Mark Newton wrote:
> It should be made completely clear during customer onboarding that the 
> facility operator can temporarily shut down a power feed at any time. 
> Advance warning should be desirable but optional.

Whilst I have some sympathy for Mark's position given the preceding 
discussion, so that colocation providers reading this list are completely 
clear: the common expectation of your network operator clients is that 
advance notice is required for planned maintenance; notice is not merely 
desirable nor optional.  If you have a different view then this should be 
discussed during contract negotiations, not later during onboarding.

Sending staff and spares to a colo site to investigate a multiple power 
supply failure is not cheap in itself, and has a high opportunity cost in 
that staff member abandoning their planned work for that half a day. 
Without prior notice these costs and possible client disappointments are 
incurred more often than they need be.

Network operators seek to manage the hazards to their network.  One colo 
doing power works is an everyday event. Two colos unknowingly doing power 
works simultaneously is a different level of risk again.  Without prior 
notification an operator cannot know what the level of risk to their 
network is: what is not known cannot be managed.

Regards, glen
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-12 Thread Jared Hirst
I think it’s more the fact that they will be losing power for 8 hours on the A 
side.

But yes, always best practice to have A and B, however, this is not always 
suitable in certain circumstances. For example in one facility we have 
dedicated servers in, we have A only. We know the risks of it as does the 
clients buying those services.

Simon, thanks for the explanation. I guess this is a decision you take as a DC 
operator that is again, not the law, but a OH & S precaution. As none of those 
standards advise that the boards need to be de energised to perform the work.

Both Global Switch and Equinix do this live or without interruption, as both 
sites that I have been in have never had an A or B interruption during annual 
maintenance.

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: 
jared.hi...@serversaustralia.com.au<mailto:jared.hi...@serversaustralia.com.au>

From: AusNOG  on behalf of Mark Smith 

Sent: Saturday, August 12, 2017 12:53:41 PM
To: Mark Newton
Cc: ; ausnog-requ...@lists.ausnog.net; 
c...@cpkws.com.au
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

+1

At least in this situation you'll likely get advanced notice your power is 
going to go away. When your gear has or sufferers from an unexpected PSU or 
other failure, you don't.

This fundamentally goes to the difference between what availability you happen 
to get verses what availability you design and engineer to be assured to get.

You'll eventually pay the price if you assume coincidental 100% past 
availability guaratees future 100% availability. It's pretending failure never 
occurs.

If you think you are or would be paying a lot for redundancy, you probably 
haven't calculated the cost of down time of the service (e.g., lost customer 
sales, staff sitting around being paid yet unable to do their jobs). That cost 
of down time is likely to be well in excess of any redundancy costs.

Technical infrastructure redundancy is a form of insurance. Would you go 
without theft, fire and other types of business insurance just because it has 
never happened to you before?



On 11 Aug. 2017 04:54, "Mark Newton" 
mailto:new...@atdot.dotat.org>> wrote:
As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the facility 
operator can temporarily shut down a power feed at any time. Advance warning 
should be desirable but optional.

If there is risk involved in doing that, it’s your job to mitigate it. The 
facility operator doesn’t know which bits of equipment in your tenancy are 
critical, and they’ve already told you to dual-feed where possible and use a 
rack-mount ATS for single-corded equipment.

Power work should be done during business hours, because it’s almost impossible 
to get emergency support or source replacement equipment out of hours.

If it isn’t safe to take a power feed offline during business hours, then you 
(the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield 
> mailto:nathan.brookfi...@simtronic.com.au>>
>  wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium price for services 
> of this fashion you expect a certain level of service.  There is a risk no 
> matter what when switching from power supplies taking extra load they would 
> not usually take as well as swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to be ignored 
> especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG 
> [mailto:ausnog-boun...@lists.ausnog.net<mailto:ausnog-boun...@lists.ausnog.net>]
>  On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>; 
> ausnog-requ...@lists.ausnog.net<mailto:ausnog-requ...@lists.ausnog.net>
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
> August
>
>
>
> On 8/10/2017 10:13 AM, 
> ausnog-requ...@lists.ausnog.net<mailto:ausnog-requ...@lists.ausnog.net> wrote:
>> From the latest update today, It appears that most of the works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is involved
>> with these devices, which is why it is crucial to receive accurate 
>> information about any pending outages or upgrades to the NextDC DataCentres 
>> which affect services.
> If these services are mission critical then you really should have duel PSU 
> units, so that when one feed gets taken offline the equipment automatically 
> switches to the other feed. They won't just di

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Mark Smith
+1

At least in this situation you'll likely get advanced notice your power is
going to go away. When your gear has or sufferers from an unexpected PSU or
other failure, you don't.

This fundamentally goes to the difference between what availability you
happen to get verses what availability you design and engineer to be
assured to get.

You'll eventually pay the price if you assume coincidental 100% past
availability guaratees future 100% availability. It's pretending failure
never occurs.

If you think you are or would be paying a lot for redundancy, you probably
haven't calculated the cost of down time of the service (e.g., lost
customer sales, staff sitting around being paid yet unable to do their
jobs). That cost of down time is likely to be well in excess of any
redundancy costs.

Technical infrastructure redundancy is a form of insurance. Would you go
without theft, fire and other types of business insurance just because it
has never happened to you before?



On 11 Aug. 2017 04:54, "Mark Newton"  wrote:

As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the
facility operator can temporarily shut down a power feed at any time.
Advance warning should be desirable but optional.

If there is risk involved in doing that, it’s your job to mitigate it. The
facility operator doesn’t know which bits of equipment in your tenancy are
critical, and they’ve already told you to dual-feed where possible and use
a rack-mount ATS for single-corded equipment.

Power work should be done during business hours, because it’s almost
impossible to get emergency support or source replacement equipment out of
hours.

If it isn’t safe to take a power feed offline during business hours, then
you (the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield <
nathan.brookfi...@simtronic.com.au> wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium price for
services of this fashion you expect a certain level of service.  There is a
risk no matter what when switching from power supplies taking extra load
they would not usually take as well as swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to be ignored
especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad
Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -,
15th August
>
>
>
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>> From the latest update today, It appears that most of the works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is involved
>> with these devices, which is why it is crucial to receive accurate
information about any pending outages or upgrades to the NextDC DataCentres
which affect services.
> If these services are mission critical then you really should have duel
PSU units, so that when one feed gets taken offline the equipment
automatically switches to the other feed. They won't just disconnect both
feeds at once because that would be stupid and if the entire DC was offline
for too much time then that would put the owners in a rather awkward
situation legally, as after say 8 or 10 hours of downtime it wouldn't be
good for the owners lets put it that way.
> If the single PSU units are a part of a customers co-located equipment
then really your terms of service agreement should exclude liability under
your maintenance clauses.
> I don't understand why anyone would be using single PSU equipment in a DC
environment now a days when you can buy refurbished servers that come with
two PSU as standard even when you buy them without raid.
> Also for anything that is really really mission critical you should have
it hosted in multiple datacentres anyway so if something stupid does happen
that you can't control you at least still have services online as the load
balanced services would just switch.
> Regards Chad.
>
> --
> Chad Kelly
> Manager
> CPK Web Services
> Phone 03 5273 0246
> Web www.cpkws.com.au
>
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Shaun McGuane
Hi Simon,

Thank you for getting back to the group we appreciate your input :)

We are aware of the legal requirement to complete the checks every 5 years. 
Generally as we have seen in the industry
thermals are taken of the boards to check for any hot spots which are then  
rectified, by a means of a maintenance window.

If the hot spot is behind a breaker or within a breaker then an outage is a 
requirement to either replace the breaker or tighten
Any loose connections, however if bus bars need to be tightened we have seen 
many cases of these being completed live using
the appropriate OH&S safety equipment and Safe Work Method Statement.

For sake of clarification, and from what you have explained, NextDC seem to be 
taking the safe route by de-energising
The boards rather than work on them live. Is this because the design of the 
boards does not allow enough room for a
safe work space and you deem this an OH&S high risk?

The law component is the actual testing and not the outage itself.

Kind Regards
Shaun McGuane



From: Simon Cooper [mailto:simon.coo...@nextdc.com]
Sent: Friday, 11 August 2017 11:14 PM
To: Shaun McGuane 
Cc: ausnog@lists.ausnog.net
Subject: RE: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

Hi Shaun,

Happy to clarify, and sorry it's taken me a while to get back to the group.

Under the Electrical Safety Act compliance with AS3000 is mandatory.

Under AS3000, and specifically AS3439, the owner of an electrical system 
(NEXTDC in this case) is responsible to institute a system of maintenance (aka 
planned maintenance program).   Through that system the manufacturers 
recommendations should be addressed as well as the recommendations of AS2467.  
It specifically goes on to state that "Doing so will minimise the risk of 
injury or breakdown and any consequent human suffering and/or loss of supply."

AS2467 suggests that indoor switchgear be examined (examination is more than 
inspection) at 5 year intervals.  Examination includes ensuring that bus mounts 
and restraints are adequately torqued.

Typical circuit breakers O&M manual advise that the devices are examined and 
tested in their 5th year of operation.

Clearly complying to the above is best practice.  Equally, no responsible owner 
would want to be in the position of having failed to comply, then to have 
something happen and have to explain how they had made all reasonable efforts 
to mitigate risk.

In order to comply, both to examine the switchgear and to complete the circuit 
breaker manufacturer's advice, the switch board needs to be de-energised.   
WH&S practises dictate this, as do other parts of AS3000.   There are certain 
circumstances under which work can be done on or near live boards, and 
certainly inspection is one of those - but examination is not and neither is 
testing a circuit breaker.

Not quite as punchy as one of the ten commandments, but fundamentally - it's 
all based on safety.

Trust that helps.   As mentioned earlier, happy to discuss offline.  Have a 
great weekend everyone.

Best,
Simon






Simon Cooper
Chief Operating Officer
Direct: +61 7 3177 4721
Mobile: +61 488 235 624
Email: simon.coo...@nextdc.com<mailto:simon.coo...@nextdc.com>

NEXTDC (ASX: NXT)
www.nextdc.com<http://www.nextdc.com>
From: Shaun McGuane [mailto:sh...@rackcentral.com]
Sent: Friday, 11 August 2017 4:58 PM
To: Simon Cooper mailto:simon.coo...@nextdc.com>>
Cc: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>
Subject: RE: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

Hi Simon,

For the sake of clarification and not to question NextDC's position, would you 
mind sharing with us the
Explanation of the Law that you are referring to with your response from 
yesterday?

As if you are the only datacentre following this law then others need to follow 
suite and it would be good
To understand if something is not being done that other providers are legally 
bound to do.

Kind Regards
Shaun McGuane


From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Jared Hirst
Sent: Friday, 11 August 2017 10:17 AM
To: Mark Newton mailto:new...@atdot.dotat.org>>; Nathan 
Brookfield 
mailto:nathan.brookfi...@simtronic.com.au>>
Cc: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>; 
ausnog-requ...@lists.ausnog.net<mailto:ausnog-requ...@lists.ausnog.net>; Chad 
Kelly mailto:c...@cpkws.com.au>>
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

Mark,

Totally agree. I would just like to know what law Simon was referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: 
jared.hi...@serversaustralia.com.au<mailto:jared.hi...@serversaustralia.com.au>

From: AusNOG 
mailto:ausnog-boun...@lists.ausnog.net>> on 
behalf of Mark Newton mailto:new...@atdot.dota

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Matt Perkins
It would be really nice if the next DC engineer responsible posted a 
nice Blog post with the technical details. The vacuum is causing  more 
damage then it's worth i would think at this point.



Matt.



On 11/8/17 10:34 pm, Chad Kelly wrote:


Hi I did post the following link to the list the other day.

http://www.ohsrep.org.au/faqs/ohs-reps-@-work-electrical-safety-/electrical-equipment-what-are-the-lawsguidelines 
but this could also just be a NextDC OH&S policy as well, as 
regulation from government in the tech space can be interesting as 
they are not always up to date with stuff.




On 8/11/2017 10:05 PM, Sam Silvester wrote:

Hey Chad,

That's a pretty general site you're pointing to.

Could you possibly be a bit more specific? Clicked through a couple 
of links on it but everything was very high level.


As I noted elsewhere I am in SA but my employer is national so 
keeping across all this is never a bad thing.


Cheers,

Sam

On Friday, 11 August 2017, Chad Kelly <mailto:c...@cpkws.com.au>> wrote:


It comes under the Victorian Occupational Health and safety Act
2004 from the bit of reading I did yesterday.

https://www.worksafe.vic.gov.au/laws/ohs
<https://www.worksafe.vic.gov.au/laws/ohs>


On 8/11/2017 10:17 AM, Jared Hirst wrote:

Mark,

Totally agree. I would just like to know what law Simon was
referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au


*From:* AusNOG 

on behalf of Mark Newton 

*Sent:* Friday, August 11, 2017 4:54:10 AM
*To:* Nathan Brookfield
*Cc:* ausnog@lists.ausnog.net
;
ausnog-requ...@lists.ausnog.net
    ;
    Chad Kelly
    *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
Maintenance -, 15th August
As someone who has run colo facilities before:

It should be made completely clear during customer onboarding
that the facility operator can temporarily shut down a power
feed at any time. Advance warning should be desirable but optional.

If there is risk involved in doing that, it’s your job to
mitigate it. The facility operator doesn’t know which bits of
equipment in your tenancy are critical, and they’ve already told
you to dual-feed where possible and use a rack-mount ATS for
single-corded equipment.

Power work should be done during business hours, because it’s
almost impossible to get emergency support or source replacement
equipment out of hours.

If it isn’t safe to take a power feed offline during business
hours, then you (the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield


wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium
price for services of this fashion you expect a certain level of
service. There is a risk no matter what when switching from
power supplies taking extra load they would not usually take as
well as swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to
be ignored especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net
]
On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net
;
    ausnog-requ...@lists.ausnog.net

> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power
Maintenance -, 15th August
>
>
>
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net

wrote:
>> From the latest update today, It appears that most of the
works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is
involved
>> with these devices, which is why it is crucial to receive
accurate information about any pending outages or upgrades to
the NextDC DataCentres which affect services.
> If these services are mission critical then you really should
have duel PSU units, so that when one feed gets taken offline
the equipment automatically switches to the other feed. They
won't just disconnect both feeds at once because that would be
stupid and if the entire DC was offline for too much time then
that would put the owners in a rather awkward situation legally,
as after say 8 or 10 hours of downtime it wouldn't be good for
the owners lets put it that way.
> If the single PSU units are a part of a customers co-located
equipment then really your terms of service

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Jared Hirst
I don’t buy it.

