Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-27 Thread Ray Walters via RE-wrenches
to find threaded lengths, so I used very high pressure Poly. When it's rated for 300psi it has a very thick wall and is hard to get onto fittings, but is light weight and moderately flexible. Brad On Sun, May 26, 2024 at 11:17 AM Ray Walters via RE-wrenches wrote: Hi Brad; I've seen

Re: [RE-wrenches] Water system with Grundfos SQFlex

2024-05-26 Thread Ray Walters via RE-wrenches
Hi Brad; I've seen a lot of leaks with barb fittings on poly pipe. I just replace most of the poly plumbing at my place, because I just couldn't get it to stop leaking. Black poly pipe is the lowest cost per foot, but not quite bomb proof.   Barb fittings are really more suited for irrigation

Re: [RE-wrenches] PWM Controllers in parallel

2024-05-07 Thread Ray Walters via RE-wrenches
Rewiring the array is not that hard.  Why is he against that? With old Jbox type modules, it usually is safer too, as those often were paralleled at the modules, and often over loaded the connectors.  It would also increase his total power output by reducing line losses.   I think a careful

Re: [RE-wrenches] XW Pro Firmware 2.04 melting devices

2024-04-25 Thread Ray Walters via RE-wrenches
That sounds like a generator problem.  I've seen many gen sets put out a horrible waveform under load, when battery charging. The waveform, (if you have an O-scope) usually has a spike on the front of the wave, and then the wave flattens significantly after.  The peak should be 169 v on a 120

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Ray Walters via RE-wrenches
Hi Michael; I don't think its 12v, I have old Trace 48 v systems still humming along 24 years later, too. Some of it, is the customers. The old school off grid folks knew how to conserve energy, watch the sun, and were not going to call unless they couldn't fix it themselves. Also, the

Re: [RE-wrenches] PV/Charge Controller Troubleshoot Help

2024-04-23 Thread Ray Walters via RE-wrenches
Isn't that too much array power for an MX60?  Just based on the numbers you gave, it looks like over 3kw, which is 63 amps at 48vdc.  He didn't mention the actual PV module ratings, but I suspect its just way too much array power.  It might work for awhile, but its going to start cooking

Re: [RE-wrenches] Plaques

2024-03-30 Thread Ray Walters via RE-wrenches
I once got a trophy company to engrave some plaques and it was stupid expensive. ($50/ plaque)  Then I started using PV Labels.com, and their pricing is quite reasonable (under $10/ plaque).  Turn around time has always been quick too.  I'd have to be printing a lot of plaques for doing it in

Re: [RE-wrenches] Minimum bus size, new requirements

2024-03-28 Thread Ray Walters via RE-wrenches
So to be clear, the inspector is wrong:  it is NOT an NEC requirement.  It is only a California requirement.   NEC 2023 only requires a 100 A main load center and disconnect per 225.39(C). Further, 710.15(A) allows the inverter and feeder to the Load center to be even less in off grid

Re: [RE-wrenches] Redundant gensets: Must I switch the neutral in the manual transfer switch?

2024-03-13 Thread Ray Walters via RE-wrenches
I've gotten into discussions like this before with EEs.  They are not experts at what we do, and can get confused, and go down strange rabbit holes like the rest of us.  I agree with you that not switching the Neutrals is the way to go.  Its how we've always done it in most scenarios.  It only

Re: [RE-wrenches] Insurance for solar design and inspections

2024-03-11 Thread Ray Walters via RE-wrenches
Something else to consider for us small operators:  LLC and incorporation offer some protection as well.  If your company is sued, and then declares bankruptcy, there's not going to be much for the other party's attorneys to go after.  I've heard it described by my attorney, that most

Re: [RE-wrenches] TPM Search

2024-03-10 Thread Ray Walters via RE-wrenches
he module and rail? Kent Osterberg On 3/8/2024 4:23 PM, Ray Walters via RE-wrenches wrote: Here's another mount at the edge of failure, from the same system. Hardware is tight.  Like many, I had lots of love for good ol' fashion bottom mounting vs top mount, until this happened about 5 years ago

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Ray Walters via RE-wrenches
Here's another mount at the edge of failure, from the same system. Hardware is tight.  Like many, I had lots of love for good ol' fashion bottom mounting vs top mount, until this happened about 5 years ago. This is how we learn. On 3/8/2024 5:15 PM, Ray Walters via RE-wrenches wrote: I've

