I read through this thread, and I don't think one important as
422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Jason Szumlanski via RE-wrenches
> *Sent:* Monday, October 30, 2023 7:33 AM
> *To:* RE-w
ischarged very carefully. I do not believe
> AC-coupled charging is a good way to charge lithium batteries, or any
> battery.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar
www.millersolar.com
CA Lic. 773985
*From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski via RE-wrenches
*Sent:* Monday, October 30, 2023 7:33 AM
*To:* RE-wrenches
*Cc:* Jason Szumlanski
*Subject:* Re: [RE-wrenches] AC Coupling
I read
of 100% AC coupled PV, but
> these days there are very few legitimate concerns or issues... Most if not
> all of which disappear with a 10% - 60% DC coupled system.
>
> Thanks,
> Kienan
>
>
> *Green-Go Solar Wholesale Distribution*
> *maxfieldso...@hotmail.com *
>
ieldso...@hotmail.com<mailto:maxfieldso...@hotmail.com>
(801) 631-5584 (Cell)
www.distribution.solar
From: RE-wrenches on behalf of
Jerry Shafer via RE-wrenches
Sent: Saturday, October 28, 2023 11:14 PM
To: William Miller ; RE-wrenches
Cc: Jerry Shafer
Subje
inverters
> is a crude affair. I am not a fan.
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* Jay [mailto:jay.p
t:* Saturday, October 28, 2023 1:58 PM
*To:* will...@millersolar.com; RE-wrenches
*Subject:* Re: [RE-wrenches] AC Coupling
I’m going to both agree and disagree
Agree The older inverters ( Schneider, Outback, etc) your drawing is
correct.
Disagree For many new inverters ( sol ark, ev4, fortress) t
And just to muddy the waters a little, 2023 NEC uses AC Connected and DC
connected wording in place of coupled. Same concept, new name.
On Sat, Oct 28, 2023 at 5:01 PM Roland - RES via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Agreed and we'll understand the differences, all of
Agreed and we'll understand the differences, all of our SMA SI systems utilize both dc charging and AC coupled charging.Roland ShackelfordPresident / OwnerNABCEP PVIP #091209-162Office 808.775.7410Mobile 808.938.9239Power Solutions for Generations Renewable Energy Services, Inc." Where there is
I’m going to both agree and disagree Agree The older inverters ( Schneider, Outback, etc) your drawing is correct. Disagree For many new inverters ( sol ark, ev4, fortress) they bring ac coupling into the inverter directly. Usually on the generator input and not in the backup loads panel. And I
I agree totally with your drawings.
On Sat, Oct 28, 2023 at 4:17 PM William Miller via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Friends:
>
>
>
> I am starting to get the impression that there is a diversion on the
> understanding of the definition of AC coupling within the
Friends:
I am starting to get the impression that there is a diversion on the
understanding of the definition of AC coupling within the industry. I
think this definition needs to be clarified.
Below is a diagram of what I understand is a DC coupled system (I hope
these diagrams come
Are there any options out there similar to the Enphase System Controller
MID that directly couple the AC outputs of a PV inverter and generator to
simultaneously power loads? And can any do it with or without batteries
involved?
Jason Szumlanski
Florida Solar Design Group
Sam,
Thanks for pointing me in that direction. It looks like you can update some
of the grid protection settings, although I am not sure if that will allow
for freq-watt control. My LG rep told me to use CA rule 21 grid profile,
but I am not sure if there is something like that on the old A series
Good Morning, Dave,
Take a look at this pdf and see if the info about setting up "Grid
Protection" gets you anywhere. Starting on page three it shows how to make
the Vmin/max and Fmin/max for screened inverters. What I can't verify for
you is whether the A series has the same menu structure as
Hi all,
Does anyone know if you can make the SolarEdge inverters (the A series,
before the HD wave inverters) respond to frequency control? I cannot find a
way to update the grid settings, and was wondering if anyone else has AC
coupled these inverters to a non-SolarEdge battery system. If not,
I can use in the book as a universal explanation of how this
> works? It can be SMA documentation, or other ref. You can reply here if
> it's useful to the list, and/or contact me off-line.
>
> Thanks! – Windy
>
> On Dec 1, 2022, at 5:47 PM, re-wrenches-requ...@lists.re-wrenches.or
e.
Thanks! – Windy
> On Dec 1, 2022, at 5:47 PM, re-wrenches-requ...@lists.re-wrenches.org wrote:
>
> From: Harry Mahon <mailto:michael.ma...@sma-america.com>>
> Subject: Re: [RE-wrenches] AC Coupling Standard?
