Brian look back at the archives, in 13R there are situations where full
attic systems are required. It has to do with the building code, and
separations in the attic to sub divide the space at all hall and party
walls. If you only do the 3000 or 6000 Sf smoke partitions you'll end up
with the attic
Thanks!
Looks like there are also times in a 13R system that they can be eliminated.
6.8.5 (2002)
Brian Harris
FDFP INC.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry, David
Sent: Thursday, May 13,
13D 2002, Edition
8.6.5
David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
** Note new email address: david.au...@nebraska.gov
-Original Message-
From: sprinklerforum-boun...@firesprinkler.or
I don't spend allot of time in 13D or 13R but I seem to remember that one
of them does not require sprinklers in the attic, can someone point me in
the right direction?
Thanks!
bh
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.or
does anyone have the justification that added both requirements to 25.
I can see backflow test after flowing water because these stupid
devices fail so often but I'd certainly like to see a statistical
analysis of failures to open, a data based probability of how how
many of the anticipated invento
Not done by us but we do exclude that in our contract.
John
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number: 301-474-1136
Mobile Telephone Number: 301-343-1457
FIRE SPRINKLERS SAVE LIVES
-Original Me
Add THAT to the long list of NFPA 25 requirements never completed - at least
'round here.
Mark A. Sornsin, PE | Fire Protection Engineer
Ulteig Engineers, Inc. |Fargo, ND
Direct:701. 280.8591 | www.ulteig.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailt
Oregon does not require special licensing for forward flow testing.
I think Doug was referring to backflow testing, not forward flow testing.
However, NFPA 25 does require a backflow function test after the forward
flow test is completed.
Forest Wilson
Project Manager
Cherokee Fire Protection C
Basically I like this approach, with one exception. If you're getting paid
for this advice, hire an FPE to assign a class for this storage, and then
mark it up. If this is free advice the AHJ wants help with, make very sure,
in writing that the opinions expressed here are for his use only and do no
THAT is opening a can of worms. What NFPA 13 and 25 require is not Backflow
testing in the same sense as is required by Oregon (or other jurisdictions).
We are not testing the device for its ability to prevent backflow. We are
flowing water through it to ensure it allows the design flow rate
Chris is right! There are many ways to skin this cat, and all of them are OK
if properly applied, which it sounds like you're doing.
Just as you could use room design, area density or residential design.
Since your using area density, there is no requirement that you use the
reduction in area for
I like this, transfer the decision to the AHJ and owner. You remain just the
number cruncher not the decision maker. AHJ then can be the bad guy if
necessary. Owner can change arrangement if he wants to. AHJ's are used to
playing the bad guy role. As AHJ I used to use this same technique in
rev
Nope as designer it's your choice. There is/was something in 13 that says
to the effect when there are many ways to skin the cat all are not equal but
are acceptable.
Having trouble finding the exact section this morning so even if not in 13
the point remains. Think of all the different ways to
The Peter Principal for sprinklers?! Each system
rises to its level of incompetence.
At 10:15 AM 5/13/2010, you wrote:
>This is not really my area of expertise, but how
>about calcing to Class IV ( your best guess) and if
>it fails, new ball game, if it succeeds, re calc
>at next higher commo
This is not really my area of expertise, but how about calcing to Class IV (
your best guess) and if
it fails, new ball game, if it succeeds, re calc at next higher commodity
level(s) until it fails. You
might therefore report to AHJ and owner what commodity the system will support
at what it w
We cannot control what the owner does with the building after the fact. That
control falls on the local Fire/Building Official. I agree that the Owner's
information Cert. would be a good idea to have for record purposes. But even
without, if you qualify your analysis based on the given data a
I am calculating a redesign for some apartments on the 18th floor of
a building. 13 system; commercial QR sprinklers. There are a lot of
closets and small rooms within the area. If I calculate the 900 sqft
with the QR reduction, I am calculating 13 sprinklers. If I calculate
1500 sqft and can e
This is a guessing game. I did an existing
warehouse addition where they said the products
would be similar to what was there, which I
determined to be Class IV. When I went to do the
final walk through, there were camp stoves and
propane cylinders in the racks. "Oh, the buyer
got a good deal
IV would appear reasonable, look at the items and consider the makeup of each.
While mowers and weedeaters are primarily metal, based on the NFPA 13 def. of
Class IV consisting of 5-15% plastic by weight. A 5 lb weedeater would only
require 1/4 of a pound (12 oz.) of plastics to achieve the 5%.
Yes I know, I understand that there is a 15% allowance for plastics in Class
IV. How do you reasonably take a varied mix like this and assign a % to it.
Especially in a case like this where the fire marshall is prepared to tell
someone they have to spend tens of thousands on this old building to
Plastic packaging can introduce expanded plastic.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise
Sent: Thursday, May 13, 2010 9:30 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: RE: Warehou
No gas in this area. These are all new.
Greg McGahan
Living Water Fire Protection
(850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matthew J. Willis
I would watch for (I saw this in a hardware warehouse): they would occasionally
receive shipments of plastic trashcans, sleds and things like that even though
it was not their typical product.
Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO
913.888.0647
What is the status of Gas and such in the tanks?
R/
Matt
Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
m...@norredfire.com
> >-Original Message-
> >From: sprinklerforum-boun...@firesprinkler.
The AHJ has asked us to run some quick calcs on the scenario below to
satisfy his curiosity, any help is appreciated!
1) Existing building - 50 yrs old. Originally had a pump and tank
and some time in the past pump and tank were abandoned and tied into
public water.
2) Was built for
This was well a written editorial. Locals should make sure send kudos
to the authors.
John
John August Denhardt, P.E.
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number: 301-474-1136
Mobile Telephone Number: 301-343-1457
FIRE SPRINKLER
Or you could turn the discharge from the T&P up. :)
TD
If this was a hospital or class room with VAV boxes and fans above the
ceiling you wouldn't even blink. Now what if they have a re-heat coil in
that duct? Same as a WH it's a resistance heating element. Most would say
still not required. NFP
http://www.pennlive.com/editorials/index.ssf/2010/05/builders_bulk_by_sprinkler_sys.html
In related news, I received this note yesterday PM:
"The suit filed by the Pennsylvania Builders Association's in Commonwealth
Court (alleging the unconstitutional adoption of the 2009 International Cod