Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-25 Thread George Medina Jr





Than you all for your valued inputs and expertise.
 
 In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When 
not used in accordance with section 504.2 or 506.3 of the California Building 
Code an Automatic Sprinkler System installed in accordance with section 
903.3.1.2 shall be allowed in Group R-2.1 Occupancies. Is it safe to assume 
that since it doesn't specifically mention  an R-2 occupancy not being used in 
accordance with section 504.2 or 506.3 of the 2010 C.F.C. that it be allowed to 
be installed in accordance with Section 903.3.1.2 of the  2010 C.F.C. (Did I 
say that correctly?)

 George Medina Jr. 
 Mobile: 323-906-5701
 



 

 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-25 Thread George Medina Jr


Than you all for your valued inputs and expertise.
 
 In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When 
not used in accordance with section 504.2 or 506.3 of the California Building 
Code an Automatic Sprinkler System installed in accordance with section 
903.3.1.2 shall be allowed in Group R-2.1 Occupancies. Is it safe to assume 
that since it doesn't specifically mention an R-2 occupancy not being used in 
accordance with section 504.2 or 506.3 of the 2010 C.F.C. that it be allowed to 
be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. (Did I say 
that correctly?)

 George Medina Jr. 
 Mobile: 323-906-5701

 
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-25 Thread George Medina Jr

Than you all for your valued inputs and expertise.
 
 In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When 
not used in accordance with section 504.2 or 506.3 of the California Building 
Code an Automatic Sprinkler System installed in accordance with section 
903.3.1.2 shall be allowed in Group R-2.1 Occupancies. Is it safe to assume 
that since it doesn't specifically mention an R-2 occupancy not being used in 
accordance with section 504.2 or 506.3 of the 2010 C.F.C. that it be allowed to 
be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. (Did I say 
that correctly?)

 George Medina Jr. 
 Mobile: 323-906-5701


 
 
-Original Message-
From: Cahill, Christopher ccah...@burnsmcd.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Tue, Apr 22, 2014 1:25 pm
Subject: RE: NFPA-13R or NFPA-13?


Let me play devil's advocate for a second. Why does NFPA 13x committees deal 
with this? Most (not all) of us in the US work with I codes and it's rather 
clear to me what to use.  I don't work in NFPA 5000 but ASSUME it's similar.  
IBC tells me which variant to use, NFPA 13x only tells me how to do it. 
(Avoiding the vernacular code/standard out of respect for Greenman.)  So the 
NFPA Committees can change or say anything they want and it's pointless.  Hell, 
they could say 13D for residential high-rises and NFPA 13D Committee would have 
little they could do about it.

Not that dissimilar to NFPA 409 and IBC 412.  In 409 ch. 5 they have all sorts 
of requirements for a building that are not required if following the basics of 
IBC.  For example, rated walls are not required in many hangars if you meet the 
height and area limits for mixed use. Don't need to protect the columns and 
don't need draft curtains, etc. True, a few places might legally adopt 409 in 
its entirety or you get there from insurance but that's not routine.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
On Behalf Of Pete Schwab
Sent: Tuesday, April 22, 2014 3:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

A heads up in regards to the 2016 edition of NFPA 13R. The committee has made a 
pretty drastic change that will significantly assist in determining if and 
when NFPA 13R applies. This was done in the First Draft phase and is currently 
open for Public Comment.

Here is the language from A.1.1 as how it appears in the First Draft Report. 
See 
the end sentences in paragraph #1.





NFPA 13R is appropriate for use as an alternative to NFPA 13 only in those 
residential occupancies, as defined in this standard, up to and including four 
aboveground stories in height, and limited to buildings that are 60 ft (18 m) 
or 
less in height above grade plane, which is consistent with limits established 
by 
model building codes for buildings of Type V construction. The height of a 
building above grade plane is determined by model building codes, which base 
the 
height on the average height of the highest roof surface above grade plane. For 
further information on the building height story limits, see model building 
codes.

Buildings that contain multiple occupancies (either separated or 
non-separated), 
accessory occupancies or incidental uses are often subject to special rules 
that 
may restrict the use of NFPA 13R. Refer to the adopted building code to 
determine whether such restrictions are applicable.

The criteria in this standard are based on full-scale fire tests of rooms 
containing typical furnishings found in residential living rooms, kitchens, and 
bedrooms. The furnishings were arranged as typically found in dwelling units in 
a manner similar to that shown in Figure A.1.1(a), Figure A.1.1(b), and Figure 
A.1.1(c). Sixty full-scale fire tests were conducted in a two-story dwelling in 
Los Angeles, California, and 16 tests were conducted in a 14 ft (4.3 m) wide 
mobile home in Charlotte, North Carolina. Sprinkler systems designed and 
installed according to this standard are expected to prevent flashover within 
the compartment of origin where sprinklers are installed in the compartment. A 
sprinkler system designed and installed according to this standard cannot, 
however, be expected to completely control a fire involving fuel loads that are 
significantly higher than average for dwelling units [10 lb/ft2 (49 kg/m2)], 
configurations of fuels other than those with typical resi
   dential occupancies, or conditions where the interior finish has an 
unusually 
high flame spread index (greater than 225).

To be effective, sprinkler systems installed in accordance with this standard 
need to open

RE: Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-25 Thread Steve Leyton
You're welcome welcome welcome welcome welcome welcome ...



 Original message 
From: George Medina Jr fireg...@aol.com 
Date:04/25/2014  9:25 AM  (GMT-08:00) 
To: sprinklerforum@lists.firesprinkler.org 
Subject: Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?) 


Than you all for your valued inputs and expertise.

In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When not 
used in accordance with section 504.2 or 506.3 of the California Building Code 
an Automatic Sprinkler System installed in accordance with section 903.3.1.2 
shall be allowed in Group R-2.1 Occupancies. Is it safe to assume that since it 
doesn't specifically mention an R-2 occupancy not being used in accordance with 
section 504.2 or 506.3 of the 2010 C.F.C. that it be allowed to be installed in 
accordance with Section 903.3.1.2 of the 2010 C.F.C. (Did I say that correctly?)

 George Medina Jr. 
 Mobile: 323-906-5701




-Original Message-
From: Cahill, Christopher ccah...@burnsmcd.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Tue, Apr 22, 2014 1:25 pm
Subject: RE: NFPA-13R or NFPA-13?


Let me play devil's advocate for a second. Why does NFPA 13x committees deal 
with this? Most (not all) of us in the US work with I codes and it's rather 
clear to me what to use.  I don't work in NFPA 5000 but ASSUME it's similar.  
IBC tells me which variant to use, NFPA 13x only tells me how to do it. 
(Avoiding the vernacular code/standard out of respect for Greenman.)  So the 
NFPA Committees can change or say anything they want and it's pointless.  Hell, 
they could say 13D for residential high-rises and NFPA 13D Committee would have 
little they could do about it.

Not that dissimilar to NFPA 409 and IBC 412.  In 409 ch. 5 they have all sorts 
of requirements for a building that are not required if following the basics of 
IBC.  For example, rated walls are not required in many hangars if you meet the 
height and area limits for mixed use. Don't need to protect the columns and 
don't need draft curtains, etc. True, a few places might legally adopt 409 in 
its entirety or you get there from insurance but that's not routine.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
On Behalf Of Pete Schwab
Sent: Tuesday, April 22, 2014 3:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

A heads up in regards to the 2016 edition of NFPA 13R. The committee has made a 
pretty drastic change that will significantly assist in determining if and 
when NFPA 13R applies. This was done in the First Draft phase and is currently 
open for Public Comment.

Here is the language from A.1.1 as how it appears in the First Draft Report. 
See 
the end sentences in paragraph #1.





NFPA 13R is appropriate for use as an alternative to NFPA 13 only in those 
residential occupancies, as defined in this standard, up to and including four 
aboveground stories in height, and limited to buildings that are 60 ft (18 m) 
or 
less in height above grade plane, which is consistent with limits established 
by 
model building codes for buildings of Type V construction. The height of a 
building above grade plane is determined by model building codes, which base 
the 
height on the average height of the highest roof surface above grade plane. For 
further information on the building height story limits, see model building 
codes.

Buildings that contain multiple occupancies (either separated or 
non-separated), 
accessory occupancies or incidental uses are often subject to special rules 
that 
may restrict the use of NFPA 13R. Refer to the adopted building code to 
determine whether such restrictions are applicable.

The criteria in this standard are based on full-scale fire tests of rooms 
containing typical furnishings found in residential living rooms, kitchens, and 
bedrooms. The furnishings were arranged as typically found in dwelling units in 
a manner similar to that shown in Figure A.1.1(a), Figure A.1.1(b), and Figure 
A.1.1(c). Sixty full-scale fire tests were conducted in a two-story dwelling in 
Los Angeles, California, and 16 tests were conducted in a 14 ft (4.3 m) wide 
mobile home in Charlotte, North Carolina. Sprinkler systems designed and 
installed according to this standard are expected to prevent flashover within 
the compartment of origin where sprinklers are installed in the compartment. A 
sprinkler system designed and installed according to this standard cannot, 
however, be expected to completely control a fire involving fuel loads that are 
significantly higher than average for dwelling units [10 lb/ft2

Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-24 Thread George Medina Jr

Than you all for your valued opinions and expertise, especially your 
I.B.C./U.B.C./C.F.C. references.  

In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When not 
used in accordance with section 504.2 or 506.3 of the California Building Code 
an Automatic Sprinkler System installed in accordance with section 903.3.1.2 
shall be allowed in Group R-2.1 Occupancies. Is it safe to assume that a R-2 
occupancy used in accordance with section 504.2 or 506.3 of the 2010 C.F.C. be 
allowed to be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. 


George Medina Jr. 
Mobile: 323-906-5701


 
 
-Original Message-
From: Travis Mack tm...@mfpdesign.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Tue, Apr 22, 2014 11:04 am
Subject: Re: NFPA-13R or NFPA-13?


Agree as well.  I am no IBC expert, but I do know a couple instances 
where the architect can take an allowance and it drives the system to 
903.3.1.1 instead of 903.3.1.2 of the IBC.  I always check these on all 
projects where 13R may be applicable.  If I find what I feel is an 
error, I will call the architect and point out my concerns.  I can't 
tell you how many times the architectural firms say they were unaware of 
the difference in those two sections.

My first check is to always go with the code study analysis and then if 
it doesn't make sense, I throw it back to the architect and make them do 
the final determination.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

On 4/22/2014 10:59 AM, Parsley Consulting wrote:
 I have to agree with Steve.  There has been many a multi-family 
 project cross my plan review table with the
 system designed to NFPA 13R because the architect called it out on 
 the drawings, while also taking several
 allowances for a fully sprinklered building.  Thanks to Steve, and a 
 couple of others, I'm now well aware of
 the limitations in the IBC (CBC out here), which allow that to be done 
 only if the design of the system conformed
 to NFPA 13.  Some pretty high profile architectural firms have made 
 that error, stamped and sealed their drawings.