> Date: December 1, 2022 at 5:47:18 PM MST
> To: RE-wren
When AC coupling using 2 or more OB radian inverters, it is only the master
inverter(at least that's where ac-coupling status shows as "yes") which can
be set to, and perform "ac-coupling", correct? The Mate3s option to enable
AC-coupling does not specify individual ports(inverters) to select and
>From an Outback application note:
"Precautions Using a Generator When AC Coupling
Most residential generators, and even some commercial grade generators, are
not designed to
synchronize with another AC source. They may experience catastrophic
failure if the other AC source is
a “stiffer” source
Jeremy
With a mate 3 and a hub. Wire the out- puts into their own breaker in a
service panel then out to the critical loads panel
- Original Message -
From: Jeremy Rodriguez
To: RE-wrenches
Sent: Friday, December 28, 2018 12:30 PM
Subject: [RE-wrenches] AC Coupling
I have been reading Outbacks AC coupling note.
It refers to using only a single Radian Inverter.
Is it possible to duplicate the equipment if more PV is installed, and use two
Radians, with their outputs paralleled to the critical loads panel?
I see it recommends 6Kw of PV with an 8048 Radian
Wrenches
You can still AC couple Outback, they just eliminated tha option because of
breaker issues but it can still be done using contactors all set to
normally open and configured by DC Voltage. With Outback there is no real
limit to battery capasity like you have with both the new SMA sunny boy
I've liked the StorEdge design of SolarEdge since it was first introduced a
few years ago, but have never done it even seen an instant with it. What
are others experience with it, especially compared to AC coupled battery
backup solutions?
Howie
On Jul 25, 2018 8:18 PM, "Scot Arey" wrote:
Yes I
Yes I had also heard from Outback that AC Coupling not supported.
Too bad because the AC coupling load center was slick setup and integration.
Scot
Get Outlook for Android
On Wed, Jul 25, 2018 at 10:29 AM -0600, "Kelly Keilwitz, Whidbey Sun & Wind"
wrote:
Larry,I
Larry,
I recommend considering retrofitting the SolarEdge “StorEdge” Li-ion battery.
It’s a high-voltage battery on the PV side of the inverter. We have a few out
there now for a few months without a problem. Really like the design concept of
the storage on the PV side, increasing system
Kirpal
Thanks for the recommendations
If you have a diagram that would be most helpful and generous
What Lithium Battery are you using with this configuration?
Much Appreciated
Larry
Larry Brown
Sun Mountain
845-657-8096
sunmount...@netstep.net
On Jul 19, 2018, at 11:15 AM, Kirpal wrote:
Larry
I have had very good luck with Outback both with the FX and the newer
Radian systems, have not tried this with the new "R" inverter system, we
have used the contactors to reduce production once the batteries are full
in the off gird application. Simple and strait forward and been good
Jerry
Larry
Outback Radians work great.
peter
- Original Message -
From: "Larry Brown"
To: "RE-wrenches"
Sent: Thursday, July 19, 2018 10:07 AM
Subject: [RE-wrenches] Ac Coupling
Does anyone have a recommendation on a battery based inverter to AC Couple
with a
Brown
To: RE-wrenches
Sent: Thursday, July 19, 2018 10:07 AM
Subject: [RE-wrenches] Ac Coupling
Does anyone have a recommendation on a battery based inverter to AC Couple with
a Solar Edge 11400A-US Inverter that is already installed?
I have been working a lot with the Schneider Conergy XW
Larry.Outback Radian would work fine but you would need 2 of the 8kW
inverters for your ~11kW GT inverter. Outback recommends a maximum 75%
loading ratio when AC coupling. We have used a simple solid state relay
controlled by the Aux Out of the Radian to turn off one leg of the
SolarEdge
I am working with a similar situation. It looks like the Tesla Powerwall
will work.
Kevin Eigel
Ecohouse Solar
On Thu, Jul 19, 2018, 10:07 AM Larry Brown wrote:
> Does anyone have a recommendation on a battery based inverter to AC Couple
> with a Solar Edge 11400A-US Inverter that is already
You could ask them? I know the XW+ works fine with the SMA TL series grid
inverters. Phone: +1 866-519-1470
Email: re.techsupp...@schneider-electric.com --Dave
> Does anyone have a recommendation on a battery based inverter to AC Couple
> with a Solar Edge 11400A-US Inverter that is already
Does anyone have a recommendation on a battery based inverter to AC Couple with
a Solar Edge 11400A-US Inverter that is already installed?
