> P Please consider the environment before printing this email.
>  
>  
> From: RE-wrenches  On Behalf Of 
> Chris Mason via RE-wrenches
> Sent: Friday, April 15, 2022 8:18 AM
> To: RE-wrenches 
> Cc: Chris Mason 
> Subject: Re: [RE-wrenches] Removing paint from solar modules
>  
> Just a razor blade. I doubt you can take if off chemically.
>  
> On Fri, Apr 15, 2022 at 9:01 AM Mac Lewis via RE-wrenches 
>  wrote:
> Hi Wrenches,
>  
> We had some painters try to paint a house in 35 mph winds and (of course) the 
> overspray got onto some recently installed solar modules.  They were using a 
> latex water-based exterior paint.  Are there any mild solvents you might 
> recommend to help clean this up?  Or just elbow grease?
>  
> Thanks!
> --
>  
>  
>  
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> 
>  
> --
> Chris Mason
> Solar systems designer
> Generac Generators Industrial technician
>  
> Comet Systems Ltd DBA Comet Solar
> Anguilla Cell  264.235.5670
> WhatsApp 264.235.5670
> Skype: netconcepts
> www.cometsolar.com
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Kirk Herander via RE-wrenches
Thanks that is exactly my request to Enphase, that they verify software
compatibility.

On Fri, Apr 15, 2022 at 12:48 PM Jason Szumlanski via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Kirk,
>
> We have seen many of the conversion kits not work out of the box. I
> believe it is a firmware/software mismatch issue. If you call Enphase, ask
> them to make sure the Envoy software is compatible with the conversion kit
> microinverter and update all software. This should resolve the issue.
>
> Jason Szumlanski
>
>
>
> On Fri, Apr 15, 2022 at 12:45 PM Kirk Herander via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> I have been dealing with a legacy Enphase system ever since the
>> installation about 11-12 years ago. And I stopped using Enphase after the
>> massive failure rate of these first gen M190 inverters. Almost all of them
>> have been replaced at least once, the good news is I only have about -15-
>> of the originals waiting to fail out of -113-.
>>
>> As some of you know RMA replacements were at first the original M190
>> (i.e. the type daisy chained w/ "internal" trunk cable), then the M215 with
>> a dedicated trunk cable, sent with adapters to mate with the M190, lastly
>> the IQ7 w/ its own adapters to the M190 and M215.
>>
>> So my system is 208, 3-phase. I just swapped out -5- more of the M190's
>> with newer generation models and am getting "ac out of range" errors on
>> half of the micros that were working fine before the swap. The error is not
>> unique to any one string.
>>
>> I wonder if all this replacing with multi-gen micros has created a phase
>> imbalance. Enphase stresses keeping the phases balanced, but I don't see
>> how they can follow their own advice mating all these different micros
>> together. I am awaiting their response.
>>
>> Are the original M190s a true 3-phase output? Or are they smart enough
>> internally to balance the phases through some sort of switching? The M215s
>> and IQ7 series are 208 single phase, and the trunk cable is wired in a
>> repeating connector-to-connector: Line  A-B, A-C, B-C single phase
>> arrangement for balancing. All thoughts welcome, thanks.
>> --
>>
>> *Kirk Herander / **kirkh@vermont.solar *
>>
>> *Owner|Principal, VT Solar, LLC*
>>
>> *Celebrating our 31st Anniversary 1991-2022!!*
>>
>> *www.vermont.solar*
>> 
>>
>> dba Vermont Solar Engineering
>>
>> 802.863.1202
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*


dba Vermont Solar Engineering

802.863.1202
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List 

Re: [RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Jason Szumlanski via RE-wrenches
Kirk,

We have seen many of the conversion kits not work out of the box. I believe
it is a firmware/software mismatch issue. If you call Enphase, ask them to
make sure the Envoy software is compatible with the conversion kit
microinverter and update all software. This should resolve the issue.