HV lines / boards / STS’s are worked on live all the time.

Infact Equinix had maintenance this morning I believe or over this weekend on 
the A1 power and there was no disruptions.

The issue I had was the way that it was ‘law’ to actually do this, not the OHS 
part.

Someone should tell that to these guys about the OHS part ;) imagine that Job!

https://youtu.be/x94BH9TUiHM

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: 
jared.hi...@serversaustralia.com.au<mailto:jared.hi...@serversaustralia.com.au>

From: Chad Kelly 
Sent: Friday, August 11, 2017 10:34:57 PM
To: Sam Silvester
Cc: Jared Hirst; Mark Newton; Nathan Brookfield; ausnog@lists.ausnog.net; 
ausnog-requ...@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August


Hi I did post the following link to the list the other day.

http://www.ohsrep.org.au/faqs/ohs-reps-@-work-electrical-safety-/electrical-equipment-what-are-the-lawsguidelines
 but this could also just be a NextDC OH&S policy as well,  as regulation from 
government in the tech space can be interesting as they are not always up to 
date with stuff.


On 8/11/2017 10:05 PM, Sam Silvester wrote:
Hey Chad,

That's a pretty general site you're pointing to.

Could you possibly be a bit more specific? Clicked through a couple of links on 
it but everything was very high level.

As I noted elsewhere I am in SA but my employer is national so keeping across 
all this is never a bad thing.

Cheers,

Sam

On Friday, 11 August 2017, Chad Kelly 
mailto:c...@cpkws.com.au>> wrote:

It comes under the Victorian Occupational Health and safety Act 2004 from the 
bit of reading I did yesterday.

https://www.worksafe.vic.gov.au/laws/ohs

On 8/11/2017 10:17 AM, Jared Hirst wrote:
Mark,

Totally agree. I would just like to know what law Simon was referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au

From: AusNOG  on behalf of Mark Newton 

Sent: Friday, August 11, 2017 4:54:10 AM
To: Nathan Brookfield
Cc: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net; Chad Kelly
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the facility 
operator can temporarily shut down a power feed at any time. Advance warning 
should be desirable but optional.

If there is risk involved in doing that, it’s your job to mitigate it. The 
facility operator doesn’t know which bits of equipment in your tenancy are 
critical, and they’ve already told you to dual-feed where possible and use a 
rack-mount ATS for single-corded equipment.

Power work should be done during business hours, because it’s almost impossible 
to get emergency support or source replacement equipment out of hours.

If it isn’t safe to take a power feed offline during business hours, then you 
(the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield 
>  wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium price for services 
> of this fashion you expect a certain level of service.  There is a risk no 
> matter what when switching from power supplies taking extra load they would 
> not usually take as well as swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to be ignored 
> especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
> August
>
>
>
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>> From the latest update today, It appears that most of the works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is involved
>> with these devices, which is why it is crucial to receive accurate 
>> information about any pending outages or upgrades to the NextDC DataCentres 
>> which affect services.
> If these services are mission critical then you really should have duel PSU 
> units, so that when one feed gets taken offline the equipment automatically 
> switches to the other feed. They won't just disconnect both feeds at once 
> because that would be stupid and if the entire DC was offline for too much 
> time then that would put the owners in a rather awkward situation legally, as 
> after say 8 o

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Chad Kelly

Hi I did post the following link to the list the other day.

http://www.ohsrep.org.au/faqs/ohs-reps-@-work-electrical-safety-/electrical-equipment-what-are-the-lawsguidelines 
but this could also just be a NextDC OH&S policy as well,  as regulation 
from government in the tech space can be interesting as they are not 
always up to date with stuff.




On 8/11/2017 10:05 PM, Sam Silvester wrote:

Hey Chad,

That's a pretty general site you're pointing to.

Could you possibly be a bit more specific? Clicked through a couple of 
links on it but everything was very high level.


As I noted elsewhere I am in SA but my employer is national so keeping 
across all this is never a bad thing.


Cheers,

Sam

On Friday, 11 August 2017, Chad Kelly <mailto:c...@cpkws.com.au>> wrote:


It comes under the Victorian Occupational Health and safety Act
2004 from the bit of reading I did yesterday.

https://www.worksafe.vic.gov.au/laws/ohs
<https://www.worksafe.vic.gov.au/laws/ohs>


On 8/11/2017 10:17 AM, Jared Hirst wrote:

Mark,

Totally agree. I would just like to know what law Simon was
referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au


*From:* AusNOG 

on behalf of Mark Newton 

*Sent:* Friday, August 11, 2017 4:54:10 AM
*To:* Nathan Brookfield
*Cc:* ausnog@lists.ausnog.net
;
ausnog-requ...@lists.ausnog.net
;
    Chad Kelly
*Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
    Maintenance -, 15th August
As someone who has run colo facilities before:

It should be made completely clear during customer onboarding
that the facility operator can temporarily shut down a power feed
at any time. Advance warning should be desirable but optional.

If there is risk involved in doing that, it’s your job to
mitigate it. The facility operator doesn’t know which bits of
equipment in your tenancy are critical, and they’ve already told
you to dual-feed where possible and use a rack-mount ATS for
single-corded equipment.

Power work should be done during business hours, because it’s
almost impossible to get emergency support or source replacement
equipment out of hours.

If it isn’t safe to take a power feed offline during business
hours, then you (the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield


wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium price
for services of this fashion you expect a certain level of
service. There is a risk no matter what when switching from power
supplies taking extra load they would not usually take as well as
swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to
be ignored especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net
]
On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net
    ;
ausnog-requ...@lists.ausnog.net
    
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power
Maintenance -, 15th August
>
>
>
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net

wrote:
>> From the latest update today, It appears that most of the
works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is
involved
>> with these devices, which is why it is crucial to receive
accurate information about any pending outages or upgrades to the
NextDC DataCentres which affect services.
> If these services are mission critical then you really should
have duel PSU units, so that when one feed gets taken offline the
equipment automatically switches to the other feed. They won't
just disconnect both feeds at once because that would be stupid
and if the entire DC was offline for too much time then that
would put the owners in a rather awkward situation legally, as
after say 8 or 10 hours of downtime it wouldn't be good for the
owners lets put it that way.
> If the single PSU units are a part of a customers co-located
equipment then really your terms of service agreement should
exclude liability under your maintenance clauses.
> I don't understand why anyone would be using single PSU
equipment in a DC environment now a days when you can buy
refurbished servers that come with two PSU

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Sam Silvester
Hey Chad,

That's a pretty general site you're pointing to.

Could you possibly be a bit more specific? Clicked through a couple of
links on it but everything was very high level.

As I noted elsewhere I am in SA but my employer is national so keeping
across all this is never a bad thing.

Cheers,

Sam

On Friday, 11 August 2017, Chad Kelly  wrote:

> It comes under the Victorian Occupational Health and safety Act 2004 from
> the bit of reading I did yesterday.
>
> https://www.worksafe.vic.gov.au/laws/ohs
>
> On 8/11/2017 10:17 AM, Jared Hirst wrote:
>
> Mark,
>
> Totally agree. I would just like to know what law Simon was referring too?
>
> Regards,
>
> Jared Hirst
> Servers Australia Pty Ltd
> Phone: +61 2 8115 8801
> Email: jared.hi...@serversaustralia.com.au
> 
> --
> *From:* AusNOG 
>  on
> behalf of Mark Newton 
> 
> *Sent:* Friday, August 11, 2017 4:54:10 AM
> *To:* Nathan Brookfield
> *Cc:* ausnog@lists.ausnog.net
> ;
> ausnog-requ...@lists.ausnog.net
> ; Chad
> Kelly
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -,
> 15th August
>
> As someone who has run colo facilities before:
>
> It should be made completely clear during customer onboarding that the
> facility operator can temporarily shut down a power feed at any time.
> Advance warning should be desirable but optional.
>
> If there is risk involved in doing that, it’s your job to mitigate it. The
> facility operator doesn’t know which bits of equipment in your tenancy are
> critical, and they’ve already told you to dual-feed where possible and use
> a rack-mount ATS for single-corded equipment.
>
> Power work should be done during business hours, because it’s almost
> impossible to get emergency support or source replacement equipment out of
> hours.
>
> If it isn’t safe to take a power feed offline during business hours, then
> you (the customer) have a design problem to solve.
>
>   - mark
>
>
>
>
> > On Aug 10, 2017, at 6:56 AM, Nathan Brookfield
> 
> 
> wrote:
> >
> > Chad,
> >
> > That's all well and good but when you're paying a premium price for
> services of this fashion you expect a certain level of service.  There is a
> risk no matter what when switching from power supplies taking extra load
> they would not usually take as well as swing load issues with PDU's.
> >
> > I completely agree with your sentiment but the risk is not to be ignored
> especially during those times.
> >
> > Kindest Regards,
> > Nathan Brookfield (VK2NAB)
> >
> > -Original Message-----
> > From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net
> ] On
> Behalf Of Chad Kelly
> > Sent: Thursday, August 10, 2017 2:54 PM
> > To: ausnog@lists.ausnog.net
> ;
> ausnog-requ...@lists.ausnog.net
> 
> > Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -,
> 15th August
> >
> >
> >
> > On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net
>  wrote:
> >> From the latest update today, It appears that most of the works are
> >> being postponed for the time being
> >>
> >> Not all devices within racks support 2 feeds and planning is involved
> >> with these devices, which is why it is crucial to receive accurate
> information about any pending outages or upgrades to the NextDC DataCentres
> which affect services.
> > If these services are mission critical then you really should have duel
> PSU units, so that when one feed gets taken offline the equipment
> automatically switches to the other feed. They won't just disconnect both
> feeds at once because that would be stupid and if the entire DC was offline
> for too much time then that would put the owners in a rather awkward
> situation legally, as after say 8 or 10 hours of downtime it wouldn't be
> good for the owners lets put it that way.
> > If the single PSU units are a part of a customers co-located equipment
> then really your terms of service agreement should exclude liability under
> your maintenance clauses.
> > I don't understand why anyone would be using single PSU equipment in a
> DC environment now a days when you can buy refurbished servers that come
> with two PSU as standard even when you buy them without raid.
> > Also for anything that is really really mission critical you should have
> it hosted in multiple datacentres anyway so if something stupid does happen
> that you can't control you at least still have services online as the load
> balanced services would just switch.
> > Regards Chad.
> >
> > --
> > Chad Kelly

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-11 Thread Chad Kelly
It comes under the Victorian Occupational Health and safety Act 2004 
from the bit of reading I did yesterday.


https://www.worksafe.vic.gov.au/laws/ohs


On 8/11/2017 10:17 AM, Jared Hirst wrote:

Mark,

Totally agree. I would just like to know what law Simon was referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au 
<mailto:jared.hi...@serversaustralia.com.au>


*From:* AusNOG  on behalf of Mark 
Newton 

*Sent:* Friday, August 11, 2017 4:54:10 AM
*To:* Nathan Brookfield
*Cc:* ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net; Chad Kelly
*Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance 
-, 15th August

As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the 
facility operator can temporarily shut down a power feed at any time. 
Advance warning should be desirable but optional.


If there is risk involved in doing that, it’s your job to mitigate it. 
The facility operator doesn’t know which bits of equipment in your 
tenancy are critical, and they’ve already told you to dual-feed where 
possible and use a rack-mount ATS for single-corded equipment.


Power work should be done during business hours, because it’s almost 
impossible to get emergency support or source replacement equipment 
out of hours.


If it isn’t safe to take a power feed offline during business hours, 
then you (the customer) have a design problem to solve.


  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield 
 wrote:

>
> Chad,
>
> That's all well and good but when you're paying a premium price for 
services of this fashion you expect a certain level of service.  There 
is a risk no matter what when switching from power supplies taking 
extra load they would not usually take as well as swing load issues 
with PDU's.

>
> I completely agree with your sentiment but the risk is not to be 
ignored especially during those times.

>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of 
Chad Kelly

> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance 
-, 15th August

>
>
>
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>> From the latest update today, It appears that most of the works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is involved
>> with these devices, which is why it is crucial to receive accurate 
information about any pending outages or upgrades to the NextDC 
DataCentres which affect services.
> If these services are mission critical then you really should have 
duel PSU units, so that when one feed gets taken offline the equipment 
automatically switches to the other feed. They won't just disconnect 
both feeds at once because that would be stupid and if the entire DC 
was offline for too much time then that would put the owners in a 
rather awkward situation legally, as after say 8 or 10 hours of 
downtime it wouldn't be good for the owners lets put it that way.
> If the single PSU units are a part of a customers co-located 
equipment then really your terms of service agreement should exclude 
liability under your maintenance clauses.
> I don't understand why anyone would be using single PSU equipment in 
a DC environment now a days when you can buy refurbished servers that 
come with two PSU as standard even when you buy them without raid.
> Also for anything that is really really mission critical you should 
have it hosted in multiple datacentres anyway so if something stupid 
does happen that you can't control you at least still have services 
online as the load balanced services would just switch.

> Regards Chad.
>
> --
> Chad Kelly
> Manager
> CPK Web Services
> Phone 03 5273 0246
> Web www.cpkws.com.au <http://www.cpkws.com.au>
>
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-10 Thread Shaun McGuane
Hi Simon,

For the sake of clarification and not to question NextDC's position, would you 
mind sharing with us the
Explanation of the Law that you are referring to with your response from 
yesterday?

As if you are the only datacentre following this law then others need to follow 
suite and it would be good
To understand if something is not being done that other providers are legally 
bound to do.

Kind Regards
Shaun McGuane


From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Jared Hirst
Sent: Friday, 11 August 2017 10:17 AM
To: Mark Newton ; Nathan Brookfield 

Cc: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net; Chad Kelly 

Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

Mark,

Totally agree. I would just like to know what law Simon was referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: 
jared.hi...@serversaustralia.com.au<mailto:jared.hi...@serversaustralia.com.au>

From: AusNOG 
mailto:ausnog-boun...@lists.ausnog.net>> on 
behalf of Mark Newton mailto:new...@atdot.dotat.org>>
Sent: Friday, August 11, 2017 4:54:10 AM
To: Nathan Brookfield
Cc: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>; 
ausnog-requ...@lists.ausnog.net<mailto:ausnog-requ...@lists.ausnog.net>; Chad 
Kelly
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the facility 
operator can temporarily shut down a power feed at any time. Advance warning 
should be desirable but optional.

If there is risk involved in doing that, it's your job to mitigate it. The 
facility operator doesn't know which bits of equipment in your tenancy are 
critical, and they've already told you to dual-feed where possible and use a 
rack-mount ATS for single-corded equipment.