Re: [RE-wrenches] TPM Search

2024-03-08 Thread Ray Walters via RE-wrenches
I've had several modules pull off of bottom mount racking in high winds, but never top mount racking.  Newer modules have much thinner frames, but are much more surface area than the old days. So to answer Kent's question: Ray Walters Remote Solar On 3/8/2024 3:50 PM, Kent via RE-wrenches

Re: [RE-wrenches] Battery Electrolyte Level Measuring

2024-02-29 Thread Ray Walters via RE-wrenches
Hi William; I agree with your original premise that checking levels is difficult by eye.  Also, I would add that many of my clients chronically over fill the cells, leading to acid loss and severe corrosion of the connectors, battery box, and floor. Your float is an interesting idea, but

Re: [RE-wrenches] Rugged Wind/Solar System For Radio

2024-02-21 Thread Ray Walters via RE-wrenches
Who carries the Superwind turbines?  We've been looking for a replacement for the old Bergey XL1 to offer clients. Thanks, Ray Walters Remote Solar On 2/21/2024 7:20 PM, John Blittersdorf via RE-wrenches wrote: As far as wind is concerned, I recommend SuperWind, made in Germany.  It is well

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
that are out there. On Sat, Feb 17, 2024, 12:33 PM jay via RE-wrenches wrote: A number of people have mentioned strict code compliance. How are lead batteries dealing with this? thanks jay On Feb 17, 2024, at 12:27 PM, Ray Walters via RE-wrenche

Re: [RE-wrenches] EG4 Equipment

2024-02-17 Thread Ray Walters via RE-wrenches
Chris; I was definitely moving to the LFP camp for off grid for all the same reasons you mentioned, but I've just had too much trouble, so I'm heading back to lead acid for now.  I missed the acid burned jeans, its a "look". Seriously, you mentioned customers coming back to a lead acid

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Ray Walters via RE-wrenches
I second using the 48v to 12 v DC DC converter.  I've had success with that, and avoided the issues Jeremy mentioned. Ray Walters Remote Solar On 2/17/2024 9:35 AM, Bradley Bassett via RE-wrenches wrote: I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work

Re: [RE-wrenches] XW EQ question

2024-02-12 Thread Ray Walters via RE-wrenches
What's funny, is the good old SWs from the Trace days had the same problem.   Never could get them to equalize.  Maybe that software carried over. Ray Walters Remote Solar On 2/12/2024 4:42 PM, jay via RE-wrenches wrote: Hi Kevin Thanks, I heard that exact thing from someone else. Do you

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
with lithium. Specifically so I don’t have an issue with finger pointing between OEMS. But that sure sucks. Jay On Feb 7, 2024, at 10:17 PM, Ray Walters via RE-wrenches wrote:  We just had a complete failure of a set of four Simpliphi 3.8 KWh batteries, 48 v

Re: [RE-wrenches] Lithium batteries

2024-02-08 Thread Ray Walters via RE-wrenches
e an issue with finger pointing between OEMS. But that sure sucks. Jay On Feb 7, 2024, at 10:17 PM, Ray Walters via RE-wrenches wrote:  We just had a complete failure of a set of four Simpliphi 3.8 KWh batteries, 48 v.  It has completely changed my thoughts on Li+

Re: [RE-wrenches] Lithium batteries

2024-02-07 Thread Ray Walters via RE-wrenches
We just had a complete failure of a set of four Simpliphi 3.8 KWh batteries, 48 v.  It has completely changed my thoughts on Li+ for off grid.  This set lasted 5 years, which is about equal to bottom of the barrel Golf Cart batteries.  The RMA/ Warranty process has not been smooth.  It took

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Ray Walters via RE-wrenches
ecalls-amphenol-connectors-sold-with-pv-modules/> Brian On Nov 9, 2023, at 4:47 PM, Ray Walters via RE-wrenches wrote:  12 Ga wire is not going to catch on fire, but the MC connectors might.  I just went back on a 7 yr old Solarworld install, and had a bad series MC connector (module to modu

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-09 Thread Ray Walters via RE-wrenches
12 Ga wire is not going to catch on fire, but the MC connectors might.  I just went back on a 7 yr old Solarworld install, and had a bad series MC connector (module to module).  It got quite crispy, deforming and bubbling the plastic on both sides of the connection.  It was still passing