I have been working a lot with the Schneider Conergy XW+ Inverters for off grid
but have no experience AC Coupling them with a Solar Edge Inverter
Any
I checked into the PRI strategy a few months back. An Outback
applications engineer responded that while they were collaborating with
SolarEdge at one time on the method, they don't recommend it any longer
and were going to pull the tech note. The response also questioned
whether SolarEdge
Hi Gary,
These Solar Edge inverters can use radio ripple control to change power
output. Its a simple control strategy that allows control of the power
output presumably from a grid-operator. You would need to enable the
RRCR. Here is a paper about that
Maverick:
Thanks for responding. You've been very helpful in the past with
my battery based solution questions.
Daily load demand from the Protected Loads Panel is about 10kWh.
With 5 average daily peak sun hours, and 75% charging efficiency,
the
How many kWh are you shooting for?
> On Oct 17, 2016, at 9:54 PM, Gary Willett
> wrote:
>
> Esteemed Wrenches:
>
> Anyone have experience setting up AC coupling with SolarEdge and the Outback
> Radian?
>
> I have a client with a SolarEdge SE1A-US
It looks like way too much power to AC couple
with a 4KW Radian. Be sure to talk to an Outback
engineer in great detail before using the GSLC175AC-120/240.
At 10:54 PM 10/17/2016, you wrote:
Esteemed Wrenches:
Anyone have experience setting up AC coupling
with SolarEdge and the Outback
Esteemed Wrenches:
Anyone have experience setting up AC coupling with SolarEdge and the
Outback Radian?
I have a client with a SolarEdge SE1A-US inverter, equipped with
31 SunPower X21-345 modules (10.7kWp) and associated SolarEdge P400
DC optimizers.
;
> Brian
>
> AEE Solar
>
> bteitelb...@aeesolar.com
>
>
>
>
>
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of Howie Michaelson
> Sent: Monday, June 06, 2016 8:56 AM
> To: RE-wrenches
> Subject: [RE-wrenches] AC coupling with Solar
Hi all,
Apparently SolarEdge is no longer officially supporting or warranting AC
Coupling - maybe because they now have the StorEdge option (has anyone
actually seen one for sale and/or operating). In any case, since I have
sold prior to missing that memo and am now in the position of installing a
RE-wrenches <re-wrenches@lists.re-wrenches.org
<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: [RE-wrenches] AC-coupling Enphase/XW Causes Flickering of
Lights
Hi Matt,
I can’t tell you the reason but I had the same problem on my Outback VFX.
I didn’t put it on a O scope,
ginal message
> From: jay <jay.pe...@gmail.com>
> Date: 09/21/2015 6:58 AM (GMT-10:00)
> To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
> Subject: [RE-wrenches] AC-coupling Enphase/XW Causes Flickering of Lights
>
> Hi Matt,
>
> I can’t tell
Hi Matt,
I can’t tell you the reason but I had the same problem on my Outback VFX.
I didn’t put it on a O scope, but sure looked like a 60 cycle flicker to me.
On my system of 2 enphase, when the loads exceeded the output of the enphase
the flicker when away.
But only 2 isn’t very real world.
I wired an Enphase string into my critical loads panel at my shop. I was
curious to see how it would work as I have customers with Enphase systems
that occasionally contact me about adding a battery backup system.
Why do the fluorescent lights and LEDs flicker once the grid power is
dropped.
-wrenches@lists.re-wrenches.org>
Subject: [RE-wrenches] AC-coupling Enphase/XW Causes Flickering of Lights
Hi Matt,
I can’t tell you the reason but I had the same problem on my Outback VFX.I
didn’t put it on a O scope, but sure looked like a 60 cycle flicker to me.
On my system of 2 enphase, wh
I'll tell you exactly how to do this, if I understand the SolarEdge
documentation. I am working on a similar project, but using a contactor to
disconnect three 10KW String inverters.
Forget the Radio Ripple. The SolarEdge has a simple four line control
system. SMA has the same thing on it's Power
Hello wrenches,
I have a request to design a modest battery backup system for a residence
that has a 10 kW grid-tied Solar Edge system using a single SolarEdge
Inverter SE1A- US. I'd like to try to utilize the solar potential that
we have on site. One idea that I had was to use DC relay(s)
Hi Mac,
It looks like they are doing all that work on the AC side.
