swingjun...@gmail.com wrote: Thanks to all who responded, The article Marco references, is the one referenced in the tinyurl in my original post. I did not find anything of significance in the previous Solar Pro issues. Based on the responses it seems there is no good data out there to

Re: [RE-wrenches] kW/MW v. kWh/MWh

2010-01-19 Thread boB Gudgel
Ian Woofenden wrote: This is one of my pet peeves too... A few snippets and observations from my frequently given electrical terms presentation: If I asked you How far is it to Vancouver? and you answered 45 miles per hour, everyone listening would know that someone was confused. But we

Re: [RE-wrenches] Inverter causing migraine?

2010-02-04 Thread boB Gudgel
Dan Fink said: That's a tricky situation. There are only two possibilities for what's causing the problem; sound or electromagnetic radiation I'm betting that it's sound. Remember how you could hear televisions singing away at 15 kHz ?? That still gives some people headaches. How old is

Re: [RE-wrenches] Inverter causing migraine?

2010-02-04 Thread boB Gudgel
of an ultrasonic alarm system back when I was in my 20's 30's - now I just hear ringing in my ears. Ron On 4-Feb-10, at 1:30 AM, boB Gudgel wrote: Dan Fink said: That's a tricky situation. There are only two possibilities for what's causing the problem; sound or electromagnetic radiation I'm

Re: [RE-wrenches] Inverter causing migraine?

2010-02-05 Thread boB Gudgel
sound occasionally. I used to be able to hear the sound of an ultrasonic alarm system back when I was in my 20's 30's - now I just hear ringing in my ears. Ron On 4-Feb-10, at 1:30 AM, boB Gudgel wrote: Dan Fink said: That's a tricky situation. There are only two possibilities

Re: [RE-wrenches] Inverter causing migraine?

2010-02-05 Thread boB Gudgel
ringing in my ears. Ron On 4-Feb-10, at 1:30 AM, boB Gudgel wrote: Dan Fink said: That's a tricky situation. There are only two possibilities for what's causing the problem; sound or electromagnetic radiation I'm betting that it's sound. Remember how you could hear televisions singing away

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread boB Gudgel
Nick Soleil wrote: Hi Jeff: I have had some similar issues with the Kohler generators in recent years, after installing hundreds of air cooled and water cooled generators from them. I have heard that they are less reliable now, and the company is harder to deal with now. Recently, I

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread boB Gudgel
. Thanks guys. boB Jason Szumlanski Fafco Solar Southwest Florida Original Message Message: 3 Date: Tue, 30 Mar 2010 12:07:28 -0700 From: boB Gudgel b...@midnitesolar.com To: RE-wrenches re-wrenches@lists.re-wrenches.org Subject: Re: [RE-wrenches] Kohler Generator Issues Message-ID

Re: [RE-wrenches] Kohler Generator Issues

2010-03-30 Thread boB Gudgel
of a backup. If they wanted to, they could just use the run time meter to decide if it is warranty or not, maybe. Thanks again, boB -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel Sent

Re: [RE-wrenches] [Fwd: Re: DC wire sizing]

2010-04-03 Thread boB Gudgel
Forwarding a message from Robin Gudgel... Robin Gudgel wrote: The CBI QY series of DC breakers have an arc shoot that is required to quench a DC arc. This breaker would work just fine as an AC breaker although is not marked as such. I am not sure if the AC breakers (QL, QZ and QZD series) have

Re: [RE-wrenches] [Fwd: Re: DC wire sizing]

2010-04-04 Thread boB Gudgel
, but it isn't there. I'm going back to my myth! Robin Gudgel boB Gudgel wrote: Forwarding a message from Robin Gudgel... Robin Gudgel wrote: The CBI QY series of DC breakers have an arc shoot that is required to quench a DC arc. This breaker would work just fine as an AC breaker although

Re: [RE-wrenches] low voltage modules in high voltage applications

2010-04-27 Thread boB Gudgel
Jeff Yago wrote: First let me say that we almost never work on failed systems, especially when its for somebody that picked our brains on pretense of buying a system, then they went out and bought everything on the internet, and when nothing worked they call us! Also, let me say that the

Re: [RE-wrenches] FM60/rectifier for gen charging

2010-04-27 Thread boB Gudgel
toddc...@finestplanet.com wrote: Don't you think the transformer is good for isolation? Todd I like transformer isolation, but I suppose as long as the neutral of the generator is tied to ground and battery negative you'll be OK. As far as capacitors go, there is usually plenty of

