Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Richard Nute
My understanding: Receptacles are not de-rated. A single load cannot exceed 80% (or some such percentage) of the branch circuit loading to allow other loads on the same branch circuit. If a single receptacle on the branch circuit, then the (single) load can be 100% of the branch circuit

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
That isn't a 'condition'. The conditions are the items in the a-b-c list in 6.1. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2017-10-11 21:42, James Pawson (U3C) wrote: It was the symmetrical control for the powering of heating elements

[PSES] US Firm Seeking Mechanical/Machinery Professional

2017-10-11 Thread Michael Violette
Hello Experts, I forward this as a potential opportunity for someone in our community. US test firm seeking experienced Machinery Directive engineers to support diverse clientele in the US. Engagement requires travel to client locations in the US to assess compliance with Machinery

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread James Pawson (U3C)
It was the symmetrical control for the powering of heating elements part that was the previous condition that was fulfilled. Hope this helps James John Woodgate wrote >OK, I've sent a digest to the committee chair. Meanwhile, I noticed >something that I don't quite understand: >

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
OK, I've sent a digest to the committee chair. Meanwhile, I noticed something that I don't quite understand: You say that "Clause 6.1 also says that symmetrical control for professional equipment is OK provided one of the “above conditions” is fulfilled (which it is, see previous bullet)"

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Nyffenegger, Dave
Not sure if your question is specific to NEC or not. There are other standards, for example UL 508A that have similar rules that are not specific to circuit sizes. And the rules are not all straight forward as they apply to conductor sizing, branch circuit protection, connectors/components,

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ralph McDiarmid
NEC article 210 writes about “branch circuits” up to 600V. I didn’t see a limit on current, so we’ve always applied it to OCP and ampacity for all conductors on circuits where the current is expected to be “continuous”, as defined in the code. ( we go up to 2000A on a 575V circuit on a custom

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Kunde, Brian
One last quick question, if I may, while we are all up on the NEC. Just to confirm, the 80% rule only applies to 15A, 20A, and 30A branch circuits. 40A and 50A branch circuits do not have the 80% rule, even in a multiple-outlet configuration? I know these larger circuits are generally

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread John Woodgate
Yes, of course quite a thin conductor will carry enough current to operate the protection, because it doesn't have time to get seriously hot. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2017-10-11 19:35, Kunde, Brian wrote: I know I

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
I don't know for sure. I was told that the low-frequency emission standards apply whether they are cited in a Generic or not.  61000-6-3 isn't restricted to 'residential, it includes 'commercial and light industrial, which is why 61000-3-11 and -12 are cited. Maybe 61000-6-3 assumes a

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ralph McDiarmid
Since you're asking for an opinion and since IEC would allow it, I think it's reasonable to allow it in N.Am too. There is no apparent hazard; the 15A OCPD adequately protects both the connector and the cordage. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Kunde, Brian
I know I started this thread, so I'm going to circuit back via another direction. The NEC allows a product with an 18 awg power cord (rated 10 amps), a 15 amp plug, and C13 IEC connector (15 amp) to be plugged into a 15 amp branch circuit. OH, you can also plug it into a 20 amp branch circuit

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread Ralph McDiarmid
That is an interesting technical point. Notice that EN61000-6-3 (generic residential) calls out 61000-3-2, -3, -11  and -12, but EN61000-6-4 (industrial) does not. Presumably, EN61000-6-4 makes full provision for the apparatus ? Ralph McDiarmid Product Compliance Engineering Solar Business

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Nyffenegger, Dave
For sure the A/C unit was not the original and it's possible the original had a NEMA 5-20P plug. It's only cooling the small bedroom and bath. The unit is rated 8.6A and the nameplate (picture of which is in my files) says in big bold letters USE ON SINGLE OUTLET CIRCUIT ONLY. -Dave

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Kunde, Brian
All, So the NEC allows you to draw the full 15 amps from a 15 amp receptacle IF it is on a dedicated circuit. BUT if the circuit is wired to more than one receptacle, then the product cannot draw more than 12 amps. What difference does that make? Same product, same power cord, same plug and

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Nyffenegger, Dave
Had a condo with a smallish through-the-wall A/C unit with NEMA 5-15P plug. In the room on one side of the unit was a dedicated 20A single outlet for the A/C unit. In the room on the other side easily within reach of the cord was a standard duplex outlet on the room circuit. Guess which