Jason Szumlanski



On Fri, Apr 15, 2022 at 12:45 PM Kirk Herander via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> I have been dealing with a legacy Enphase system ever since the
> installation about 11-12 years ago. And I stopped using Enphase after the
> massive failure rate of these first gen M190 inverters. Almost all of them
> have been replaced at least once, the good news is I only have about -15-
> of the originals waiting to fail out of -113-.
>
> As some of you know RMA replacements were at first the original M190 (i.e.
> the type daisy chained w/ "internal" trunk cable), then the M215 with a
> dedicated trunk cable, sent with adapters to mate with the M190, lastly the
> IQ7 w/ its own adapters to the M190 and M215.
>
> So my system is 208, 3-phase. I just swapped out -5- more of the M190's
> with newer generation models and am getting "ac out of range" errors on
> half of the micros that were working fine before the swap. The error is not
> unique to any one string.
>
> I wonder if all this replacing with multi-gen micros has created a phase
> imbalance. Enphase stresses keeping the phases balanced, but I don't see
> how they can follow their own advice mating all these different micros
> together. I am awaiting their response.
>
> Are the original M190s a true 3-phase output? Or are they smart enough
> internally to balance the phases through some sort of switching? The M215s
> and IQ7 series are 208 single phase, and the trunk cable is wired in a
> repeating connector-to-connector: Line  A-B, A-C, B-C single phase
> arrangement for balancing. All thoughts welcome, thanks.
> --
>
> *Kirk Herander / **kirkh@vermont.solar *
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 31st Anniversary 1991-2022!!*
>
> *www.vermont.solar*
> 
>
> dba Vermont Solar Engineering
>
> 802.863.1202
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Enphase Legacy micro replacement

2022-04-15 Thread Kirk Herander via RE-wrenches
I have been dealing with a legacy Enphase system ever since the
installation about 11-12 years ago. And I stopped using Enphase after the
massive failure rate of these first gen M190 inverters. Almost all of them
have been replaced at least once, the good news is I only have about -15-
of the originals waiting to fail out of -113-.

As some of you know RMA replacements were at first the original M190 (i.e.
the type daisy chained w/ "internal" trunk cable), then the M215 with a
dedicated trunk cable, sent with adapters to mate with the M190, lastly the
IQ7 w/ its own adapters to the M190 and M215.

So my system is 208, 3-phase. I just swapped out -5- more of the M190's
with newer generation models and am getting "ac out of range" errors on
half of the micros that were working fine before the swap. The error is not
unique to any one string.

I wonder if all this replacing with multi-gen micros has created a phase
imbalance. Enphase stresses keeping the phases balanced, but I don't see
how they can follow their own advice mating all these different micros
together. I am awaiting their response.

Are the original M190s a true 3-phase output? Or are they smart enough
internally to balance the phases through some sort of switching? The M215s
and IQ7 series are 208 single phase, and the trunk cable is wired in a
repeating connector-to-connector: Line  A-B, A-C, B-C single phase
arrangement for balancing. All thoughts welcome, thanks.
-- 

*Kirk Herander / **kirkh@vermont.solar *

*Owner|Principal, VT Solar, LLC*

*Celebrating our 31st Anniversary 1991-2022!!*

*www.vermont.solar*


dba Vermont Solar Engineering

802.863.1202
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Ray Walters via RE-wrenches
Not to sound like a commercial, but I've had good results with "Tub 
O'Towels" heavy duty wipes.   Its got a lemon base that seems easy on 
most surfaces, but it will take paint off with a few seconds of elbow 
grease.   Hoe Depot has them sometimes, or Northern Tool carries them 
too.  You'll use them for all sorts of stuff; good to keep on the truck.


Monk Wipes Heavy Duty Hand Cleaner | Large 9.6″ x 12 ...

Ray
Remote Solar


On 4/15/2022 8:56 AM, Garrison via RE-wrenches wrote:

Hi Mac,

I second the isopropyl alcohol (diluted), a soft cloth, and razor 
blade if needed.


Magic erasers would probably work too, but I believe they are made 
from very hard microscopic crystals.


Good luck.

Garrison Riegel
Celestar Solar LLC

On Apr 15, 2022, at 9:45 AM, Dana Orzel via RE-wrenches 
 wrote:




Also Latex paint come off with Isopropyl Alcohol.

Dana Orzel  Great Solar Works, Inc.

*C - 208.721.7003 d...@solarwork.com*

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136 www.greatsolarworks.com 



_"Responsible Technologies for Responsible People since 1988" ___

*P*Please consider the environment before printing this email.

*From:* RE-wrenches  *On 
Behalf Of *Mac Lewis via RE-wrenches

*Sent:* Friday, April 15, 2022 7:01 AM
*To:* RE-wrenches 
*Cc:* Mac Lewis 
*Subject:* [RE-wrenches] Removing paint from solar modules

Hi Wrenches,

We had some painters try to paint a house in 35 mph winds and (of 
course) the overspray got onto some recently installed solar 
modules.  They were using a latex water-based exterior paint.  Are 
there any mild solvents you might recommend to help clean this up?  
Or just elbow grease?


Thanks!