Re: [RE-wrenches] Transformer inrush

2010-05-13 Thread boB Gudgel
Richard L Ratico wrote: Interesting question, Mick. It may depend on the point in the cycle when the transformer lost power and the duration of the blip. Dick Ratico --- You wrote: Before I present a suggestion, here's a question: If by chance William is able to energize the transformer

Re: [RE-wrenches] RETURN AMP SETTING

2010-07-21 Thread boB Gudgel
Darryl Thayer wrote: That is a good question, I have not an answer, but of course it should be based on the amp hour of the battery bank, absorb charging voltage, and of course the charging source in the case of generators. Following Ron's advise start at C/5 for SOC less than 50% then C/10

Re: [RE-wrenches] NECPLUS Article

2010-08-06 Thread boB Gudgel
Joel Davidson wrote: Interesting news item, but the link does not connect to the fire fighter report. Does someone have the correct report link? In May 2010 the Fire Protection Research Foundation (FPRF) completed a one-year research project addressing photovoltaic (PV) power systems. The

Re: [RE-wrenches] Voltage discrepancy

2010-08-19 Thread boB Gudgel
Jeff Oldham wrote: I have seen this on my last 3 MX60 controllers and it is very frustrating and looks to be a design flaw. I can calibrate the meters to be accurate at either the Absorb point OR the Float point but NOT both!! Not only that but the meter calibrations tend to drift a bit in

Re: [RE-wrenches] Dog controller conflict with Outback inverter.

2010-08-27 Thread boB Gudgel
On 8/27/2010 7:51 PM, cvso...@aol.com wrote: Help! Has anyone delt with RF interference between a dog control device and GVFX3524. It seems that some frequency in the inverter (or maybe the FlexMax 80) is cancelling the emitted signal from a dog control device which shocks the dog when

[RE-wrenches] RE Visio shapes files

2010-09-05 Thread boB Gudgel
Hello Wrenches. Do any of you know where to find shape library files for drawing RE pix in Microsoft Visio ?? Solar, Wind, batteries, etc... Thanks, boB ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org

Re: [RE-wrenches] RE Visio shapes files

2010-09-05 Thread boB Gudgel
On 9/5/2010 9:32 PM, William Miller wrote: boB: I have a set of template and stencil files on my web site at: http://www.millersolar.com/resources/resources.html I never progressed beyond version 4.1T because it still works for me. You are probably using a newer version, but these files

Re: [RE-wrenches] RE Visio shapes files

2010-09-06 Thread boB Gudgel
Of *boB Gudgel *Sent:* Monday, September 06, 2010 12:44 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] RE Visio shapes files On 9/5/2010 9:32 PM, William Miller wrote: boB: I have a set of template and stencil files on my web site at: http://www.millersolar.com/resources/resources.html I

Re: [RE-wrenches] Inverter 1741 Listing Process

2010-10-08 Thread boB Gudgel
On 10/8/2010 6:04 PM, Matt Lafferty wrote: Hola Wrenches, Does anybody know off the top of their head if the /5-minute-wait-to-interconnect/ function is tested on 100% of inverters produced? /(i.e. every single inverter is tested with AC DC within the start parameters of the unit for at

Re: [RE-wrenches] Mac compatibility with Modsine

2010-10-09 Thread boB Gudgel
On 10/9/2010 3:07 PM, Carl Hansen wrote: Greetings, Does anyone know if newer Macintosh computers are still incompatible with Modsine inverters, and how about Mac loptops ? Thanks, Carl Hansen HansenSun elect. My Mac Book Pro (from early 2009) worked off of a

Re: [RE-wrenches] Inverter 1741 Listing Process

2010-10-18 Thread boB Gudgel
various aspects of the product for verification -- including the software. The overall UL1741 certification process is extremely complex, very time consuming, and quite expensive. Dan --- On *Fri, 10/8/10, boB Gudgel /b...@midnitesolar.com/* wrote: From: boB Gudgel b...@midnitesolar.com

Re: [RE-wrenches] paralleling FM-60's

2010-10-20 Thread boB Gudgel
On 10/20/2010 12:16 PM, jay peltz wrote: Hi Jeff, Its not the voltage but amps, the apollo is only 80amps, and the old MX's you can push to 70 so no real advantage there. j I think that what he means is that by switching to a 48V battery you can have (add) twice as much array power

Re: [RE-wrenches] Battery Placement

2010-10-22 Thread boB Gudgel
On 10/22/2010 10:25 AM, Allan Sindelar wrote: Ray, I don't think Robin has posted anything, it just came in a conversation we had. As I understand it, service equipment must have nothing interfering with designated working clearance, within a few inches of depth allowed. With Outback, Magnum,