Power work should be done during business hours, because it's almost impossible 
to get emergency support or source replacement equipment out of hours.

If it isn't safe to take a power feed offline during business hours, then you 
(the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield 
> mailto:nathan.brookfi...@simtronic.com.au>>
>  wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium price for services 
> of this fashion you expect a certain level of service.  There is a risk no 
> matter what when switching from power supplies taking extra load they would 
> not usually take as well as swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to be ignored 
> especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>; 
> ausnog-requ...@lists.ausnog.net<mailto:ausnog-requ...@lists.ausnog.net>
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
> August
>
>
>
> On 8/10/2017 10:13 AM, 
> ausnog-requ...@lists.ausnog.net<mailto:ausnog-requ...@lists.ausnog.net> wrote:
>> From the latest update today, It appears that most of the works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is involved
>> with these devices, which is why it is crucial to receive accurate 
>> information about any pending outages or upgrades to the NextDC DataCentres 
>> which affect services.
> If these services are mission critical then you really should have duel PSU 
> units, so that when one feed gets taken offline the equipment automatically 
> switches to the other feed. They won't just disconnect both feeds at once 
> because that would be stupid and if the entire DC was offline for too much 
> time then that would put the owners in a rather awkward situation legally, as 
> after say 8 or 10 hours of downtime it wouldn't be good for the owners lets 
> put it that way.
> If the single PSU units are a part of a customers co-located equipment then 
> really your terms of service agreement should exclude liability under your 
> maintenance clauses.
> I don't understand why anyone would be using single PSU equipment in a DC 
> environment now a days when you can buy refurbished servers that come with 
> two PSU as standard even when you buy them without raid.
> Also for anything that is really really mission critical you should have it 
> hosted in multiple datacentres anyw

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-10 Thread Jared Hirst
Mark,

Totally agree. I would just like to know what law Simon was referring too?

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: 
jared.hi...@serversaustralia.com.au<mailto:jared.hi...@serversaustralia.com.au>

From: AusNOG  on behalf of Mark Newton 

Sent: Friday, August 11, 2017 4:54:10 AM
To: Nathan Brookfield
Cc: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net; Chad Kelly
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August

As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the facility 
operator can temporarily shut down a power feed at any time. Advance warning 
should be desirable but optional.

If there is risk involved in doing that, it’s your job to mitigate it. The 
facility operator doesn’t know which bits of equipment in your tenancy are 
critical, and they’ve already told you to dual-feed where possible and use a 
rack-mount ATS for single-corded equipment.

Power work should be done during business hours, because it’s almost impossible 
to get emergency support or source replacement equipment out of hours.

If it isn’t safe to take a power feed offline during business hours, then you 
(the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield 
>  wrote:
>
> Chad,
>
> That's all well and good but when you're paying a premium price for services 
> of this fashion you expect a certain level of service.  There is a risk no 
> matter what when switching from power supplies taking extra load they would 
> not usually take as well as swing load issues with PDU's.
>
> I completely agree with your sentiment but the risk is not to be ignored 
> especially during those times.
>
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
>
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
> August
>
>
>
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>> From the latest update today, It appears that most of the works are
>> being postponed for the time being
>>
>> Not all devices within racks support 2 feeds and planning is involved
>> with these devices, which is why it is crucial to receive accurate 
>> information about any pending outages or upgrades to the NextDC DataCentres 
>> which affect services.
> If these services are mission critical then you really should have duel PSU 
> units, so that when one feed gets taken offline the equipment automatically 
> switches to the other feed. They won't just disconnect both feeds at once 
> because that would be stupid and if the entire DC was offline for too much 
> time then that would put the owners in a rather awkward situation legally, as 
> after say 8 or 10 hours of downtime it wouldn't be good for the owners lets 
> put it that way.
> If the single PSU units are a part of a customers co-located equipment then 
> really your terms of service agreement should exclude liability under your 
> maintenance clauses.
> I don't understand why anyone would be using single PSU equipment in a DC 
> environment now a days when you can buy refurbished servers that come with 
> two PSU as standard even when you buy them without raid.
> Also for anything that is really really mission critical you should have it 
> hosted in multiple datacentres anyway so if something stupid does happen that 
> you can't control you at least still have services online as the load 
> balanced services would just switch.
> Regards Chad.
>
> --
> Chad Kelly
> Manager
> CPK Web Services
> Phone 03 5273 0246
> Web www.cpkws.com.au<http://www.cpkws.com.au>
>
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-10 Thread Mark Newton
An STS is more expensive, is only suitable for use when the two supplies are 
phase-synchronized, and typically runs at 99% thermal efficiency.

While UPS power feeds should be phase-syncronized to mains, there are certain 
failure modes where they’ll drift, resulting in A and B losing sync; 
additionally, your colo provider might be powering your rack’s A and B supplies 
from different phases (if not today, then maybe tomorrow - it’s their 
prerogative)

Also: The only reason an STS switches to a replacement supply is if the normal 
supply has failed, so it’s difficult to imagine how that can be a no-break 
operation anyway.

A relay or contactor driven ATS typically has a high MTBF, doesn’t care about 
input phases at all, and runs with the same thermal efficiency as a piece of 
wire.

The break in an ATS is circa 50 mSec, which is well within the endurance of the 
capacitors in the cheapest switch mode power supply you’re capable of buying. 

I’ve never seen IT equipment notice a rack ATS changeover.

  - mark


> On Aug 10, 2017, at 4:24 AM, James Braunegg  
> wrote:
> 
> Dear All
>  
> Anyone with single power supply devices please do not look at getting an ATS, 
> get a STS !!!
>  
> Short version
>  
> ATS (Automatic Transfer Switch) will typically break power before it makes, 
> thus the connected device could reboot !!
>  
> STS (Static Transfer Switch) will make power before it breaks, providing no 
> break to the power  !
>  
> An example of a recommended device is below
>  
> https://www.vertivco.com/en-asia/products-catalog/critical-power/power-transfer-switches/liebert-lts-63-to-400a/
>  
> <https://www.vertivco.com/en-asia/products-catalog/critical-power/power-transfer-switches/liebert-lts-63-to-400a/>
>  
> Kindest Regards,
>  
> James Braunegg
> 
> 1300 769 972  / 0488 997 207 
> ja...@micron21.com <mailto:ja...@micron21.com>
> www.micron21.com/ <http://www.micron21.com/>  
>  <http://www.micron21.com/>
>  <https://www.facebook.com/micron21/>   
>  <https://twitter.com/micron21> 
> Follow us on Twitter <https://twitter.com/micron21> for important service and 
> system updates.
> This message is intended for the addressee named above. It may contain 
> privileged or confidential information. If you are not the intended recipient 
> of this message you must not use, copy, distribute or disclose it to anyone 
> other than the addressee. If you have received this message in error please 
> return the message to the sender by replying to it and then delete the 
> message from your computer.
>  
>  
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net 
> <mailto:ausnog-boun...@lists.ausnog.net>] On Behalf Of Matthew Smee
> Sent: Thursday, 10 August 2017 12:00 PM
> To: ausnog@lists.ausnog.net <mailto:ausnog@lists.ausnog.net>
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
> August
>  
> +1
> Every DC agreement I’ve seen (3) have mentioned that you are responsible for 
> supplying it with power and they aren’t responsible if it loses power (i.e. 
> use an ATS). 
>  
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net 
> <mailto:ausnog-boun...@lists.ausnog.net>] On Behalf Of Sam Silvester
> Sent: Thursday, 10 August 2017 10:14 AM
> To: Shaun McGuane mailto:sh...@rackcentral.com>>
> Cc: ausnog@lists.ausnog.net <mailto:ausnog@lists.ausnog.net>
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
> August
>  
> If you have single fed equipment in your rack that needs planning before it 
> can be shut down, do you not run a totally forseeable and preventable risk 
> then should that one feed trip?
>  
> This is what ATS are for.
>  
> Sam
>  
> 
> 
> On Thursday, 10 August 2017, Shaun McGuane  <mailto:sh...@rackcentral.com>> wrote:
> HI Simon,
>  
> Thank you for your input to the list.
>  
> While you may have provided notifications well in advance, your schedule 
> provided has been changed multiple times and this creates confusion.
> Without asking for further clarification last night I would never have 
> received the following updated schedule from Craig Armstrong today.
>  
> Data Hall 2 – B feed (west/blue PDU side) Tuesday 15th Aug, A feed has been 
> pushed back to later date around November, you will receive official notice 
> once new date confirmed.
> Data Hall 3 –A and B feed has been pushed back to later date around 
> October/November, you will receive official notice once new date confirmed.
> Data Hall 4 –A and B feed has been pushed back to later date around 
> October/November, you will receive official notice once new date confirmed.
>  
> From the latest update today, It

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-10 Thread Mark Newton
As someone who has run colo facilities before:

It should be made completely clear during customer onboarding that the facility 
operator can temporarily shut down a power feed at any time. Advance warning 
should be desirable but optional.

If there is risk involved in doing that, it’s your job to mitigate it. The 
facility operator doesn’t know which bits of equipment in your tenancy are 
critical, and they’ve already told you to dual-feed where possible and use a 
rack-mount ATS for single-corded equipment.

Power work should be done during business hours, because it’s almost impossible 
to get emergency support or source replacement equipment out of hours.

If it isn’t safe to take a power feed offline during business hours, then you 
(the customer) have a design problem to solve.

  - mark




> On Aug 10, 2017, at 6:56 AM, Nathan Brookfield 
>  wrote:
> 
> Chad,
> 
> That's all well and good but when you're paying a premium price for services 
> of this fashion you expect a certain level of service.  There is a risk no 
> matter what when switching from power supplies taking extra load they would 
> not usually take as well as swing load issues with PDU's.
> 
> I completely agree with your sentiment but the risk is not to be ignored 
> especially during those times.
> 
> Kindest Regards,
> Nathan Brookfield (VK2NAB)
> 
> -Original Message-
> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad Kelly
> Sent: Thursday, August 10, 2017 2:54 PM
> To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
> August
> 
> 
> 
> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>> From the latest update today, It appears that most of the works are 
>> being postponed for the time being
>> 
>> Not all devices within racks support 2 feeds and planning is involved 
>> with these devices, which is why it is crucial to receive accurate 
>> information about any pending outages or upgrades to the NextDC DataCentres 
>> which affect services.
> If these services are mission critical then you really should have duel PSU 
> units, so that when one feed gets taken offline the equipment automatically 
> switches to the other feed. They won't just disconnect both feeds at once 
> because that would be stupid and if the entire DC was offline for too much 
> time then that would put the owners in a rather awkward situation legally, as 
> after say 8 or 10 hours of downtime it wouldn't be good for the owners lets 
> put it that way.
> If the single PSU units are a part of a customers co-located equipment then 
> really your terms of service agreement should exclude liability under your 
> maintenance clauses.
> I don't understand why anyone would be using single PSU equipment in a DC 
> environment now a days when you can buy refurbished servers that come with 
> two PSU as standard even when you buy them without raid.
> Also for anything that is really really mission critical you should have it 
> hosted in multiple datacentres anyway so if something stupid does happen that 
> you can't control you at least still have services online as the load 
> balanced services would just switch.
> Regards Chad.
> 
> --
> Chad Kelly
> Manager
> CPK Web Services
> Phone 03 5273 0246
> Web www.cpkws.com.au
> 
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-10 Thread James Hodgkinson
We have a tech on site tomorrow morning in Brisbane to do live works on
a major DC panel, they need a look out with a torch, insulating matting
and a few other things but it's legal.
James


On Thu, 10 Aug 2017, at 16:04, Sam Silvester wrote:
> I also am unaware of such a law. Simon, can you advise?
> 
> I'm told in QLD that live works are not permitted, but I am in SA so I
> have not really bothered too much to check if that is hearsay or true.> 
> On Thursday, 10 August 2017, Jared Hirst
>  wrote:>> 
>> Hi Simon,
>> 
>> Maybe it could be helpful to the Ausnog list to point us to that law
>> you refer too?>> 
>> As I personally have never heard or seen this done in any DC in
>> Australia, or the world in the past 15 years I have been housing gear
>> in Data Centres.>> 
>> I agree that gear should have 2N, and it doesn’t affect me, but there
>> are people that have equipment that have single fed devices, and I
>> believe you don’t allow self installed STS devices to be installed? I
>> could be wrong.>> 
>> In any case, it would be interesting to see the law the requires you
>> to shut down boards.>> 
>> Regards,
>> 
>>  Jared Hirst
>>  Servers Australia Pty Ltd
>>  Phone: +61 2 8115 8801
>>  Email: jared.hi...@serversaustralia.com.au
>> 
>> *From:* AusNOG  on behalf of Simon
>> Cooper  *Sent:* Thursday, August 10, 2017 8:39:13 AM
>> *To:* ausnog@lists.ausnog.net *Subject:* Re: [AusNOG] NextDC
>> Melbourne - Scheduled Power Maintenance - 15th August>>  
>> Thanks guys, appreciate the feedback.
>> 
>> At NEXTDC we work very hard to keep critical infrastructure
>> maintenance that impacts racks or the environment within the data
>> hall to an absolute minimum.>> 
>> However, some works are required to happen from time to time by law
>> and one of those activities is a de-energisation and inspection of
>> each of our major switchboards.  This is all about ensuring that the
>> electrical system is safe, and is an unavoidable piece of work.
>> Rightly so.>> 
>> Every rack in a NEXTDC data centre has 2N power feeds offered to it,
>> and we highly recommend that they are used for every device in the
>> rack.  This occasional maintenance is one of the many reasons we
>> provide this capability.  Any device using the 2N supplies (aka A & B
>> feeds) will simply see its power swing from one feed to the other.
>> Any rack that is drawing no more that its contracted power level will
>> have no issue when all devices move from A to B or vice versa.>> 
>> Our notifications were made well in advance, as we want to give
>> customers time to consider the management of these works and we don't
>> assume that every rack is perfectly deployed:  We are here 24/7 to
>> assist customers with rack inspections or specific circuit down tests
>> or maybe a controlled move prior to the day (e.g. for devices that
>> are single fed).>> 
>> Also, as we work though those discussions with customers we
>> understand the timing in relation to their businesses, and we work
>> very hard to coordinate schedules despite each switch board
>> supporting many different customers and customer instances across the
>> data centre.  Occasionally that means we have to make a difficult
>> decisions which may result in schedule changes.  When that does
>> happen, we do not compromise our notification periods.>> 
>> I'll be happy to discuss these works with anyone - probably best
>> offline or on the phone - but trust me when I say we are doing our
>> absolute best to keep your data centre operating safely and reliably
>> for many years to come.>> 
>> Thanks,
>> Simon
>> COO, NEXTDC
>> 
>>> -Original Message-
>>> *From:* nat...@nightsys.net
>>> *Sent:* Thu, 10 Aug 2017 05:39:02 +1000
>>> *To:* sh...@rackcentral.com
>>> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
>>> Maintenance - 15th August>>> 
>>> This seems reasonable? As long as no single Data Hall has both A and
>>> B feeds removed simultaneously, that seems normal. Doing B on Hall 2
>>> and A on Hall 3 on the same day does seem slightly adventurous, but
>>> not entirely unreasonable (mostly in terms of if something goes bad
>>> in both, staff get stretched thin remediating issues).>>> 
>>> A and B feeds are designed to provide redundancy to equipment,
>>> allowing one feed to fail and systems to continue on the other.
>>> Anything mission critical should 

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-09 Thread Chad Kelly

Yeah bit of a dammed if you do, dammed if you don't type situation.