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Pete Perkins
Dave, The question is what was the rated current on the A/C unit? With the 15A plug it was probably rated at 12A unless it clearly specified a 'dedicated circuit'. I guess it's too long ago to go check on it. :>) br, Pete Peter E Perkins, PE Principal Product Safety &

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Pete Perkins
Ralph, Ted et al, Dunno how many times I have had this conversation with the project engineer who wants to use the full rated current from the duplex outlet (and not leave any for the other user who plugs into that outlet - which gives rise to the 80% rule) - except if they want to

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
61000-3-2, -3, -11  and -12 do not have to be cited in the Generics; they apply independently. 61000-3-4 assumes a dedicated MV/LV transformer, but the product is only 3 kW, so one can't assume that. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh,

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread Ralph McDiarmid
I wonder if your customer's triac equipment falls under the EN61000-6-4 (EMC) Emission standard for industrial environments? I didn't see 61000-3-2 called out in that generic standard. Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: James Pawson (U3C)

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
If there is only a very remote chance of the product being connected to *public* LV mains supplies (as opposed to industrial supplies from a dedicated MV/LV transformer), 61000-3-2 doesn't apply. Does it meet the Class A limits?  I agree that it's 'professional equipment', but, as you see, the

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread James Pawson (U3C)
Hello John, It uses phase angle control hence the concern about the harmonics generated. Manufacturer specs are single phase, 230V nominal, 3kW. Typically used at less than a 15% duty cycle, often less, in an industrial environment or powered from a generator. My *feeling* is that should

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ralph McDiarmid
Sounds like an example of the 125% rule for continuous (>3hr) current. (20/16) Ralph McDiarmid Product Compliance Engineering Solar Business Schneider Electric From: Ted Eckert [mailto:07cf6ebeab9d-dmarc-requ...@ieee.org] Sent: Wednesday, October 11, 2017 5:50 AM To:

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
I should also have asked what the rated power actually is, and whether it's 1-phase or 3-phase? John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2017-10-11 16:54, John Woodgate wrote: True, but it's a cumbersome procedure and is not

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
True, but it's a cumbersome procedure and is not clearly enough indicated. I will try to get an improvement. John Woodgate OOO-Own Opinions Only J M Woodgate and Associates www.woodjohn.uk Rayleigh, Essex UK On 2017-10-11 15:59, Scott Aldous wrote: Hi James, The flowchart in Clause 7 in the

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread John Woodgate
I agree that there appears to be a need for clarification, and I will take that up with the committee responsible. But for your particular case, what is critical is the nature of the 'triac control'. Is it phase-angle control, or 'burst firing' or something else? John Woodgate OOO-Own

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread James Pawson (U3C)
Hi Scott, thanks for your input. I agree with you, but as far as I can tell the equipment does comply with the techniques allowed in 6.1. Then it gets passed down the chart to the “Belongs to exceptions of Clause 7…” box where it is exempted and deemed to conform without ever having

Re: [PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread Scott Aldous
Hi James, The flowchart in Clause 7 in the version of the standard that I have access to sends you to Clause 4 for professional equipment that uses techniques not allowed by 6.1. The second paragraph of Clause 4 addresses professional equipment that does not comply with the requirements of the

[PSES] IEC 61000-3-2 Confusion

2017-10-11 Thread James Pawson (U3C)
Hi folks, I apologise as I seem to be all take and not much give on this forum at the moment; I'm trying to do a lot of learning very quickly. Someone ask a question about HDMI so that I can feel useful! Today's question is what appears to be a contradiction in IEC 61000-3-2:2014. *

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread Ted Eckert
NFPA 70 allows 20 A connectors to be used at 20 A under a number of circumstances. The derating issue only applies in certain cases. Just changing the rating doesn’t resolve the issue as it would eliminate already accepted safe use of the connectors at their full rating. Ted Eckert Microsoft

Re: [PSES] NEMA 5-20P with IEC 60320 C13

2017-10-11 Thread John Woodgate
Yes, it could be difficult to change to respecting the rated values, so how about respecting the de-rated values instead? Instead of saying that you can only use this 20 A connector up to 16 A, call it a 16 A connector? John Woodgate OOO-Own Opinions Only J M Woodgate and Associates