RE: Residential water lines and meters for fire sprinkler systems

2008-06-19 Thread John Drucker
Ron, The scenario you described (and loss of smoke alarms when the power is cutout as well) creates whats referred to as an unsafe structure (lack of fire protection). The building is posted, fire department advised and occupancy prohibited until protection is restored. The order to restore such

RE: Restraint of Branch Lines

2008-06-19 Thread bill . brooks
A branch line can be a single head per the definition in NFPA 13. Does this mean each arm-over, drop, or return bend regardless of length must have a branch line restraint? It seems sprigs are given special attention in Chapter 9 but the other categories of branch line are not. I guess I'm

RE: Restraint of Branch Lines

2008-06-19 Thread Matthew J. Willis
Bill, I do not see the definition that way. I think you are reading into it to much. The Pipes supplying sprinklerS, either directly, or Through.. Sprigs, drops, etc It is making a distinction in the different ones, further clarified by the definitions for sprig, drop, armover., etc.. R/

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
The way we view that is, if you have a pipe from a cross main feeding a sprinkler or sprinklers - this would require a restraint - it is a branch line. Branch lines supply sprinkler(s) directly or through sprigs, drops, return bends, or arm-overs - only branch lines require them per 9.3.6 so the

RE: Sprinkler MixMatch

2008-06-19 Thread Fletcher, Ron
Why not re-calc with K81 and see if the pipe sizes still work? You are not mixing orifice sizes for balancing so there is now rule against. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Aydin ÖZKAYA Sent:

RE: PIV 40ft from Building

2008-06-19 Thread Mark Sornsin
Thanks for all of the input. If I were writing code I would strongly encourage the use of outside PIVs. In the cold parts of the world, it gives easier access to control the water line to the sprinklers inside the building, without having to dig through snow or chip away ice. I like the idea of

Re: Sprinkler MixMatch

2008-06-19 Thread Roland Huggins
Both K 7.9 and K 8.1 are in the same allowed range so are considered the same. You are suppose to be using the nominal K factor for both. Roland On Jun 19, 2008, at 1:28 AM, Aydın ÖZKAYA wrote: Let me give some more details: - area is approx. 2500 m2 single space - the ocupancy

Re: Restraint of Branch Lines

2008-06-19 Thread Roland Huggins
I disagree that the definition states a single sprinkler is a branch line. It says supplying sprinklers (plural) and that pipe can have individual sprinklers off of it feeding arm-overs, sprigs etc. Just like risers are all vertical pipes (for 4 way braces) but a sprig is excluded since

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
The only reason I say a pipe feeding a single sprinkler can be a branch line is per definition. 3.5.1 BRANCH LINES The pipes supplying sprinklers 3.5.2 CROSS MAINS The pipes supplying the branch lines either directly or through risers. 3.5.9 ARM-OVER A horizontal pipe that extends from a

RE: Wall hydrants

2008-06-19 Thread Steve Leyton
Would you be calculating the interior piping for the combined flows of the exterior streams and interior sprinkler system? Keeping in mind that a wall hydrant - if it's a real wall hydrant and part of the site fire flow design - would likely have to discharge 1500 GPM minimum, perhaps more per

RE: Restraint of Branch Lines

2008-06-19 Thread Eckard, Mark - Mark E
NFPA-13 2007 Chapter 3.5 specifically defines branch lines, cross mains, feed, mains, risers, arm-over, etc. Mark E. Eckard S.E.T. Engineering Manager Lowe's Companies 1605 Curtis Bridge Road REEC Dock Wilkesboro, N.C. 28697 Phone: (336) 658-4359 Fax: (336) 658-3257 Cell: (336) 467-0194 Email:

T-Bar Penetration Clearance

2008-06-19 Thread Gregg Fontes
All the discussion on the branch line restraint has reminded me to ask the question regarding T-Bar penetration per the 2007 CBC. Chapter 13 address Seismic Design for Categories D through F which is basically all of California. Has anyone come across this or have seen it enforced?