If you do the DC side, you'll lose the comm from the optimizers causing error
messages etc.
For the few times a year this will actually need to regulate, depending on the
battery inverter I'd install a AC relay and kill the
Mac
Outback makes a AC couple ready radian wired box its nice because it
already has the relay to kill the PV system along with the programming to
make it work
Jerry
On Wed, Dec 10, 2014 at 6:04 AM, jay peltz j...@asis.com wrote:
Hi Mac,
It looks like they are doing all that work on the AC
Question
Is the Hz shift/ power reduction included/required in all battery less
inverters?
Thanks
Jay
Peltz power___
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address settings:
| Address: 3700 Gilmore Way, Burnaby, BC V5G4M1
*** Please consider the environment before printing this e-mail
From:
jay peltz j...@asis.com
To:
RE-wrenches re-wrenches@lists.re-wrenches.org,
Date:
12/10/2014 10:13 AM
Subject:
Re: [RE-wrenches] AC coupling SolarEdge
Sent by:
RE-wrenches re
Hello Wrenches,
Do the relays that break the current from the direct grid tie
inverters, in AC coupled systems, need to be motor rated or can they
simply be rated for the amperage of the inverter output? How
inductive is the current between the two inverter systems? Will the
current tend to
Since grid-tie inverters sell back with a power factor of 1, the load
~should~ be entirely resistive and
not inductive or capacitive so a appropriately rated relay contacts
~should~ be fine.
Except maybe if the inverter is designed to supply VARs like the last
Solar-Pro magazine talks
Hi Drake,
I think you can put a power diode in parallel to the gt inverter that can
conduct that inductive current if you need to. However, I think BoB is
correct, there should just be induction of the wiring itself for most
grid-tied inverter. The relay engineer recommended this diode for a DC
with his comments (below).
Dan
On Mon, 6/16/14, Mac Lewis maclew...@gmail.com wrote:
Subject: Re: [RE-wrenches] AC Coupling Relays
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Date: Monday, June 16, 2014, 10:59 AM
Hi Drake,
I think you can put
-wrenches re-wrenches@lists.re-wrenches.org
Sent: Wednesday, April 16, 2014 4:44 PM
Subject: [RE-wrenches] AC coupling with Fronius
Hello wrenches,
Has anyone had good success AC coupling with Fronius Inverters? If so, what
equipment did you use? Was this with an IG or an IG Plus?
I have had
We did one and it seems to work fine. We AC
coupled a pair of Sunny Islands to a Fronius IG
Plus 10.0-1 UNI. There might be a problem if you
are using a Radian with the Fronius.
At 04:44 PM 4/16/2014, you wrote:
Hello wrenches,
Has anyone had good success AC coupling with
Fronius
Have one with dual Xantrex XWs and a IG plus 10.0. Working good
Jeremy Rodriguez
All Solar
CO USA
- Original Message -
From: Drake
To: RE-wrenches
Sent: Thursday, April 17, 2014 9:15 AM
Subject: Re: [RE-wrenches] AC coupling with Fronius
We did one and it seems to work
Mac,
I have a customer with 17kW on 3 Fronius inverters. He connected a cheap 40kW
china diesel generator during a week long power outrage. I was amazed when he
told me they sync'd up with no problems.
Larry
On Apr 16, 2014, at 1:44 PM, Mac Lewis maclew...@gmail.com wrote:
Hello wrenches,
Hello wrenches,
Has anyone had good success AC coupling with Fronius Inverters? If so,
what equipment did you use? Was this with an IG or an IG Plus?
I have had quite a few people lately with Fronius Inverters that would like
a backup solution and I'm not comfortable AC coupling these, but
We have done a number of off grid AC coupling projects over the last eight
years. We have found they are successful with anything that comes close to a
true sign wave, including some of the old Trace inverters. I would be
careful to not come too close to the wattage of the source inverter, and
Hi Lars
I'm curious what you found those efficiency differences to be?
And how are you measuring inverter charging efficiency in the bi directional
mode
Thanks
Jay
Peltz power
Sent from my iPhone
On May 28, 2013, at 10:53 AM, lars Ortegren l...@cal-solar.com wrote:
We have done a
Lars,
With the old Trace inverters? Were they 4.01 firmware or
4.10/4.30? Did you use the GTI? How did you AC couple them - which
input/output terminals?
And what was the rationale in an off grid scenario - distance to
sun in a shady forest?