Re: [RE-wrenches] Positive-ground question re Sunpower

2010-11-20 Thread boB Gudgel
On 11/20/2010 4:36 PM, Mark Frye wrote: From the 2006 white paper: * Polarization * Incorrect grounding of SunPower modules can inducea surface charge which would lower the energyproduction. Previously SunPower has announced the discovery of the surface polarization effect which creates

Re: [RE-wrenches] Roofers installing solar = creative, new installation methods

2011-01-28 Thread boB Gudgel
On 1/28/2011 8:41 AM, Solar Energy Solutions wrote: Joel, Our company cannot survive without selling an entire system. When we help the unqualified and untrained we legitimize unsubstantiated pv businesses. We get a dozen phone calls a month from folks wanting us to install their systems.

Re: [RE-wrenches] module / panel

2011-02-08 Thread boB Gudgel
On 2/8/2011 3:40 PM, David Brearley wrote: However, the term panel does appear in the NEC in the context of Article 690 Solar Photovoltaic Systems. (You'll have to submit a proposal to the Code Making Panel to change the name of the Article, Michael.) Panel is defined a collection of modules

Re: [RE-wrenches] Electromagnetic Pulse (EMP)

2011-03-19 Thread boB Gudgel
On 3/19/2011 7:53 AM, Drake wrote: Hello Wrenches, I had an inquiry concerning the effect of EMP on photovoltaic systems. We are heading for a period of solar activity that likely will produce this effect. According to a local AEP (American Electric Power) representative, the utility is

Re: [RE-wrenches] Enphase Inards - Any Guesses?

2011-04-25 Thread boB Gudgel
On 4/25/2011 8:56 AM, Mark Frye wrote: Folks, I have an Enphase D380 micro inverter sitting on my workbench (such as it is). With my ohm meter I can detect continuity between the chasis and the AC equipment ground pin, between the chasis and the DC- pin, and between the AC equipment

Re: [RE-wrenches] PV powered music festival

2011-04-27 Thread boB Gudgel
On 4/27/2011 3:51 PM, benn kilburn wrote: Wrenches, I have been asked about sizing PV systems for a couple different music festivals that have been run solely off of generators in the past. The problem i'm having is determining the energy consumption of music/stage (amps, speakers, lights,

Re: [RE-wrenches] PV powered music festival

2011-04-27 Thread boB Gudgel
On 4/27/2011 4:50 PM, Starlight Solar, Larry Crutcher wrote: Benn, I've had requests like this in the past and have found in EVERY case the customer has no idea that it will take a $$$multi-tens-of-thousands to replace the generator power. If you have the estimating experience, throw out a

Re: [RE-wrenches] PV powered music festival

2011-04-27 Thread boB Gudgel
Just as an aside, today's inverters are pretty much a Class D audio amplifier anyway. An inverter ~could~ actually be used for a subwoofer amplifer in some cases. I've always wanted to have an inverter with an audio jack on it just for that and actually did try that back a Trace

Re: [RE-wrenches] Magnum: meter won't reset; Internal Bridge error

2008-09-22 Thread boB Gudgel
boB asked: Does this customer have another charging source besides a generator, like PV? Mick says: No...that is unfortunate because the customer doesn't want to allow the generator to grind away for the additional hours required for a full recharge. boB says: That's certainly

Re: [RE-wrenches] Magnum: meter won't reset; Internal Bridge error

2008-09-22 Thread boB Gudgel
boB says: I forgot one possibly important thing !! Mick says: The battery string is 400 amp hours, which also happens to be the Magnum default. This setting pre-disposes the Magnum charger for a 120 minute absorption period before shifting to float. 2% of 400 is only eight amps, so I'll bet the

Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5

2008-10-31 Thread boB Gudgel
Hi David. Gary Baxter says he apologizes for not having that exact wiring diagram for the Kohler RES generator and the answer you got over the phone. (we gotta get him on this list too soon) Magnum Energy does rely somewhat on customers to help with different generator wiring if they

Re: [RE-wrenches] Magnum AGS with Kohler RES 8.5

2008-10-31 Thread boB Gudgel
boB Gudgel wrote: Hi David. Gary Baxter says he apologizes for not having that exact wiring diagram for the Kohler RES generator and the answer you got over the phone. (we gotta get him on this list too soon) Magnum Energy does rely somewhat on customers to help with different generator

Re: [RE-wrenches] Soldering electrical conductors

2008-12-03 Thread boB Gudgel
From: The Office of Tom Duffy [EMAIL PROTECTED] About 28 years ago I read a study, by either Niehoff or Prestolite, on the pros and cons of soldering or crimping, heavy duty starter cables, for over the road trucks. The finding was, that a properly crimped lug made a solid (molecular)

Re: [RE-wrenches] Has Xantrex Changed Ownership?

