You must meet all expected source output potentials within the design and
operating limits, as long as the distribution panel and connected wiring is
rated for the max output of the protected source then you are good. A 200
ATS connected to a 10 kW genny does not require 2/0 as it will never meet
that rating. Just remember its whatever the max output can be plus your
margin.

On Fri, Apr 15, 2022, 5:44 PM Chris Sparadeo via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:

> Hi Jason,
>
> You bring up a valid point….in an off-grid scenario with the 15k do you
> size the conductors to the continuous capacity, surge capacity or the OCPD
> of the unit?
>
> -Chris
>
> On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> P.S. ICYMI, this inverter has a massive combined AC coupled and DC
>> coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive.
>>
>>
>>
>>
>>
>>
>> On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski <
>> ja...@floridasolardesigngroup.com> wrote:
>>
>>> I'm not following the wiring diagrams for this new inverter. It has 200A
>>> pass-through capability with an integrated 200A load disconnect. But then
>>> it says the wire gauge for the load out wiring can be #4 to 2/0.
>>>
>>> In an off-grid scenario where there is no generator, the max continuous
>>> output is 62.5A, so I assume 80A circuit protection could be used with 80A
>>> rated wire (#4), but how is that circuit protection implemented if the 200A
>>> breaker is integrated? Do you have to run a short piece of 2/0 to an
>>> external 80A rated OCPD and then step down to #4?
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> --
> Chris Sparadeo
>
>
> C_802-369-4458
> H_802-728-3059
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to