David, et al,
I just learned that a toroid core is wound from a single strip of metal,
like a coiled clock spring, one continuous piece. But whether this one
is welded, I cannot say. My guess is probably not. As for impregnation,
I do not think so. The construction details I saw describe core,
Hi,
Thanks for those that replied.
Basically, I would conclude that this test it's not a must requirement.
Just an additional test that the customer requires.
Regards
Koh
Koh wrote:
Hi group,
We had a request from an India customer. They need to have the
following test performed on our
In message
f72651ec60c2c945878cf1cf6a3e5af401bc8...@ntxboimbx13.micron.com, dated
Thu, 22 Dec 2005, drcuthb...@micron.com writes
Loading a transformer secondary does absolutely nothing to the
magnetic core flux. The core flux is set by the magnetizing current and
not the load current. Does
To first order it is true that the magnetic flux in the core does not
change with load current. It would be exactly true if the permeability of
the core were infinite. For real materials with finite permeability, a load
current on the secondary does force some flux out of the core into the air.
Peter,
When John Woodgate said that secondary current does not change the core
flux I went back to the books to see where I went wrong. Here is what I
think is going on:
The primary current that is caused by the secondary load creates a
magnetic flux in the core. The secondary current creates a
I should have added that the most probable cause of noise besides lamination,
is the mmf between loaded windings.
Are the windings tightly constrained or impregnated?
Best Regards
David Greig
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of David Greig
Sent: 22 December 2005
Is the lamination stack welded?
This could provide a outside rigid axis for the laminations to pivot
against, given that any impregnation will be more
compressible than the weld. Welds may also distort the stack.
Best Regards
David Greig
__
GigaDyne Ltd
Buchan
I don't see any contradiction here. Step 3 clearly states that if the sample
passes the earlier test, then keep increasing the voltage until the sample
fails.
Regards, Ravinder
Server PCB Development
Hitachi Global Storage Technologies
Email: ravinder.ajm...@hitachigst.com
Robert A. Macy
8 matches