2008-12-07 Thread boB Gudgel
Kelly Keilwitz, Whidbey Sun Wind wrote: Hi All, Xantrex is gone from Washington. I’m fairly sure that it’s complete. They’ve been moving out since they bought Trace. Perhaps the Xantrex rep can confirm. -Kelly I know that there is at least one (1) Xantrex person still here in

Re: [RE-wrenches] CFL lighting and the mercury hazard.

2008-12-09 Thread boB Gudgel
Ian Woofenden wrote: Great stuff, Dan I realize this subject should go to another list, but I had to mention that if you receive flu shots, then you more than likely are also injecting mercury by way of the preservative, Thimerosal, which in the doses they give, are only insignificant if

Re: [RE-wrenches] Inverter with two strings of different orientation

2008-12-28 Thread boB Gudgel
Peter Parrish wrote: Bill, I looked into this several years ago, and I was able to get some digitized I-V data. I can't find that now (but I will). The data supports my claim. Vmp does change with irradiance. It just changes very little. Depends on your definition of change I guess.

Re: [RE-wrenches] fire safety vs. fire hysteria?

2009-01-05 Thread boB Gudgel
Date: Mon, 05 Jan 2009 16:07:58 -0500 From: Nicholas Ponzio npon...@buildingenergyus.com I just got this email forwarded from a coworker that volunteers as a firefigher. Your comments are welcome: I agree that fire access may be restricted, but a bunch of this report I would say is

Re: [RE-wrenches] Back feeding battery inverter with grid-tie inverter

2009-01-19 Thread boB Gudgel
Chris Schaefer wrote: Also Robin at Midnight Solar has been promising to come out with a higher VOC charge controller too. How about it Robin? I'll be needed one for this spring for use at our Design and Training Center for use in a class. Be happy to do some Beta testing for you. Chris

Re: [RE-wrenches] Magnum MS4448AE Compatibility Question

2009-02-10 Thread boB Gudgel
David Katz wrote: Hi Allan, This is not an unusual problem. i have seen it with conventional forced air heating systems. The burner controls would not run on A Xantrex or Outback sine wave inverter. There is something about waveforms from inverters designed by Trace legacy engineers. I

Re: [RE-wrenches] Energy Savings - What is Real?

2009-04-11 Thread boB Gudgel
Travis Creswell wrote: While were on the subject of magic boxes. Watch the top video in below link. On the residential and commercial installs he tells you to watch the power factor (which does improve) but at the top of the meter you also see kW which they do not highlight. You'll have to

Re: [RE-wrenches] Fronius IG4000 problem

2009-04-20 Thread boB Gudgel
boB Gudgel wrote: Mark Dickson wrote: Hi Bob, From what I understand the State 108 code means that the grid frequency is out of whack. Frequency and voltage windows are both related to anti-islanding detection, so I don't doubt you would receive this message. I would be surprised if the error

Re: [RE-wrenches] Inverter Data

2009-04-21 Thread boB Gudgel
Orion Thornton wrote: Wrenches, Can anyone help me to determine the commutation type and rated power factor (%) for a Fronius 4000 IG. These are required line items on a permit application. The options for commutation type are forced and line. I feel like this may apply to older

Re: [RE-wrenches] nabcep executive director

2009-06-10 Thread boB Gudgel
paul wilkins wrote: congratulations, ezra Gee... I thought Ezra ~WAS~ already the head of all NAPCEP ?? Congrats anyhowz, Ezra ! boB ___ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-26 Thread boB Gudgel
Larry Crutcher, Starlight Solar wrote: If the SB50 is like other Solar Boost products, there is a zener diode on the PV input that will open if the voltage exceeds the Voc maximum. The controller will not burn up or be fried but you will have to replace the diode. Why it has not happened yet

Re: [RE-wrenches] Solar Boost Controller in Senegal

2009-06-27 Thread boB Gudgel
Wind-sun.com wrote: Yes, it is a poor design. though you may not have any problems there with the heat de-rating of the panels. If the panel temperature gets under about 40C you may blow out the input. As long as you have a load on the output of the contgroller, it will keep the voltage down,