Re: [RE-wrenches] Need a hand with Sunny Island/Sunny boy AC couple

2023-10-21 Thread Ray Walters via RE-wrenches
What is the array size vs the battery size?  Sounds like a big array on a small battery for the voltage to go that high that fast. Ray Remote Solar On 10/21/2023 5:46 PM, William Miller via RE-wrenches wrote: Friends: I’m kinda stuck on a project setting up a SI/SB AC coupled system off

Re: [RE-wrenches] Wind machines

2023-08-17 Thread Ray Walters via RE-wrenches
I've watched VAWT pop up like its a new idea every few years for almost the past 50 years.  VAWT is just basically a bad idea, as it's trying to make usable power too close to the ground.  I've never seen any that lasted very long, or matched their power claims. It can however be Kinetic art,

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Ray Walters via RE-wrenches
, 2023, at 5:08 PM, Ray Walters via RE-wrenches wrote:  The aux off is only if the generator doesn't start.  You need to set the gen start voltage higher. Aux off is last ditch shut down, set for 44v for lead acid, or 47 to 49v, depending on the battery and inverter.   Hopefully DC coupled PV

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-20 Thread Ray Walters via RE-wrenches
The aux off is only if the generator doesn't start.  You need to set the gen start voltage higher. Aux off is last ditch shut down, set for 44v for lead acid, or 47 to 49v, depending on the battery and inverter.   Hopefully DC coupled PV will raise the voltage enough to turn the inverters back

Re: [RE-wrenches] Damaged PV module cells

2023-07-16 Thread Ray Walters via RE-wrenches
These days modules are so cheap, and so much more efficient, that I just reuse the racks, even if the existing modules are good. Racking, wiring, excavation all exceed the cost of the mods, so its what ever gets the customer the power they need for the lowest cost. OTOH, if the system is

Re: [RE-wrenches] Inverter On/Off Switch use Outback FX

2023-07-13 Thread Ray Walters via RE-wrenches
Hi Mac; I've used the aux control on charge controllers to turn on/off the FX inverters, just as you planned.  Works fine, and solves the LBCO programming issue. Now, if someone from the manufacturing side could PLEASE explain why they limited the LBCO on all these inverter models.

Re: [RE-wrenches] Inverter output fluctuations

2023-07-03 Thread Ray Walters via RE-wrenches
It could be the LED bulbs.  I've had different brands flicker like crazy on grid and off.  Seems to relate to other loads that are on, especially stuff like washing machines with VFD drives, and well pumps.   Add dimmers and it can get even worse. IMHO, they really need to improve the quality

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Ray Walters via RE-wrenches
ions from Covid. *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *Ray Walters via RE-wrenches *Sent:* Wednesday, May 31, 2023 1:51 PM *To:* re-wrenches@lists.re-wrenches.org *Cc:* Ray Walters *Subject:* Re: [RE

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Ray Walters via RE-wrenches
What were the issues?  I've not seen a Magnum have power quality troubles, but they are not the "grid" either.  My experience is that they are similar or a bit better than Outback, but certainly have measurable THD in the 4 to 5% range.  Its almost always finicky loads, and the inverter has

Re: [RE-wrenches] Metering

2023-05-11 Thread Ray Walters via RE-wrenches
If you have a built in monitoring system for the PV (inverter's onboard metering?) that should tell you PV production, and then subtract that from the monthly utility readings to get the household loads.  I don't see the need for a separate inline meter, but I guess it depends how

Re: [RE-wrenches] Solar direct water pumping

2023-05-08 Thread Ray Walters via RE-wrenches
Just with all other solar equipment, you definitely don't want to go CCC.  I'd recommend you take a look at the Grundfos SQ flex line.  2nd, you need to look at the pump charts to see what the actual flow rate will be at the head you're considering.  The pump you are looking at doesn't even

Re: [RE-wrenches] Truss finder

2023-04-17 Thread Ray Walters via RE-wrenches
If the temperature is right, my IR camera can see the rafters. Best to check early on a cold morning with the heat on in the building.  Otherwise I'm of the William "Hammer" system persuasion.  Never found anything better. On 4/17/2023 1:31 PM, Garrison via RE-wrenches wrote: Hi Kris, I

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-04 Thread Ray Walters via RE-wrenches
tp://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060* On 2023-04-04 4:21 pm, Ray Walters via RE-wrenches wrote: So the 24 batteries are actually 72 individual cells that are trying to charge equally, with essentially no BMS. Its not just max strings, but max # of cells,