On 8/10/2017 4:11 PM, Peter Tiggerdine wrote:

disagree.

Outside of business hours costs more with limited staff around to
assist. They're doing you a favour by doing this because if your PSU
fails on server, you'll have time raise tickets with vendor and get
same day resolution.


Regards,

Peter Tiggerdine

GPG Fingerprint: 2A3F EA19 F6C2 93C1 411D 5AB2 D5A8 E8A8 0E74 6127


On Thu, Aug 10, 2017 at 3:14 PM, Chad Kelly  wrote:

Hmm yes actually deciding to do this during business hours does appear to be
an odd choice, even with two PSU in the server, they would be better off
doing this out of business hours I would of thought.
Regards Chad.


On 8/10/2017 2:56 PM, Nathan Brookfield wrote:

Chad,

That's all well and good but when you're paying a premium price for
services of this fashion you expect a certain level of service.  There is a
risk no matter what when switching from power supplies taking extra load
they would not usually take as well as swing load issues with PDU's.

I completely agree with your sentiment but the risk is not to be ignored
especially during those times.

Kindest Regards,
Nathan Brookfield (VK2NAB)

-Original Message-
From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad
Kelly
Sent: Thursday, August 10, 2017 2:54 PM
To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -,
15th August



On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:

   From the latest update today, It appears that most of the works are
being postponed for the time being

Not all devices within racks support 2 feeds and planning is involved
with these devices, which is why it is crucial to receive accurate
information about any pending outages or upgrades to the NextDC DataCentres
which affect services.

If these services are mission critical then you really should have duel
PSU units, so that when one feed gets taken offline the equipment
automatically switches to the other feed. They won't just disconnect both
feeds at once because that would be stupid and if the entire DC was offline
for too much time then that would put the owners in a rather awkward
situation legally, as after say 8 or 10 hours of downtime it wouldn't be
good for the owners lets put it that way.
If the single PSU units are a part of a customers co-located equipment
then really your terms of service agreement should exclude liability under
your maintenance clauses.
I don't understand why anyone would be using single PSU equipment in a DC
environment now a days when you can buy refurbished servers that come with
two PSU as standard even when you buy them without raid.
Also for anything that is really really mission critical you should have
it hosted in multiple datacentres anyway so if something stupid does happen
that you can't control you at least still have services online as the load
balanced services would just switch.
Regards Chad.

--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-09 Thread Peter Tiggerdine
disagree.

Outside of business hours costs more with limited staff around to
assist. They're doing you a favour by doing this because if your PSU
fails on server, you'll have time raise tickets with vendor and get
same day resolution.


Regards,

Peter Tiggerdine

GPG Fingerprint: 2A3F EA19 F6C2 93C1 411D 5AB2 D5A8 E8A8 0E74 6127


On Thu, Aug 10, 2017 at 3:14 PM, Chad Kelly  wrote:
>
> Hmm yes actually deciding to do this during business hours does appear to be
> an odd choice, even with two PSU in the server, they would be better off
> doing this out of business hours I would of thought.
> Regards Chad.
>
>
> On 8/10/2017 2:56 PM, Nathan Brookfield wrote:
>>
>> Chad,
>>
>> That's all well and good but when you're paying a premium price for
>> services of this fashion you expect a certain level of service.  There is a
>> risk no matter what when switching from power supplies taking extra load
>> they would not usually take as well as swing load issues with PDU's.
>>
>> I completely agree with your sentiment but the risk is not to be ignored
>> especially during those times.
>>
>> Kindest Regards,
>> Nathan Brookfield (VK2NAB)
>>
>> -Original Message-
>> From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad
>> Kelly
>> Sent: Thursday, August 10, 2017 2:54 PM
>> To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
>> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -,
>> 15th August
>>
>>
>>
>> On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>>>
>>>   From the latest update today, It appears that most of the works are
>>> being postponed for the time being
>>>
>>> Not all devices within racks support 2 feeds and planning is involved
>>> with these devices, which is why it is crucial to receive accurate
>>> information about any pending outages or upgrades to the NextDC DataCentres
>>> which affect services.
>>
>> If these services are mission critical then you really should have duel
>> PSU units, so that when one feed gets taken offline the equipment
>> automatically switches to the other feed. They won't just disconnect both
>> feeds at once because that would be stupid and if the entire DC was offline
>> for too much time then that would put the owners in a rather awkward
>> situation legally, as after say 8 or 10 hours of downtime it wouldn't be
>> good for the owners lets put it that way.
>> If the single PSU units are a part of a customers co-located equipment
>> then really your terms of service agreement should exclude liability under
>> your maintenance clauses.
>> I don't understand why anyone would be using single PSU equipment in a DC
>> environment now a days when you can buy refurbished servers that come with
>> two PSU as standard even when you buy them without raid.
>> Also for anything that is really really mission critical you should have
>> it hosted in multiple datacentres anyway so if something stupid does happen
>> that you can't control you at least still have services online as the load
>> balanced services would just switch.
>> Regards Chad.
>>
>> --
>> Chad Kelly
>> Manager
>> CPK Web Services
>> Phone 03 5273 0246
>> Web www.cpkws.com.au
>>
>> ___
>> AusNOG mailing list
>> AusNOG@lists.ausnog.net
>> http://lists.ausnog.net/mailman/listinfo/ausnog
>
>
> --
> Chad Kelly
> Manager
> CPK Web Services
> Phone 03 5273 0246
> Web www.cpkws.com.au
>
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Sam Silvester
Hi James,

A quick Google tells me APC ATS are break before make, so that is certainly
not the defining feature of an ATS vs. STS.

For cost effective provision of a 'C feed' in racks to catch those pesky
single corded devices you just can't live without I see no reason at all to
go to the expense of typically larger and more expensive STS, happy to
learn more though.

Sam



On Thursday, 10 August 2017, James Braunegg 
wrote:

> Dear All
>
>
>
> Anyone with single power supply devices please do not look at getting an
> ATS, get a STS !!!
>
>
>
> *Short version*
>
>
>
> ATS (Automatic Transfer Switch) will typically break power before it
> makes, thus the connected device could reboot !!
>
>
>
> STS (Static Transfer Switch) will make power before it breaks, providing
> no break to the power  !
>
>
>
> An example of a recommended device is below
>
>
>
> https://www.vertivco.com/en-asia/products-catalog/
> critical-power/power-transfer-switches/liebert-lts-63-to-400a/
>
>
>
> Kindest Regards,
>
>
>
> *James Braunegg*
>
> [image: cid:image001.png@01D280A4.01865B60]
>
> 1300 769 972 / 0488 997 207 <1300%20769%20972>
>
> *ja...@micron21.com *
>
> www.micron21.com/
>
> [image: cid:image002.png@01D280A4.01865B60] <http://www.micron21.com/>
>
> [image: cid:image003.png@01D280A4.01865B60]
> <https://www.facebook.com/micron21/>
>
> [image: cid:image004.png@01D280A4.01865B60] <https://twitter.com/micron21>
>
> Follow us on Twitter <https://twitter.com/micron21> for important service
> and system updates.
>
> This message is intended for the addressee named above. It may contain
> privileged or confidential information. If you are not the intended
> recipient of this message you must not use, copy, distribute or disclose it
> to anyone other than the addressee. If you have received this message in
> error please return the message to the sender by replying to it and then
> delete the message from your computer.
>
>
>
>
>
> *From:* AusNOG [mailto:ausnog-boun...@lists.ausnog.net
> ] *On
> Behalf Of *Matthew Smee
> *Sent:* Thursday, 10 August 2017 12:00 PM
> *To:* ausnog@lists.ausnog.net
> 
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
>
>
> +1
>
> Every DC agreement I’ve seen (3) have mentioned that you are responsible
> for supplying it with power and they aren’t responsible if it loses power
> (i.e. use an ATS).
>
>
>
> *From:* AusNOG [mailto:ausnog-boun...@lists.ausnog.net
> ] *On
> Behalf Of *Sam Silvester
> *Sent:* Thursday, 10 August 2017 10:14 AM
> *To:* Shaun McGuane  >
> *Cc:* ausnog@lists.ausnog.net
> 
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
>
>
> If you have single fed equipment in your rack that needs planning before
> it can be shut down, do you not run a totally forseeable and preventable
> risk then should that one feed trip?
>
>
>
> This is what ATS are for.
>
>
>
> Sam
>
>
>
>
>
> On Thursday, 10 August 2017, Shaun McGuane  > wrote:
>
> HI Simon,
>
>
>
> Thank you for your input to the list.
>
>
>
> While you may have provided notifications well in advance, your schedule
> provided has been changed multiple times and this creates confusion.
>
> Without asking for further clarification last night I would never have
> received the following updated schedule from Craig Armstrong today.
>
>
>
> Data Hall 2 – B feed (west/blue PDU side) Tuesday 15th Aug, A feed has
> been pushed back to later date around November, you will receive official
> notice once new date confirmed.
>
> Data Hall 3 –A and B feed has been pushed back to later date around
> October/November, you will receive official notice once new date confirmed.
>
> Data Hall 4 –A and B feed has been pushed back to later date around
> October/November, you will receive official notice once new date confirmed.
>
>
>
> From the latest update today, It appears that most of the works are being
> postponed for the time being
>
>
>
> Not all devices within racks support 2 feeds and planning is involved with
> these devices, which is why it is crucial to receive accurate information
> about any pending outages or upgrades
> to the NextDC DataCentres which affect services.
>
>
>
> Additionally, I have not received these updates via the normal NextDC
> E-Mail communication method, so I am sure other customers will be wondering
> whats happening too.
>
>
>
> Happy to have a conversation offline about this feel free to give me a
> ca

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Jared Hirst
Yes but the wording was;

“However, some works are required to happen from time to time by law and one of 
those activities is a de-energisation and inspection of each of our major 
switchboards”

I have never heard of a law that requires de-energisation of a board for 
inspection. Our electricians (Schneider) do this live, with Flir Heat mapping 
equipment and many other cool tools.

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au

From: Sam Silvester 
Sent: Thursday, August 10, 2017 4:04:29 PM
To: Jared Hirst
Cc: Simon Cooper; ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

I also am unaware of such a law. Simon, can you advise?

I'm told in QLD that live works are not permitted, but I am in SA so I have not 
really bothered too much to check if that is hearsay or true.

On Thursday, 10 August 2017, Jared Hirst 
mailto:jared.hi...@serversaustralia.com.au>>
 wrote:
Hi Simon,

Maybe it could be helpful to the Ausnog list to point us to that law you refer 
too?

As I personally have never heard or seen this done in any DC in Australia, or 
the world in the past 15 years I have been housing gear in Data Centres.

I agree that gear should have 2N, and it doesn’t affect me, but there are 
people that have equipment that have single fed devices, and I believe you 
don’t allow self installed STS devices to be installed? I could be wrong.

In any case, it would be interesting to see the law the requires you to shut 
down boards.

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au

From: AusNOG  on behalf of Simon Cooper 

Sent: Thursday, August 10, 2017 8:39:13 AM
To: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

Thanks guys, appreciate the feedback.

At NEXTDC we work very hard to keep critical infrastructure maintenance that 
impacts racks or the environment within the data hall to an absolute minimum.

However, some works are required to happen from time to time by law and one of 
those activities is a de-energisation and inspection of each of our major 
switchboards.  This is all about ensuring that the electrical system is safe, 
and is an unavoidable piece of work. Rightly so.

Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we 
highly recommend that they are used for every device in the rack.  This 
occasional maintenance is one of the many reasons we provide this capability.  
Any device using the 2N supplies (aka A & B feeds) will simply see its power 
swing from one feed to the other.  Any rack that is drawing no more that its 
contracted power level will have no issue when all devices move from A to B or 
vice versa.

Our notifications were made well in advance, as we want to give customers time 
to consider the management of these works and we don't assume that every rack 
is perfectly deployed:  We are here 24/7 to assist customers with rack 
inspections or specific circuit down tests or maybe a controlled move prior to 
the day (e.g. for devices that are single fed).

Also, as we work though those discussions with customers we understand the 
timing in relation to their businesses, and we work very hard to coordinate 
schedules despite each switch board supporting many different customers and 
customer instances across the data centre.  Occasionally that means we have to 
make a difficult decisions which may result in schedule changes.  When that 
does happen, we do not compromise our notification periods.

I'll be happy to discuss these works with anyone - probably best offline or on 
the phone - but trust me when I say we are doing our absolute best to keep your 
data centre operating safely and reliably for many years to come.

Thanks,
Simon
COO, NEXTDC

-Original Message-
From: nat...@nightsys.net
Sent: Thu, 10 Aug 2017 05:39:02 +1000
To: sh...@rackcentral.com
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

This seems reasonable? As long as no single Data Hall has both A and B feeds 
removed simultaneously, that seems normal. Doing B on Hall 2 and A on Hall 3 on 
the same day does seem slightly adventurous, but not entirely unreasonable 
(mostly in terms of if something goes bad in both, staff get stretched thin 
remediating issues).

A and B feeds are designed to provide redundancy to equipment, allowing one 
feed to fail and systems to continue on the other. Anything mission critical 
should be able to draw from either feed as required (dual PSU), and if there is 
a power deficit on one feed (causing circuits to trip), that would imply the 
circuits are incorrectly sized?

In addition, anything mission critical with a single power supply would be on 
an ATS you would assume, or a p

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Sam Silvester
I also am unaware of such a law. Simon, can you advise?

I'm told in QLD that live works are not permitted, but I am in SA so I have
not really bothered too much to check if that is hearsay or true.