Re: [RE-wrenches] Inverter AM Interference

2009-07-15 Thread boB Gudgel
solar...@aol.com wrote: This is a brand new 5000 US. EMT on all dc runs. The radio is a BOSE...and is 27 feet away. The interference is runs 24/7... so it must be AC related. Does the radio noise go away when you completely disconnect the SMA inverter ? boB

Re: [RE-wrenches] Inverter AM Interference

2009-07-15 Thread boB Gudgel
solar...@aol.com wrote: It disappears when the breaker is thrown. Pat Redgate OK, is that the AC breaker or the PV input breaker ? How about when you throw the PV input breaker (when not MPPTing) ? Does that help ? i.e. We know now that it's the inverter's auxiliary power supply, but is

Re: [RE-wrenches] Trace non-volatile memory after market

2009-07-17 Thread boB Gudgel
Allan Sindelar wrote: Randy, We have a very clean, very early used takeout SW4024 (serial #255 or so) with Rev 1.0 firmware (and a few Rev. 4.01 chipsets to match yours). It appears to have worked flawlessly for 15 years (there’s a way to tell with the earliest ones). Contact me offlist if

Re: [RE-wrenches] Fwd: Grounding on a glacier??

2009-07-23 Thread boB Gudgel
Larry Crutcher, Starlight Solar wrote: Hi Jay, An interesting quandary indeed. This is another good example of an application that I was trying to grill Sunpower about --- as far as grounding their modules that need to be positive grounded in order to take advantage of their higher

Re: [RE-wrenches] Fwd: Grounding on a glacier, SunPower modules

2009-07-23 Thread boB Gudgel
, boB Gudgel wrote: Larry Crutcher, Starlight Solar wrote: Hi Jay, An interesting quandary indeed. This is another good example of an application that I was trying to grill Sunpower about --- as far as grounding their modules that need to be positive grounded in order to take advantage

Re: [RE-wrenches] CBI circuit breakers

2009-07-28 Thread boB Gudgel
Allan Sindelar wrote: Dan, My understanding is that CBI breakers aren't based on a temperature-related mechanical action, but a magnetic-hydraulic function. I recall that this was marketed (by Outback? Robin?) as superior to thermal-trip mechanisms as it was not prone to heat-induced nuisance

Re: [RE-wrenches] CBI circuit breakers

2009-07-29 Thread boB Gudgel
Nick Lucchese wrote: Wrenches, While we're on the subject of CBI breakers does anyone know a sure way to distinguish between the AC and DC versions? Depending on the order we get our stock from both Outback (or Outback vendors) as well as directly from Midnite. It's obvious with Midnite's

Re: [RE-wrenches] Power Factor

2009-07-30 Thread boB Gudgel
factors. Not 100% sure, but I think GT inverters would help not hurt the PF problem in most situations. Correct me on any and all of this, Oh fellow wrenches, R. Walters Solarray.com NABCEP # 04170442 On Jul 30, 2009, at 9:19 AM, boB Gudgel wrote: Ron Young wrote: Ok, so all seem

Re: [RE-wrenches] Power Factor

2009-07-30 Thread boB Gudgel
or at least very low. boB boB Gudgel b...@midnitesolar.com wrote: Matt wrote: Possibly a PF question, or maybe one for Magnum - boB, One of the guys at work is (almost) running a 3/4 hp sub pump with a Magna AE 48. Or rather, he isn't. According to him when he first fired

Re: [RE-wrenches] Power Factor

2009-07-30 Thread boB Gudgel
On Jul 30, 2009, at 4:03 PM, Matt wrote: Unh - hunh, but it will run on the generator. If it didn't, I would go for the bad starter or motor, but it seems like the PF could be an issue?? Matt T boB Gudgel b...@midnitesolar.com wrote: Matt wrote: Possibly a PF question, or maybe

Re: [RE-wrenches] Starting 3/4 Sub Pump (was Power Factor)

2009-07-30 Thread boB Gudgel
...@lists.re-wrenches.org] On Behalf Of boB Gudgel Sent: Thursday, July 30, 2009 4:45 PM To: Matt Cc: RE-wrenches Subject: Re: [RE-wrenches] Power Factor Matt wrote: Possibly a PF question, or maybe one for Magnum - boB, One of the guys at work is (almost) running a 3/4 hp sub pump with a Magna

Re: [RE-wrenches] Surge protector update?