RE: Restraint of Branch Lines

2008-06-19 Thread Steven P. Biship, P.E.
Bobby is correct. I have talked to NFPA on this matter and had an informal interpretation done. Steven P. Biship, P.E. Pacific Fire Engineering www.pacificfireeng.com The only reason I say a pipe feeding a single sprinkler can be a branch line is per definition. 3.5.1 BRANCH LINES The

RE: Restraint of Branch Lines

2008-06-19 Thread Thom McMahon
If it has a sprinkler head (Up down or around) on the pipe, and the pipe requires a hanger, restrain it. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -Original Message- From: [EMAIL PROTECTED]

Re: Restraint of Branch Lines

2008-06-19 Thread Roland Huggins
so would you restrain one and not the other? I still think the restraint does not apply to an arm-over regardless if it is tied directly to a cross main or a branch line. Short is short (or should I say vertically challenged?). Having said that, I have given up on trying to say what any

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
That would be extreme overkill and could become very costly. The restraints have minimal requirements for a reason. But since they are called BRANCH LINE restraints that is where they are expectedand we have fought this fight with all kinds of AHJ's. Bobby Gillett Project Manager [EMAIL

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
Roland, But it is not an arm-over if it is a horizontal pipe (not a return bend, drop or sprig) fed from a cross main...it is, by definition, a branch line. You must restrain it if it is required to have a hanger. Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130

RE: Wall hydrants

2008-06-19 Thread Dewayne Martinez
In the past, the AHJ's have only required 250 GPM at the wall hydrant. This would be combined in at the point of connection to a common system point. I think the intent is to provide an outside hose connection for the FDP when it is impractical / impossible to get their pumper truck to this

Re: Restraint of Branch Lines

2008-06-19 Thread Roland Huggins
There was a proposal (13-283) to require restraint on drops greater than 10 ft which the TC rejected. Roland On Jun 19, 2008, at 9:01 AM, Roland Huggins wrote: Having said that, I have given up on trying to say what any large group will ultimately decide (that being the technical

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
(in this case horizontally challenged) Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Thursday, June 19, 2008 11:01 AM To: sprinklerforum@firesprinkler.org

RE: Wall hydrants

2008-06-19 Thread Steve Leyton
Regardless of the specifics, if the AHJ wants a wall hydrant and will approve the primary and auxiliary water supply arrangement(s) with combined mains, and if you can calculate an adequate allowance for the require outside streams, then I can't see why this would be any different than taking a

RE: Wall hydrants

2008-06-19 Thread Dewayne Martinez
Thanks Steve for the insight. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Thursday, June 19, 2008 11:38 AM To: sprinklerforum@firesprinkler.org Subject: RE: Wall hydrants Regardless of the specifics, if the AHJ wants a wall

RE: Restraint of Branch Lines

2008-06-19 Thread bill . brooks
Bobby, Thanks for holding this dead horse down while I beat it some more. I don't necessarily agree with your statement that hanger = restraint. 9.3.6.3 says nothing about any hanger - only that the end sprinkler on a line shall be restrained and there's nothing in 9.3.6 that links a restraint

RE: Restraint of Branch Lines

2008-06-19 Thread Thom McMahon
I don't believe the intent was to restrain the individual armovers, as their short length usually will not allow them the motion we're trying to prevent.(Perhaps the TC could provide a maximum length of armovers, vs. single head branchlines.) But the branchline they are attached to must be

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
Bill, You are correct about the hanger means restraint, but typically what we run into is if it is short enough that it doesn't require a hanger, then the AHJ's don't require the restraintit usually has to be horizontally challenged (short) not to require a hanger in a seismic zone,

RE: Restraint of Branch Lines

2008-06-19 Thread Bobby Gillett
But it does say if it is a horizontal pipe from a cross main then it is a branch line...doesn't mean I agree, but they do make us apply it. Bobby Gillett Project Manager [EMAIL PROTECTED] (731)-424-0130 -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On

Re: T-Bar Penetration Clearance

2008-06-19 Thread Ron Greenman
Still a Californian but no longer living in California I have no notion of the CBC. But if you are talking about the giant hole in the ceiling tile when end of drop restraint is not used then the answer is yes, It is being enforced in Washington. On Thu, Jun 19, 2008 at 8:34 AM, Gregg Fontes

Re: Bill AB2288

2008-06-19 Thread Ron Greenman
/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __ Information from ESET NOD32 Antivirus, version of virus signature database 3201 (20080619) __ The message was checked by ESET NOD32 Antivirus