Re: [RE-wrenches] Discover Xanbus SOC jumpy

2024-05-03 Thread Kent via RE-wrenches
Mac, I have a system that does this (or something similar) with all of the Insight data a few times every day. I'm pretty sure it is lost data resulting from communications drop outs. Internet to the site is via StarLink. If you are only seeing this on the SOC data there might be a problem

Re: [RE-wrenches] Ballasted ground mounts

2024-03-21 Thread Kent via RE-wrenches
A possibility for a smaller ballasted ground mount system is the Sunmodo Sunturf mount. It is difficult to find info on their website but you will find the Sunturf mount in the catalog and the configuration too. This mount can be installed on cast in place piers, earth screws, or concrete

Re: [RE-wrenches] Redundant gensets: Must I switch the neutral in the manual transfer switch?

2024-03-13 Thread Kent via RE-wrenches
First, I'll say that I agree with William's discussion. Let me add another way of thinking about this: Assume that, instead on two generators, your system is one backup generator and one utility company serving a commercial building. If the disconnect switch is your service connection, there

Re: [RE-wrenches] TPM Search

2024-03-11 Thread Kent via RE-wrenches
hold modules in place.  But its just not true anymore.    I added 3/4" angle stainless steel to reinforce the attachments on the top modules. Ray Walters On 3/9/2024 12:44 PM, Kent via RE-wrenches wrote: Ray, It appears that there is something between the module frame and rail that m

Re: [RE-wrenches] TPM Search

2024-03-09 Thread Kent via RE-wrenches
Walters via RE-wrenches wrote: I've had several modules pull off of bottom mount racking in high winds, but never top mount racking.  Newer modules have much thinner frames, but are much more surface area than the old days. Ray Walters Remote Solar On 3/8/2024 3:50 PM, Kent via RE-wrenches

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Kent via RE-wrenches
Jeremy, I think the Solar RacksWorks TPMs are virtually identical to the DPW TPMs. My go to TPM is General Specialties ; They are a solid design and I think they are easier to assemble. They also have UL listed TPMs but they have top mounting clamps,

Re: [RE-wrenches] Clamping CTs Around Live Conductors - White Paper References and/or Anecdotal Information Requested

2024-03-08 Thread Kent via RE-wrenches
Sam, As long as the CT leads are properly terminated, opening or closing the clamp-on CT core is nothing different that what a clamp-on ammeter is doing. Make a mistake and pull the leads out of the multimeter and you may have a high voltage arc. There are other problems with using a

Re: [RE-wrenches] State of Charge Meter for Sol-Ark

2024-02-10 Thread Kent via RE-wrenches
5-438-5600 www.millersolar.com <http://www.millersolar.com> On Fri, Feb 9, 2024 at 3:19 PM Kent via RE-wrenches wrote: William, I think that the SOC determined by lithium BMSs come with similar accuracy issues that occur with the Trimetric, FNDC, Magnum BMK,... - small me

Re: [RE-wrenches] Cleaning PV mods

2023-10-20 Thread Kent via RE-wrenches
Jason, This is the way thermal shock was explained to me. Thermal shock creates micro fractures in the glass. PV modules have tough tempered glass so one thermal shock event, or a few dozen events, is unlikely to cause a module to fracture; but eventually the glass gets to the last straw when

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread Kent via RE-wrenches
fracture direction. Kent Osterberg Blue Mountain Solar On 7/16/2023 2:58 PM, Kent via RE-wrenches wrote: Found some damage to a customer's Grape CS-S-180-DJ PV modules this morning. Unlike anything I've ever seen; so I'm hoping that someone on this list can tell me the cause. I've put several

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread Kent via RE-wrenches
is output and how old are the panels? *Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060* On 2023-07-16 2:58 pm, Kent via RE-wrenches wrote: Found some damage to a customer's Grape CS-S

[RE-wrenches] Damaged PV module cells

2023-07-16 Thread Kent via RE-wrenches
Found some damage to a customer's Grape CS-S-180-DJ PV modules this morning. Unlike anything I've ever seen; so I'm hoping that someone on this list can tell me the cause. I've put several photos of the cells online

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-11 Thread Kent via RE-wrenches
Mac, I think you've got an elegant solution to the problem. All you need is an inexpensive relay and to program the Aux output for loadshed. I believe shutting down the inverter with the remote on/off contacts is actually less stressful on the inverter than opening a relay or contactor on

Re: [RE-wrenches] Metering

2023-05-11 Thread Kent via RE-wrenches
If the inverter(s) provided energy production data, you would already have all the information you really need. Sounds like it must not. So, if you are looking for something that is relative inexpensive and reasonably accurate, but not revenue grade, you could use an Efergy True Power meter

Re: [RE-wrenches] Need 1 Sanyo (Panasonic) HIP-195BA19 or equiv

2023-04-24 Thread Kent via RE-wrenches
Jeff, I'm nearly as far away from NE as one can be in the continental US, but I have a HIP-195BA19 orphan, never installed, sitting in my garage. Kent Osterberg Blue Mountain Solar 70177 Ponderosa Ln Cove, OR 97824 cell: 541-975-3930 On 4/21/2023 8:45 AM, Jeff Clearwater via RE-wrenches

Re: [RE-wrenches] SolArk and Tigo compatibility

2022-11-16 Thread Kent via RE-wrenches
As of the March 2022 manuals there are contradictory statements: * (+15, -16) 12V power supply for RSD transmitters: such as TIGO and Midnite Rated for a maximum of 1.2W (100mA @12V) and * TIGO Optimizers are compatible with the Sol-Ark 8K (Do not use the built in 12V Power supply in

Re: [RE-wrenches] Accuracy of Enphase consumption monitoring

2022-10-27 Thread Kent via RE-wrenches
Jason, Since the difference is not a consistent percentage, I'd look at the consumption meter settings. Make sure that the solar energy is accounted for correctly: either included or not included with the consumption metering. Kent Osterberg Blue Mountain Solar On 10/27/2022 8:59 AM,

Re: [RE-wrenches] Integrating Lithium batteries with legacy inverters.

2022-10-20 Thread Kent via RE-wrenches
William, I think Right Hand Engineering still makes the device that will keep the SW memory alive. Batteries need to be changed every few years. Kent Osterberg Blue Mountain Solar On 10/20/2022 9:43 AM, William Miller via

Re: [RE-wrenches] GJ 250 circuit breaker DC 250

2022-05-31 Thread Kent via RE-wrenches
I've seen a couple of those old Trace breakers with damaged set screw connectors. Its been a while back but I replaced one of the old Trace breakers with a Magnum breaker. Easy replacement, but you'll need to put lugs on the cables. That's a good improvement anyway. Kent Osterberg Blue