P.S. ICYMI, this inverter has a massive combined AC coupled and DC coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski < [email protected]> wrote: > I'm not following the wiring diagrams for this new inverter. It has 200A > pass-through capability with an integrated 200A load disconnect. But then > it says the wire gauge for the load out wiring can be #4 to 2/0. > > In an off-grid scenario where there is no generator, the max continuous > output is 62.5A, so I assume 80A circuit protection could be used with 80A > rated wire (#4), but how is that circuit protection implemented if the 200A > breaker is integrated? Do you have to run a short piece of 2/0 to an > external 80A rated OCPD and then step down to #4? > > Jason Szumlanski > > > > > >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org