I
I also saw that webinar. We had just coupled a Fronius 10K to a pair
of Sunny Islands. It seems to be working fine. It is a backup
system, so we have only tested it. SMA tech support assured me it
would work before we bought the system.
Is the Outback wave form unique in any way, causing
Maybe their position has changed, but
the last time I looked into AC coupling a Fronius inverter I was
told by Fronius that it would void their warranty. Has that policy
changed?
Regards,
Gary Willett
Icarus Engineering LLC
It seems a little vague on that point. Talking to Fronius tech
support did not produce a definitive answer. I think so long as the
system is basically grid tied, it likely wouldn't. In the webinar,
the presenter said that Fronius wasn't worried about the AC relay
being switched on and off by
Jeremy
I have a system on my house with 6 kW of grid tie inverters AC coupled to an
Outback Radian, which is actually two 4 kW inverters in one box. It works
great in full sun with the grid off. I don't see a problem with what you are
doing.
David Katz
Sent from my iPhone
On May 25, 2013, at
Hi Jeremy,
FYI: I heard that Fronius is the most sensitive of the GT inverters and so the
most difficult to fool or keep on in an AC coupled system. That was from the
Magnum AC Coupling webinar.
Blessings,
Kelly
Kelly Larson
Electrical Engineer
NABCEP Certified Solar PV Installation
Hope everyone is enjoying their weekend!
I have a system where we have Installed a pair of XW inverters along with a 10k
Fronius inverter.
We have been told that we need to limit the PV watts to the lowest XW inverter.
We have XW capacity in excess of the array, so why can't they entire array
What brand of inverter are your using for the off-grid inverter. SMA has
addressed this issue with the Sunny Island. I'm looking at an all-SMA
option for a new installation, and also an SMA-Enphase AC Coupled system,
so I'll be interested to see what others with more AC coupling experience
have to
Wrenches,
Here is my situation: GT string inverter - 3 strings of mods, 10KW DC. We need
to reduce the PV when the grid is down as to not overload the AC coupled
inverters.
Is there a good way to limit PV input like shunt off some power or short part
of the array? (part)
I was first thinking
Hi Jeremy
Seems like a perfect place for the 600v controller from xantrex
Jay
Peltz power.
Sent from my iPhone
On Mar 18, 2013, at 7:23 PM, Jeremy Rodriguez- All Solar Inc.
allso...@scswifi.net wrote:
Wrenches,
Here is my situation: GT string inverter - 3 strings of mods, 10KW DC.
(many years of data comms experience B4 solar)
From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of mac Lewis
Sent: Thursday, October 04, 2012 9:41 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling and Outback inverters
Hi
-wrenches.org] On Behalf Of David Katz
Sent: Friday, October 05, 2012 2:11 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC coupling and Outback inverters
Hi Kirk,
All of the Outback inverters will work AC coupled (GT and FX) as will any
bi-directional H-bridge type inverter. I have used old
smartphone on the Now Network from Sprint!
- Reply message -
From: Kirk Herander k...@vtsolar.com
To: apos;RE-wrenchesapos; re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] AC coupling and Outback inverters
Date: Fri, Oct 5, 2012 5:08 am
I am leaning towards the SunnyIsland. I
I have AC-coupled an Outback quad-stack with multiple SunnyBoy 6000US
inverters and it's been running fine for 4 years. I used the off-grid
version of Outbacks.
Now I have an application where a customer wants to add battery backup to an
existing SunnyBoy 5000US system. And expand his array by a
Wrenches,
I found a post/thread from last April that Marc Edmunds had posted regarding
tech notes for the XW series inverters.
Also, Fronius cannot advise on how to ac couple their inverters! I am trying to
utilize an existing system and add battery backup, if possible.
Can anyone direct me to
, 2012 5:34 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] AC Coupling
I currently have a dual Outback GTVFX system for the office at home and am
adding an SMA 4KW GIT system. We are going for 100% solar powered on the office
home. Yahoo!
I would like to be able to AC support the battery based GTVFX
I currently have a dual Outback GTVFX system for the office at home and am
adding an SMA 4KW GIT system. We are going for 100% solar powered on the
office home. Yahoo!
I would like to be able to AC support the battery based GTVFX system in the
event of an extended power outage. I spoke with
My query to Enphase on the subject and there response
Hello,
Here is a technote which talks about how to use the Xantrex XW with a grid
tied inverter.
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Saturday, September 03, 2011 1:47 PM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling
Brian,
Is this the drawing?
