RE: Building Heights Requiring Standpipes

2018-08-09 Thread tstone52
If you are using electric flow switches most of them have a built in retard
feature (or time delay) witch allow the flow switch to absorb a pressure
surge with out activating the alarms. This was meant to replace the old
fashioned Retard Chamber used in conjunction with Alarm Valves.

Regards,
G. Tim Stone
 
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
 
   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
     tston...@comcast.net



-Original Message-
From: Sprinklerforum  On
Behalf Of Cesar Lira
Sent: Thursday, August 9, 2018 1:53 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes

Hi.

I have a doubt. NFPA13 request that all sprinklers system shall have a
Retarding device. But in our  sprinkler systems installed we are not using
it. Because we have a water flow sensor above check alarm instead of an
alarm pressure switch or water motor alarm.
Is it correct as I have it?. What would be the purpose of installing the
retarding device if the alarm pressure switch or water motor alarm are not
installed. My client demands to me this devices and I am looking for how can
defend that I not having installed it

I need to know if a water flow alarm and the pressure switch alarm are both
necessary? Or just one of this options.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-09 Thread Bob
Cesar,
I believe that this is only required for alarm check valves.  Does your
system have one?  If not the retard device should not be required.

Thank you,
 
Bob Knight, CET III
208-318-3057
 
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Cesar Lira
Sent: Thursday, August 09, 2018 11:53 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes

Hi.

I have a doubt. NFPA13 request that all sprinklers system shall have a
Retarding device. But in our  sprinkler systems installed we are not using
it. Because we have a water flow sensor above check alarm instead of an
alarm pressure switch or water motor alarm.
Is it correct as I have it?. What would be the purpose of installing the
retarding device if the alarm pressure switch or water motor alarm are not
installed. My client demands to me this devices and I am looking for how can
defend that I not having installed it

I need to know if a water flow alarm and the pressure switch alarm are both
necessary? Or just one of this options.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-09 Thread Cesar Lira
Hi.

I have a doubt. NFPA13 request that all sprinklers system shall have a
Retarding device. But in our  sprinkler systems installed we are not using
it. Because we have a water flow sensor above check alarm instead of an
alarm pressure switch or water motor alarm.
Is it correct as I have it?. What would be the purpose of installing the
retarding device if the alarm pressure switch or water motor alarm are not
installed. My client demands to me this devices and I am looking for how can
defend that I not having installed it

I need to know if a water flow alarm and the pressure switch alarm are both
necessary? Or just one of this options.

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-09 Thread John Drucker
2015 IBC

[F] 905.3 Required installations.
Standpipe systems shall be installed where required by Sections 905.3.1 through 
905.3.8.Standpipe
systems are allowed to be combined with automatic sprinkler systems.

Exception: Standpipe systems are not required in Group R-3 occupancies.

[F] 905.3.1 Height.

Class III standpipe systems shall be installed throughout buildings where the 
floor level of the highest
story is located more than 30 feet (9144 mm) above the lowest level of fire 
department vehicle access,
or where the floor level of the lowest story is located more than 30 feet (9144 
mm) below the highest
level of fire department vehicle access.

Exceptions:
1. Class I standpipes are allowed in buildings equipped throughout with an
automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2.
2. Class I manual standpipes are allowed in open parking garages where the 
highest
floor is located not more than 150 feet (45 720 mm) above the lowest level of 
fire
department vehicle access.
3. Class I manual dry standpipes are allowed in open parking garages that are
subject to freezing temperatures, provided that the hose connections are located
as required for Class II standpipes in accordance with Section 905.5.
4. Class I standpipes are allowed in basements equipped throughout with an
automatic sprinkler system.
5. In determining the lowest level of fire department vehicle access, it shall 
not be
required to consider either of the following:
5.1. Recessed loading docks for four vehicles or less.
5.2. Conditions where topography makes access from the fire department
vehicle to the building impractical or impossible

John Drucker, CET
Fire and Electrical Subcode Official
Building Inspector
Building Department
Borough of Red Bank, NJ 
Cell/Text 732-904-6823




From: Sprinklerforum [sprinklerforum-boun...@lists.firesprinkler.org] on behalf 
of Taylor Schumacher [tay...@sfsprinkler.com]
Sent: Thursday, August 09, 2018 8:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes


We had already walked through the IBC and all the pictures but he wants more 
solid info. I’ve reached out to the State Fire Marshal and they had agreed to 
write up an explanation. 
  
Like Steve explained, the access to the building and stairwells is at grade 
plane, which is first floor in this case, and is where the fire fighting 
appurtenances are located. 
  
Thanks, 
  
Taylor Schumacher 
  
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steele, Andrew
Sent: Wednesday, August 08, 2018 5:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes 
Good example diagrams are in the ICC Fire /Bldg Code Commentary books. 
  