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-04 Thread Ray Walters via RE-wrenches
So the 24 batteries are actually 72 individual cells that are trying to charge equally, with essentially no BMS.  Its not just max strings, but max # of cells, and that's double my maximum. You mentioned they use it pretty hard, so that's the other big part of how long L16s will last.  If the

Re: [RE-wrenches] replace part of rolls battery bank

2023-04-03 Thread Ray Walters via RE-wrenches
My 2 cents:  L16s are not a good choice in the first place. Compare the cycle life vs cost. 2nd that sounds like way too many batteries/ strings and definitely a candidate for larger format 2 v cells or Li+. I second William's idea of creating 2 strings of the best cells, and start shopping

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-31 Thread Ray Walters via RE-wrenches
Group NABCEP Certified Solar Professional (PVIP) Florida State Certified Solar Contractor CVC56956 On Thu, Mar 30, 2023 at 9:45 PM Ray Walters via RE-wrenches wrote: Hi Jason; I was like you: thinking good ol' bottom mounting with SS hardware was the best.  All of us old wrenches

Re: [RE-wrenches] Attaching Array To or Through Ply

2023-03-30 Thread Ray Walters via RE-wrenches
Hi Jason; I was like you: thinking good ol' bottom mounting with SS hardware was the best.  All of us old wrenches were wrong. The top down mounting system is much stronger.  I've only had a handful of failures over 25 years, and all were bottom mounted. The module completely ripped off the

Re: [RE-wrenches] Off Grid Battery Charging

2023-03-16 Thread Ray Walters via RE-wrenches
As I recall from pushing the "wayback" button, Backwoods and Real Goods used to sell something like that in the 90s.  I would only see a pyschological benefit, based on the system size. I recall that the charge rate was less than 50 watts, so its really not going to be worth wiring into the

[RE-wrenches] Fire Sprinklers (was Re: Cell phone based relay control)

2023-03-14 Thread Ray Walters via RE-wrenches
ers do not test and recommend these kinds of systems. The best answer I have been able to come up with is they fear people prepared like this would have a tendency to "stay and defend" their homes rather than evacuating. Todd On Monday, March 13, 2023 6:37pm, "Ray Walters vi

Re: [RE-wrenches] Cell phone based relay control

2023-03-13 Thread Ray Walters via RE-wrenches
Michael; Can you share more about your sprinkler system and the power supply for it?  Over the years, at least two of my customers have lost their homes (and PV arrays) in wild fires. Ray Walters Remote Solar On 3/13/2023 2:34 PM, Michael Morningstar via RE-wrenches wrote: WebRelay. I use

Re: [RE-wrenches] PV and EMP

2023-03-09 Thread Ray Walters via RE-wrenches
I'm not an EMP expert by any means, but I've dealt with quite a few lightning damaged systems.  Having a good connection to a low impedance grounding system (steel cased well, Ufer ground) is crucial.  I also have had fantastic luck with Midnite's MNSPD line.  Delta, not so much. On 3/9/2023

[RE-wrenches] 60v Inverter?

2023-03-02 Thread Ray Walters via RE-wrenches
Hi all; I'm putting together a small backup system that will use an electric motorcycle battery (60 V, 35 AH, Li+) Normal charge voltage is at 67.2v, so that excludes most inverters I know of. I've found a few from China that claim 60v and 72v nominal input, but output is listed at 230vac,

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
for anything greater than 60 amps for 2 poles, other than large DPDT switches which get pricey and hard to source especially for 200 amps? Howie On Thu, Mar 2, 2023, 6:23 PM Ray Walters via RE-wrenches wrote: I probably still have one of the old QO boxes on the shelf, but I never liked

Re: [RE-wrenches] Inverter bypass

2023-03-02 Thread Ray Walters via RE-wrenches
I probably still have one of the old QO boxes on the shelf, but I never liked them.  Single pole, very tight, and you had to double lug or use a weird split bolt arrangement with exposed copper out past the breaker. I started using these 60A T switches from Northern:

[RE-wrenches] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-09 Thread Ray Walters via RE-wrenches
at 6:43 PM Jerry Shafer via RE-wrenches wrote: Pet heater have worked for me, I air gap a sealed heater box under the battery, thermostat inside the top of the battery.  It's slow and low power but does the trick Fun times On Wed, Feb 8, 2023, 3:05 PM Ray Walters via R