On Thursday, 10 August 2017, Jared Hirst <
jared.hi...@serversaustralia.com.au> wrote:

> Hi Simon,
>
> Maybe it could be helpful to the Ausnog list to point us to that law you
> refer too?
>
> As I personally have never heard or seen this done in any DC in Australia,
> or the world in the past 15 years I have been housing gear in Data Centres.
>
> I agree that gear should have 2N, and it doesn’t affect me, but there are
> people that have equipment that have single fed devices, and I believe you
> don’t allow self installed STS devices to be installed? I could be wrong.
>
> In any case, it would be interesting to see the law the requires you to
> shut down boards.
>
> Regards,
>
> Jared Hirst
> Servers Australia Pty Ltd
> Phone: +61 2 8115 8801
> Email: jared.hi...@serversaustralia.com.au
> 
> --
> *From:* AusNOG  > on
> behalf of Simon Cooper  >
> *Sent:* Thursday, August 10, 2017 8:39:13 AM
> *To:* ausnog@lists.ausnog.net
> 
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
> Thanks guys, appreciate the feedback.
>
> At NEXTDC we work very hard to keep critical infrastructure maintenance
> that impacts racks or the environment within the data hall to an absolute
> minimum.
>
> However, some works are required to happen from time to time by law and
> one of those activities is a de-energisation and inspection of each of our
> major switchboards.  This is all about ensuring that the electrical system
> is safe, and is an unavoidable piece of work. Rightly so.
>
> Every rack in a NEXTDC data centre has 2N power feeds offered to it, and
> we highly recommend that they are used for every device in the rack.  This
> occasional maintenance is one of the many reasons we provide this
> capability.  Any device using the 2N supplies (aka A & B feeds) will simply
> see its power swing from one feed to the other.  Any rack that is drawing
> no more that its contracted power level will have no issue when all devices
> move from A to B or vice versa.
>
> Our notifications were made well in advance, as we want to give customers
> time to consider the management of these works and we don't assume that
> every rack is perfectly deployed:  We are here 24/7 to assist customers
> with rack inspections or specific circuit down tests or maybe a controlled
> move prior to the day (e.g. for devices that are single fed).
>
> Also, as we work though those discussions with customers we understand the
> timing in relation to their businesses, and we work very hard to coordinate
> schedules despite each switch board supporting many different customers and
> customer instances across the data centre.  Occasionally that means we have
> to make a difficult decisions which may result in schedule changes.  When
> that does happen, we do not compromise our notification periods.
>
> I'll be happy to discuss these works with anyone - probably best offline
> or on the phone - but trust me when I say we are doing our absolute best to
> keep your data centre operating safely and reliably for many years to come.
>
> Thanks,
> Simon
> COO, NEXTDC
>
> -Original Message-
> *From:* nat...@nightsys.net
> 
> *Sent:* Thu, 10 Aug 2017 05:39:02 +1000
> *To:* sh...@rackcentral.com
> 
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
> This seems reasonable? As long as no single Data Hall has both A and B
> feeds removed simultaneously, that seems normal. Doing B on Hall 2 and A on
> Hall 3 on the same day does seem slightly adventurous, but not entirely
> unreasonable (mostly in terms of if something goes bad in both, staff get
> stretched thin remediating issues).
>
> A and B feeds are designed to provide redundancy to equipment, allowing
> one feed to fail and systems to continue on the other. Anything mission
> critical should be able to draw from either feed as required (dual PSU),
> and if there is a power deficit on one feed (causing circuits to trip),
> that would imply the circuits are incorrectly sized?
>
> In addition, anything mission critical with a single power supply would be
> on an ATS you would assume, or a pair of equivalent devices installed with
> one on each rail?
>
> Things break in datacentres, planned maintenance happens sometimes, better
> than no maintenance at all :) The fact they are notifying you is better
> than not, and it being scheduled is probably still better than unscheduled
&

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th, August

2017-08-09 Thread Chad Kelly



On 8/10/2017 2:47 PM, ausnog-requ...@lists.ausnog.net wrote:

Maybe it could be helpful to the Ausnog list to point us to that law you refer 
too?

As I personally have never heard or seen this done in any DC in Australia, or 
the world in the past 15 years I have been housing gear in Data Centres.

I agree that gear should have 2N, and it doesn?t affect me, but there are 
people that have equipment that have single fed devices, and I believe you 
don?t allow self installed STS devices to be installed? I could be wrong.

In any case, it would be interesting to see the law the requires you to shut 
down boards.
Given you own a few DC's in NSW it would pay to check the OHS laws in 
that state, but the Electrical safety stuff comes under those laws hear 
in Vic.

http://www.ohsrep.org.au/faqs/ohs-reps-@-work-electrical-safety-/electrical-equipment-what-are-the-lawsguidelines
So basically its more red tape from government.
Not sure when they last did it but Micron21 have had to do similar work 
in the last few years as well.

Regards Chad.

--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-09 Thread Chad Kelly


Hmm yes actually deciding to do this during business hours does appear 
to be an odd choice, even with two PSU in the server, they would be 
better off doing this out of business hours I would of thought.

Regards Chad.

On 8/10/2017 2:56 PM, Nathan Brookfield wrote:

Chad,

That's all well and good but when you're paying a premium price for services of 
this fashion you expect a certain level of service.  There is a risk no matter 
what when switching from power supplies taking extra load they would not 
usually take as well as swing load issues with PDU's.

I completely agree with your sentiment but the risk is not to be ignored 
especially during those times.

Kindest Regards,
Nathan Brookfield (VK2NAB)

-Original Message-
From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad Kelly
Sent: Thursday, August 10, 2017 2:54 PM
To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August



On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:

  From the latest update today, It appears that most of the works are
being postponed for the time being

Not all devices within racks support 2 feeds and planning is involved
with these devices, which is why it is crucial to receive accurate information 
about any pending outages or upgrades to the NextDC DataCentres which affect 
services.

If these services are mission critical then you really should have duel PSU 
units, so that when one feed gets taken offline the equipment automatically 
switches to the other feed. They won't just disconnect both feeds at once 
because that would be stupid and if the entire DC was offline for too much time 
then that would put the owners in a rather awkward situation legally, as after 
say 8 or 10 hours of downtime it wouldn't be good for the owners lets put it 
that way.
If the single PSU units are a part of a customers co-located equipment then 
really your terms of service agreement should exclude liability under your 
maintenance clauses.
I don't understand why anyone would be using single PSU equipment in a DC 
environment now a days when you can buy refurbished servers that come with two 
PSU as standard even when you buy them without raid.
Also for anything that is really really mission critical you should have it 
hosted in multiple datacentres anyway so if something stupid does happen that 
you can't control you at least still have services online as the load balanced 
services would just switch.
Regards Chad.

--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-09 Thread Nathan Brookfield
Chad,

That's all well and good but when you're paying a premium price for services of 
this fashion you expect a certain level of service.  There is a risk no matter 
what when switching from power supplies taking extra load they would not 
usually take as well as swing load issues with PDU's.

I completely agree with your sentiment but the risk is not to be ignored 
especially during those times.

Kindest Regards,
Nathan Brookfield (VK2NAB)

-Original Message-
From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Chad Kelly
Sent: Thursday, August 10, 2017 2:54 PM
To: ausnog@lists.ausnog.net; ausnog-requ...@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th 
August



On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:
>  From the latest update today, It appears that most of the works are 
> being postponed for the time being
>
> Not all devices within racks support 2 feeds and planning is involved 
> with these devices, which is why it is crucial to receive accurate 
> information about any pending outages or upgrades to the NextDC DataCentres 
> which affect services.
If these services are mission critical then you really should have duel PSU 
units, so that when one feed gets taken offline the equipment automatically 
switches to the other feed. They won't just disconnect both feeds at once 
because that would be stupid and if the entire DC was offline for too much time 
then that would put the owners in a rather awkward situation legally, as after 
say 8 or 10 hours of downtime it wouldn't be good for the owners lets put it 
that way.
If the single PSU units are a part of a customers co-located equipment then 
really your terms of service agreement should exclude liability under your 
maintenance clauses.
I don't understand why anyone would be using single PSU equipment in a DC 
environment now a days when you can buy refurbished servers that come with two 
PSU as standard even when you buy them without raid.
Also for anything that is really really mission critical you should have it 
hosted in multiple datacentres anyway so if something stupid does happen that 
you can't control you at least still have services online as the load balanced 
services would just switch.
Regards Chad.

--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -, 15th August

2017-08-09 Thread Chad Kelly



On 8/10/2017 10:13 AM, ausnog-requ...@lists.ausnog.net wrote:

 From the latest update today, It appears that most of the works are being 
postponed for the time being

Not all devices within racks support 2 feeds and planning is involved with 
these devices, which is why it is crucial to receive accurate information about 
any pending outages or upgrades
to the NextDC DataCentres which affect services.
If these services are mission critical then you really should have duel 
PSU units, so that when one feed gets taken offline the equipment 
automatically switches to the other feed. They won't just disconnect 
both feeds at once because that would be stupid and if the entire DC was 
offline for too much time then that would put the owners in a rather 
awkward situation legally, as after say 8 or 10 hours of downtime it 
wouldn't be good for the owners lets put it that way.
If the single PSU units are a part of a customers co-located equipment 
then really your terms of service agreement should exclude liability 
under your maintenance clauses.
I don't understand why anyone would be using single PSU equipment in a 
DC environment now a days when you can buy refurbished servers that come 
with two PSU as standard even when you buy them without raid.
Also for anything that is really really mission critical you should have 
it hosted in multiple datacentres anyway so if something stupid does 
happen that you can't control you at least still have services online as 
the load balanced services would just switch.

Regards Chad.

--
Chad Kelly
Manager
CPK Web Services
Phone 03 5273 0246
Web www.cpkws.com.au

___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Matt Perkins
Smells of them having to lift the supply neutral to the input of the UPS 
stacks. This would require a shutdown of the entire eqipment if the 
Natural earth bond needs to be split for whatever reason.  (Although I 
have done a temporary bond in DC's before to keep the UPS array going 
but a lot of engineers get skittish about that especially  if HV is 
involved)


Matt.




On 10/8/17 1:22 pm, Jared Hirst wrote:

Hi Simon,

Maybe it could be helpful to the Ausnog list to point us to that law 
you refer too?


As I personally have never heard or seen this done in any DC in 
Australia, or the world in the past 15 years I have been housing gear 
in Data Centres.


I agree that gear should have 2N, and it doesn’t affect me, but there 
are people that have equipment that have single fed devices, and I 
believe you don’t allow self installed STS devices to be installed? I 
could be wrong.


In any case, it would be interesting to see the law the requires you 
to shut down boards.


Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: jared.hi...@serversaustralia.com.au 
<mailto:jared.hi...@serversaustralia.com.au>


*From:* AusNOG  on behalf of Simon 
Cooper 

*Sent:* Thursday, August 10, 2017 8:39:13 AM
*To:* ausnog@lists.ausnog.net
*Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance 
- 15th August

Thanks guys, appreciate the feedback.

At NEXTDC we work very hard to keep critical infrastructure 
maintenance that impacts racks or the environment within the data hall 
to an absolute minimum.


However, some works are required to happen from time to time by law 
and one of those activities is a de-energisation and inspection of 
each of our major switchboards.  This is all about ensuring that the 
electrical system is safe, and is an unavoidable piece of work. 
Rightly so.


Every rack in a NEXTDC data centre has 2N power feeds offered to it, 
and we highly recommend that they are used for every device in the 
rack.  This occasional maintenance is one of the many reasons we 
provide this capability.  Any device using the 2N supplies (aka A & B 
feeds) will simply see its power swing from one feed to the other. 
 Any rack that is drawing no more that its contracted power level will 
have no issue when all devices move from A to B or vice versa.


Our notifications were made well in advance, as we want to give 
customers time to consider the management of these works and we don't 
assume that every rack is perfectly deployed:  We are here 24/7 to 
assist customers with rack inspections or specific circuit down tests 
or maybe a controlled move prior to the day (e.g. for devices that are 
single fed).


Also, as we work though those discussions with customers we understand 
the timing in relation to their businesses, and we work very hard to 
coordinate schedules despite each switch board supporting many 
different customers and customer instances across the data centre. 
 Occasionally that means we have to make a difficult decisions which 
may result in schedule changes.  When that does happen, we do not 
compromise our notification periods.


I'll be happy to discuss these works with anyone - probably best 
offline or on the phone - but trust me when I say we are doing our 
absolute best to keep your data centre operating safely and reliably 
for many years to come.


Thanks,
Simon
COO, NEXTDC

-Original Message-
*From:* nat...@nightsys.net
*Sent:* Thu, 10 Aug 2017 05:39:02 +1000
*To:* sh...@rackcentral.com
    *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
Maintenance - 15th August

This seems reasonable? As long as no single Data Hall has both A
and B feeds removed simultaneously, that seems normal. Doing B on
Hall 2 and A on Hall 3 on the same day does seem slightly
adventurous, but not entirely unreasonable (mostly in terms of if
something goes bad in both, staff get stretched thin remediating
issues).

A and B feeds are designed to provide redundancy to equipment,
allowing one feed to fail and systems to continue on the other.
Anything mission critical should be able to draw from either feed
as required (dual PSU), and if there is a power deficit on one
feed (causing circuits to trip), that would imply the circuits are
incorrectly sized?

In addition, anything mission critical with a single power supply
would be on an ATS you would assume, or a pair of equivalent
devices installed with one on each rail?

Things break in datacentres, planned maintenance happens
sometimes, better than no maintenance at all :) The fact they are
notifying you is better than not, and it being scheduled is
probably still better than unscheduled :) (easier to ensure
sufficient staffing to keep a close eye on things)

Nathan.

On Wed, Aug 9, 2017 at 3:43 PM, Sh

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Jared Hirst
Hi Simon,

Maybe it could be helpful to the Ausnog list to point us to that law you refer 
too?

As I personally have never heard or seen this done in any DC in Australia, or 
the world in the past 15 years I have been housing gear in Data Centres.

I agree that gear should have 2N, and it doesn’t affect me, but there are 
people that have equipment that have single fed devices, and I believe you 
don’t allow self installed STS devices to be installed? I could be wrong.

In any case, it would be interesting to see the law the requires you to shut 
down boards.

Regards,

Jared Hirst
Servers Australia Pty Ltd
Phone: +61 2 8115 8801
Email: 
jared.hi...@serversaustralia.com.au<mailto:jared.hi...@serversaustralia.com.au>

From: AusNOG  on behalf of Simon Cooper 

Sent: Thursday, August 10, 2017 8:39:13 AM
To: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

Thanks guys, appreciate the feedback.

