We recently had a customer replace their mate.
Not all the settings are retained in the FX units - many of the generator
start settings were lost in the swap, causing a service call for
reprogramming...
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
We have bought a few recently, but be careful - there has been some
manufacturing shortage (according to Multi-Contact) and all have been
shipped with crimping dies for the MC-3 connector and not the MC-4s that we
bought them for...
Of course the dies we are told are not sold separately...
William,
I also have found your calculator to be a real timesaver.
Thank you.
Glenn Burt
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bob Clark
Sent: Sunday, February 21, 2010 3:03 PM
To: 'RE-wrenches'
Subject: Re
I recently bought a 345.
It is a great tool - I use it on every commercial commissioning and QA
inspection I do.
I had a customer with high utility voltage and the meter recorded this very
well.
Interesting to watch the voltage and current measurements on a residential
PV install when the inverter
Here is another widget that might be worth looking at.
It seems to be priced around the TED option, but may have more bling.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Philip
Boutelle
Sent: Tuesday, April 13
Interesting training videos on the 3M website covering recommended practices
in taping splices.
http://solutions.3m.com/wps/portal/3M/en_US/3MElectrical/Home/Support/Traini
ng/
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
We have been intrigued by the S-5! Offering for work on corrugated roofing
jobs, but have not yet used them either. Anyone else?
http://www.s-5.com/clamps/index_1032.cfm
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
How about a nice Power-One Aurora inverter with two MPP string inputs?
http://www.power-one.com/renewable-energy/grid-tie-solar-inverters.php
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
inverters. He told me his experience
with the TED was very similar to mine, it would lose communications with the
display at unpredictable times.
So reliable? Not in my experience. Inexpensive? Yes.
YMMV
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
I just saw this firsthand this week -
I was out camping and had a Morningstar SureSine 300W inverter inverter
setup on the camper to charge a few things, and as Field day was
approaching, setup my HF ham radio (running off the same deep cycle
battery), adjacent to the inverter. My antenna was up
The Sunpower system is based on the WattNode hardware by Continental Control
Systems.
http://www.ccontrolsys.com/
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: Tuesday, June 22, 2010 11:37 AM
To:
We have done something similar when slate roofs are involved - replace the
slate directly under the array with comp shingles.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Aladdin
Solar
Sent: Wednesday, July 14, 2010
Can you see where the rafter tails were nailed at the soffit?
How is the ridge constructed? A vent you could lift to see the ridge end of
the rafters?
Good Luck!
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
We get ours in 10AWG from Allied Wire Cable in Collegville, PA. It is not
white, but they stripe it white with no trouble - about 3 stripes if I
recall. I can't see why they wouldn't have larger gauges it is pretty
close to VT.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
tape (electrically questionable).
Any recommendations?
Bubble gum?
Glenn Burt
NABCEP Certified PV Installer
NYSERDA Eligible Installer
Technical Specialist
Alteris_RGB.gif
Alteris RenewablesT
120 Broadway
Albany, NY 12204
Tel:(518) 512-5154
Cell: (518) 681-2274
Fax: (518) 514
Most racking manufacturers have a minimum setback distance from the edges of
a roof for wind loading.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mick Abraham
Sent: Wednesday, August 25, 2010 2:09 PM
To: RE
Speaking as a ham radio operator, I find operating conditions are much
better after sundown.
Band conditions are much more conducive to distance operating and are much
quieter at that time.
Glenn Burt
KA2DTH
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re
Ask them how the listing of the 240VAC Sunny Island is coming - another
promise I have customers waiting for - 'real soon now'.
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of North Texas
Renewable
Hello all,
I found this link to the 2011 NEC effective on August 25, 2010.
If you have / create an account with the NFPA, you can view it for no
charge.
http://www.nfpa.org/AboutTheCodes/AboutTheCodes.asp?DocNum=70
Regards,
Glenn Burt
.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Friday, October 01, 2010 2:44 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Tranformless inverter
Ah so..double-insulated is the key. I
There is a good Technical Note on the SMA website that talks about sizing an
AC combining panel that may provide some guidance on this.
http://download.sma.de/smaprosa/dateien/4307/Multiple%20SB%20Installation%20
on%203%20Phase%20Utility%20Tech%20Note%20V21.pdf
-Glenn Burt
From: re
conductors inside the load center, prior to their landing on the main
breaker.
-Glenn Burt
Alteris Renewables, Inc.
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dave Palumbo
Sent: Sunday, October 31, 2010 2:35 PM
To: 'RE
from our office, so I will need to
plan on a couple of options to take with me, and expect to spend some time
testing...
Regards,
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent
There is a letter on the Fat Spaniel website welcoming all customers to
Power One.
Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Emerson
Sent: Monday, November 08, 2010 8:46 PM
To: 'RE-wrenches'
Subject: Re
resistance.
We test our homeruns after pulling, and AC runs after pulling, but only with
unlanded conductors.
Glenn Burt
NABCEP Certified PV Installer
NYSERDA Eligible Installer
Technical Specialist
Alteris_RGB.gif
Alteris RenewablesT
120 Broadway
Albany, NY 12204
Tel:(518) 512
We have invested in an Iota charger with the IQ4 board for this purpose.
Pricy, yes, but seems to have the best chance of success for reviving the
bank as a unit.
http://www.iotaengineering.com/dls5413.htm
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
Would the walls of the bale house be considered part of the dwelling and
require careful consideration of whether metallic conduit is REQUIRED on the
DC run? 690.31 (E)
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
If you use the SMA solution, a web box can collect many points of data from
the Sunny Island on both sides of the inverter.
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dan Fink
Sent: Saturday,
Hi Phil,
I posted some information that is relevant back in March of 2009. It should
be in the searchable archives.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Philip
Boutelle
Sent: Monday, November 29
Hi Ray,
I have for my last 2 battery jobs used the Cobra X-Flex in 2/0 size with MTW
rating.
At the battery end I have found the Thomas Betts 54163-TB lugs, available
at my local Grainger store to be a good match both mechanically and
specification wise (also the correct hole size for M8
So have you seen the widespread recall on the Xantrex GT and Sunpower SPRx
line?
Bulletin reports instances of the wiring cover blowing off the inverter
suggests all inverters be shut down until a retrofit kit is available for
installation.
-Glenn Burt
power system is present and the location(s) of the means of
disconnect
Regards,
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Adams
Sent: Friday, March 25, 2011 10:35 AM
To: RE-wrenches
We have had success in many cases, contacting the manufacturer of the
installed breaker and asking if the device was suitable for backfeeding (ala
solar). Some will certify that it is OK, some do not.
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
My favorite part was when the test results arrived by mail, it had a postage
due notice on it.
Had to pony up more $$ to tell if I passed or failed!!
Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Nick Vida
Sent
paperwork to be filled out for each site requiring signatures from
the customer and an unposted envelope to submit to receive reimbursement for
the trouble...
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
Would be a good one to ask John Wiles - he has been very responsive to my
questions.
Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Sunday, April 17, 2011 9:09 PM
To: 'RE-wrenches'
Subject: [RE
systems so work can
begin. Carts for those working within 15' of a building edge.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of North Texas
Renewable Energy Inc
Sent: Monday, May 02, 2011 12:57 PM
To: RE-wrenches
Subject
. However, history tells us that these polyurethane caulks are
exceptional in their durability on comp shingle roofs, so use the DAP
product if you think the caulk manufacturer needs to backup the application.
Bill.
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Glenn Burt
Sent
We found one of these recently it turned out to be a loose fuseholder for
the GFDI fuse in the inverter.
Slightly pinching the holder arms cured it.
Might be worth a try?
Regards,
Glenn Burt
Technical Specialist
Renewable Power Systems, LLC
PO Box 967
Averill Park, NY 12018
V: 518-674-5808
C
Radiantec makes a heat dump valve that activates at a temp you set via a
controller that may be a safer way to divert over heated water...
http://www.radiantec.com/pdf/End_Uses_of_the_Solar_Energy.pdf
pp4
-Glenn Burt
_
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf
Perhaps this is the one you are thinking of?
SC2636M225FPV
http://ecatalog.squared.com/pubs/Electrical%20Distribution/Combination%20Ser
vice%20Entrance%20Devices/4119HO0801.pdf
Regards,
Glenn Burt
Technical Specialist
RPS Logo 2008
Renewable Power Systems, LLC
PO Box 967
.
http://www.sunnyportal.com/Templates/PublicPageOverview.aspx?plant=eb64b842-
a776-4ed3-a9f2-f26d9c891d4b
http://www.sunnyportal.com/Templates/PublicPageOverview.aspx?plant=eb64b842
-a776-4ed3-a9f2-f26d9c891d4bsplang=en-US splang=en-US
Regards,
Glenn Burt
Technical Specialist
RPS Logo
Carmanah seems to have a lot of interesting products along these lines.
http://www.carmanah.com/
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Monday, January 19, 2009 1:42 PM
To: RE Wrenches
Our engineer has told us that filling a pipe with concrete (for a pole mount
application) is not strengthening it.
As soon as the wind blows the pipe bends/twists the concrete begins to
break up inside, making it useful only as a water wick.
We did a few this way, but ultimately stopped
I just downloaded the new 4.0 version of the Solar Pathfinder Assistant
program.
It not has a module for SDHW that may interest you.
-Glenn
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Matthew
Arner
Sent: Thursday,
Peter,
We use a couple of torque screwdrivers made by Genius, model TO-227L. It is
easy to use has a reasonable price.
http://www.geniustools.net/aspx/readset.aspx?item=TO-227L
Comes in a nice plastic case with many tips. I do find that I often must use
a longer extension than what is
/knowledge that must be proven to join?
Am I off base in thinking that this forum is for 'working questions' from
all levels of experience?
-Glenn Burt
___
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options
to availability - after many calls, the only sources
I could locate of the appropriate adapter had many weeks as lead times.
Hope this helps!
-Glenn Burt
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Blick
Sent: Wednesday
Is it UL listed?
The spec says 'Designed to meet UL1741 and CSA STD No. 107.1-01'
-Glenn Burt
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of David Katz
Sent: Sunday, March 15, 2009 12:34 AM
To: al
Great article on performance calculations in the previous issue of Solar
Pro, pp24.
I made a quick dirty spreadsheet that we use to plug in measured values on
site to give us a ballpark during checkups.
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
Sunpower makes a 215w 225w in an all dark configuration.
http://www.sunpowercorp.com/Products-and-Services/Residential-Solar-Panels.a
spx
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff
I was at an SMA training yesterday in New Jersey was told 'this summer'.
Last time I spoke with their support it was April.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Sent: Tuesday, March 24, 2009 9:02 PM
Yeah, and they should make fully dimensioned constructs available in ACAD
and SketchUp freely available!!!
-Glenn Burt
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Matt
Lafferty
Sent: Friday, May 08, 2009 1:26 PM
Hi Greg,
We use this tool on the first page where you setup a new report, you can
specify the 'surface tilt settings' and override the Latitude default.
You can create a full report, then 'edit report' and change the tilt to run
other scenarios.
HTH
-Glenn Burt
From: re-wrenches
Seems that if it is only frequency you are looking for, a simple Fluke with
min/max capture is all you really need (of course it must measure
frequency).
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
I just tried to get pricing availability (have a customer that has been
patiently waiting for one), and was told by a big solar distributor - due to
large backlog @ SMA they will not get stock for at least a month...
Maybe in time for Christmas?!
-Glenn Burt
_
From: re-wrenches
I second the Tom Lane book.
A little tough to read, but tons of real world experience.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Bill Loesch
Sent: Thursday, October 29, 2009 8:41 AM
To: RE-wrenches
Subject: Re:
Make sure it does not have any 'eco-throttle' setting engaged.
This is a feature where it idles down when there is no load detected - I
think it is an option on this model too.
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun
2008 NEC: http://www.nfpa.org/freecodes/free_access_agreement.asp?id=7008SB
http://www.nfpa.org/freecodes/free_access_agreement.asp?id=7008SBcookie%5F
test=1 cookie%5Ftest=1
-Glenn Burt
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org
We have bought refurb 3 phase meters and new meter pans from Austin
International with good success.
http://www.electricalconnector.com/
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Carl Adams
If I recall, there is one on the website of our esteemed colleague, William
Miller in a spreadsheet format.
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
r...@solar4maine.com
Sent: Tuesday
How about using a piece of cardboard under the scanner, on the roof for a
smooth rolling surface?
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Hans
Frederickson
Sent: Tuesday, December 15, 2009
We have been looking at the Blue Oak line of fused combiners/load break
rated DC disconnects, but can't get the right fit / cost.
Maybe a couple would do the trick at the array for you?
-Glenn Burt
_
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
, but did I mention it was free?
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Thursday, June 09, 2011 2:53 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] commercial system monitoring
I'm
If I am not mistaken, the OSHA 10 can be completed online these days.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of North Texas
Renewable Energy Inc
Sent: Saturday, July 16, 2011 10:45 PM
To: RE-wrenches
Subject: Re
] On Behalf Of Ray Walters
Sent: Sunday, July 17, 2011 8:21 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] OSHA Certification?
Yes, but is it actually required for solar installers?
Ray
On 7/17/2011 5:33 PM, Glenn Burt wrote:
If I am not mistaken, the OSHA 10 can be completed online these days
This is an event that was foretold to us during a training session with SMA
early last year. I am surprised it took so long!
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Tuesday, July 19
Cut and paste the entire url - not all of it correctly formed in Bill's
email.
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Wednesday, July 20, 2011 10:27 AM
To: RE-wrenches
Don’t you have to be a licensed electrician as part of the prereqs to sit for
the test?
Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
d...@foxfire-energy.com
Sent: Thursday, July 21, 2011 9:46 AM
To: RE-wrenches
So the PVA-600 doesn’t require a Windows specific program to access the logging
device?
This has been a question for me as most tablets now run Android OS and not a
Microsoft product.
Is it just browser based perhaps?
Thanks!
Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
for an
Android version known to them.
Regards,
Gary Willett, PE
g...@icarussolarservices.com
On 7/30/2011 9:47 AM, Glenn Burt wrote:
So the PVA-600 doesn’t require a Windows specific program to access the logging
device?
This has been a question for me as most tablets now run Android OS
!
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jesse Dahl
Sent: Friday, August 05, 2011 10:03 PM
To: g...@icarussolarservices.com; RE-wrenches
Subject: Re: [RE-wrenches] Solmetric PVA-600
Here in NY (upstate), the utility (NatGrid, NYSEG) will not agree to an
interconnection until they have replaced the existing unidirectional kWh
meter with a bidirectional one. This is the signal that the PV system can be
energized and connected to the grid.
-Glenn
From:
We too have had this happen - customer didn't feel he had to wait for
utility approval, turned on the system after we left.
His next bill came he tried to blame it on us...
All the meters the utilities are replacing here are electronic AMR style
units. It has been a long time since I saw a
How about feeding both systems into an AC combining subpanel before feeding
the main load center?
Often the calculations required will allow you to do more backfeeding than
the simple backfeeding a load center with individual breakers.
-Glenn
From:
Hi James,
Breakers/fuses/disconnects/load centers have an Ampere Interrupt Current
(AIC) rating as well as voltage and rated trip current. This tells how much
of an arc might be created during a fault or de-energization under full
load.
When selecting an overcurrent protection device at
in the enclosure need only be rated to the protection rating of the
enclosure, as long as all conduits are properly terminated with fittings
that meet the minimum rating of the enclosure.
Thanks,
Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re
Dave,
Is the 8000 one of the transformerless inverters? Maybe there is a grounding
problem causing excess electrical noise when the inverter is in the 'grey'
zone where there is not quite enough energy from the sun to remain in a
known state.
-Glenn
From:
Siemens makes a line that are UL listed.
Their VBII series like HNF361PV – 30A
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
la...@starlightsolar.com
Sent: Sunday, November 06, 2011 2:45 PM
To: RE-wrenches
Subject:
I just received a notice email from SMA that the Sunny Boy 240 will be
available mid 2012.
There is also a webinar by SMA on 11/15 to cover their new products,
including a 'step up' transformer with other bells whistles.
FWIW there is a webinar tomorrow by Sunpower to introduce their two
Are you sure you need to split them?
IIR, there are only a pair of conductors going from each SB into the tower.
They must be combined on the SMA side of the touch-safe fuse holders in some
way.
We opted to run all our source circuits from array through 6 external discos
then into the ST
SMA makes a fused combiner specifically for their TL line of inverters as well.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Monday, November 21, 2011 11:07 AM
To: RE-wrenches
Subject: Re:
We recently began using the PVA-600 Solmetric with its wireless options.
I have found it to be a real timesaver for commercial commissioning. Testing
can be done from the rooftop, both V I without making a run to the
inverter(s) and waiting for generation (to measure each string's Imp).
Running
ASHRAE temp data as applicable to PV can be found (with some digging) on the
Solar ABCs website.
http://solarabcs.org/about/publications/reports/expedited-permit/map/map_int
ro.html
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
and voltage taps. It seems to be
their most cost effective solution at this time for 3 phase commercial
systems.
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Joel
Davidson
Sent: Wednesday, December
We have never placed modules over any vent pipes - if they cannot be
relocated, they will limit the available area for the array.
Glenn
Alteris Renewables / Real Goods Solar
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of
If you are talking about commercial flat roofs, we never use PVC - too much
expansion potential.
All our rooftop conduit runs here in the Albany, NY area are RMC of the
galvanized type, and of course, threaded.
There are standard plumbing supports with rollers, as well as standard
expansion
Send an email to Greg Smith at SMA and ask him for suggestions to get the
ball rolling.
He is one of their trainers very knowledgeable.
greg.sm...@sma-america.com
-Glenn
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
We have been using the AET RayPort on the last few jobs. Much like the
RapidRac in design, but made of stainless steel.
Goes together quickly. Looks good, easy grounding. Slight drawback is
walkability between rows is a little more tricky.
http://aetenergy.com/products/
YMMV
Glenn
time.
SI detects return of grid communicates with SB and returns it to normal UL
1741 mode
Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry Brown
Sent: Sunday, March 04, 2012 11:13 AM
To: RE-wrenches
Subject
Nicely done William - thank you for sharing your inventiveness with the
group!
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Saturday, March 03, 2012 2:57 AM
To: RE
We have been using the Siemens line of disconnects. They are designed for
use on DC circuits, and are UL listed for this application.
http://www.sea.siemens.com/us/internet-dms/btlv/CircuitProtection/HeavyDutyS
afetySwitches/docs_HeavyDutySafetySwitches/PV%20datasheet%20Sept2010.pdf
-Glenn
Sunpower is in the process of releasing their own microinverter if I recall
- maybe another option.
-Glenn
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jason
Szumlanski
Sent: Wednesday, April 04, 2012 2:58 PM
To:
Look at the Acme T-3-53044-S.
I used this in my last system.
-Glenn Burt
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Aaron
Mandelkorn
Sent: Friday, April 13, 2012 6:41 PM
To: RE-wrenches
Subject: [RE-wrenches] Sunny
AET Rayport
http://aetenergy.com/products/rayport-solar-rack-solution
Go up quickly, minimal materials, stainless steel, integrated grounding...
Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
/write the SW memory from Right Hand Engineering and Maui Solar
Software - anyone used them or recommend against them?
Thanks,
Glenn Burt
glb, Consulting Company
NABCEP Certified Solar PV Installer TM
NYSERDA Eligible Installer
Microsoft Certified Professional
Maybe this organization will make some headway on the interoperability
question.
http://www.sunspec.org/
-Glenn Burt
-Original Message-
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar Power
We have used a variety of sealants over the years, and determined simple
Henry roofing cement is the best product for use on comp roofing.
We also used to bend our own L-foot flashing, which we cut from standard Al
coil stock (before all the manufactured options were available). This might
be
I recently attended training by Magnum and all these options were discussed.
Isn't that normally how we learn about new products and options? It has been
in my experience with SMA, Sunpower, Blue Sky Energy, Morningstar, Fronius,
etc.
-Glenn Burt
From: re-wrenches-boun...@lists.re
And if used with rails, helps with lowering module temperature (increasing
distance from roof) as well as discouraging rodent nesting (again the
further away from the roof deck the modules is, the less likely nesting is
to occur) in my experience.
-Glenn