On Aug 8, 2018 18:01, Jim Davidson  wrote: 
Go to the Building Code for the definition of height above lowest level of FD 
Access, if ICC’s IBC then call for a code interpretation and if needed ask for 
a written response. 
The ICC has been through this problem a few times. Some jurisdictions 
specifically define the height above the lowest level of FD access.   
Have a fire safe day!   
Jim Davidson 
From: Sprinklerforum  On Behalf 
Of Taylor Schumacher
Sent: Wednesday, August 8, 2018 5:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes 
I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30’ height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong? 
Taylor Schumacher 
  
  
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-09 Thread Taylor Schumacher
We had already walked through the IBC and all the pictures but he wants more 
solid info. I've reached out to the State Fire Marshal and they had agreed to 
write up an explanation.

Like Steve explained, the access to the building and stairwells is at grade 
plane, which is first floor in this case, and is where the fire fighting 
appurtenances are located.

Thanks,

Taylor Schumacher

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Steele, Andrew
Sent: Wednesday, August 08, 2018 5:45 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Building Heights Requiring Standpipes

Good example diagrams are in the ICC Fire /Bldg Code Commentary books.

On Aug 8, 2018 18:01, Jim Davidson 
mailto:jdavid...@davidsonassociates.net>> 
wrote:
Go to the Building Code for the definition of height above lowest level of FD 
Access, if ICC's IBC then call for a code interpretation and if needed ask for 
a written response.
The ICC has been through this problem a few times. Some jurisdictions 
specifically define the height above the lowest level of FD access.
Have a fire safe day!
Jim Davidson

From: Sprinklerforum 
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Taylor Schumacher
Sent: Wednesday, August 8, 2018 5:55 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Building Heights Requiring Standpipes

I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30' height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong?


Taylor Schumacher


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-08 Thread Steele, Andrew
Good example diagrams are in the ICC Fire /Bldg Code Commentary books.

On Aug 8, 2018 18:01, Jim Davidson  wrote:
Go to the Building Code for the definition of height above lowest level of FD 
Access, if ICC's IBC then call for a code interpretation and if needed ask for 
a written response.
The ICC has been through this problem a few times. Some jurisdictions 
specifically define the height above the lowest level of FD access.
Have a fire safe day!
Jim Davidson

From: Sprinklerforum  On Behalf 
Of Taylor Schumacher
Sent: Wednesday, August 8, 2018 5:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes

I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30' height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong?


Taylor Schumacher


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: Building Heights Requiring Standpipes

2018-08-08 Thread Mark Eckard
I think the code says if the highest floor elevation exceeds 30' above the
lowest level of fire department access, stand pipes are required. Not
quoting just remembering off the top of my head.

On Wed, Aug 8, 2018, 5:55 PM Taylor Schumacher 
wrote:

> I have an AHJ that is adamant that a 3-story 13R project I have requires
> Class I standpipes because the underground parking level will exceed the
> 30’ height requirement. I have always viewed these heights as from the
> parking lot closest to main entry or where the FDC is located rather than
> the fire truck driving into the garage. Have I been looking at this wrong?
>
>
>
>
>
> *Taylor Schumacher*
> ___
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-08 Thread Steve Leyton
What Jim said.   The measurement is from grade plane, so if there is a fire 
apparatus access at the lowest (basement) level, then standpipes in fact might 
be required.  But if the ground (first of three) floor is the access grade 
plane, then the metrics are from that surface to the finished third floor in 
this case and if it's below 30' I would agree that standpipes aren't required.  
 The AHJ doesn't have to take anyone's word for it because these terms and 
requirements are clearly defined in the building code.

Steve L.

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Taylor Schumacher
Sent: Wednesday, August 08, 2018 2:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes

I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30' height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong?


Taylor Schumacher
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: Building Heights Requiring Standpipes

2018-08-08 Thread Jim Davidson
Go to the Building Code for the definition of height above lowest level of FD 
Access, if ICC's IBC then call for a code interpretation and if needed ask for 
a written response.
The ICC has been through this problem a few times. Some jurisdictions 
specifically define the height above the lowest level of FD access.
Have a fire safe day!
Jim Davidson

From: Sprinklerforum  On Behalf 
Of Taylor Schumacher
Sent: Wednesday, August 8, 2018 5:55 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Building Heights Requiring Standpipes

I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30' height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong?


Taylor Schumacher
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Building Heights Requiring Standpipes

2018-08-08 Thread Taylor Schumacher
I have an AHJ that is adamant that a 3-story 13R project I have requires Class 
I standpipes because the underground parking level will exceed the 30' height 
requirement. I have always viewed these heights as from the parking lot closest 
to main entry or where the FDC is located rather than the fire truck driving 
into the garage. Have I been looking at this wrong?