At NEXTDC we work very hard to keep critical infrastructure maintenance that 
impacts racks or the environment within the data hall to an absolute minimum.

However, some works are required to happen from time to time by law and one of 
those activities is a de-energisation and inspection of each of our major 
switchboards.  This is all about ensuring that the electrical system is safe, 
and is an unavoidable piece of work. Rightly so.

Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we 
highly recommend that they are used for every device in the rack.  This 
occasional maintenance is one of the many reasons we provide this capability.  
Any device using the 2N supplies (aka A & B feeds) will simply see its power 
swing from one feed to the other.  Any rack that is drawing no more that its 
contracted power level will have no issue when all devices move from A to B or 
vice versa.

Our notifications were made well in advance, as we want to give customers time 
to consider the management of these works and we don't assume that every rack 
is perfectly deployed:  We are here 24/7 to assist customers with rack 
inspections or specific circuit down tests or maybe a controlled move prior to 
the day (e.g. for devices that are single fed).

Also, as we work though those discussions with customers we understand the 
timing in relation to their businesses, and we work very hard to coordinate 
schedules despite each switch board supporting many different customers and 
customer instances across the data centre.  Occasionally that means we have to 
make a difficult decisions which may result in schedule changes.  When that 
does happen, we do not compromise our notification periods.

I'll be happy to discuss these works with anyone - probably best offline or on 
the phone - but trust me when I say we are doing our absolute best to keep your 
data centre operating safely and reliably for many years to come.

Thanks,
Simon
COO, NEXTDC

-Original Message-
From: nat...@nightsys.net
Sent: Thu, 10 Aug 2017 05:39:02 +1000
To: sh...@rackcentral.com
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

This seems reasonable? As long as no single Data Hall has both A and B feeds 
removed simultaneously, that seems normal. Doing B on Hall 2 and A on Hall 3 on 
the same day does seem slightly adventurous, but not entirely unreasonable 
(mostly in terms of if something goes bad in both, staff get stretched thin 
remediating issues).

A and B feeds are designed to provide redundancy to equipment, allowing one 
feed to fail and systems to continue on the other. Anything mission critical 
should be able to draw from either feed as required (dual PSU), and if there is 
a power deficit on one feed (causing circuits to trip), that would imply the 
circuits are incorrectly sized?

In addition, anything mission critical with a single power supply would be on 
an ATS you would assume, or a pair of equivalent devices installed with one on 
each rail?

Things break in datacentres, planned maintenance happens sometimes, better than 
no maintenance at all :) The fact they are notifying you is better than not, 
and it being scheduled is probably still better than unscheduled :) (easier to 
ensure sufficient staffing to keep a close eye on things)

Nathan.

On Wed, Aug 9, 2017 at 3:43 PM, Shaun McGuane 
mailto:sh...@rackcentral.com>> wrote:

Here is the entire scheduled maintenance windows for all the halls we occupy.



DataHall 2

A Feed - Tuesday 8th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.



DataHall 3

A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10
B Feed - Monday 14th August 2017 07:00 UTC +10 until 16:00 UTC +10



DataHall 4

B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.



· So looks like no power on 3 data halls B feeds on the same day.

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread James Braunegg
Dear All

Anyone with single power supply devices please do not look at getting an ATS, 
get a STS !!!

Short version

ATS (Automatic Transfer Switch) will typically break power before it makes, 
thus the connected device could reboot !!

STS (Static Transfer Switch) will make power before it breaks, providing no 
break to the power  !

An example of a recommended device is below

https://www.vertivco.com/en-asia/products-catalog/critical-power/power-transfer-switches/liebert-lts-63-to-400a/

Kindest Regards,

James Braunegg



[cid:image001.png@01D280A4.01865B60]

1300 769 972 / 0488 997 207

ja...@micron21.com<mailto:ja...@micron21.com>

www.micron21.com/<http://www.micron21.com/>


[cid:image002.png@01D280A4.01865B60]<http://www.micron21.com/>


[cid:image003.png@01D280A4.01865B60]<https://www.facebook.com/micron21/>

[cid:image004.png@01D280A4.01865B60]<https://twitter.com/micron21>

Follow us on Twitter<https://twitter.com/micron21> for important service and 
system updates.


This message is intended for the addressee named above. It may contain 
privileged or confidential information. If you are not the intended recipient 
of this message you must not use, copy, distribute or disclose it to anyone 
other than the addressee. If you have received this message in error please 
return the message to the sender by replying to it and then delete the message 
from your computer.




From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Matthew Smee
Sent: Thursday, 10 August 2017 12:00 PM
To: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

+1
Every DC agreement I’ve seen (3) have mentioned that you are responsible for 
supplying it with power and they aren’t responsible if it loses power (i.e. use 
an ATS).

From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Sam Silvester
Sent: Thursday, 10 August 2017 10:14 AM
To: Shaun McGuane mailto:sh...@rackcentral.com>>
Cc: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

If you have single fed equipment in your rack that needs planning before it can 
be shut down, do you not run a totally forseeable and preventable risk then 
should that one feed trip?

This is what ATS are for.

Sam



On Thursday, 10 August 2017, Shaun McGuane 
mailto:sh...@rackcentral.com>> wrote:
HI Simon,

Thank you for your input to the list.

While you may have provided notifications well in advance, your schedule 
provided has been changed multiple times and this creates confusion.
Without asking for further clarification last night I would never have received 
the following updated schedule from Craig Armstrong today.

Data Hall 2 – B feed (west/blue PDU side) Tuesday 15th Aug, A feed has been 
pushed back to later date around November, you will receive official notice 
once new date confirmed.
Data Hall 3 –A and B feed has been pushed back to later date around 
October/November, you will receive official notice once new date confirmed.
Data Hall 4 –A and B feed has been pushed back to later date around 
October/November, you will receive official notice once new date confirmed.

From the latest update today, It appears that most of the works are being 
postponed for the time being

Not all devices within racks support 2 feeds and planning is involved with 
these devices, which is why it is crucial to receive accurate information about 
any pending outages or upgrades
to the NextDC DataCentres which affect services.

Additionally, I have not received these updates via the normal NextDC E-Mail 
communication method, so I am sure other customers will be wondering whats 
happening too.

Happy to have a conversation offline about this feel free to give me a call on 
my mobile.

Regards
Shaun



From: AusNOG 
[mailto:ausnog-boun...@lists.ausnog.net]
 On Behalf Of Simon Cooper
Sent: Thursday, 10 August 2017 8:39 AM
To: 
ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

Thanks guys, appreciate the feedback.

At NEXTDC we work very hard to keep critical infrastructure maintenance that 
impacts racks or the environment within the data hall to an absolute minimum.

However, some works are required to happen from time to time by law and one of 
those activities is a de-energisation and inspection of each of our major 
switchboards.  This is all about ensuring that the electrical system is safe, 
and is an unavoidable piece of work. Rightly so.

Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we 
highly recommend that they are used for every device in the rack.  This 
occasional maintenance is one of the many reasons we provide this capability.  
Any device using the 2N supplies (aka A & B feeds) will simply see its power 
swing from one feed to the other.  Any rack that is drawing n

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Matthew Smee
+1
Every DC agreement I’ve seen (3) have mentioned that you are responsible for 
supplying it with power and they aren’t responsible if it loses power (i.e. use 
an ATS).

From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Sam Silvester
Sent: Thursday, 10 August 2017 10:14 AM
To: Shaun McGuane 
Cc: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

If you have single fed equipment in your rack that needs planning before it can 
be shut down, do you not run a totally forseeable and preventable risk then 
should that one feed trip?

This is what ATS are for.

Sam



On Thursday, 10 August 2017, Shaun McGuane 
mailto:sh...@rackcentral.com>> wrote:
HI Simon,

Thank you for your input to the list.

While you may have provided notifications well in advance, your schedule 
provided has been changed multiple times and this creates confusion.
Without asking for further clarification last night I would never have received 
the following updated schedule from Craig Armstrong today.

Data Hall 2 – B feed (west/blue PDU side) Tuesday 15th Aug, A feed has been 
pushed back to later date around November, you will receive official notice 
once new date confirmed.
Data Hall 3 –A and B feed has been pushed back to later date around 
October/November, you will receive official notice once new date confirmed.
Data Hall 4 –A and B feed has been pushed back to later date around 
October/November, you will receive official notice once new date confirmed.

From the latest update today, It appears that most of the works are being 
postponed for the time being

Not all devices within racks support 2 feeds and planning is involved with 
these devices, which is why it is crucial to receive accurate information about 
any pending outages or upgrades
to the NextDC DataCentres which affect services.

Additionally, I have not received these updates via the normal NextDC E-Mail 
communication method, so I am sure other customers will be wondering whats 
happening too.

Happy to have a conversation offline about this feel free to give me a call on 
my mobile.

Regards
Shaun



From: AusNOG 
[mailto:ausnog-boun...@lists.ausnog.net]
 On Behalf Of Simon Cooper
Sent: Thursday, 10 August 2017 8:39 AM
To: 
ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

Thanks guys, appreciate the feedback.

At NEXTDC we work very hard to keep critical infrastructure maintenance that 
impacts racks or the environment within the data hall to an absolute minimum.

However, some works are required to happen from time to time by law and one of 
those activities is a de-energisation and inspection of each of our major 
switchboards.  This is all about ensuring that the electrical system is safe, 
and is an unavoidable piece of work. Rightly so.

Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we 
highly recommend that they are used for every device in the rack.  This 
occasional maintenance is one of the many reasons we provide this capability.  
Any device using the 2N supplies (aka A & B feeds) will simply see its power 
swing from one feed to the other.  Any rack that is drawing no more that its 
contracted power level will have no issue when all devices move from A to B or 
vice versa.

Our notifications were made well in advance, as we want to give customers time 
to consider the management of these works and we don't assume that every rack 
is perfectly deployed:  We are here 24/7 to assist customers with rack 
inspections or specific circuit down tests or maybe a controlled move prior to 
the day (e.g. for devices that are single fed).

Also, as we work though those discussions with customers we understand the 
timing in relation to their businesses, and we work very hard to coordinate 
schedules despite each switch board supporting many different customers and 
customer instances across the data centre.  Occasionally that means we have to 
make a difficult decisions which may result in schedule changes.  When that 
does happen, we do not compromise our notification periods.

I'll be happy to discuss these works with anyone - probably best offline or on 
the phone - but trust me when I say we are doing our absolute best to keep your 
data centre operating safely and reliably for many years to come.

Thanks,
Simon
COO, NEXTDC

-Original Message-
From: nat...@nightsys.net
Sent: Thu, 10 Aug 2017 05:39:02 +1000
To: sh...@rackcentral.com
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August
This seems reasonable? As long as no single Data Hall has both A and B feeds 
removed simultaneously, that seems normal. Doing B on Hall 2 and A on Hall 3 on 
the same day does seem slightly adventurous, but not entirely unreasonable 
(mostly in terms of if something goes bad in both, staff get stretched thin 
remediating issues).

A and B feeds are designed to p

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Sam Silvester
If you have single fed equipment in your rack that needs planning before it
can be shut down, do you not run a totally forseeable and preventable risk
then should that one feed trip?

This is what ATS are for.

Sam



On Thursday, 10 August 2017, Shaun McGuane  wrote:

> HI Simon,
>
>
>
> Thank you for your input to the list.
>
>
>
> While you may have provided notifications well in advance, your schedule
> provided has been changed multiple times and this creates confusion.
>
> Without asking for further clarification last night I would never have
> received the following updated schedule from Craig Armstrong today.
>
>
>
> Data Hall 2 – B feed (west/blue PDU side) Tuesday 15th Aug, A feed has
> been pushed back to later date around November, you will receive official
> notice once new date confirmed.
>
> Data Hall 3 –A and B feed has been pushed back to later date around
> October/November, you will receive official notice once new date confirmed.
>
> Data Hall 4 –A and B feed has been pushed back to later date around
> October/November, you will receive official notice once new date confirmed.
>
>
>
> From the latest update today, It appears that most of the works are being
> postponed for the time being
>
>
>
> Not all devices within racks support 2 feeds and planning is involved with
> these devices, which is why it is crucial to receive accurate information
> about any pending outages or upgrades
> to the NextDC DataCentres which affect services.
>
>
>
> Additionally, I have not received these updates via the normal NextDC
> E-Mail communication method, so I am sure other customers will be wondering
> whats happening too.
>
>
>
> Happy to have a conversation offline about this feel free to give me a
> call on my mobile.
>
>
>
> Regards
>
> Shaun
>
>
>
>
>
>
>
> *From:* AusNOG [mailto:ausnog-boun...@lists.ausnog.net
> ] *On
> Behalf Of *Simon Cooper
> *Sent:* Thursday, 10 August 2017 8:39 AM
> *To:* ausnog@lists.ausnog.net
> 
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
>
>
> Thanks guys, appreciate the feedback.
>
>
>
> At NEXTDC we work very hard to keep critical infrastructure maintenance
> that impacts racks or the environment within the data hall to an absolute
> minimum.
>
>
>
> However, some works are required to happen from time to time by law and
> one of those activities is a de-energisation and inspection of each of our
> major switchboards.  This is all about ensuring that the electrical system
> is safe, and is an unavoidable piece of work. Rightly so.
>
>
>
> Every rack in a NEXTDC data centre has 2N power feeds offered to it, and
> we highly recommend that they are used for every device in the rack.  This
> occasional maintenance is one of the many reasons we provide this
> capability.  Any device using the 2N supplies (aka A & B feeds) will simply
> see its power swing from one feed to the other.  Any rack that is drawing
> no more that its contracted power level will have no issue when all devices
> move from A to B or vice versa.
>
>
>
> Our notifications were made well in advance, as we want to give customers
> time to consider the management of these works and we don't assume that
> every rack is perfectly deployed:  We are here 24/7 to assist customers
> with rack inspections or specific circuit down tests or maybe a controlled
> move prior to the day (e.g. for devices that are single fed).
>
>
>
> Also, as we work though those discussions with customers we understand the
> timing in relation to their businesses, and we work very hard to coordinate
> schedules despite each switch board supporting many different customers and
> customer instances across the data centre.  Occasionally that means we have
> to make a difficult decisions which may result in schedule changes.  When
> that does happen, we do not compromise our notification periods.
>
>
>
> I'll be happy to discuss these works with anyone - probably best offline
> or on the phone - but trust me when I say we are doing our absolute best to
> keep your data centre operating safely and reliably for many years to come.
>
>
>
> Thanks,
>
> Simon
>
> COO, NEXTDC
>
>
>
> -Original Message-
> *From:* nat...@nightsys.net
> 
> *Sent:* Thu, 10 Aug 2017 05:39:02 +1000
> *To:* sh...@rackcentral.com
> 
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
> This seems reasonable? As long as no single Data Hall has both A and B
> feeds removed simultaneously, that seems normal. Doing B on Hall 2 and A on
> Hall 3 o

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Shaun McGuane
HI Simon,

Thank you for your input to the list.