2009-07-31 Thread boB Gudgel
North Texas Renewable Energy Inc wrote: August I made a service call to a residential PVinstallation several years ago that I did not install. The vintage Trace, size I don't recall, had quit working. The Delta surge suppressor had actually ruptured along it's radial seam, a result I had

Re: [RE-wrenches] solid vs stranded AC vs DC

2009-08-01 Thread boB Gudgel
jay peltz wrote: Hi Darryl, But what are the differences and when do they come into play? Question interruptus and my 2 cents worth, Jay... Except for REAL long lines, like utility transmission lines, the AC skin effect, which is what I think you might be referring to here, is probably

Re: [RE-wrenches] Power Factor

2009-08-01 Thread boB Gudgel
not), a motor starter problem or an inverter issue? I have to admit to being somewhat baffled by this one because it ran the pump once, but not after. Matt T boB Gudgel b...@midnitesolar.com wrote: boB Gudgel wrote: So, because of the different ways of specifying PF, it is always best

Re: [RE-wrenches] Magnum inverters (not really a power factor issue)

2009-08-01 Thread boB Gudgel
Larry Crutcher, Starlight Solar wrote: Hey Matt, I sure wish their techie's would get to the bottom of it. I am getting gun-shy about selling Magnum and they are about the best available for small 12 volt systems. I have spend hours trying to solve the problem. My customer is still not a

Re: [RE-wrenches] Magnum inverters (not really a power factor issue)

2009-08-01 Thread boB Gudgel
the peak DC voltage seen at the inverter terminals due to L-C resonance. boB --- On Sat, 8/1/09, boB Gudgel b...@midnitesolar.com wrote: From: boB Gudgel b...@midnitesolar.com Subject: Re: [RE-wrenches] Magnum inverters (not really a power factor issue) To: RE-wrenches re-wrenches@lists.re

Re: [RE-wrenches] solid vs stranded AC vs DC

2009-08-03 Thread boB Gudgel
Wind-sun.com wrote: See http://en.wikipedia.org/wiki/Eddy_current The practical effects of running a single wire in 98% of the systems that any solar installers will ever see is probably just about zero, and it also only applies to AC currents (or rapidly varying DC, which is not common).

Re: [RE-wrenches] solid vs stranded AC vs DC

2009-08-03 Thread boB Gudgel
Matt Tritt wrote: Darryl, Say what?! This would seem to indicate that solid core is actually better for DC than stranded wire. Can this possibly be true?? Matt The reason that stranded is higher resistance than solid is that there is more air in between the strands. Solid wire doesn't

Re: [RE-wrenches] utility line voltage issues

2009-08-16 Thread boB Gudgel
Marv Dargatz wrote: Check out the following link. Just ONE example of what the utility must deal with. http://tdworld.com/customer_service/power_new_technology_solves/ I'm not defending the utilities. They definitely have their faults (argh, argh), but they have some severe challenges that

Re: [RE-wrenches] power factor

2009-08-19 Thread boB Gudgel
Drake Chamberlin wrote: One question about power factor: We know it is the ratio of the real power to the apparent power, and that most utility meters only register real power (watts). Reactive power doesn't dissipate as heat like power loss through a resistor. The question is: What is

Re: [RE-wrenches] power factor

2009-08-20 Thread boB Gudgel
temperature superconductors will play a big roll in reducing all losses. boB Brian Teitelbaum AEE Solar -Original Message- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of boB Gudgel Sent: Wednesday, August 19, 2009 9:28 PM

Re: [RE-wrenches] raintite box mounting angle

2009-08-26 Thread boB Gudgel
Conrad Geyser wrote: We always fill any conduit at the point of building penetrations for air sealing. Otherwise in winter, not only will the conduit get house moisture condensing inside of it, but it will act a a nice thermo siphon for pulling warm air out of the house….. Just a note

Re: [RE-wrenches] Magnum Battery Charger Question

2009-09-27 Thread boB Gudgel
Jason Lerner wrote: Hi Bob, I put on an old Todd charger with Voltage regulation, but not absorb and float. I can change the voltage up or down as needed. Changing out the remote is a good idea. I do have another Magnum inverter at another location, but was trying to avoid another

Re: [RE-wrenches] Magnum Battery Charger Question

2009-09-27 Thread boB Gudgel
boB Gudgel wrote: Jason Lerner wrote: Hi Bob, I put on an old Todd charger with Voltage regulation, but not absorb and float. I can change the voltage up or down as needed. Changing out the remote is a good idea. I do have another Magnum inverter at another location, but was trying

Re: [RE-wrenches] AC Coupled Re-visited

2009-10-21 Thread boB Gudgel
Jeff Yago wrote: There have been some good advice related to battery bank sizing and a better description of how Sunny Islands work with SunnyBoys, but I am afraid we are getting away from my original post that started this and that was: Since a battery based inverter has a battery charging