--

Mac Lewis**

"Yo solo sé que no sé nada." *-Sócrates***

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:

https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



___
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
I'm not following the wiring diagrams for this new inverter. It has 200A
pass-through capability with an integrated 200A load disconnect. But then
it says the wire gauge for the load out wiring can be #4 to 2/0.

In an off-grid scenario where there is no generator, the max continuous
output is 62.5A, so I assume 80A circuit protection could be used with 80A
rated wire (#4), but how is that circuit protection implemented if the 200A
breaker is integrated? Do you have to run a short piece of 2/0 to an
external 80A rated OCPD and then step down to #4?

Jason Szumlanski
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread George McClellan via RE-wrenches
Tarps work great too!

George McClellan | Senior Technical Sales Manager | REC Americas LLC
330 James Way Ste 150 | Pismo Beach, CA 93449 | USA
Cell phone +1 805 704 3226 | Fax +1 805 357 6104
www.recgroup.com | 
george.mcclel...@recgroup.com


From: RE-wrenches  On Behalf Of 
Garrison via RE-wrenches
Sent: Friday, April 15, 2022 7:57 AM
To: RE-wrenches 
Cc: Garrison 
Subject: Re: [RE-wrenches] Removing paint from solar modules

Hi Mac,

I second the isopropyl alcohol (diluted), a soft cloth, and razor blade if 
needed.

Magic erasers would probably work too, but I believe they are made from very 
hard microscopic crystals.

Good luck.

Garrison Riegel
Celestar Solar LLC


On Apr 15, 2022, at 9:45 AM, Dana Orzel via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>> 
wrote:

Also Latex paint come off with Isopropyl Alcohol.



Dana Orzel  Great Solar Works, Inc.
C - 208.721.7003   
d...@solarwork.com
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136   
www.greatsolarworks.com
"Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email.


From: RE-wrenches 
mailto:re-wrenches-boun...@lists.re-wrenches.org>>
 On Behalf Of Mac Lewis via RE-wrenches
Sent: Friday, April 15, 2022 7:01 AM
To: RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org>>
Cc: Mac Lewis mailto:maclew...@gmail.com>>
Subject: [RE-wrenches] Removing paint from solar modules

Hi Wrenches,

We had some painters try to paint a house in 35 mph winds and (of course) the 
overspray got onto some recently installed solar modules.  They were using a 
latex water-based exterior paint.  Are there any mild solvents you might 
recommend to help clean this up?  Or just elbow grease?

Thanks!
--



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



This message is private and confidential and may be privileged. Any 
unauthorized use, dissemination of the information or copying of this message 
is prohibited. If you have received this message in error, please notify us 
immediately and remove it from your system. Thank you.



This message is private and confidential and may be privileged. Any 
unauthorized use, dissemination of the information or copying of this message 
is prohibited. If you have received this message in error, please notify us 
immediately and remove it from your system. Thank you.
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Garrison via RE-wrenches
Hi Mac,

I second the isopropyl alcohol (diluted), a soft cloth, and razor blade if 
needed.  

Magic erasers would probably work too, but I believe they are made from very 
hard microscopic crystals.

Good luck.

Garrison Riegel
Celestar Solar LLC

> On Apr 15, 2022, at 9:45 AM, Dana Orzel via RE-wrenches 
>  wrote:
> 
> 
> Also Latex paint come off with Isopropyl Alcohol.
>  
>  
>  
> Dana Orzel  Great Solar Works, Inc.
> C - 208.721.7003   d...@solarwork.com
> Idaho Contractor - # 028765 Idaho PV # 028374
> NABCEP # 051112-136   www.greatsolarworks.com
> "Responsible Technologies for Responsible People since 1988" 
> P Please consider the environment before printing this email.
>  
>  
> From: RE-wrenches  On Behalf Of 
> Mac Lewis via RE-wrenches
> Sent: Friday, April 15, 2022 7:01 AM
> To: RE-wrenches 
> Cc: Mac Lewis 
> Subject: [RE-wrenches] Removing paint from solar modules
>  
> Hi Wrenches,
>  
> We had some painters try to paint a house in 35 mph winds and (of course) the 
> overspray got onto some recently installed solar modules.  They were using a 
> latex water-based exterior paint.  Are there any mild solvents you might 
> recommend to help clean this up?  Or just elbow grease?
>  
> Thanks!
> --
>  
>  
>  
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Dana Orzel via RE-wrenches
Also Latex paint come off with Isopropyl Alcohol.

 

 

 

Dana Orzel  Great Solar Works, Inc. 