While you may have provided notifications well in advance, your schedule 
provided has been changed multiple times and this creates confusion.
Without asking for further clarification last night I would never have received 
the following updated schedule from Craig Armstrong today.

Data Hall 2 – B feed (west/blue PDU side) Tuesday 15th Aug, A feed has been 
pushed back to later date around November, you will receive official notice 
once new date confirmed.
Data Hall 3 –A and B feed has been pushed back to later date around 
October/November, you will receive official notice once new date confirmed.
Data Hall 4 –A and B feed has been pushed back to later date around 
October/November, you will receive official notice once new date confirmed.

From the latest update today, It appears that most of the works are being 
postponed for the time being

Not all devices within racks support 2 feeds and planning is involved with 
these devices, which is why it is crucial to receive accurate information about 
any pending outages or upgrades
to the NextDC DataCentres which affect services.

Additionally, I have not received these updates via the normal NextDC E-Mail 
communication method, so I am sure other customers will be wondering whats 
happening too.

Happy to have a conversation offline about this feel free to give me a call on 
my mobile.

Regards
Shaun



From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Simon Cooper
Sent: Thursday, 10 August 2017 8:39 AM
To: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

Thanks guys, appreciate the feedback.

At NEXTDC we work very hard to keep critical infrastructure maintenance that 
impacts racks or the environment within the data hall to an absolute minimum.

However, some works are required to happen from time to time by law and one of 
those activities is a de-energisation and inspection of each of our major 
switchboards.  This is all about ensuring that the electrical system is safe, 
and is an unavoidable piece of work. Rightly so.

Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we 
highly recommend that they are used for every device in the rack.  This 
occasional maintenance is one of the many reasons we provide this capability.  
Any device using the 2N supplies (aka A & B feeds) will simply see its power 
swing from one feed to the other.  Any rack that is drawing no more that its 
contracted power level will have no issue when all devices move from A to B or 
vice versa.

Our notifications were made well in advance, as we want to give customers time 
to consider the management of these works and we don't assume that every rack 
is perfectly deployed:  We are here 24/7 to assist customers with rack 
inspections or specific circuit down tests or maybe a controlled move prior to 
the day (e.g. for devices that are single fed).

Also, as we work though those discussions with customers we understand the 
timing in relation to their businesses, and we work very hard to coordinate 
schedules despite each switch board supporting many different customers and 
customer instances across the data centre.  Occasionally that means we have to 
make a difficult decisions which may result in schedule changes.  When that 
does happen, we do not compromise our notification periods.

I'll be happy to discuss these works with anyone - probably best offline or on 
the phone - but trust me when I say we are doing our absolute best to keep your 
data centre operating safely and reliably for many years to come.

Thanks,
Simon
COO, NEXTDC

-Original Message-
From: nat...@nightsys.net<mailto:nat...@nightsys.net>
Sent: Thu, 10 Aug 2017 05:39:02 +1000
To: sh...@rackcentral.com<mailto:sh...@rackcentral.com>
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August
This seems reasonable? As long as no single Data Hall has both A and B feeds 
removed simultaneously, that seems normal. Doing B on Hall 2 and A on Hall 3 on 
the same day does seem slightly adventurous, but not entirely unreasonable 
(mostly in terms of if something goes bad in both, staff get stretched thin 
remediating issues).

A and B feeds are designed to provide redundancy to equipment, allowing one 
feed to fail and systems to continue on the other. Anything mission critical 
should be able to draw from either feed as required (dual PSU), and if there is 
a power deficit on one feed (causing circuits to trip), that would imply the 
circuits are incorrectly sized?

In addition, anything mission critical with a single power supply would be on 
an ATS you would assume, or a pair of equivalent devices installed with one on 
each rail?

Things break in datacentres, planned maintenance happens sometimes, better than 
no maintenance at all :) The fact they are notifying you is better than not, 
and it being schedule

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Karl Hardisty
An off-the-cuff observation with little real thought put into it:

offloading an A feed in one hall and a B feed in the other (if at the same 
time) seems a reasonable method - intentional or not - of keeping the 
cumulative data centre load even across feeds. 

They should be fine standalone anyway, but high current loads have a way of 
finding any weakness in the circuit path. 

As mentioned, use redundant power/ATS whatever to ensure your critical kit up, 
and have faith in your choice of DC. 

Karl


> On 10/08/2017, at 10:39 AM, Simon Cooper  wrote:
> 
> Thanks guys, appreciate the feedback.
> 
> At NEXTDC we work very hard to keep critical infrastructure maintenance that 
> impacts racks or the environment within the data hall to an absolute minimum.
> 
> However, some works are required to happen from time to time by law and one 
> of those activities is a de-energisation and inspection of each of our major 
> switchboards.  This is all about ensuring that the electrical system is safe, 
> and is an unavoidable piece of work. Rightly so.
> 
> Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we 
> highly recommend that they are used for every device in the rack.  This 
> occasional maintenance is one of the many reasons we provide this capability. 
>  Any device using the 2N supplies (aka A & B feeds) will simply see its power 
> swing from one feed to the other.  Any rack that is drawing no more that its 
> contracted power level will have no issue when all devices move from A to B 
> or vice versa.
> 
> Our notifications were made well in advance, as we want to give customers 
> time to consider the management of these works and we don't assume that every 
> rack is perfectly deployed:  We are here 24/7 to assist customers with rack 
> inspections or specific circuit down tests or maybe a controlled move prior 
> to the day (e.g. for devices that are single fed).
> 
> Also, as we work though those discussions with customers we understand the 
> timing in relation to their businesses, and we work very hard to coordinate 
> schedules despite each switch board supporting many different customers and 
> customer instances across the data centre.  Occasionally that means we have 
> to make a difficult decisions which may result in schedule changes.  When 
> that does happen, we do not compromise our notification periods.
> 
> I'll be happy to discuss these works with anyone - probably best offline or 
> on the phone - but trust me when I say we are doing our absolute best to keep 
> your data centre operating safely and reliably for many years to come.
> 
> Thanks,
> Simon
> COO, NEXTDC
> 
> -Original Message-----
> From: nat...@nightsys.net
> Sent: Thu, 10 Aug 2017 05:39:02 +1000
> To: sh...@rackcentral.com
> Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
> August
> 
> This seems reasonable? As long as no single Data Hall has both A and B feeds 
> removed simultaneously, that seems normal. Doing B on Hall 2 and A on Hall 3 
> on the same day does seem slightly adventurous, but not entirely unreasonable 
> (mostly in terms of if something goes bad in both, staff get stretched thin 
> remediating issues).
> 
> A and B feeds are designed to provide redundancy to equipment, allowing one 
> feed to fail and systems to continue on the other. Anything mission critical 
> should be able to draw from either feed as required (dual PSU), and if there 
> is a power deficit on one feed (causing circuits to trip), that would imply 
> the circuits are incorrectly sized?
> 
> In addition, anything mission critical with a single power supply would be on 
> an ATS you would assume, or a pair of equivalent devices installed with one 
> on each rail?
> 
> Things break in datacentres, planned maintenance happens sometimes, better 
> than no maintenance at all :) The fact they are notifying you is better than 
> not, and it being scheduled is probably still better than unscheduled :) 
> (easier to ensure sufficient staffing to keep a close eye on things)
> 
> Nathan.
> 
> On Wed, Aug 9, 2017 at 3:43 PM, Shaun McGuane  <mailto:sh...@rackcentral.com>> wrote:
> Here is the entire scheduled maintenance windows for all the halls we occupy.
> 
>  
> 
> DataHall 2
> 
> A Feed - Tuesday 8th August 2017 07:00 UTC +10 until 16:00 UTC +10.
> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
> 
>  
> 
> DataHall 3
> 
> A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10
> B Feed - Monday 14th August 2017 07:00 UTC +10 until 16:00 UTC +10
> 
>  
> 
> DataHall 4
> 
> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
> 
>

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Simon Cooper





Thanks guys, appreciate the feedback.At NEXTDC we work very hard to keep critical infrastructure maintenance that impacts racks or the environment within the data hall to an absolute minimum.However, some works are required to happen from time to time by law and one of those activities is a de-energisation and inspection of each of our major switchboards.  This is all about ensuring that the electrical system is safe, and is an unavoidable piece of work. Rightly so.Every rack in a NEXTDC data centre has 2N power feeds offered to it, and we highly recommend that they are used for every device in the rack.  This occasional maintenance is one of the many reasons we provide this capability.  Any device using the 2N supplies (aka A & B feeds) will simply see its power swing from one feed to the other.  Any rack that is drawing no more that its contracted power level will have no issue when all devices move from A to B or vice versa.Our notifications were made well in advance, as we want to give customers time to consider the management of these works and we don't assume that every rack is perfectly deployed:  We are here 24/7 to assist customers with rack inspections or specific circuit down tests or maybe a controlled move prior to the day (e.g. for devices that are single fed).Also, as we work though those discussions with customers we understand the timing in relation to their businesses, and we work very hard to coordinate schedules despite each switch board supporting many different customers and customer instances across the data centre.  Occasionally that means we have to make a difficult decisions which may result in schedule changes.  When that does happen, we do not compromise our notification periods.I'll be happy to discuss these works with anyone - probably best offline or on the phone - but trust me when I say we are doing our absolute best to keep your data centre operating safely and reliably for many years to come.Thanks,SimonCOO, NEXTDC-Original Message-From: nat...@nightsys.netSent: Thu, 10 Aug 2017 05:39:02 +1000To: sh...@rackcentral.comSubject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th AugustThis seems reasonable? As long as no single Data Hall has both A and B feeds removed simultaneously, that seems normal. Doing B on Hall 2 and A on Hall 3 on the same day does seem slightly adventurous, but not entirely unreasonable (mostly in terms of if something goes bad in both, staff get stretched thin remediating issues).A and B feeds are designed to provide redundancy to equipment, allowing one feed to fail and systems to continue on the other. Anything mission critical should be able to draw from either feed as required (dual PSU), and if there is a power deficit on one feed (causing circuits to trip), that would imply the circuits are incorrectly sized?In addition, anything mission critical with a single power supply would be on an ATS you would assume, or a pair of equivalent devices installed with one on each rail?Things break in datacentres, planned maintenance happens sometimes, better than no maintenance at all :) The fact they are notifying you is better than not, and it being scheduled is probably still better than unscheduled :) (easier to ensure sufficient staffing to keep a close eye on things)Nathan.On Wed, Aug 9, 2017 at 3:43 PM, Shaun McGuane <sh...@rackcentral.com> wrote:







Here is the entire scheduled maintenance windows for all the halls we occupy.
 
DataHall 2
A Feed - Tuesday 8th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
 
DataHall 3
A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10
B Feed - Monday 14th August 2017 07:00 UTC +10 until 16:00 UTC +10
 
DataHall 4
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
 
·
So looks like no power on 3 data halls B feeds on the same day.

·
Data Hall 2 was scheduled for A rail on the 8th of August but has been re-scheduled with no new date of works.
·
Data Hall 3 was scheduled for A rail on the

 
Problem is that I have 3x separate dates on 3 separate e-mails for Data Hall 3 and I have requested a revised clarification

Just now on the above as there has already been re-schedules for Data Hall 2 and 3.
 
This feels like it’s going sideways and it has not even started.
 
Regards
Shaun
 
 


From: AusNOG [mailto:ausnog-bounces@lists.ausnog.net]
On Behalf Of Murat Sener
Sent: Wednesday, 9 August 2017 3:20 PM
To: Matthew VK3EVL <hit...@itglowz.com>; ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August


 
We have been told only Feed B in Data hall 2 will be effected as per original schedule and Feed A is yet
 to be rescheduled.
 
 
 








Murat Sener Datacentre
 Manager




PREMIER Technology Solutions
P.
1300 76 76 48   
F.
1300 76 76 49   
M.
0450 604 350





 




How am I 

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-09 Thread Nathan Sullivan
This seems reasonable? As long as no single Data Hall has both A and B
feeds removed simultaneously, that seems normal. Doing B on Hall 2 and A on
Hall 3 on the same day does seem slightly adventurous, but not entirely
unreasonable (mostly in terms of if something goes bad in both, staff get
stretched thin remediating issues).

A and B feeds are designed to provide redundancy to equipment, allowing one
feed to fail and systems to continue on the other. Anything mission
critical should be able to draw from either feed as required (dual PSU),
and if there is a power deficit on one feed (causing circuits to trip),
that would imply the circuits are incorrectly sized?

In addition, anything mission critical with a single power supply would be
on an ATS you would assume, or a pair of equivalent devices installed with
one on each rail?

Things break in datacentres, planned maintenance happens sometimes, better
than no maintenance at all :) The fact they are notifying you is better
than not, and it being scheduled is probably still better than unscheduled
:) (easier to ensure sufficient staffing to keep a close eye on things)

Nathan.

On Wed, Aug 9, 2017 at 3:43 PM, Shaun McGuane  wrote:

> Here is the entire scheduled maintenance windows for all the halls we
> occupy.
>
>
>
> DataHall 2
>
> A Feed - Tuesday 8th August 2017 07:00 UTC +10 until 16:00 UTC +10.
> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
>
>
>
> DataHall 3
>
> A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10
> B Feed - Monday 14th August 2017 07:00 UTC +10 until 16:00 UTC +10
>
>
>
> DataHall 4
>
> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
>
>
>
> · So looks like no power on 3 data halls B feeds on the same day.
>
> · Data Hall 2 was scheduled for A rail on the 8th of August but
> has been re-scheduled with no new date of works.
>
> · Data Hall 3 was scheduled for A rail on the
>
>
>
> Problem is that I have 3x separate dates on 3 separate e-mails for Data
> Hall 3 and I have requested a revised clarification
>
> Just now on the above as there has already been re-schedules for Data Hall
> 2 and 3.
>
>
>
> This feels like it’s going sideways and it has not even started.
>
>
>
> Regards
>
> Shaun
>
>
>
>
>
> *From:* AusNOG [mailto:ausnog-boun...@lists.ausnog.net] *On Behalf Of *Murat
> Sener
> *Sent:* Wednesday, 9 August 2017 3:20 PM
> *To:* Matthew VK3EVL ; ausnog@lists.ausnog.net
>
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
>
>
> We have been told only Feed B in Data hall 2 will be effected as per
> original schedule and Feed A is yet to be rescheduled.
>
>
>
>
>
>
>
> *Murat Sener* Datacentre Manager
>
> *PREMIER* Technology Solutions
> *P. *1300 76 76 48*F. *1300 76 76 49*M. *0450 604 350
>
>
>
> *How am I doing? Let us know!*
> SIMPLY CLICK ON A FACE TO GIVE FEEDBACK
>
> *GREAT*
>
> *AVERAGE*
>
> *BAD*
>
>
> <https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=5>
>
>
> <https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=0>
>
>
> <https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=-5>
>
>
>
> *From:* AusNOG [mailto:ausnog-boun...@lists.ausnog.net
> ] *On Behalf Of *Matthew VK3EVL
> *Sent:* Wednesday, 9 August 2017 3:13 PM
> *To:* ausnog@lists.ausnog.net
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
>
>
> What about both feeds happening on the same day at the same time?
>
>
>
> On 9/08/2017 2:55 PM, Shaun McGuane wrote:
>
> HI Damien,
>
>
>
> My apologies that’s correct – but isn’t anyone concerned about the works
> being completed during business hours?
>
> What about increased loading of the active rail once one of them is
> switched off for these works?
>
>
>
> Regards
>
> Shaun
>
>
>
>
>
> *From:* Damien Gardner Jnr [mailto:rend...@rendrag.net
> ]
> *Sent:* Wednesday, 9 August 2017 2:39 PM
> *To:*  
>  ; Shaun McGuane
>  
> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance -
> 15th August
>
>
>
> It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)
>
>
>
> On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane 
> wrote:
>
> HI Noggers,
>
>
>
> Has anyone seen this scheduled maintenance notification happening next
> week?
>
> They maybe upgrading feeds or boards throughou

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-08 Thread Shaun McGuane
Here is the entire scheduled maintenance windows for all the halls we occupy.

DataHall 2
A Feed - Tuesday 8th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.

DataHall 3
A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10
B Feed - Monday 14th August 2017 07:00 UTC +10 until 16:00 UTC +10

DataHall 4
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.


· So looks like no power on 3 data halls B feeds on the same day.

· Data Hall 2 was scheduled for A rail on the 8th of August but has 
been re-scheduled with no new date of works.

· Data Hall 3 was scheduled for A rail on the

Problem is that I have 3x separate dates on 3 separate e-mails for Data Hall 3 
and I have requested a revised clarification
Just now on the above as there has already been re-schedules for Data Hall 2 
and 3.

This feels like it’s going sideways and it has not even started.

Regards
Shaun


From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Murat Sener
Sent: Wednesday, 9 August 2017 3:20 PM
To: Matthew VK3EVL ; ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

We have been told only Feed B in Data hall 2 will be effected as per original 
schedule and Feed A is yet to be rescheduled.



[cid:image001.png@01D31125.F3826EB0]

Murat Sener Datacentre Manager

PREMIER Technology Solutions
P. 1300 76 76 48F. 1300 76 76 49M. 0450 604 350


How am I doing? Let us know!
SIMPLY CLICK ON A FACE TO GIVE FEEDBACK

GREAT

AVERAGE

BAD

[cid:image002.png@01D31125.F3826EB0]<https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=5>

[cid:image003.png@01D31125.F3826EB0]<https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=0>

[cid:image004.png@01D31125.F3826EB0]<https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=-5>



From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Matthew 
VK3EVL
Sent: Wednesday, 9 August 2017 3:13 PM
To: ausnog@lists.ausnog.net<mailto:ausnog@lists.ausnog.net>
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August


What about both feeds happening on the same day at the same time?

On 9/08/2017 2:55 PM, Shaun McGuane wrote:
HI Damien,

My apologies that’s correct – but isn’t anyone concerned about the works being 
completed during business hours?
What about increased loading of the active rail once one of them is switched 
off for these works?

Regards
Shaun


From: Damien Gardner Jnr [mailto:rend...@rendrag.net]
Sent: Wednesday, 9 August 2017 2:39 PM
To: <mailto:ausnog@lists.ausnog.net> 
<mailto:ausnog@lists.ausnog.net>; Shaun McGuane 
<mailto:sh...@rackcentral.com>
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)

On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane 
mailto:sh...@rackcentral.com>> wrote:
HI Noggers,

Has anyone seen this scheduled maintenance notification happening next week?
They maybe upgrading feeds or boards throughout the datacentre – has everyone 
seen this notification of works?
It appears to be happening starting 5PM through to 2AM AEST for all Datahalls 
on the same date.


WHAT:
NEXTDC M1 Melbourne data centre, with the assistance of specialist contractors, 
will conduct offline preventative electrical maintenance work on high-voltage 
and low-voltage main isolators. This will affect A and B feeds to the racks in 
Data Hall 2/3/4 on the 15th of August.

WHEN:
A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.

HOW AM I AFFECTED?
Due to the nature of the work a single feed will be removed as per the dates 
and times above. We recommend that customers balance the power between both 
power rails to minimise impact during this period. If you have single feed 
devices we recommend you:

Regards
Shaun



___
AusNOG mailing list
AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>
http://lists.ausnog.net/mailman/listinfo/ausnog
--

Damien Gardner Jnr
VK2TDG. Dip EE. GradIEAust
rend...@rendrag.net<mailto:rend...@rendrag.net> -  http://www.rendrag.net/
--
We rode on the winds of the rising storm,
 We ran to the sounds of thunder.
We danced among the lightning bolts,
 and tore the world asunder



___

AusNOG mailing list

AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>

http://lists.ausnog.net/mailman/listinfo/ausnog


MESSAGE PROTECTED BY PREMIER TECHNOLOGY 
SOLUTIONS<http://www.premiertech.com.au> - POWERED BY 
MAILGUARD<http://www.mailguard

Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-08 Thread Murat Sener
We have been told only Feed B in Data hall 2 will be effected as per original 
schedule and Feed A is yet to be rescheduled.



[cid:image001.png@01D31122.E6282FF0]

Murat Sener Datacentre Manager

PREMIER Technology Solutions
P. 1300 76 76 48F. 1300 76 76 49M. 0450 604 350


How am I doing? Let us know!
SIMPLY CLICK ON A FACE TO GIVE FEEDBACK

GREAT

AVERAGE

BAD

[cid:image002.png@01D31122.E6282FF0]<https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=5>

[cid:image003.png@01D31122.E6282FF0]<https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=0>

[cid:image004.png@01D31122.E6282FF0]<https://www.crewhu.com/survey.html?crewHuID=qm0Hxbzstp&employeeID=rLeIz2SkIa&type=signat&rating=-5>



From: AusNOG [mailto:ausnog-boun...@lists.ausnog.net] On Behalf Of Matthew 
VK3EVL
Sent: Wednesday, 9 August 2017 3:13 PM
To: ausnog@lists.ausnog.net
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August


What about both feeds happening on the same day at the same time?

On 9/08/2017 2:55 PM, Shaun McGuane wrote:
HI Damien,

My apologies that’s correct – but isn’t anyone concerned about the works being 
completed during business hours?
What about increased loading of the active rail once one of them is switched 
off for these works?

Regards
Shaun


From: Damien Gardner Jnr [mailto:rend...@rendrag.net]
Sent: Wednesday, 9 August 2017 2:39 PM
To: <mailto:ausnog@lists.ausnog.net> 
<mailto:ausnog@lists.ausnog.net>; Shaun McGuane 
<mailto:sh...@rackcentral.com>
Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)

On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane 
mailto:sh...@rackcentral.com>> wrote:
HI Noggers,

Has anyone seen this scheduled maintenance notification happening next week?
They maybe upgrading feeds or boards throughout the datacentre – has everyone 
seen this notification of works?
It appears to be happening starting 5PM through to 2AM AEST for all Datahalls 
on the same date.


WHAT:
NEXTDC M1 Melbourne data centre, with the assistance of specialist contractors, 
will conduct offline preventative electrical maintenance work on high-voltage 
and low-voltage main isolators. This will affect A and B feeds to the racks in 
Data Hall 2/3/4 on the 15th of August.

WHEN:
A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.

HOW AM I AFFECTED?
Due to the nature of the work a single feed will be removed as per the dates 
and times above. We recommend that customers balance the power between both 
power rails to minimise impact during this period. If you have single feed 
devices we recommend you:

Regards
Shaun



___
AusNOG mailing list
AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>
http://lists.ausnog.net/mailman/listinfo/ausnog
--

Damien Gardner Jnr
VK2TDG. Dip EE. GradIEAust
rend...@rendrag.net<mailto:rend...@rendrag.net> -  http://www.rendrag.net/
--
We rode on the winds of the rising storm,
 We ran to the sounds of thunder.
We danced among the lightning bolts,
 and tore the world asunder




___

AusNOG mailing list

AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>

http://lists.ausnog.net/mailman/listinfo/ausnog


MESSAGE PROTECTED BY PREMIER TECHNOLOGY 
SOLUTIONS<http://www.premiertech.com.au> - POWERED BY 
MAILGUARD<http://www.mailguard.com.au/mg>.
Report this message as 
spam<https://console.mailguard.com.au/ras/1RqQHQIE5J/6DWUZjiMDnlts7JYyCLNB3/0>

-- 
MESSAGE PROTECTED BY PREMIER TECHNOLOGY SOLUTIONS - POWERED BY MAILGUARD.


___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-08 Thread Matthew VK3EVL

What about both feeds happening on the same day at the same time?


On 9/08/2017 2:55 PM, Shaun McGuane wrote:


HI Damien,

My apologies that’s correct – but isn’t anyone concerned about the 
works being completed during business hours?


What about increased loading of the active rail once one of them is 
switched off for these works?


Regards

Shaun

*From:*Damien Gardner Jnr [mailto:rend...@rendrag.net]
*Sent:* Wednesday, 9 August 2017 2:39 PM
*To:*  ; Shaun 
McGuane 
*Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance 
- 15th August


It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)

On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane <mailto:sh...@rackcentral.com>> wrote:


HI Noggers,

Has anyone seen this scheduled maintenance notification happening
next week?

They maybe upgrading feeds or boards throughout the datacentre –
has everyone seen this notification of works?

It appears to be happening starting 5PM through to 2AM AEST for
all Datahalls on the same date.

*WHAT:*
NEXTDC M1 Melbourne data centre, with the assistance of specialist
contractors, will conduct offline preventative electrical
maintenance work on high-voltage and low-voltage main isolators.
This will affect A and B feeds to the racks in Data Hall 2/3/4 on
the 15th of August.

*WHEN:*
A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.

*HOW AM I AFFECTED?*
Due to the nature of the work a single feed will be removed as per
the dates and times above. We recommend that customers balance the
power between both power rails to minimise impact during this
period. If you have single feed devices we recommend you:

Regards

Shaun

___
AusNOG mailing list
AusNOG@lists.ausnog.net <mailto:AusNOG@lists.ausnog.net>
http://lists.ausnog.net/mailman/listinfo/ausnog

--

Damien Gardner Jnr
VK2TDG. Dip EE. GradIEAust
rend...@rendrag.net <mailto:rend...@rendrag.net> - 
http://www.rendrag.net/_

_--
We rode on the winds of the rising storm,
 We ran to the sounds of thunder.
We danced among the lightning bolts,
 and tore the world asunder



___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-08 Thread Shaun McGuane
HI Damien,

My apologies that’s correct – but isn’t anyone concerned about the works being 
completed during business hours?
What about increased loading of the active rail once one of them is switched 
off for these works?

Regards
Shaun


From: Damien Gardner Jnr [mailto:rend...@rendrag.net]
Sent: Wednesday, 9 August 2017 2:39 PM
To:  ; Shaun McGuane 

Subject: Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th 
August

It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)

On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane 
mailto:sh...@rackcentral.com>> wrote:
HI Noggers,

Has anyone seen this scheduled maintenance notification happening next week?
They maybe upgrading feeds or boards throughout the datacentre – has everyone 
seen this notification of works?
It appears to be happening starting 5PM through to 2AM AEST for all Datahalls 
on the same date.


WHAT:
NEXTDC M1 Melbourne data centre, with the assistance of specialist contractors, 
will conduct offline preventative electrical maintenance work on high-voltage 
and low-voltage main isolators. This will affect A and B feeds to the racks in 
Data Hall 2/3/4 on the 15th of August.

WHEN:
A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.

HOW AM I AFFECTED?
Due to the nature of the work a single feed will be removed as per the dates 
and times above. We recommend that customers balance the power between both 
power rails to minimise impact during this period. If you have single feed 
devices we recommend you:

Regards
Shaun



___
AusNOG mailing list
AusNOG@lists.ausnog.net<mailto:AusNOG@lists.ausnog.net>
http://lists.ausnog.net/mailman/listinfo/ausnog
--

Damien Gardner Jnr
VK2TDG. Dip EE. GradIEAust
rend...@rendrag.net<mailto:rend...@rendrag.net> -  http://www.rendrag.net/
--
We rode on the winds of the rising storm,
 We ran to the sounds of thunder.
We danced among the lightning bolts,
 and tore the world asunder
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog


Re: [AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

2017-08-08 Thread Damien Gardner Jnr
It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)

On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane  wrote:

> HI Noggers,
>
>
>
> Has anyone seen this scheduled maintenance notification happening next
> week?
>
> They maybe upgrading feeds or boards throughout the datacentre – has
> everyone seen this notification of works?
>
> It appears to be happening starting 5PM through to 2AM AEST for all
> Datahalls on the same date.
>
>
>
>
>
> *WHAT:*
> NEXTDC M1 Melbourne data centre, with the assistance of specialist
> contractors, will conduct offline preventative electrical maintenance work
> on high-voltage and low-voltage main isolators. This will affect A and B
> feeds to the racks in Data Hall 2/3/4 on the 15th of August.
>
> *WHEN:*
> A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10.
>
> *HOW AM I AFFECTED?*
> Due to the nature of the work a single feed will be removed as per the
> dates and times above. We recommend that customers balance the power
> between both power rails to minimise impact during this period. If you have
> single feed devices we recommend you:
>
>
>
> Regards
>
> Shaun
>
>
>
>
>
>
> ___
> AusNOG mailing list
> AusNOG@lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
>
-- 

Damien Gardner Jnr
VK2TDG. Dip EE. GradIEAust
rend...@rendrag.net -  http://www.rendrag.net/
--
We rode on the winds of the rising storm,
 We ran to the sounds of thunder.
We danced among the lightning bolts,
 and tore the world asunder
___
AusNOG mailing list
AusNOG@lists.ausnog.net
http://lists.ausnog.net/mailman/listinfo/ausnog