have been posts about this issue before on the list.
Best,
August
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Benn Kilburn
*Sent:* Tuesday, September 06, 2016 4:22 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Wire nuts
August, et al,
Do
Sent: 9/6/2016 19:21
>> To: RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
>> Subject: Re: [RE-wrenches] Wire nuts
>>
>> August, et al,
>> Do you have any issues with crimping the fine wires that are typically on a
>> microinverter cable, to
rn
> Sent: 9/6/2016 19:21
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Wire nuts
>
> August, et al,
> Do you have any issues with crimping the fine wires that are typically on a
> microinverter cable, to a coarse stranded or solid wire?
> Or, do you know if there
Do you mean beyond the NEC listing violation?
-Original Message-
From: "Benn Kilburn"
Sent: 9/6/2016 19:21
To: "RE-wrenches"
Subject: Re: [RE-wrenches] Wire nuts
August, et al,
Do you have any issues with crimping the fine wires that are typically on a
micro
re-packed with grease likely would have been okay in a very wet box
>>> provided they were assembled properly. We are putting weep holes in our
>>> boxes and conduit bodies because we’ve had multiple issues with water
>>> flooding boxes and conduits. Dirty conductive w
; August
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski
> *Sent:* Tuesday, September 06, 2016 1:25 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Wire nuts
>
>
>
> I was just called last week to
be found on eBay.
Eric Stevens, Vermont Made Energy
> Message: 7
> Date: Tue, 6 Sep 2016 13:32:00 -0700
> From: "MDElectricSolar ."
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Wire nuts
> Message-ID:
>
> Content-Type: text/plain; charset="utf-8&q
ater and 600 VDC don’t mix well.
>
> August
>
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
> Behalf Of Jason Szumlanski
> Sent: Tuesday, September 06, 2016 1:25 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Wire nuts
>
> I was just c
*Sent:* Tuesday, September 06, 2016 1:25 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Wire nuts
I was just called last week to a three phase Enphase system installed by
others with three of eight strings that were exhibiting erratic voltages on
random phases. First I checked the combiner
ns on the DC input circuits.
From: Jerry Shafer <mailto:jerrysgarag...@gmail.com>
Sent: 9/6/2016 14:32
To: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Wire nu
st
>>
>> Luminalt
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
>> Behalf Of *Benn Kilburn
>> *Sent:* Tuesday, September 06, 2016 12:02 PM
>> *To:* RE-wrenches
>> *Subject:* Re: [RE-wrenches] Wire nuts
ilburn
> *Sent:* Tuesday, September 06, 2016 12:02 PM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Wire nuts
>
>
>
> The reason i'm asking is that the only time i have seen a short,
> first-hand, in a wire nut, was because it appeared that one wire was pushed
>
; Be aware that SMA explicitly prohibits the use of wire nuts in their
>> installation instructions on the DC input circuits.
>> --
>> From: Jerry Shafer
>> Sent: 9/6/2016 14:32
>> To: RE-wrenches@lists.re-wrenches.org
>> Subject:
> Subject: Re: [RE-wrenches] Wire nuts
>
> Wrenches
> Better pic
>
> On Sep 5, 2016 4:52 PM, "Jerry Shafer" wrote:
>
>> To my fellow wrenches
>> It comes up every so often and with DC, I will not use, approve or pass
>> any wire nuts on any DC side. S
:* RE-wrenches
*Subject:* Re: [RE-wrenches] Wire nuts
The reason i'm asking is that the only time i have seen a short,
first-hand, in a wire nut, was because it appeared that one wire was pushed
down rather than binding with the other wire, which would have happened if
the wires were not
Be aware that SMA explicitly prohibits the use of wire nuts in their
installation instructions on the DC input circuits.
-Original Message-
From: "Jerry Shafer"
Sent: 9/6/2016 14:32
To: "RE-wrenches@lists.re-wrenches.org"
Subject: Re: [RE-wrenches] Wire nuts
Wre
I also concurr, NEVER use wire nuts on the roof, I've personally installed
them, and come back 3-4 years later, and found them melted. Wire nuts are
simply for insulating a splice, not to be counted on for the mechanical
connection. I make my guys twist solid wire together before installing a
wire
The reason i'm asking is that the only time i have seen a short,
first-hand, in a wire nut, was because it appeared that one wire was pushed
down rather than binding with the other wire, which would have happened if
the wires were not held tightly when the nut was twisted on. Also, it was
a strand
All the other nuts are tight so l cant not say it was or not but l see this
alot and this was one that was caught just at the right time.
Jerry
On Sep 6, 2016 8:44 AM, "Benn Kilburn" wrote:
> Jerry,
> Can you confirm that this was caused by a failure of the wire nut, itself,
> and not due to use
Jerry,
Can you confirm that this was caused by a failure of the wire nut, itself, and
not due to user error (not properly stripping enough jacket, inserting even
length wires and sufficiently twisting on the wire nut)
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
> On Sep 6, 2016, at 12:32 PM