[RE-wrenches] Fortress Battery Heater

2023-02-08 Thread Ray Walters via RE-wrenches
Hi All; I have a fresh Fortress Evault installation with a Solark inverter.  The batteries are indoors in the center of the house, but the customer is not there full time, so the battery is unfortunately going below freezing.  What are the best options for setting up a heating system for the

Re: [RE-wrenches] Magnum MS4024 grief

2022-12-16 Thread Ray Walters via RE-wrenches
Undoing the N-G bond at the E panel may not do it either.  Are you sure neutral isn't also bonded in the main distribution panel?  It usually is bonded at the generator, so you definitely have to unbond there.  I'd say 60 to 70% of off grid systems are not bonded correctly that I've seen. 

Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Ray Walters via RE-wrenches
To add to Jeff's suggestion of targeting 95%, many Li+ batteries have a spike in voltage as they reach 100%.  We just don't have to worry anymore about sulfate damage from under charging. Ray Walters Remote Solar On 11/19/2022 7:14 AM, Jeff Clearwater via RE-wrenches wrote: Hi Kris What

Re: [RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-17 Thread Ray Walters via RE-wrenches
...@lists.re-wrenches.org] *On Behalf Of *Ray Walters via RE-wrenches *Sent:* Thursday, November 17, 2022 1:43 AM *To:* re-wrenches@lists.re-wrenches.org *Cc:* Ray Walters *Subject:* Re: [RE-wrenches] Sol-Ark/Fortress charging issue Talk to Thomas Honey.  He is the Fortress rep, nice guy

Re: [RE-wrenches] Sol-Ark/Fortress charging issue

2022-11-16 Thread Ray Walters via RE-wrenches
Talk to Thomas Honey.  He is the Fortress rep, nice guy, and knowledgeable wrench.   He has stepped in on my issue. Ray On 11/16/2022 10:58 PM, Howie Michaelson via RE-wrenches wrote: Good Evening, I have a frustrating charging issue involving 2 Fortress eVault Maxs connected to a Sol-Ark

Re: [RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Ray Walters via RE-wrenches
On Wed, Nov 16, 2022 at 2:02 PM Ray Walters via RE-wrenches wrote: Greetings Fellow Wrenches; Based on glowing reports from the RE list, I finally used Fortress for a battery replacement for a long time customer. Overall, it seems to be a better

[RE-wrenches] Fortress Battery Problems

2022-11-16 Thread Ray Walters via RE-wrenches
Greetings Fellow Wrenches; Based on glowing reports from the RE list, I finally used Fortress for a battery replacement for a long time customer. Overall, it seems to be a better solution than others I've seen. However, we are having issues.  First the two batteries are supposed to be linked

Re: [RE-wrenches] sol ark reliability question

2022-09-30 Thread Ray Walters via RE-wrenches
One thing I can say:  trouble shooting problems over the phone has its limitations.  I had a customer issue with a system we hadn't installed that was quite vexing.  Turned out to be a loose main DC connection to the inverter.  Bizarre behavior as the connection heated up and the resistance

Re: [RE-wrenches] Discover AES Wall Mount Considerations

2022-09-06 Thread Ray Walters via RE-wrenches
I agree with James here.  I will relate a "funny" story about a neighbor mounting a large Elk antler rack on his wall with lags. Worked fine, till one night they heard a big crash, and the antlers had pulled the wall stud right out of the wall into the living room. The 2x 4 came right out of 

Re: [RE-wrenches] Battery Monitor for Li

2022-09-02 Thread Ray Walters via RE-wrenches
Default efficiency on the TriMet was 94%, needs to be quite a bit higher for Li+.  I'd try 98%. 2nd point:  Customers have always obsessed about meter readings: they need to take a chill pill, and accept its not going to be better than +/- 10% accuracy.  Or get a Fortress battery with built

Re: [RE-wrenches] Removing paint from solar modules

2022-04-15 Thread Ray Walters via RE-wrenches
Not to sound like a commercial, but I've had good results with "Tub O'Towels" heavy duty wipes.   Its got a lemon base that seems easy on most surfaces, but it will take paint off with a few seconds of elbow grease.   Hoe Depot has them sometimes, or Northern Tool carries them too.  You'll use