C - 208.721.7003   d...@solarwork.com

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136   www.greatsolarworks.com 
 

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches  On Behalf Of Mac 
Lewis via RE-wrenches
Sent: Friday, April 15, 2022 7:01 AM
To: RE-wrenches 
Cc: Mac Lewis 
Subject: [RE-wrenches] Removing paint from solar modules

 

Hi Wrenches,

 

We had some painters try to paint a house in 35 mph winds and (of course) the 
overspray got onto some recently installed solar modules.  They were using a 
latex water-based exterior paint.  Are there any mild solvents you might 
recommend to help clean this up?  Or just elbow grease?

 

Thanks!

-- 

 

 

 

Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Razors & Removing paint from solar modules

2022-04-15 Thread Dana Orzel via RE-wrenches
If your use a razor only use a fresh razor blades. The moment you feel burrs 
stop & replace the razor as the burrs will scratch the glass. Also keep the 
surface always wet with a soapy solution [surfactant] to keep the surface slick 
& this extends the short life of a razors edge.

Use a razor handle to hold the blade & keep a first aid kit available. Soapy 
water & razor blades have interesting incidents.  I owned a window tint shop 40 
years ago & definitely had my share of razor cuts.

 

 

Dana Orzel  Great Solar Works, Inc. 

C - 208.721.7003   d...@solarwork.com

Idaho Contractor - # 028765 Idaho PV # 028374

NABCEP # 051112-136 
www.greatsolarworks.com

"Responsible Technologies for Responsible People since 1988"  

P Please consider the environment before printing this email.

 

 

From: RE-wrenches  On Behalf Of 
Chris Mason via RE-wrenches
Sent: Friday, April 15, 2022 8:18 AM
To: RE-wrenches 
Cc: Chris Mason 
Subject: Re: [RE-wrenches] Removing paint from solar modules

 

Just a razor blade. I doubt you can take if off chemically.

 

On Fri, Apr 15, 2022 at 9:01 AM Mac Lewis via RE-wrenches 
mailto:re-wrenches@lists.re-wrenches.org> > 
wrote:

Hi Wrenches,

 

We had some painters try to paint a house in 35 mph winds and (of course) the 
overspray got onto some recently installed solar modules.  They were using a 
latex water-based exterior paint.  Are there any mild solvents you might 
recommend to help clean this up?  Or just elbow grease?

 

Thanks!

-- 

 

 

 

Mac Lewis

"Yo solo sé que no sé nada." -Sócrates

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org 
 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org




 

-- 

Chris Mason

Solar systems designer

Generac Generators Industrial technician

 

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670

WhatsApp 264.235.5670

Skype: netconcepts

www.cometsolar.com  

___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Chris Mason via RE-wrenches
Just a razor blade. I doubt you can take if off chemically.

On Fri, Apr 15, 2022 at 9:01 AM Mac Lewis via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi Wrenches,
>
> We had some painters try to paint a house in 35 mph winds and (of course)
> the overspray got onto some recently installed solar modules.  They were
> using a latex water-based exterior paint.  Are there any mild solvents you
> might recommend to help clean this up?  Or just elbow grease?
>
> Thanks!
> --
>
>
>
> Mac Lewis
>
> *"Yo solo sé que no sé nada." -Sócrates*
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Maverick Brown via RE-wrenches
I’ve had good results from a combo of power washing and the Magic Eraser for 
paint dust in the texture of the glass. 

Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
maver...@mavericksolar.com
512-460-9825


> On Apr 15, 2022, at 8:01 AM, Mac Lewis via RE-wrenches 
>  wrote:
> 
> 
> Hi Wrenches,
> 
> We had some painters try to paint a house in 35 mph winds and (of course) the 
> overspray got onto some recently installed solar modules.  They were using a 
> latex water-based exterior paint.  Are there any mild solvents you might 
> recommend to help clean this up?  Or just elbow grease?
> 
> Thanks!
> -- 
> 
> 
> 
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> ___
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Mac Lewis via RE-wrenches
Hi Wrenches,

We had some painters try to paint a house in 35 mph winds and (of course)
the overspray got onto some recently installed solar modules.  They were
using a latex water-based exterior paint.  Are there any mild solvents you
might recommend to help clean this up?  Or just elbow grease?

Thanks!
-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



[RE-wrenches] Water well telemetry

2022-04-15 Thread William Miller via RE-wrenches
Friends:

Can anyone recommend manufacturers of equipment for remote telemetry for Ag
wells?

Thanks in advance.

William Miller
-- 

William Miller
Miller Solar.com
895-438-5600
www.millersolar.com
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org