Re: [RE-wrenches] SW Parallel stacking cable

2009-11-04 Thread boB Gudgel
Brian Teitelbaum wrote: William, The SW Parallel Stacking Interface (SWI/PAR) was much more than just a cable (like the Series Stacking Cable -SWI). it was a separate box, like the Grid Tie Interface (GTI) unit was. It retailed for about $345.00 Good luck finding one. Brian

Re: [RE-wrenches] Strings and series of batteries with reverse return linkup

2009-12-05 Thread boB Gudgel
Antony Tersol wrote: Assume 3 parallel battery stings, with identical batteries of internal resistance r. Assume identical wire leads of resistance R. Then when the batteries have the same state of charge and their internal resistances are equal, one can solve for the current in each

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread boB Gudgel
OK, I've been hearing for years now that one battery string is best and maybe two but no more should be used. What is the reason for this fear ???What is the experience with multiple strings in parallel ?? If it is because of current sharing of the strings, that shouldn't be an

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread boB Gudgel
was system reliability and redundancy and the idea of a single string failure was a big worry which is why I never would consider it. Tom *From:* boB Gudgel mailto:b...@midnitesolar.com *Sent:* Tuesday, May 31, 2011 8:16 PM *To:* RE-wrenches mailto:re-wrenches@lists.re-wrenches.org *Subject:* Re: [RE

Re: [RE-wrenches] 24 volt Battery Bank comparison, Why a single string?

2011-06-01 Thread boB Gudgel
business. Larry Crutcher Starlight Solar Power Systems 11871 S Fortuna Road, #210 Yuma, AZ 85367 la...@starlightsolar.com mailto:la...@starlightsolar.com (928) 342-9103 On May 31, 2011, at 11:16 PM, boB Gudgel wrote: OK, I've been hearing for years now that one battery string is best and maybe

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-01 Thread boB Gudgel
with the imager. I just wish they were cheaper ! boB boB Gudgel wrote at 01:00 AM 6/1/2011: This might be a good reason for an installer to have one of those FLIR (or similar) thermal imager cameras.  They're a bit on the expensive side, but could really be helpful for so many things. Â

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread boB Gudgel
it for finding uninsulated spaces, but cannot attest to its durability or suitability for the other uses mentioned above. boB Gudgel wrote at 01:00 AM 6/1/2011: This might be a good reason for an installer to have one of those FLIR (or similar) thermal imager cameras.  They're a bit

Re: [RE-wrenches] 24 volt Battery Bank comparison

2011-06-02 Thread boB Gudgel
Bank comparison From: boB Gudgel b...@midnitesolar.com mailto:b...@midnitesolar.com Date: Thu, June 02, 2011 8:56 pm To: RE-wrenches re-wrenches@lists.re-wrenches.org mailto:re-wrenches@lists.re-wrenches.org Nobody mentioned this in this thread, but it occurs to me

Re: [RE-wrenches] how would you measure a partial short circuit

2011-06-30 Thread boB Gudgel
On 6/30/2011 8:35 PM, Nick Vida wrote: Hi wrenches. I had an interesting case today that I have been thinking about since it happened. I dont have all the details because the homeownter had to leave before I was done with the service call, but here is what I do know. SB5000 with 2 strings of

Re: [RE-wrenches] how would you measure a partial short circuit

2011-07-01 Thread boB Gudgel
...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *boB Gudgel *Sent:* Thursday, June 30, 2011 10:19 PM *To:* RE-wrenches *Cc:* Nick Vida *Subject:* Re: [RE-wrenches] how would you measure a partial short circuit On 6/30/2011 8:35 PM, Nick Vida wrote: Hi

Re: [RE-wrenches] how would you measure a partial short circuit

2011-07-01 Thread boB Gudgel
On 6/30/2011 8:35 PM, Nick Vida wrote: Hi wrenches. I had an interesting case today that I have been thinking about since it happened. I dont have all the details because the homeownter had to leave before I was done with the service call, but here is what I do know. SB5000 with 2 strings of

Re: [RE-wrenches] how would you measure a partial short circuit

2011-07-01 Thread boB Gudgel
On 6/30/2011 11:35 PM, boB Gudgel wrote: On 6/30/2011 8:35 PM, Nick Vida wrote: Hi wrenches. I had an interesting case today that I have been thinking about since it happened. I dont have all the details because the homeownter had to leave before I was done with the service call, but here