Magnum ac coupled diagram
http://www.google.com/url?sa=tsource
One should also factor in the availability of generator fuel if an extended
outage occurs. In some communities, the fuel will be scarce or non-existent,
especially if significant damage occurs to fuel transporation and storage
infrastructure.
brbrbr--- Original Message ---
On
volt section. The
only way this can be made up is to overcharge the 12-24 volt section such that
the 12 volt get charged.
DT
From: R Ray Walters r...@solarray.com
To: RE-wrenches re-wrenches@lists.re-wrenches.org
Sent: Saturday, September 3, 2011 6:18 PM
Subject: Re: [RE-wrenches] AC Coupling
ber 02, 2011 4:45 PM
To: RE-wrenches
Subject: Re:
[RE-wrenches] AC Coupling
Brian,
Could you speak a bit more to this, please? My understanding is that
the need with a string (or, I suppose, micro-) inverter and a
battery-based inverter is for a way to disconnect full batteries from
be
Hi Jay;
I agree, for long outages, a generator is the way to go. It just doesn't make
sense to have 5 days of lead acid battery sitting there for years waiting to be
used once or twice in an epic ice storm.
On the other hand, many places have very unreliable grid power with short
outages every
Wrenches,
After Hurricane Irene left a lot of people without power here in the
Northeast, customers who have grid-tied systems are asking about some
battery backup to power some essential loads.
We have used Sunny Islands but they require either 2 Sunny Islands or
a step up transformer
Yes, there should be an uptick in at least inquiries about solar backup here in
the NE.
I went to a site in CT where I was called in to see why the customer was upset
about why her backup batteries went dead when she was told the solar would stay
on line and charge them during what is now week
Hi Larry,
Magnum MS PAE inverters do indeed shift the inverter output frequency
when the battery is full in order to disconnect grid-tied inverters used
in AC coupled systems. It was designed to work in conjunction with a DC
diversion load - which is recommended if the system is larger than a
Brian,
Could you speak a bit more to this, please? My understanding is that
the need with a string (or, I suppose, micro-) inverter and a
battery-based inverter is for a way to disconnect full batteries
from being overcharged when the grid is down and sell is disabled.
...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Friday, September 02, 2011 4:45 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling
Brian,
Could you speak a bit more to this, please? My understanding is that the
need with a string (or, I
Of Brian Faley
Sent: Friday, September 02, 2011 5:21 PM
To: al...@positiveenergysolar.com; RE-wrenches
Subject: Re: [RE-wrenches] AC Coupling
Hi Allen,
I'll try to describe the typical AC coupled system as well as I can.
In such a system, a NON-grid tied battery based inverter (i.e. Magnum MS PAE
HI Larry,
I'll chime in here with the other option, ie no batteries at all.
Instead its a back up generator.
I've found them to be much cheaper, and if you are expecting a longer outage
then weather is usually a problem ie its overcast and therefor you'll need a
backup for your battery system
Allan,
You're not the only one with your eyes spinning here. Let me clarify a bit as I
think you are making it more complicated than it is. There is no need for a
manual switch. The GT inverters feed into the sub panel which is being fed by
the Magnum. Since the Magnum is fed by the main panel
I read the application note here:
http://www.global-download.schneider-electric.com/852577A4005D7372/all/8
FA29D94B918A0FB8525781F0072FCA7/$File/ac-coupling-app-note(976-0240-01-0
1_rev-a).pdf
...and I contacted Xantrex to make sure the application note applies to
other brands of grid-tie
: Tuesday, May 03, 2011 6:18 AM
To: RE-wrenches
Subject: [RE-wrenches] AC Coupling Xantrex XW Inverters to
EnphaseMicroinverters
I read the application note here:
http://www.global-download.schneider-electric.com/852577A4005D7372/all/8FA29
D94B918A0FB8525781F0072FCA7/$File/ac-coupling-app-note(976
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark
Frye
Sent: Tuesday, May 03, 2011 9:32 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] AC Coupling Xantrex XW Inverters
toEnphaseMicroinverters
Jason,
My guess is that this will work just fine.
My comment is that according
03, 2011 9:32 AM
*To:* 'RE-wrenches'
*Subject:* Re: [RE-wrenches] AC Coupling Xantrex XW Inverters
toEnphaseMicroinverters
Jason,
My guess is that this will work just fine.
My comment is that according to my conversations with Enphase, they
would consider this an off-grid application