 A significant number of AHJ's don't seem to know that's the case, at 
 least based on the training classes I've attended
 and taught.  More's the pity.

 Ken


 On 4/22/2014 10:46 AM, Steve Leyton wrote:
 Chris:

 You know we're buds, right?  Good, 'cause that's just 
 regoddamnediculous.Many AHJ's don't have all the information 
 ...???   TFB - they owe their customers the professional service to 
 acquire and apply that information. You wanna be sued into oblivion 
 after a fire loss?   Do the code analysis apart from the enforcing 
 agency (especially if someone can show evidence later of 
 correspondence or opinion by the AHJ that maybe it should have been a 
 different basis of design) and then prosecute your work based on that 
 independent opinion.

 I agree that the architect is in responsible charge and typically 
 they do a code analysis.  But they very often simply put Sprinklers 
 - Yes or words to that effect into the note block.  It says in the 
 code which design to use and if the Architect can't or won't answer, 
 then the BO should have the final say.  Legally, in most cities and 
 states, they do have the final say.

 SML





 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Cahill, Christopher
 Sent: Tuesday, April 22, 2014 10:41 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA-13R or NFPA-13?

 I agree Arch is better to ask.  As a sprinkler contractor you 
 probably don't have all the information to ask correctly.  Many AHJ's 
 don't have all the information either.  I've seen many a project go 
 forward on this issue long before an AHJ sees it. And if you call the 
 fire marshal because that's who the sprinkler permit is through 
 probably the building official approved the type of sprinkler.  I was 
 an AHJ for a long time and wouldn't answer.  I'd ask you what the 
 Arch said and the building official agreed to.  If I discovered a 
 problem later I took it up with the building official. When I was an 
 contractor I sure drove a lot of Arch's nuts asking.  And yes they 
 rarely knew the answer.  We'd talk it out and caveat the bid.

 Chris Cahill, PE*
 Associate Fire Protection Engineer
 Burns  McDonnell
 Phone:  952.656.3652
 Fax:  952.229.2923
 ccah...@burnsmcd.com
 www.burnsmcd.com
 *Registered in: MN


 Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Forest Wilson
 Sent: Tuesday, April 22, 2014 11:39 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: NFPA-13R or NFPA-13?

 I ask the Architect

Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-24 Thread George Medina Jr



Than you all for your valued opinions and expertise, especially your 
I.B.C./U.B.C./C.F.C. references.  
 
In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When not 
used in accordance with section 504.2 or 506.3 of the California Building Code 
an Automatic Sprinkler System installed in accordance with section 903.3.1.2 
shall be allowed in Group R-2.1 Occupancies. Is it safe to assume that a R-2 
occupancy used in accordance with section 504.2 or 506.3 of the 2010 C.F.C. be 
allowed to be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. 

 
George Medina Jr. 
Mobile: 323-906-5701


 
 
 
-Original Message-
From: George Medina Jr fireg...@aol.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Thu, Apr 24, 2014 12:06 pm
Subject: Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)


Than you all for your valued opinions and expertise, especially your 
I.B.C./U.B.C./C.F.C. references.  
 
In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When not 
used in accordance with section 504.2 or 506.3 of the California Building Code 
an Automatic Sprinkler System installed in accordance with section 903.3.1.2 
shall be allowed in Group R-2.1 Occupancies. Is it safe to assume that a R-2 
occupancy used in accordance with section 504.2 or 506.3 of the 2010 C.F.C. be 
allowed to be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. 

 
George Medina Jr. 
Mobile: 323-906-5701
 

 
 
-Original Message-
From: Travis Mack tm...@mfpdesign.com
To: sprinklerforum sprinklerforum@lists.firesprinkler.org
Sent: Tue, Apr 22, 2014 11:04 am
Subject: Re: NFPA-13R or NFPA-13?


Agree as well.  I am no IBC expert, but I do know a couple instances 
where the architect can take an allowance and it drives the system to 
903.3.1.1 instead of 903.3.1.2 of the IBC.  I always check these on all 
projects where 13R may be applicable.  If I find what I feel is an 
error, I will call the architect and point out my concerns.  I can't 
tell you how many times the architectural firms say they were unaware of 
the difference in those two sections.

My first check is to always go with the code study analysis and then if 
it doesn't make sense, I throw it back to the architect and make them do 
the final determination.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

On 4/22/2014 10:59 AM, Parsley Consulting wrote:
 I have to agree with Steve.  There has been many a multi-family 
 project cross my plan review table with the
 system designed to NFPA 13R because the architect called it out on 
 the drawings, while also taking several
 allowances for a fully sprinklered building.  Thanks to Steve, and a 
 couple of others, I'm now well aware of
 the limitations in the IBC (CBC out here), which allow that to be done 
 only if the design of the system conformed
 to NFPA 13.  Some pretty high profile architectural firms have made 
 that error, stamped and sealed their drawings.

 A significant number of AHJ's don't seem to know that's the case, at 
 least based on the training classes I've attended
 and taught.  More's the pity.

 Ken


 On 4/22/2014 10:46 AM, Steve Leyton wrote:
 Chris:

 You know we're buds, right?  Good, 'cause that's just 
 regoddamnediculous.Many AHJ's don't have all the information 
 ...???   TFB - they owe their customers the professional service to 
 acquire and apply that information. You wanna be sued into oblivion 
 after a fire loss?   Do the code analysis apart from the enforcing 
 agency (especially if someone can show evidence later of 
 correspondence or opinion by the AHJ that maybe it should have been a 
 different basis of design) and then prosecute your work based on that 
 independent opinion.

 I agree that the architect is in responsible charge and typically 
 they do a code analysis.  But they very often simply put Sprinklers 
 - Yes or words to that effect into the note block.  It says in the 
 code which design to use and if the Architect can't or won't answer, 
 then the BO should have the final say.  Legally, in most cities and 
 states, they do have the final say.

 SML





 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Cahill, Christopher
 Sent: Tuesday, April 22, 2014 10:41 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA-13R or NFPA-13?

 I agree Arch is better to ask.  As a sprinkler contractor you 
 probably don't have all the information to ask correctly.  Many AHJ's 
 don't have all the information either.  I've seen many a project go 
 forward on this issue long before an AHJ sees it. And if you call the 
 fire marshal because that's who the sprinkler permit is through 
 probably the building official approved the type of sprinkler.  I was 
 an AHJ for a long time

Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-24 Thread George Medina Jr


Thank you all for your valued opinions and expertise, especially your 
I.B.C./U.B.C./C.F.C. references.  
 
In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When not 
used in accordance with section 504.2 or 506.3 of the California Building Code 
an Automatic Sprinkler System installed in accordance with section 903.3.1.2 
shall be allowed in Group R-2.1 Occupancies. Is it safe to assume that a R-2 
occupancy used in accordance with section 504.2 or 506.3 of the 2010 C.F.C. be 
allowed to be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. 

 
George Medina Jr. 
 Mobile: 323-906-5701
 


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Area increase factor based on C.F.C. 506.3 (NFPA-13R or NFPA-13?)

2014-04-24 Thread George Medina Jr



Than you all for your valued inputs and expertise.

 In the 2nd to last paragraph in the 2010 California Fire Code 903.2.8 'When 
not used in accordance with section 504.2 or 506.3 of the California Building 
Code an Automatic Sprinkler System installed in accordance with section 
903.3.1.2 shall be allowed in Group R-2.1 Occupancies. Is it safe to assume 
that since it doesn't specifically mention an R-2 occupancy not being used in 
accordance with section 504.2 or 506.3 of the 2010 C.F.C. that it be allowed to 
be installed in accordance with Section 903.3.1.2 of the 2010 C.F.C. (Did I say 
that correctly?)

George Medina Jr. 
Mobile: 323-906-5701
 

 

 

 
 
-Original Message-
From: George Medina Jr fireg...@aol.com
To: sprinklerforum sprinklerfo...@firesprinkler.org
Sent: Mon, Apr 21, 2014 10:17 pm
Subject: NFPA-13R or NFPA-13?



Forum,
Can anyone please add there 2 cents in and help clarify when to classify as a 
13 system versus a 13R
I have a project that consist of 3 stories with an occupancy of R2/S2 and 
Construction Type VA. The project is lay ed out like a horse shoe
with 3 sides  and a corridor running down the middle from  1 required stairwell 
to another on the opposite end, with a court yard in the middle. There are 
private garages around the perimeter of the building (which all have access 
from a common 1st floor corridor only) All the Garages have a 2 hour separation 
between them and the 2nd level  residential units and the 1st floor corridor. 
There are residential units on the 1st floor (opposite the garages) facing the 
court yard.
 
I figured the Garage calculations shall conform to NFPA-13, based on NFPA-13R 
(2013ed.) Sec. 7.3.1. My question is if the building can be classified as a 13R 
(with garage areas calced at NFPA-13) or should it be classified as a NFPA-13 
with dwelling units  residential heads (calculations based on the greater of 
the area/density @ .10 or the head listing). If not, what is the determining 
factor or the threshold.
 

 
 
 
George Medina Jr. 
Mobile: 323-906-5701
 




___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA-13R or NFPA-13?

2014-04-22 Thread Todd Williams
I would say that if the garages are for resident use only and they are 
ancillary to the primary occupancy, then you could use 13R

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


 On Apr 22, 2014, at 1:17 AM, George Medina Jr fireg...@aol.com wrote:
 
 
 
 Forum,
 Can anyone please add there 2 cents in and help clarify when to classify as a 
 13 system versus a 13R
 I have a project that consist of 3 stories with an occupancy of R2/S2 and 
 Construction Type VA. The project is lay ed out like a horse shoe
 with 3 sides  and a corridor running down the middle from  1 required 
 stairwell to another on the opposite end, with a court yard in the middle. 
 There are private garages around the perimeter of the building (which all 
 have access from a common 1st floor corridor only) All the Garages have a 2 
 hour separation between them and the 2nd level  residential units and the 1st 
 floor corridor. There are residential units on the 1st floor (opposite the 
 garages) facing the court yard.
 
 I figured the Garage calculations shall conform to NFPA-13, based on NFPA-13R 
 (2013ed.) Sec. 7.3.1. My question is if the building can be classified as a 
 13R (with garage areas calced at NFPA-13) or should it be classified as a 
 NFPA-13 with dwelling units  residential heads (calculations based on the 
 greater of the area/density @ .10 or the head listing). If not, what is the 
 determining factor or the threshold.
 
 
 
 
 
 George Medina Jr. 
 Mobile: 323-906-5701
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA-13R or NFPA-13?

2014-04-22 Thread Travis Mack
What does the code study sheet say! Did the architect use the sprinkler system 
to increase the allowable area per floor? If he did, you are doing NFPA 13 
throughout. If he did not, 13R may be applicable. 

Travis Mack, SET
MFP Design, LLC

Sent from my iPhone

 On Apr 21, 2014, at 10:17 PM, George Medina Jr fireg...@aol.com wrote:
 
 
 
 Forum,
 Can anyone please add there 2 cents in and help clarify when to classify as a 
 13 system versus a 13R
 I have a project that consist of 3 stories with an occupancy of R2/S2 and 
 Construction Type VA. The project is lay ed out like a horse shoe
 with 3 sides  and a corridor running down the middle from  1 required 
 stairwell to another on the opposite end, with a court yard in the middle. 
 There are private garages around the perimeter of the building (which all 
 have access from a common 1st floor corridor only) All the Garages have a 2 
 hour separation between them and the 2nd level  residential units and the 1st 
 floor corridor. There are residential units on the 1st floor (opposite the 
 garages) facing the court yard.
 
 I figured the Garage calculations shall conform to NFPA-13, based on NFPA-13R 
 (2013ed.) Sec. 7.3.1. My question is if the building can be classified as a 
 13R (with garage areas calced at NFPA-13) or should it be classified as a 
 NFPA-13 with dwelling units  residential heads (calculations based on the 
 greater of the area/density @ .10 or the head listing). If not, what is the 
 determining factor or the threshold.
 
 
 
 
 
 George Medina Jr. 
 Mobile: 323-906-5701
 
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org
 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Mark A. Sornsin, P.E.
A word of caution regarding semantics:

The building is either designed to 13 or 13R.  There is no 13 for this area 
and 13R for that area.  If the garages are considered part of the building and 
the building is eligible for 13R (as this one appears it may be) then the 
building is designed to 13R.  The garage calculations would be done to 13R 
(which happens to reference 13 rules, except for the hose allowances).

Only if the garages are determined to be separate buildings would be able to 
say 13R for the main building and 13 for the garages.

This sounds petty on the surface, but when we use these terms loosely, the 
Architects and plumbing engineers pick up on it and start spreading false 
premises:

We're gonna design these rooms to that 13R code and these areas to 13.
You need residential sprinklers everywhere, except the laundry rooms, because 
those have to be designed to 13.
The apartments above are to 13R but the first floor mercantile - including the 
open stair to the apartments- is designed to 13.

No, No, and No. One building - one design standard.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of George 
Medina Jr
Sent: Tuesday, April 22, 2014 12:18 AM
To: sprinklerfo...@firesprinkler.org
Subject: NFPA-13R or NFPA-13?



Forum,
Can anyone please add there 2 cents in and help clarify when to classify as a 
13 system versus a 13R I have a project that consist of 3 stories with an 
occupancy of R2/S2 and Construction Type VA. The project is lay ed out like a 
horse shoe with 3 sides  and a corridor running down the middle from  1 
required stairwell to another on the opposite end, with a court yard in the 
middle. There are private garages around the perimeter of the building (which 
all have access from a common 1st floor corridor only) All the Garages have a 2 
hour separation between them and the 2nd level  residential units and the 1st 
floor corridor. There are residential units on the 1st floor (opposite the 
garages) facing the court yard.

I figured the Garage calculations shall conform to NFPA-13, based on NFPA-13R 
(2013ed.) Sec. 7.3.1. My question is if the building can be classified as a 13R 
(with garage areas calced at NFPA-13) or should it be classified as a NFPA-13 
with dwelling units  residential heads (calculations based on the greater of 
the area/density @ .10 or the head listing). If not, what is the determining 
factor or the threshold.

George Medina Jr.
Mobile: 323-906-5701

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA-13R or NFPA-13?

2014-04-22 Thread rongreenman .
Go Mark!

And even if the garages are used by non-tenants I believe the 13R
designation could still apply. If you look at 13R and garages, and I'm
imagining the 2007 edition  so it may have changed, there are three
criteria for garages in 13R. Depending on how they communicate, or don't,
with each other and the building itself seems to define how they are
defined for design purposes. As Mark says, just because 13R references you
to 13 for a single point of design to follow in a special circumstance
doesn't necessarily mean you default entirely to 13. 13 references 24 but
we don't install all the piping to 24 (although I did once see a backflow
installed about 20 feet off the floor, with glanded flanges, Megalugs and
rodding). 13 also references 72 but because I have to do a thing (hook up
alarm stuff) doesn't mean it completely trumps everything else. I know this
is silly but it's not far off. Just because 13R looks a lot like 13 doesn't
make it the same. A zebra looks like a striped horse


On Tue, Apr 22, 2014 at 7:27 AM, Mark A. Sornsin, P.E. 
masorn...@kfi-eng.com wrote:

 A word of caution regarding semantics:

 The building is either designed to 13 or 13R.  There is no 13 for this
 area and 13R for that area.  If the garages are considered part of the
 building and the building is eligible for 13R (as this one appears it may
 be) then the building is designed to 13R.  The garage calculations would be
 done to 13R (which happens to reference 13 rules, except for the hose
 allowances).

 Only if the garages are determined to be separate buildings would be able
 to say 13R for the main building and 13 for the garages.

 This sounds petty on the surface, but when we use these terms loosely, the
 Architects and plumbing engineers pick up on it and start spreading false
 premises:

 We're gonna design these rooms to that 13R code and these areas to 13.
 You need residential sprinklers everywhere, except the laundry rooms,
 because those have to be designed to 13.
 The apartments above are to 13R but the first floor mercantile -
 including the open stair to the apartments- is designed to 13.

 No, No, and No. One building - one design standard.

 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
 http://www.kfiengineers.com

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of George
 Medina Jr
 Sent: Tuesday, April 22, 2014 12:18 AM
 To: sprinklerfo...@firesprinkler.org
 Subject: NFPA-13R or NFPA-13?



 Forum,
 Can anyone please add there 2 cents in and help clarify when to classify
 as a 13 system versus a 13R I have a project that consist of 3 stories with
 an occupancy of R2/S2 and Construction Type VA. The project is lay ed out
 like a horse shoe with 3 sides  and a corridor running down the middle from
  1 required stairwell to another on the opposite end, with a court yard in
 the middle. There are private garages around the perimeter of the building
 (which all have access from a common 1st floor corridor only) All the
 Garages have a 2 hour separation between them and the 2nd level
  residential units and the 1st floor corridor. There are residential units
 on the 1st floor (opposite the garages) facing the court yard.

 I figured the Garage calculations shall conform to NFPA-13, based on
 NFPA-13R (2013ed.) Sec. 7.3.1. My question is if the building can be
 classified as a 13R (with garage areas calced at NFPA-13) or should it be
 classified as a NFPA-13 with dwelling units  residential heads
 (calculations based on the greater of the area/density @ .10 or the head
 listing). If not, what is the determining factor or the threshold.

 George Medina Jr.
 Mobile: 323-906-5701

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Steve Leyton
I'm a little late to this thread, but I did want to address the initial
question, i.e. when do you use this standard or that standard.
Notwithstanding the annex language in 13R that's intended to clarify its
application, the bottom line answer is that it's up to the building
official.   If you - as a bidding contractor or design consultant or
whatever your stake in the issue - cannot clearly determine the
applicable standard, a formal query should be directed to the building
official with jurisdiction.  

Steve L.

 




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
Sent: Tuesday, April 22, 2014 7:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

Go Mark!

And even if the garages are used by non-tenants I believe the 13R
designation could still apply. If you look at 13R and garages, and I'm
imagining the 2007 edition  so it may have changed, there are three
criteria for garages in 13R. Depending on how they communicate, or
don't, with each other and the building itself seems to define how they
are defined for design purposes. As Mark says, just because 13R
references you to 13 for a single point of design to follow in a special
circumstance doesn't necessarily mean you default entirely to 13. 13
references 24 but we don't install all the piping to 24 (although I did
once see a backflow installed about 20 feet off the floor, with glanded
flanges, Megalugs and rodding). 13 also references 72 but because I have
to do a thing (hook up alarm stuff) doesn't mean it completely trumps
everything else. I know this is silly but it's not far off. Just because
13R looks a lot like 13 doesn't make it the same. A zebra looks like a
striped horse


On Tue, Apr 22, 2014 at 7:27 AM, Mark A. Sornsin, P.E. 
masorn...@kfi-eng.com wrote:

 A word of caution regarding semantics:

 The building is either designed to 13 or 13R.  There is no 13 for 
 this area and 13R for that area.  If the garages are considered part 
 of the building and the building is eligible for 13R (as this one 
 appears it may
 be) then the building is designed to 13R.  The garage calculations 
 would be done to 13R (which happens to reference 13 rules, except for 
 the hose allowances).

 Only if the garages are determined to be separate buildings would be 
 able to say 13R for the main building and 13 for the garages.

 This sounds petty on the surface, but when we use these terms loosely,

 the Architects and plumbing engineers pick up on it and start 
 spreading false
 premises:

 We're gonna design these rooms to that 13R code and these areas to
13.
 You need residential sprinklers everywhere, except the laundry rooms,

 because those have to be designed to 13.
 The apartments above are to 13R but the first floor mercantile - 
 including the open stair to the apartments- is designed to 13.

 No, No, and No. One building - one design standard.

 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of George 
 Medina Jr
 Sent: Tuesday, April 22, 2014 12:18 AM
 To: sprinklerfo...@firesprinkler.org
 Subject: NFPA-13R or NFPA-13?



 Forum,
 Can anyone please add there 2 cents in and help clarify when to 
 classify as a 13 system versus a 13R I have a project that consist of 
 3 stories with an occupancy of R2/S2 and Construction Type VA. The 
 project is lay ed out like a horse shoe with 3 sides  and a corridor 
 running down the middle from
  1 required stairwell to another on the opposite end, with a court 
 yard in the middle. There are private garages around the perimeter of 
 the building (which all have access from a common 1st floor corridor 
 only) All the Garages have a 2 hour separation between them and the 
 2nd level  residential units and the 1st floor corridor. There are 
 residential units on the 1st floor (opposite the garages) facing the
court yard.

 I figured the Garage calculations shall conform to NFPA-13, based on 
 NFPA-13R (2013ed.) Sec. 7.3.1. My question is if the building can be 
 classified as a 13R (with garage areas calced at NFPA-13) or should it

 be classified as a NFPA-13 with dwelling units  residential heads 
 (calculations based on the greater of the area/density @ .10 or the 
 head listing). If not, what is the determining factor or the
threshold.

 George Medina Jr.
 Mobile: 323-906-5701

 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
 er.org




--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Taylor, Galen
Let me add to what Steve just said: During the building plan check process a 
trade-off may occur in which an otherwise acceptable 13R system is required to 
be upgraded to a full 13 system. This fact may or may not be fully revealed 
upfront to bidding contractors, so it pays to ask. And any questions you have 
concerning the application of the code should be directed to the AHJ.

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
galen.tay...@fire.lacounty.gov

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Tuesday, April 22, 2014 9:06 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I'm a little late to this thread, but I did want to address the initial 
question, i.e. when do you use this standard or that standard.
Notwithstanding the annex language in 13R that's intended to clarify its 
application, the bottom line answer is that it's up to the building
official.   If you - as a bidding contractor or design consultant or
whatever your stake in the issue - cannot clearly determine the applicable 
standard, a formal query should be directed to the building official with 
jurisdiction.  

Steve L.

 




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
rongreenman .
Sent: Tuesday, April 22, 2014 7:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

Go Mark!

And even if the garages are used by non-tenants I believe the 13R designation 
could still apply. If you look at 13R and garages, and I'm imagining the 2007 
edition  so it may have changed, there are three criteria for garages in 13R. 
Depending on how they communicate, or don't, with each other and the building 
itself seems to define how they are defined for design purposes. As Mark says, 
just because 13R references you to 13 for a single point of design to follow in 
a special circumstance doesn't necessarily mean you default entirely to 13. 13 
references 24 but we don't install all the piping to 24 (although I did once 
see a backflow installed about 20 feet off the floor, with glanded flanges, 
Megalugs and rodding). 13 also references 72 but because I have to do a thing 
(hook up alarm stuff) doesn't mean it completely trumps everything else. I know 
this is silly but it's not far off. Just because 13R looks a lot like 13 
doesn't make it the same. A zebra looks like a striped h
 orse


On Tue, Apr 22, 2014 at 7:27 AM, Mark A. Sornsin, P.E.  masorn...@kfi-eng.com 
wrote:

 A word of caution regarding semantics:

 The building is either designed to 13 or 13R.  There is no 13 for 
 this area and 13R for that area.  If the garages are considered part 
 of the building and the building is eligible for 13R (as this one 
 appears it may
 be) then the building is designed to 13R.  The garage calculations 
 would be done to 13R (which happens to reference 13 rules, except for 
 the hose allowances).

 Only if the garages are determined to be separate buildings would be 
 able to say 13R for the main building and 13 for the garages.

 This sounds petty on the surface, but when we use these terms loosely,

 the Architects and plumbing engineers pick up on it and start 
 spreading false
 premises:

 We're gonna design these rooms to that 13R code and these areas to
13.
 You need residential sprinklers everywhere, except the laundry rooms,

 because those have to be designed to 13.
 The apartments above are to 13R but the first floor mercantile - 
 including the open stair to the apartments- is designed to 13.

 No, No, and No. One building - one design standard.

 Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection 
 Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
 http://www.kfiengineers.com

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
 sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of George 
 Medina Jr
 Sent: Tuesday, April 22, 2014 12:18 AM
 To: sprinklerfo...@firesprinkler.org
 Subject: NFPA-13R or NFPA-13?



 Forum,
 Can anyone please add there 2 cents in and help clarify when to 
 classify as a 13 system versus a 13R I have a project that consist of
 3 stories with an occupancy of R2/S2 and Construction Type VA. The 
 project is lay ed out like a horse shoe with 3 sides  and a corridor 
 running down the middle from
  1 required stairwell to another on the opposite end, with a court 
 yard in the middle. There are private garages around the perimeter of 
 the building (which all have access from a common 1st floor corridor
 only) All the Garages have a 2 hour separation between them and the 
 2nd level  residential units and the 1st floor corridor. There are 
 residential units on the 1st floor (opposite the garages

Re: NFPA-13R or NFPA-13?

2014-04-22 Thread Forest Wilson

I ask the Architect.
The problem with asking the AHJ is that they can change their mind later.
In Ohio, most of their approval stamps have an exception clause.
Ask the Architect, let the Architect ask the AHJ.
Then if the AHJ changes their mind, the Architect is caught in the 
middle of the dispute.



On 4/22/2014 12:28 PM, Taylor, Galen wrote:

Let me add to what Steve just said: During the building plan check process a 
trade-off may occur in which an otherwise acceptable 13R system is required to 
be upgraded to a full 13 system. This fact may or may not be fully revealed 
upfront to bidding contractors, so it pays to ask. And any questions you have 
concerning the application of the code should be directed to the AHJ.

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
galen.tay...@fire.lacounty.gov

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Tuesday, April 22, 2014 9:06 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I'm a little late to this thread, but I did want to address the initial 
question, i.e. when do you use this standard or that standard.
Notwithstanding the annex language in 13R that's intended to clarify its 
application, the bottom line answer is that it's up to the building
official.   If you - as a bidding contractor or design consultant or
whatever your stake in the issue - cannot clearly determine the applicable 
standard, a formal query should be directed to the building official with 
jurisdiction.

Steve L.

  





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
rongreenman .
Sent: Tuesday, April 22, 2014 7:45 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

Go Mark!

And even if the garages are used by non-tenants I believe the 13R designation 
could still apply. If you look at 13R and garages, and I'm imagining the 2007 
edition  so it may have changed, there are three criteria for garages in 13R. 
Depending on how they communicate, or don't, with each other and the building 
itself seems to define how they are defined for design purposes. As Mark says, 
just because 13R references you to 13 for a single point of design to follow in 
a special circumstance doesn't necessarily mean you default entirely to 13. 13 
references 24 but we don't install all the piping to 24 (although I did once 
see a backflow installed about 20 feet off the floor, with glanded flanges, 
Megalugs and rodding). 13 also references 72 but because I have to do a thing 
(hook up alarm stuff) doesn't mean it completely trumps everything else. I know 
this is silly but it's not far off. Just because 13R looks a lot like 13 
doesn't make it the same. A zebra looks like a striped

 h

  orse


On Tue, Apr 22, 2014 at 7:27 AM, Mark A. Sornsin, P.E.  masorn...@kfi-eng.com 
wrote:


A word of caution regarding semantics:

The building is either designed to 13 or 13R.  There is no 13 for
this area and 13R for that area.  If the garages are considered part
of the building and the building is eligible for 13R (as this one
appears it may
be) then the building is designed to 13R.  The garage calculations
would be done to 13R (which happens to reference 13 rules, except for
the hose allowances).

Only if the garages are determined to be separate buildings would be
able to say 13R for the main building and 13 for the garages.

This sounds petty on the surface, but when we use these terms loosely,
the Architects and plumbing engineers pick up on it and start
spreading false
premises:

We're gonna design these rooms to that 13R code and these areas to

13.

You need residential sprinklers everywhere, except the laundry rooms,
because those have to be designed to 13.
The apartments above are to 13R but the first floor mercantile -
including the open stair to the apartments- is designed to 13.

No, No, and No. One building - one design standard.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:
sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of George
Medina Jr
Sent: Tuesday, April 22, 2014 12:18 AM
To: sprinklerfo...@firesprinkler.org
Subject: NFPA-13R or NFPA-13?



Forum,
Can anyone please add there 2 cents in and help clarify when to
classify as a 13 system versus a 13R I have a project that consist of
3 stories with an occupancy of R2/S2 and Construction Type VA. The
project is lay ed out like a horse shoe with 3 sides  and a corridor
running down the middle from
  1 required stairwell to another on the opposite end, with a court
yard in the middle. There are private

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Steve Leyton
Not sure how the building official gets off changing their mind after
the fact.  If the fire official can't decide which standard applies they
should get the same opinion from the Building Official that the
architect or sprinkie would get.   Ohio uses the same basic code as
California and the basis of design for sprinklers is a prescriptive
based on occupancy class.  In mixed occupancies, issues of separation
can complicate interpreting the code, and that's the subjective part.
So if the BO is bending one way and other stakeholders bending the
other, it comes down to who actually has jurisdiction, and that's
usually the BO, not the FO or the Architect.

SML 

 




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Forest Wilson
Sent: Tuesday, April 22, 2014 9:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

I ask the Architect.
The problem with asking the AHJ is that they can change their mind
later.
In Ohio, most of their approval stamps have an exception clause.
Ask the Architect, let the Architect ask the AHJ.
Then if the AHJ changes their mind, the Architect is caught in the
middle of the dispute.


On 4/22/2014 12:28 PM, Taylor, Galen wrote:
 Let me add to what Steve just said: During the building plan check
process a trade-off may occur in which an otherwise acceptable 13R
system is required to be upgraded to a full 13 system. This fact may or
may not be fully revealed upfront to bidding contractors, so it pays to
ask. And any questions you have concerning the application of the code
should be directed to the AHJ.

 Galen Taylor
 County of Los Angeles Fire Department
 Fire Prevention Engineering
 323-890-4339
 galen.tay...@fire.lacounty.gov

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Steve Leyton
 Sent: Tuesday, April 22, 2014 9:06 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA-13R or NFPA-13?

 I'm a little late to this thread, but I did want to address the
initial question, i.e. when do you use this standard or that standard.
 Notwithstanding the annex language in 13R that's intended to clarify
its application, the bottom line answer is that it's up to the building
 official.   If you - as a bidding contractor or design consultant or
 whatever your stake in the issue - cannot clearly determine the
applicable standard, a formal query should be directed to the building
official with jurisdiction.

 Steve L.

   




 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
rongreenman .
 Sent: Tuesday, April 22, 2014 7:45 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: NFPA-13R or NFPA-13?

 Go Mark!

 And even if the garages are used by non-tenants I believe the 13R
designation could still apply. If you look at 13R and garages, and I'm
imagining the 2007 edition  so it may have changed, there are three
criteria for garages in 13R. Depending on how they communicate, or
don't, with each other and the building itself seems to define how they
are defined for design purposes. As Mark says, just because 13R
references you to 13 for a single point of design to follow in a special
circumstance doesn't necessarily mean you default entirely to 13. 13
references 24 but we don't install all the piping to 24 (although I did
once see a backflow installed about 20 feet off the floor, with glanded
flanges, Megalugs and rodding). 13 also references 72 but because I have
to do a thing (hook up alarm stuff) doesn't mean it completely trumps
everything else. I know this is silly but it's not far off. Just because
13R looks a lot like 13 doesn't make it the same. A zebra looks like a
striped
  h
   orse


 On Tue, Apr 22, 2014 at 7:27 AM, Mark A. Sornsin, P.E. 
masorn...@kfi-eng.com wrote:

 A word of caution regarding semantics:

 The building is either designed to 13 or 13R.  There is no 13 for
 this area and 13R for that area.  If the garages are considered part
 of the building and the building is eligible for 13R (as this one
 appears it may
 be) then the building is designed to 13R.  The garage calculations
 would be done to 13R (which happens to reference 13 rules, except for
 the hose allowances).

 Only if the garages are determined to be separate buildings would be
 able to say 13R for the main building and 13 for the garages.

 This sounds petty on the surface, but when we use these terms
loosely,
 the Architects and plumbing engineers pick up on it and start
 spreading false
 premises:

 We're gonna design these rooms to that 13R code and these areas to
 13.
 You need residential sprinklers everywhere, except the laundry
rooms,
 because those have to be designed to 13.
 The apartments above are to 13R but the first floor mercantile

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Cahill, Christopher
I agree Arch is better to ask.  As a sprinkler contractor you probably don't 
have all the information to ask correctly.  Many AHJ's don't have all the 
information either.  I've seen many a project go forward on this issue long 
before an AHJ sees it. And if you call the fire marshal because that's who the 
sprinkler permit is through probably the building official approved the type of 
sprinkler.  I was an AHJ for a long time and wouldn't answer.  I'd ask you what 
the Arch said and the building official agreed to.  If I discovered a problem 
later I took it up with the building official. When I was an contractor I sure 
drove a lot of Arch's nuts asking.  And yes they rarely knew the answer.  We'd 
talk it out and caveat the bid.   

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Tuesday, April 22, 2014 11:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

I ask the Architect.
The problem with asking the AHJ is that they can change their mind later.
In Ohio, most of their approval stamps have an exception clause.
Ask the Architect, let the Architect ask the AHJ.
Then if the AHJ changes their mind, the Architect is caught in the middle of 
the dispute.


On 4/22/2014 12:28 PM, Taylor, Galen wrote:
 Let me add to what Steve just said: During the building plan check process a 
 trade-off may occur in which an otherwise acceptable 13R system is required 
 to be upgraded to a full 13 system. This fact may or may not be fully 
 revealed upfront to bidding contractors, so it pays to ask. And any questions 
 you have concerning the application of the code should be directed to the AHJ.

 Galen Taylor
 County of Los Angeles Fire Department
 Fire Prevention Engineering
 323-890-4339
 galen.tay...@fire.lacounty.gov

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
 Leyton
 Sent: Tuesday, April 22, 2014 9:06 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA-13R or NFPA-13?

 I'm a little late to this thread, but I did want to address the initial 
 question, i.e. when do you use this standard or that standard.
 Notwithstanding the annex language in 13R that's intended to clarify its 
 application, the bottom line answer is that it's up to the building
 official.   If you - as a bidding contractor or design consultant or
 whatever your stake in the issue - cannot clearly determine the applicable 
 standard, a formal query should be directed to the building official with 
 jurisdiction.

 Steve L.

   




 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rongreenman .
 Sent: Tuesday, April 22, 2014 7:45 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: NFPA-13R or NFPA-13?

 Go Mark!

 And even if the garages are used by non-tenants I believe the 13R designation 
 could still apply. If you look at 13R and garages, and I'm imagining the 2007 
 edition  so it may have changed, there are three criteria for garages in 13R. 
 Depending on how they communicate, or don't, with each other and the building 
 itself seems to define how they are defined for design purposes. As Mark 
 says, just because 13R references you to 13 for a single point of design to 
 follow in a special circumstance doesn't necessarily mean you default 
 entirely to 13. 13 references 24 but we don't install all the piping to 24 
 (although I did once see a backflow installed about 20 feet off the floor, 
 with glanded flanges, Megalugs and rodding). 13 also references 72 but 
 because I have to do a thing (hook up alarm stuff) doesn't mean it completely 
 trumps everything else. I know this is silly but it's not far off. Just 
 because 13R looks a lot like 13 doesn't make it the same. A zebra looks like 
 a striped
  h
   orse


 On Tue, Apr 22, 2014 at 7:27 AM, Mark A. Sornsin, P.E.  
 masorn...@kfi-eng.com wrote:

 A word of caution regarding semantics:

 The building is either designed to 13 or 13R.  There is no 13 for
 this area and 13R for that area.  If the garages are considered part
 of the building and the building is eligible for 13R (as this one
 appears it may
 be) then the building is designed to 13R.  The garage calculations
 would be done to 13R (which happens to reference 13 rules, except for
 the hose allowances).

 Only if the garages are determined to be separate buildings would be
 able to say 13R for the main building and 13 for the garages.

 This sounds petty on the surface, but when we use

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Steve Leyton
Chris:

You know we're buds, right?  Good, 'cause that's just regoddamnediculous.
Many AHJ's don't have all the information ...???   TFB - they owe their 
customers the professional service to acquire and apply that information.   You 
wanna be sued into oblivion after a fire loss?   Do the code analysis apart 
from the enforcing agency (especially if someone can show evidence later of 
correspondence or opinion by the AHJ that maybe it should have been a different 
basis of design) and then prosecute your work based on that independent 
opinion.

I agree that the architect is in responsible charge and typically they do a 
code analysis.  But they very often simply put Sprinklers - Yes or words to 
that effect into the note block.  It says in the code which design to use and 
if the Architect can't or won't answer, then the BO should have the final say.  
Legally, in most cities and states, they do have the final say.

SML

 




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, April 22, 2014 10:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I agree Arch is better to ask.  As a sprinkler contractor you probably don't 
have all the information to ask correctly.  Many AHJ's don't have all the 
information either.  I've seen many a project go forward on this issue long 
before an AHJ sees it. And if you call the fire marshal because that's who the 
sprinkler permit is through probably the building official approved the type of 
sprinkler.  I was an AHJ for a long time and wouldn't answer.  I'd ask you what 
the Arch said and the building official agreed to.  If I discovered a problem 
later I took it up with the building official. When I was an contractor I sure 
drove a lot of Arch's nuts asking.  And yes they rarely knew the answer.  We'd 
talk it out and caveat the bid.   

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Tuesday, April 22, 2014 11:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

I ask the Architect.
The problem with asking the AHJ is that they can change their mind later.
In Ohio, most of their approval stamps have an exception clause.
Ask the Architect, let the Architect ask the AHJ.
Then if the AHJ changes their mind, the Architect is caught in the middle of 
the dispute.


On 4/22/2014 12:28 PM, Taylor, Galen wrote:
 Let me add to what Steve just said: During the building plan check process a 
 trade-off may occur in which an otherwise acceptable 13R system is required 
 to be upgraded to a full 13 system. This fact may or may not be fully 
 revealed upfront to bidding contractors, so it pays to ask. And any questions 
 you have concerning the application of the code should be directed to the AHJ.

 Galen Taylor
 County of Los Angeles Fire Department
 Fire Prevention Engineering
 323-890-4339
 galen.tay...@fire.lacounty.gov

 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org 
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
 Leyton
 Sent: Tuesday, April 22, 2014 9:06 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA-13R or NFPA-13?

 I'm a little late to this thread, but I did want to address the initial 
 question, i.e. when do you use this standard or that standard.
 Notwithstanding the annex language in 13R that's intended to clarify its 
 application, the bottom line answer is that it's up to the building
 official.   If you - as a bidding contractor or design consultant or
 whatever your stake in the issue - cannot clearly determine the applicable 
 standard, a formal query should be directed to the building official with 
 jurisdiction.

 Steve L.

   




 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 rongreenman .
 Sent: Tuesday, April 22, 2014 7:45 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: NFPA-13R or NFPA-13?

 Go Mark!

 And even if the garages are used by non-tenants I believe the 13R designation 
 could still apply. If you look at 13R and garages, and I'm imagining the 2007 
 edition  so it may have changed, there are three criteria for garages in 13R. 
 Depending on how they communicate, or don't, with each other and the building 
 itself seems to define how they are defined for design purposes. As Mark 
 says, just because 13R references you to 13 for a single point of design to 
 follow

Re: NFPA-13R or NFPA-13?

2014-04-22 Thread Parsley Consulting
I have to agree with Steve.  There has been many a multi-family project 
cross my plan review table with the
system designed to NFPA 13R because the architect called it out on the 
drawings, while also taking several
allowances for a fully sprinklered building.  Thanks to Steve, and a 
couple of others, I'm now well aware of
the limitations in the IBC (CBC out here), which allow that to be done 
only if the design of the system conformed
to NFPA 13.  Some pretty high profile architectural firms have made that 
error, stamped and sealed their drawings.


A significant number of AHJ's don't seem to know that's the case, at 
least based on the training classes I've attended

and taught.  More's the pity.

Ken


On 4/22/2014 10:46 AM, Steve Leyton wrote:

Chris:

You know we're buds, right?  Good, 'cause that's just regoddamnediculous.Many AHJ's don't 
have all the information ...???   TFB - they owe their customers the professional service to 
acquire and apply that information.   You wanna be sued into oblivion after a fire loss?   Do the 
code analysis apart from the enforcing agency (especially if someone can show evidence later of 
correspondence or opinion by the AHJ that maybe it should have been a different basis of design) 
and then prosecute your work based on that independent opinion.

I agree that the architect is in responsible charge and typically they do a code 
analysis.  But they very often simply put Sprinklers - Yes or words to that 
effect into the note block.  It says in the code which design to use and if the Architect 
can't or won't answer, then the BO should have the final say.  Legally, in most cities 
and states, they do have the final say.

SML

  





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, April 22, 2014 10:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I agree Arch is better to ask.  As a sprinkler contractor you probably don't 
have all the information to ask correctly.  Many AHJ's don't have all the 
information either.  I've seen many a project go forward on this issue long 
before an AHJ sees it. And if you call the fire marshal because that's who the 
sprinkler permit is through probably the building official approved the type of 
sprinkler.  I was an AHJ for a long time and wouldn't answer.  I'd ask you what 
the Arch said and the building official agreed to.  If I discovered a problem 
later I took it up with the building official. When I was an contractor I sure 
drove a lot of Arch's nuts asking.  And yes they rarely knew the answer.  We'd 
talk it out and caveat the bid.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Tuesday, April 22, 2014 11:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

I ask the Architect.
The problem with asking the AHJ is that they can change their mind later.
In Ohio, most of their approval stamps have an exception clause.
Ask the Architect, let the Architect ask the AHJ.
Then if the AHJ changes their mind, the Architect is caught in the middle of 
the dispute.


On 4/22/2014 12:28 PM, Taylor, Galen wrote:

Let me add to what Steve just said: During the building plan check process a 
trade-off may occur in which an otherwise acceptable 13R system is required to 
be upgraded to a full 13 system. This fact may or may not be fully revealed 
upfront to bidding contractors, so it pays to ask. And any questions you have 
concerning the application of the code should be directed to the AHJ.

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
galen.tay...@fire.lacounty.gov

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Tuesday, April 22, 2014 9:06 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I'm a little late to this thread, but I did want to address the initial 
question, i.e. when do you use this standard or that standard.
Notwithstanding the annex language in 13R that's intended to clarify its 
application, the bottom line answer is that it's up to the building
official.   If you - as a bidding contractor or design consultant or
whatever your stake in the issue - cannot clearly determine the applicable 
standard, a formal query should be directed to the building official with 
jurisdiction.

Steve L.

   





-Original Message-
From: sprinklerforum-boun

Re: NFPA-13R or NFPA-13?

2014-04-22 Thread Travis Mack
Agree as well.  I am no IBC expert, but I do know a couple instances 
where the architect can take an allowance and it drives the system to 
903.3.1.1 instead of 903.3.1.2 of the IBC.  I always check these on all 
projects where 13R may be applicable.  If I find what I feel is an 
error, I will call the architect and point out my concerns.  I can't 
tell you how many times the architectural firms say they were unaware of 
the difference in those two sections.