Re: [RE-wrenches] how would you measure a partial short circuit

2011-07-01 Thread boB Gudgel
On 7/1/2011 12:07 AM, boB Gudgel wrote: On 6/30/2011 11:35 PM, boB Gudgel wrote: On 6/30/2011 8:35 PM, Nick Vida wrote: Hi wrenches. I had an interesting case today that I have been thinking about since it happened. I dont have all the details because the homeownter had to leave before I

Re: [RE-wrenches] how would you measure a partial short circuit

2011-07-01 Thread boB Gudgel
/2011 12:12 AM, boB Gudgel wrote: On 7/1/2011 12:07 AM, boB Gudgel wrote: On 6/30/2011 11:35 PM, boB Gudgel wrote: On 6/30/2011 8:35 PM, Nick Vida wrote: Hi wrenches. I had an interesting case today that I have been thinking about since it happened. I dont have all the details because

Re: [RE-wrenches] Fwd: Car charging station without grid

2011-07-14 Thread boB Gudgel
On 7/14/2011 1:43 PM, Allan Sindelar wrote: Wrenches, I'm stumped as to the best approach for a customer who wants a non-grid-tied, batteryless PV-powered EV charging station. See below, from one of our salespeople. Any ideas? Thank you, Allan So, does this car in the car charging station

Re: [RE-wrenches] 1987 NEC

2011-07-19 Thread boB Gudgel
On 7/19/2011 2:34 PM, David Brearley wrote: Presumably the latter---added as part of the cycle of revisions initiated in 1987. The array shorting requirement must have gone away near 1993 or 1994 as I designed an opening and shorting of the array style GFPD version in 1994 while at Trace

Re: [RE-wrenches] Power Factor (was Efficient step up, down transformers)

2011-07-26 Thread boB Gudgel
On 7/26/2011 4:42 PM, Joel Davidson wrote: Power factor less than 1.0 can shorten the life of and damage equipment and reduce PV production. We installed a 200 kW PV system on a facility with a lot of 3-phase motors and monitored the PV and the grid. We measured around 0.7 PF being delivered

Re: [RE-wrenches] 2 SW inverters on three phase

2011-07-28 Thread boB Gudgel
Do you just want to charge batteries and are these regular 120VAC SWs ?? 120/208 ?? If so, you should just be able to connect each SW from neutral to hot. No stacking necessary. A regular SW stacking cable won't work for delta connections because that assumes the phases are going to

Re: [RE-wrenches] 2 SW inverters on three phase

2011-07-28 Thread boB Gudgel
On 7/28/2011 12:32 PM, William Miller wrote: Friends: First of all, the inverters are PS series, not SW. Second, I have created a solution: I can acquire a transformer that will connect a primary across two of the 208 generator phases and create 120/240 off of the secondary. This will

Re: [RE-wrenches] 2 SW inverters on three phase

2011-07-28 Thread boB Gudgel
Of *boB Gudgel *Sent:* Thursday, July 28, 2011 10:56 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] 2 SW inverters on three phase Do you just want to charge batteries and are these regular 120VAC SWs ?? 120/208 ?? If so, you should just be able to connect each SW from neutral to hot

Re: [RE-wrenches] Large, off grid

2011-08-15 Thread boB Gudgel
On 8/15/2011 6:34 PM, Darryl Thayer wrote: Hi wrenches, I have been informed off list that my system is not a supported configuration, that one phase can be paralelled, but the other two can not, one only on each of the other legs. So unless Outback comes back with more info, I was wrong.

Re: [RE-wrenches] Evergreen goes down

2011-08-18 Thread boB Gudgel
On 8/18/2011 11:10 AM, Marco Mangelsdorf wrote: Evergreen Solar, one of the last remaining independent U.S. module manufacturers, announced their plan to file for bankruptcy protection this week. Done in by plummeting module pricing no doubt. I'm sure you all are getting the same kind of

[RE-wrenches] Louis Valenta / interisland Solar

2011-08-29 Thread boB Gudgel
I am sad to report that /Louis Valenta of interisland Solar in Hawaii has passed away in the last few days. Louis had a heart attack about a week ago and this is probably related to that. //He was a very good person, friend and also extremely knowledgeable in our industry. // We will

Re: [RE-wrenches] unique battery bank design question

2011-09-03 Thread boB Gudgel
On 9/3/2011 7:57 PM, Darryl Thayer wrote: I have had one experiance with equalizers, the batteries be came very unequal. (over time of course) *From:* R Ray Walters r...@solarray.com *To:* RE-wrenches re-wrenches@lists.re-wrenches.org *Sent:* Saturday, September 3, 2011 5:55 PM *Subject:* Re: