not accepted that argument.
To be clear, the Buchanan splice caps and insulators are only rated for dry
locations.
I’ve heard that NYSERDA has allowed them to be used with dielectric gel applied
to the interior of a splice cap insulator, but have not been able to confirm.
Best Regards,
Isaac Opalinsky
– reconfigure the jumper and fuse
position and then check the voltage and polarity of the array before you
recommission.
If you have any difficulty finding what you need, please feel free to contact
me directly.
Best Regards,
Isaac Opalinsky | Director, Training & Field Enablement
mobile 443-277-
enhancements such as remote
command functions that had previously been only available to technical support
or when on site doing commissioning.
Contact me offline if you need instructions or help getting access.
Best Regards,
Isaac Opalinsky | Director, Training & Field Enablement
mobile
Jason,
Please contact me offline, and we can help you out.
Best Regards,
Isaac Opalinsky | Senior Manager, Training & Field Enablement
office 443-569-3476 | mobile 443-277-6286 |
isaac.opalin...@sunpower.com<mailto:isaac.opalin...@sunpower.com>
[sp_2014_logo_black_orange_CMYK-01]
. As a manufacturers’ declaration,
it is not a third party certification. I’d stay away from products that are
CE, and not UL, TUV, CSA, etc.
Isaac Opalinsky | Technical Sales
77 Rio Robles, San Jose, CA 95134 | office 443-569-3476 | mobile 443-277-6286 |
isaac.opalin...@sunpower.com
basically be sized to the feeder ampacity.
Other than that, I don’t see any other issues other than making sure you treat
each interconnection as a separate “system”, which would include disconnect,
labeling and directory requirements.
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk
:
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of William Miller
Sent: Tuesday, October 07, 2014 12:01 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] TL inverter
of power clipping (say 1% total annual
energy), are many customers likely to notice/care?
3. If they do notice, does the customer service aspect of having to
defend a design decision outweigh the potential economic benefits of a smaller
inverter?
Isaac Opalinsky | Technical Trainer
to clipping) with
Enphase, would it be worth avoiding the supply side connection? What if I get
1472 kWh/kW? Where would you draw the line.
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re
for 12, 24 or 48V systems without a relatively high voltage MPPT
controller, I haven't encountered any complications with the higher voltage
controllers or AC coupling, of course.
Cheers,
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
-Original
, it would be good to see solutions that simplify installation, reduce
points of maintenance, reduce cost and maintain or increase safety.
Isaac Opalinsky | Technical Trainer | More Energy. For Life.
Desk 443-277-6286 | Cell 443-277-6286
Original message
From: Jason Szumlanski
with a string inverter just
as we do with microinverters. Has anyone tried this?
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
Of Glenn Burt
Sent: Wednesday, June 25, 2014 10
) and another to disconnect the conductors from the array (i.e., at the
array)? Doesn’t seem very “rapid”, but 690.12 isn’t very specific.
Isaac Opalinsky
SunPower Corporation
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re
How have you found the range of the Bluetooth? Have you had flexibility with
the relative location of the inverter/monitoring components?
Isaac Opalinsky | Technical Trainer | SunPower Corporation
Desk 443-569-3476 | Cell 443-277-6286
___
List
?fn=4703.html.
Isaac Opalinsky
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re
I don't know anything about this company, but beware the phrase
Certifications Pending followed by a low resolution image of a UL mark.
Isaac Opalinsky
Technical Trainer
SunPowerCorporation
___
List sponsored by Home Power magazine
List Address: RE
ungrounded conductor).
An inspector should appreciate the value of maintaining the functionality of
the ground fault protection system. 690.13 makes this clear, by allowing the
grounded conductor to be disconnected by service personnel.
Isaac Opalinsky
Disconnecting a normally grounded conductor would defeat the purpose of ground
fault protection and detection. If there is anything an inspector should
respect, it is ground fault protection (and 690.13).
Isaac Opalinsky
___
List sponsored by Home
the receptacle. You may need to plan the module placement very
carefully to avoid this issue.
Please contact me off line at isaac.opalin...@sunpowercorp.com if you want
to talk about your specific application and how to make it work.
Regards,
Isaac Opalinsky
Technical Trainer
SunPower
Message: 2
Date
fuses, both for the battery and the light.
Isaac Opalinsky
On Tue, Dec 20, 2011 at 1:26 PM,
re-wrenches-requ...@lists.re-wrenches.orgwrote:
Send RE-wrenches mailing list submissions to
re-wrenches@lists.re-wrenches.org
To subscribe or unsubscribe via the World Wide Web, visit
http
are a simple solution but require a little more planning
I'd love to see if the vents make a hot spot on the panels - maybe they'd
help shed snow more quickly.
Isaac Opalinsky
Message: 1
Date: Thu, 15 Dec 2011 14:31:10 -0500
From: Allen Frishman amfr...@aeonsolar.com
To: re-wrenches