My first check is to always go with the code study analysis and then if 
it doesn't make sense, I throw it back to the architect and make them do 
the final determination.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

On 4/22/2014 10:59 AM, Parsley Consulting wrote:
I have to agree with Steve.  There has been many a multi-family 
project cross my plan review table with the
system designed to NFPA 13R because the architect called it out on 
the drawings, while also taking several
allowances for a fully sprinklered building.  Thanks to Steve, and a 
couple of others, I'm now well aware of
the limitations in the IBC (CBC out here), which allow that to be done 
only if the design of the system conformed
to NFPA 13.  Some pretty high profile architectural firms have made 
that error, stamped and sealed their drawings.


A significant number of AHJ's don't seem to know that's the case, at 
least based on the training classes I've attended

and taught.  More's the pity.

Ken


On 4/22/2014 10:46 AM, Steve Leyton wrote:

Chris:

You know we're buds, right?  Good, 'cause that's just 
regoddamnediculous.Many AHJ's don't have all the information 
...???   TFB - they owe their customers the professional service to 
acquire and apply that information. You wanna be sued into oblivion 
after a fire loss?   Do the code analysis apart from the enforcing 
agency (especially if someone can show evidence later of 
correspondence or opinion by the AHJ that maybe it should have been a 
different basis of design) and then prosecute your work based on that 
independent opinion.


I agree that the architect is in responsible charge and typically 
they do a code analysis.  But they very often simply put Sprinklers 
- Yes or words to that effect into the note block.  It says in the 
code which design to use and if the Architect can't or won't answer, 
then the BO should have the final say.  Legally, in most cities and 
states, they do have the final say.


SML





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
Cahill, Christopher

Sent: Tuesday, April 22, 2014 10:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I agree Arch is better to ask.  As a sprinkler contractor you 
probably don't have all the information to ask correctly.  Many AHJ's 
don't have all the information either.  I've seen many a project go 
forward on this issue long before an AHJ sees it. And if you call the 
fire marshal because that's who the sprinkler permit is through 
probably the building official approved the type of sprinkler.  I was 
an AHJ for a long time and wouldn't answer.  I'd ask you what the 
Arch said and the building official agreed to.  If I discovered a 
problem later I took it up with the building official. When I was an 
contractor I sure drove a lot of Arch's nuts asking.  And yes they 
rarely knew the answer.  We'd talk it out and caveat the bid.


Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
Forest Wilson

Sent: Tuesday, April 22, 2014 11:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

I ask the Architect.
The problem with asking the AHJ is that they can change their mind 
later.

In Ohio, most of their approval stamps have an exception clause.
Ask the Architect, let the Architect ask the AHJ.
Then if the AHJ changes their mind, the Architect is caught in the 
middle of the dispute.



On 4/22/2014 12:28 PM, Taylor, Galen wrote:
Let me add to what Steve just said: During the building plan check 
process a trade-off may occur in which an otherwise acceptable 13R 
system is required to be upgraded to a full 13 system. This fact may 
or may not be fully revealed upfront to bidding contractors, so it 
pays to ask. And any questions you have concerning the application 
of the code should be directed to the AHJ.


Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
galen.tay...@fire.lacounty.gov

-Original Message-
From

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Cahill, Christopher
Yes, we're buds.  Drink waiting next time I get to SD.  Medium interfering with 
communication.  

I used to get calls it's x story apartment, 13R or 13? This is the first I've 
ever hear of such project.  Now mind you I'm talking to the sprinkler 
contractor as I was the permitting authority for sprinklers NOT the building 
department.  I ask what type of construction.  And the conversation usually 
ended right there as most didn't have any idea what type meant.   In theory 
could be type III, IV or V and be 'wood'.  I was in an old city so on remodels 
III and IV were plausible.  So yeah AHJ did NOT have all the information to 
make a determination.  I'd ask what the code sheet said and they'd say there 
was none in the sprinkler package. Imagine my surprise it wasn't in the 
sprinkler package ( a little sarcasm there if it wasn't painfully obvious), AHJ 
did NOT have all the information to make a determination.  What did the BO or 
Arch say?  This is preliminary hasn't gone for permit and Arch didn't know.  
AHJ did NOT have all the information to make a determination.  Conversation 
might go other ways, fire lanes, draft stops, attics, fire walls, blah, blah, 
blah from there with the same result, AHJ did NOT have all the information to 
make a determination.  Believe me I tried to help but AHJ did NOT have all the 
information to make a determination.

If it ain't in the BO's office for review the BO probably did NOT have all the 
information to make a determination.  A phone call from a sprinkler contractor 
who doesn't know the building code results in bad decision making.  

I AGREE, with a PROPER Arch or FPE code analysis AND a submittal to AHJ (BO) 
NOW they have all the information to make a concurrence of the determination.  
A whole lotta stuff actually happens before this point where the AHJ did NOT 
have all the information to make a determination. 

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Tuesday, April 22, 2014 12:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

Chris:

You know we're buds, right?  Good, 'cause that's just regoddamnediculous.
Many AHJ's don't have all the information ...???   TFB - they owe their 
customers the professional service to acquire and apply that information.   You 
wanna be sued into oblivion after a fire loss?   Do the code analysis apart 
from the enforcing agency (especially if someone can show evidence later of 
correspondence or opinion by the AHJ that maybe it should have been a different 
basis of design) and then prosecute your work based on that independent 
opinion.

I agree that the architect is in responsible charge and typically they do a 
code analysis.  But they very often simply put Sprinklers - Yes or words to 
that effect into the note block.  It says in the code which design to use and 
if the Architect can't or won't answer, then the BO should have the final say.  
Legally, in most cities and states, they do have the final say.

SML

 




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, April 22, 2014 10:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I agree Arch is better to ask.  As a sprinkler contractor you probably don't 
have all the information to ask correctly.  Many AHJ's don't have all the 
information either.  I've seen many a project go forward on this issue long 
before an AHJ sees it. And if you call the fire marshal because that's who the 
sprinkler permit is through probably the building official approved the type of 
sprinkler.  I was an AHJ for a long time and wouldn't answer.  I'd ask you what 
the Arch said and the building official agreed to.  If I discovered a problem 
later I took it up with the building official. When I was an contractor I sure 
drove a lot of Arch's nuts asking.  And yes they rarely knew the answer.  We'd 
talk it out and caveat the bid.   

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For




-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest 
Wilson
Sent: Tuesday, April 22, 2014 11:39 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

I ask the Architect.
The problem with asking the AHJ

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Cahill, Christopher
One more thought, the BO and I had a great relationship.  Often they would 
accept the yes on the plan sheet and defer to me for the right type of 
sprinklers.

Chris

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, April 22, 2014 1:19 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

Yes, we're buds.  Drink waiting next time I get to SD.  Medium interfering with 
communication.

I used to get calls it's x story apartment, 13R or 13? This is the first I've 
ever hear of such project.  Now mind you I'm talking to the sprinkler 
contractor as I was the permitting authority for sprinklers NOT the building 
department.  I ask what type of construction.  And the conversation usually 
ended right there as most didn't have any idea what type meant.   In theory 
could be type III, IV or V and be 'wood'.  I was in an old city so on remodels 
III and IV were plausible.  So yeah AHJ did NOT have all the information to 
make a determination.  I'd ask what the code sheet said and they'd say there 
was none in the sprinkler package. Imagine my surprise it wasn't in the 
sprinkler package ( a little sarcasm there if it wasn't painfully obvious), AHJ 
did NOT have all the information to make a determination.  What did the BO or 
Arch say?  This is preliminary hasn't gone for permit and Arch didn't know.  
AHJ did NOT have all the information to make a determination.  Convers
 ation might go other ways, fire lanes, draft stops, attics, fire walls, blah, 
blah, blah from there with the same result, AHJ did NOT have all the 
information to make a determination.  Believe me I tried to help but AHJ did 
NOT have all the information to make a determination.

If it ain't in the BO's office for review the BO probably did NOT have all the 
information to make a determination.  A phone call from a sprinkler contractor 
who doesn't know the building code results in bad decision making.

I AGREE, with a PROPER Arch or FPE code analysis AND a submittal to AHJ (BO) 
NOW they have all the information to make a concurrence of the determination.  
A whole lotta stuff actually happens before this point where the AHJ did NOT 
have all the information to make a determination.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Steve 
Leyton
Sent: Tuesday, April 22, 2014 12:47 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

Chris:

You know we're buds, right?  Good, 'cause that's just regoddamnediculous.
Many AHJ's don't have all the information ...???   TFB - they owe their 
customers the professional service to acquire and apply that information.   You 
wanna be sued into oblivion after a fire loss?   Do the code analysis apart 
from the enforcing agency (especially if someone can show evidence later of 
correspondence or opinion by the AHJ that maybe it should have been a different 
basis of design) and then prosecute your work based on that independent 
opinion.

I agree that the architect is in responsible charge and typically they do a 
code analysis.  But they very often simply put Sprinklers - Yes or words to 
that effect into the note block.  It says in the code which design to use and 
if the Architect can't or won't answer, then the BO should have the final say.  
Legally, in most cities and states, they do have the final say.

SML






-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, April 22, 2014 10:41 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I agree Arch is better to ask.  As a sprinkler contractor you probably don't 
have all the information to ask correctly.  Many AHJ's don't have all the 
information either.  I've seen many a project go forward on this issue long 
before an AHJ sees it. And if you call the fire marshal because that's who the 
sprinkler permit is through probably the building official approved the type of 
sprinkler.  I was an AHJ for a long time and wouldn't answer.  I'd ask you what 
the Arch said and the building official agreed to.  If I discovered a problem 
later I took it up with the building official. When I was an contractor I sure 
drove a lot of Arch's nuts asking.  And yes they rarely knew the answer.  We'd 
talk it out and caveat the bid.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Ed Kramer
I too have seen this more than once.  About to start on a motel where the
architect took an allowance for increased building size (thus requiring a 13
system), but the project engineer specified a 13R system.  When they get
that worked out, I'll start design.

Ed Kramer
Lawrence, KS

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Travis
Mack
Sent: Tuesday, April 22, 2014 1:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

Agree as well.  I am no IBC expert, but I do know a couple instances where
the architect can take an allowance and it drives the system to
903.3.1.1 instead of 903.3.1.2 of the IBC.  I always check these on all
projects where 13R may be applicable.  If I find what I feel is an error, I
will call the architect and point out my concerns.  I can't tell you how
many times the architectural firms say they were unaware of the difference
in those two sections.

My first check is to always go with the code study analysis and then if it
doesn't make sense, I throw it back to the architect and make them do the
final determination.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

On 4/22/2014 10:59 AM, Parsley Consulting wrote:
 I have to agree with Steve.  There has been many a multi-family 
 project cross my plan review table with the system designed to NFPA 
 13R because the architect called it out on the drawings, while also 
 taking several allowances for a fully sprinklered building.  Thanks to 
 Steve, and a couple of others, I'm now well aware of the limitations 
 in the IBC (CBC out here), which allow that to be done only if the 
 design of the system conformed to NFPA 13.  Some pretty high profile 
 architectural firms have made that error, stamped and sealed their 
 drawings.

 A significant number of AHJ's don't seem to know that's the case, at 
 least based on the training classes I've attended and taught.  More's 
 the pity.

 Ken


 On 4/22/2014 10:46 AM, Steve Leyton wrote:
 Chris:

 You know we're buds, right?  Good, 'cause that's just 
 regoddamnediculous.Many AHJ's don't have all the information 
 ...???   TFB - they owe their customers the professional service to 
 acquire and apply that information. You wanna be sued into oblivion 
 after a fire loss?   Do the code analysis apart from the enforcing 
 agency (especially if someone can show evidence later of 
 correspondence or opinion by the AHJ that maybe it should have been a 
 different basis of design) and then prosecute your work based on that 
 independent opinion.

 I agree that the architect is in responsible charge and typically 
 they do a code analysis.  But they very often simply put Sprinklers
 - Yes or words to that effect into the note block.  It says in the 
 code which design to use and if the Architect can't or won't answer, 
 then the BO should have the final say.  Legally, in most cities and 
 states, they do have the final say.

 SML





 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Cahill, Christopher
 Sent: Tuesday, April 22, 2014 10:41 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: RE: NFPA-13R or NFPA-13?

 I agree Arch is better to ask.  As a sprinkler contractor you 
 probably don't have all the information to ask correctly.  Many AHJ's 
 don't have all the information either.  I've seen many a project go 
 forward on this issue long before an AHJ sees it. And if you call the 
 fire marshal because that's who the sprinkler permit is through 
 probably the building official approved the type of sprinkler.  I was 
 an AHJ for a long time and wouldn't answer.  I'd ask you what the 
 Arch said and the building official agreed to.  If I discovered a 
 problem later I took it up with the building official. When I was an 
 contractor I sure drove a lot of Arch's nuts asking.  And yes they 
 rarely knew the answer.  We'd talk it out and caveat the bid.

 Chris Cahill, PE*
 Associate Fire Protection Engineer
 Burns  McDonnell
 Phone:  952.656.3652
 Fax:  952.229.2923
 ccah...@burnsmcd.com
 www.burnsmcd.com
 *Registered in: MN


 Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work 
 For




 -Original Message-
 From: sprinklerforum-boun...@lists.firesprinkler.org
 [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of 
 Forest Wilson
 Sent: Tuesday, April 22, 2014 11:39 AM
 To: sprinklerforum@lists.firesprinkler.org
 Subject: Re: NFPA-13R or NFPA-13?

 I ask the Architect.
 The problem with asking the AHJ is that they can change their mind 
 later.
 In Ohio, most of their approval stamps have an exception clause.
 Ask the Architect, let the Architect ask the AHJ.
 Then if the AHJ changes their mind, the Architect is caught

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Steve Leyton
That's what I was alluding to and that Ken reiterated.  You can take
credit with a 13R for certain things that require the building to be
furnished throughout with an approved automatic fire sprinkler system
but increase in height and area are not among those certain things and
that mistake is made ALL the time.   The committee has been wrestling
with how to deal with mixed occupancies for three cycles.  Once upon a
time it was simple:  if the building is classified as multiple
occupancies, then it was a 13 (or should have been).  Now we have to
determine if residential is the predominant use or not.  If it is,
such as a hotel, then the other uses such as A, B and S2 occupancies are
considered accessory and you design per 13R but protect areas outside
the dwelling per 13.  AS PRESCRIBED IN 13R.

But if you read A.1.1 in the 2013 edition of 13R, you will see a
provision that states, Where buildings of mixed use can be totally
separated so that the residential portion is considered a separate
building under the local code, NFPA 13R can be used in the residential
portion while NFPA 13 is used in the rest of the building.   This part
requires that all the stakeholders put on their thinking caps and
determine 1) Do the occupancy separations qualify as building
separations and, 2) Is it cost-effective to offer up separate bases of
design in such a circumstance.  I would postulate that in 99% of cases,
it's just a helluva lot easier to treat mixed uses as 13 and primarily
residential uses as 13R.  13R offers a much wider range of flexibility
than many users of the standard are aware of, and includes provisions
for more conservative design in the non-dwelling areas.  There have been
some roof burn-offs in Type 5 buildings that prompted proposals to
require sprinklers in combustible concealed spaces the last two cycles,
but those proposals were rejected.   The life-safety record of 13R
systems is still exemplary, even in buildings with a certain amount of
non-residential uses ... 

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 13D/13R Technical Committee on Residential
Sprinkler Systems.

SML

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ed
Kramer
Sent: Tuesday, April 22, 2014 11:26 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

I too have seen this more than once.  About to start on a motel where
the architect took an allowance for increased building size (thus
requiring a 13 system), but the project engineer specified a 13R system.
When they get that worked out, I'll start design.

Ed Kramer
Lawrence, KS

-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of
Travis Mack
Sent: Tuesday, April 22, 2014 1:04 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: NFPA-13R or NFPA-13?

Agree as well.  I am no IBC expert, but I do know a couple instances
where the architect can take an allowance and it drives the system to
903.3.1.1 instead of 903.3.1.2 of the IBC.  I always check these on all
projects where 13R may be applicable.  If I find what I feel is an
error, I will call the architect and point out my concerns.  I can't
tell you how many times the architectural firms say they were unaware of
the difference in those two sections.

My first check is to always go with the code study analysis and then if
it doesn't make sense, I throw it back to the architect and make them do
the final determination.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:tm...@mfpdesign.com

On 4/22/2014 10:59 AM, Parsley Consulting wrote:
 I have to agree with Steve.  There has been many a multi-family 
 project cross my plan review table with the system designed to NFPA 
 13R because the architect called it out on the drawings, while also 
 taking several allowances for a fully sprinklered building.  Thanks to

 Steve, and a couple of others, I'm now well aware of the limitations 
 in the IBC (CBC out here), which allow that to be done only if the 
 design of the system conformed to NFPA 13.  Some pretty high profile 
 architectural firms have made that error, stamped and sealed their 
 drawings.

 A significant number of AHJ's don't seem to know that's the case, at 
 least based on the training classes I've attended and taught.  More's 
 the pity.

 Ken


 On 4/22/2014 10:46 AM, Steve Leyton wrote:
 Chris:

 You know we're buds, right?  Good, 'cause that's just 
 regoddamnediculous.Many AHJ's don't have all the information 
 ...???   TFB - they owe their customers the professional service to 
 acquire and apply that information. You wanna be sued into oblivion 
 after a fire loss?   Do the code analysis apart from the enforcing 
 agency (especially if someone can show evidence later

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Pete Schwab
A heads up in regards to the 2016 edition of NFPA 13R. The committee has made a 
pretty drastic change that will significantly assist in determining if and 
when NFPA 13R applies. This was done in the First Draft phase and is currently 
open for Public Comment.

Here is the language from A.1.1 as how it appears in the First Draft Report. 
See the end sentences in paragraph #1.





NFPA 13R is appropriate for use as an alternative to NFPA 13 only in those 
residential occupancies, as defined in this standard, up to and including four 
aboveground stories in height, and limited to buildings that are 60 ft (18 m) 
or less in height above grade plane, which is consistent with limits 
established by model building codes for buildings of Type V construction. The 
height of a building above grade plane is determined by model building codes, 
which base the height on the average height of the highest roof surface above 
grade plane. For further information on the building height story limits, see 
model building codes.

Buildings that contain multiple occupancies (either separated or 
non-separated), accessory occupancies or incidental uses are often subject to 
special rules that may restrict the use of NFPA 13R. Refer to the adopted 
building code to determine whether such restrictions are applicable.

The criteria in this standard are based on full-scale fire tests of rooms 
containing typical furnishings found in residential living rooms, kitchens, and 
bedrooms. The furnishings were arranged as typically found in dwelling units in 
a manner similar to that shown in Figure A.1.1(a), Figure A.1.1(b), and Figure 
A.1.1(c). Sixty full-scale fire tests were conducted in a two-story dwelling in 
Los Angeles, California, and 16 tests were conducted in a 14 ft (4.3 m) wide 
mobile home in Charlotte, North Carolina. Sprinkler systems designed and 
installed according to this standard are expected to prevent flashover within 
the compartment of origin where sprinklers are installed in the compartment. A 
sprinkler system designed and installed according to this standard cannot, 
however, be expected to completely control a fire involving fuel loads that are 
significantly higher than average for dwelling units [10 lb/ft2 (49 kg/m2)], 
configurations of fuels other than those with typical resi
 dential occupancies, or conditions where the interior finish has an unusually 
high flame spread index (greater than 225).

To be effective, sprinkler systems installed in accordance with this standard 
need to open the sprinklers closest to the fire before the fire exceeds the 
ability of the sprinkler discharge to extinguish or control the fire. 
Conditions that allow the fire to grow beyond that point before sprinkler 
activation or that interfere with the quality of water distribution can produce 
conditions beyond the capabilities of the sprinkler system described in this 
standard. Unusually high ceilings or ceiling configurations that tend to divert 
the rising hot gases from sprinkler locations or change the sprinkler discharge 
pattern from its standard pattern can produce fire conditions that cannot be 
extinguished or controlled by the systems described in this standard.

NFPA 13R references NFPA 13 in many aspects (hanging and bracing, design 
densities and spacing outside of dwelling unit, painting and finish of 
sprinklers, welding, etc.). If this standard does not specifically address a 
situation, NFPA 13 is a good resource that can be utilized by the installer and 
the authority having jurisdiction for a solution. It is not the intent of this 
standard to require compliance with NFPA 13 when NFPA 13R is silent on a 
subject. Only AHJ approval should be required.





There is a committee input that adds language into A.1.1 discussing separated 
and non-separated occupancies, podiums, incidental occupancies and where to 
find that info in the (2) Model Building codes. That task group spent several 
days developing the language. However, the committee felt that the installation 
standard should not say when, just how. I am in disagreement but was in the 
minority. End result: More NFPA 13 systems throughout entire buildings because 
fire AHJ's will not be versed in how to navigate the building codes and will 
simply insist on the better life safety.


It should be recognized that the above is my opinion only, and has not been 
processed as a formal interpretation in accordance with the NFPA Regulations 
Governing Committee Projects and should therefore not be considered, nor relied 
upon, as the official position of the NFPA, nor any of their technical 
committees.



Peter Schwab

VP of Purchasing  Engineering Technologies



Wayne Automatic Fire Sprinklers Inc.

222 Capitol Court

Ocoee, Fl 34761



Mobile: (407) 468-8248

Direct: (407) 877-5570

Fax: (407) 656-8026



www.waynefire.com







We're hiring great people at all of our locations!  Please check out our 
website for the details!





-Original

RE: NFPA-13R or NFPA-13?

2014-04-22 Thread Cahill, Christopher
Let me play devil's advocate for a second. Why does NFPA 13x committees deal 
with this? Most (not all) of us in the US work with I codes and it's rather 
clear to me what to use.  I don't work in NFPA 5000 but ASSUME it's similar.  
IBC tells me which variant to use, NFPA 13x only tells me how to do it. 
(Avoiding the vernacular code/standard out of respect for Greenman.)  So the 
NFPA Committees can change or say anything they want and it's pointless.  Hell, 
they could say 13D for residential high-rises and NFPA 13D Committee would have 
little they could do about it.

Not that dissimilar to NFPA 409 and IBC 412.  In 409 ch. 5 they have all sorts 
of requirements for a building that are not required if following the basics of 
IBC.  For example, rated walls are not required in many hangars if you meet the 
height and area limits for mixed use. Don't need to protect the columns and 
don't need draft curtains, etc. True, a few places might legally adopt 409 in 
its entirety or you get there from insurance but that's not routine.

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns  McDonnell
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com
*Registered in: MN


Proud to be #14 on FORTUNE's 2014 List of 100 Best Companies to Work For





-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org 
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Pete Schwab
Sent: Tuesday, April 22, 2014 3:06 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: NFPA-13R or NFPA-13?

A heads up in regards to the 2016 edition of NFPA 13R. The committee has made a 
pretty drastic change that will significantly assist in determining if and 
when NFPA 13R applies. This was done in the First Draft phase and is currently 
open for Public Comment.

Here is the language from A.1.1 as how it appears in the First Draft Report. 
See the end sentences in paragraph #1.





NFPA 13R is appropriate for use as an alternative to NFPA 13 only in those 
residential occupancies, as defined in this standard, up to and including four 
aboveground stories in height, and limited to buildings that are 60 ft (18 m) 
or less in height above grade plane, which is consistent with limits 
established by model building codes for buildings of Type V construction. The 
height of a building above grade plane is determined by model building codes, 
which base the height on the average height of the highest roof surface above 
grade plane. For further information on the building height story limits, see 
model building codes.

Buildings that contain multiple occupancies (either separated or 
non-separated), accessory occupancies or incidental uses are often subject to 
special rules that may restrict the use of NFPA 13R. Refer to the adopted 
building code to determine whether such restrictions are applicable.

The criteria in this standard are based on full-scale fire tests of rooms 
containing typical furnishings found in residential living rooms, kitchens, and 
bedrooms. The furnishings were arranged as typically found in dwelling units in 
a manner similar to that shown in Figure A.1.1(a), Figure A.1.1(b), and Figure 
A.1.1(c). Sixty full-scale fire tests were conducted in a two-story dwelling in 
Los Angeles, California, and 16 tests were conducted in a 14 ft (4.3 m) wide 
mobile home in Charlotte, North Carolina. Sprinkler systems designed and 
installed according to this standard are expected to prevent flashover within 
the compartment of origin where sprinklers are installed in the compartment. A 
sprinkler system designed and installed according to this standard cannot, 
however, be expected to completely control a fire involving fuel loads that are 
significantly higher than average for dwelling units [10 lb/ft2 (49 kg/m2)], 
configurations of fuels other than those with typical resi
   dential occupancies, or conditions where the interior finish has an 
unusually high flame spread index (greater than 225).

To be effective, sprinkler systems installed in accordance with this standard 
need to open the sprinklers closest to the fire before the fire exceeds the 
ability of the sprinkler discharge to extinguish or control the fire. 
Conditions that allow the fire to grow beyond that point before sprinkler 
activation or that interfere with the quality of water distribution can produce 
conditions beyond the capabilities of the sprinkler system described in this 
standard. Unusually high ceilings or ceiling configurations that tend to divert 
the rising hot gases from sprinkler locations or change the sprinkler discharge 
pattern from its standard pattern can produce fire conditions that cannot be 
extinguished or controlled by the systems described in this standard.

NFPA 13R references NFPA 13 in many aspects (hanging and bracing, design 
densities and spacing outside of dwelling unit, painting and finish of 
sprinklers, welding, etc.). If this standard does

Re: NFPA-13R or NFPA-13?

2014-04-22 Thread Roland Huggins
The 13R technical committee first addressed it because the IBC didn’t really do 
a very good job with it several cycles ago.  Actually it should have been the 
13 TC since when does a lower level of protection standard dictate combining 
with a higher level system (but that’s s different story).  

I attempted to have the annex of 13R changed by a TIA since it is wrong 
(regarding must be a separate building).  The starting point in wrapping ones 
mind around combining 13 and 13R in a single building is to realize that the 
IBC allows some combinations of occupancies to have a portion of the building 
protected with a 13 system and another portion to have NO PROTECTION AT ALL. 
From that point on, it’s easy to accept that some conditions exist where part 
of the building is 13 and part is 13R.  Business continuity is NOT a concern of 
the code like it is within the 13 mindset (so burning off the roof is ok if the 
top floor is residential but the lower floors are commercial).  A vague rule of 
thumb is that depending upon the occupancies (since some occupancies require 
sprinklers through the BUILDING per 903.1.1) if the building is classified as a 
Separated Mixed occupancies it COULD allow both types of systems within the 
single building.

I’m surprised that this group has a problem with this issue since I assume 
everyone has a FREE subscription to Sprinkler Age.  We did an article in 2013 
on it.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.   ---  Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Apr 22, 2014, at 1:25 PM, Cahill, Christopher ccah...@burnsmcd.com wrote:

 Let me play devil's advocate for a second. Why does NFPA 13x committees deal 
 with this? Most (not all) of us in the US work with I codes and it's rather 
 clear to me what to use.  I don't work in NFPA 5000 but ASSUME it's similar.  
 IBC tells me which variant to use, NFPA 13x only tells me how to do it. 
 (Avoiding the vernacular code/standard out of respect for Greenman.)  So the 
 NFPA Committees can change or say anything they want and it's pointless.  
 Hell, they could say 13D for residential high-rises and NFPA 13D Committee 
 would have little they could do about it.
 
 Not that dissimilar to NFPA 409 and IBC 412.  In 409 ch. 5 they have all 
 sorts of requirements for a building that are not required if following the 
 basics of IBC.  For example, rated walls are not required in many hangars if 
 you meet the height and area limits for mixed use. Don't need to protect the 
 columns and don't need draft curtains, etc. True, a few places might legally 
 adopt 409 in its entirety or you get there from insurance but that's not 
 routine.
 
 Chris Cahill, PE*
 Associate Fire Protection Engineer

___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


NFPA-13R or NFPA-13?

2014-04-21 Thread George Medina Jr


Forum,
Can anyone please add there 2 cents in and help clarify when to classify as a 
13 system versus a 13R
I have a project that consist of 3 stories with an occupancy of R2/S2 and 
Construction Type VA. The project is lay ed out like a horse shoe
with 3 sides  and a corridor running down the middle from  1 required stairwell 
to another on the opposite end, with a court yard in the middle. There are 
private garages around the perimeter of the building (which all have access 
from a common 1st floor corridor only) All the Garages have a 2 hour separation 
between them and the 2nd level  residential units and the 1st floor corridor. 
There are residential units on the 1st floor (opposite the garages) facing the 
court yard.

I figured the Garage calculations shall conform to NFPA-13, based on NFPA-13R 
(2013ed.) Sec. 7.3.1. My question is if the building can be classified as a 13R 
(with garage areas calced at NFPA-13) or should it be classified as a NFPA-13 
with dwelling units  residential heads (calculations based on the greater of 
the area/density @ .10 or the head listing). If not, what is the determining 
factor or the threshold.





George Medina Jr. 
Mobile: 323-906-5701


___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


Re: NFPA-13R or NFPA-13?

2014-04-21 Thread IPA
Sounds like a 13R to me.

I'm not so sure about the assessment of 7.3.1 criteria for the garage - I
wouldn't think a two hour separation is enough to classify the garages as a
'separate building'. That's usually when you have residential over a
parking garage structure - think podium style. I would be looking more into
7.3.2.

It sounds like you're on the right track - I would double check your local
ammendments, the architect's code analysis and any specs or insurance
requirements that may require more than 13r.




On Mon, Apr 21, 2014 at 10:17 PM, George Medina Jr fireg...@aol.com wrote:



 Forum,
 Can anyone please add there 2 cents in and help clarify when to classify
 as a 13 system versus a 13R
 I have a project that consist of 3 stories with an occupancy of R2/S2 and
 Construction Type VA. The project is lay ed out like a horse shoe
 with 3 sides  and a corridor running down the middle from  1 required
 stairwell to another on the opposite end, with a court yard in the middle.
 There are private garages around the perimeter of the building (which all
 have access from a common 1st floor corridor only) All the Garages have a 2
 hour separation between them and the 2nd level  residential units and the
 1st floor corridor. There are residential units on the 1st floor (opposite
 the garages) facing the court yard.

 I figured the Garage calculations shall conform to NFPA-13, based on
 NFPA-13R (2013ed.) Sec. 7.3.1. My question is if the building can be
 classified as a 13R (with garage areas calced at NFPA-13) or should it be
 classified as a NFPA-13 with dwelling units  residential heads
 (calculations based on the greater of the area/density @ .10 or the head
 listing). If not, what is the determining factor or the threshold.





 George Medina Jr.
 Mobile: 323-906-5701


 ___
 Sprinklerforum mailing list
 Sprinklerforum@lists.firesprinkler.org

 http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




On Mon, Apr 21, 2014 at 10:17 PM, George Medina Jr fireg...@aol.com wrote:



 Forum,
 Can anyone please add there 2 cents in and help clarify when to classify
 as a 13 system versus a 13R
 I have a project that consist of 3 stories with an occupancy of R2/S2 and
 Construction Type VA. The project is lay ed out like a horse shoe
 with 3 sides  and a corridor running down the middle from  1 required
 stairwell to another on the opposite end, with a court yard in the middle.
 There are private garages around the perimeter of the building (which all
 have access from a common 1st floor corridor only) All the Garages have a 2
 hour separation between them and the 2nd level  residential units and the
 1st floor corridor. There are residential units on the 1st floor (opposite
 the garages) facing the court yard.

 I figured the Garage calculations shall conform to NFPA-13, based on
 NFPA-13R (2013ed.) Sec. 7.3.1. My question is if the building can be
 classified as a 13R (with garage areas calced at NFPA-13) or should it be
 classified as a NFPA-13 with dwelling units  residential heads
 (calculations based on the greater of the area/density @ .10 or the head
 listing). If not, what is the determining factor or the threshold.





 George Medina Jr.