See Window Sprinklers in index. This line in the referenced sections is
important: listed window sprinkler.
Window sprinklers are installed per install sheet.
Horizontal mullions. Last time I looked, no.
And the other comment that always comes up, "it's only common sense
that the
Scott (and others),
I agree with you that this is not a matter of “actually” providing any
equivalent fire protection to a 2 hr wall. This is checking the box on a Code
requirement. That being said, I don’t see this provision significantly reducing
the hazard of a fully sprinklered skywalk
Might want to also take a look at FM Global Data Sheet 1-20 “Protection Against
Exterior Fire Exposure” which talks about this issue.
Passive protection to accomplish required or desired separations are typically
the preferred first choice such as fire rated partitions or walls but in cases
Thank you so much !
On Mon, Nov 7, 2016 at 2:11 PM, Ryan Labrie <
rlab...@criticalsystemsolutions.com> wrote:
> NFPA 13R 2010 9.2) 30 minutes
>
> NFPA 13D 2010 6.1.2 - 6.1.3) 10 or 7 minutes
>
>
>
> *Ryan Labrie*
>
> Fire Protection Designer
>
>
>
>
> *Critical System Solutions, LLC*2830 Scherer
Awesome,
Thanks guys!!
On Mon, Nov 7, 2016 at 1:59 PM, Taylor Schumacher
wrote:
> NFPA 13R 2010 9.2
>
>
>
> I believe this applies to 13D as well.
>
>
>
> *TAYLOR SCHUMACHER, CET*
>
> Security Fire Sprinkler
>
> *P* 320.656.0847 | *F* 320.656.0312 | *E*
David,
I’ll stand by what I wrote, to the best of my knowledge there hasn’t been
testing to prove sprinklers as an effective strategy or an equivalency for
rated construction. Window sprinklers for glazing are the exception, but to
use a ‘water curtain’ in any manner in lieu of a required
NFPA 13R 2010 9.2) 30 minutes
NFPA 13D 2010 6.1.2 - 6.1.3) 10 or 7 minutes
Ryan Labrie
Fire Protection Designer
Critical System Solutions, LLC
2830 Scherer Drive, Suite 300
St. Petersburg, FL 33716
Office: 727.209.5122
Fax: 727.209.5126
Cell: 813.394.3978
Email:
NFPA 13R 2010 9.2
I believe this applies to 13D as well.
TAYLOR SCHUMACHER, CET
Security Fire Sprinkler
P 320.656.0847 | F 320.656.0312 | E tay...@sfsprinkler.com
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of William Sparano
Sent: Monday,
Bingo, but architects in general don’t care if it is ‘completely’ wetted, they
are just looking at the method…
I’ve argued until I’m blue in the face that they can’t wet the entire surface
with standard sprinklers at the ceiling above…
Scott
Office: (763) 425-1001 x 2
Cell: (612) 759-5556
Someone please put me out of my misery.
What is the water duration for 13R & 13D systems?
Thanks in advanced ... Bill
___
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
I suspect the equivalency would be valid but I have not actually opened the CFC
for its exact wording, I’ll leave further comment on it to those applying it.
Nonetheless, lets transition to the IBC and 13R. Unless the local adoption
deletes the portions of chap 9 that exceeds 13R requirements
Roland,
Great comment about building code trumps the standard, so may sprinkler
contractors and engineers only think standard and never look at the building
code. Which does lead to a beating.
Have a fire safe day!
Regards
Jim
Davidson Associates
Fire Protection
Uhhh, ya.
That Stodgy Old TC Member comment came from left field.
I couldn't believe I actually wrote it, when i read it the next morning.
Consider me properly admonished, and pitifully ashamed of myself.
I only drink whiskey a couple times a year-- and that was one of them.
On Nov 7, 2016 11:56
Brad,
I took great offense at your rude statement regarding "stodgy old
TC members" needing to be voted out.
The 200+ or so men and women who serve on those committees are
charged with a daunting task, for which they receive no pay. Indeed, in
the 2016 code cycle the NFPA 13, 13R,
You’re dealing with exposure protection between and one bldg. being considered
the “Exposed Bldg” and the other the “Exposing Bldg” using a water curtain.
NFPA 13, 2013 7.8.
These are sometimes designed as open head deluge systems to create the curtain
effect to provide separation. Depending
I'm a little confused by that too, Mark, since the CFC (California has
to have their own, you see), clearly makes reference to NFPA 13D being
an acceptable equivalent to the guidelines presented in the CFC. It
would seem the design could follow 13D, and still be in conformance with
the CRC (or
Just for my benefit, if the building is a single family residence, and 13D is
the design standard, wouldn’t the locally adopted building code need to
recognize some form of the IRC, and not so much the IBC for this application?
Mark at Aero
602 820-7894
From: Sprinklerforum
We need a ‘like’ button on here but since we don’t have one – Well said Roland.
And besides, Steve is always ‘gruff’ this early in the morning :)
Cliff Whitfield
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Roland Huggins
Sent: Monday,
Slow down Amigo. Before withdrawing from the fun, consider the following:
A - we will never all agree
B - just because something is said with enthusiasm, it doesn’t make it right
(otherwise I’d never be wrong)
C - the building code trumps the standard so knowing what it says (when it’s
No, no that's not the spirit of my comment. I just chose yours for response
because it was the most recent but the implication was that this is being over
thought. The question perhaps should be, "Is a screen porch a room?"Is
"Porch" a defined term in the IRC or the sprinkler standard?
I will note we don’t even have glazing in the walls in question.
On a previous job at a community college for an after the install wall upgrade,
we used Firelite in the entry doors where we couldn’t get sprinklers to work,
window sprinklers where we have glazing and “closely spaced” sprinklers
You're getting there Grasshopper.
The Truth lies in the Relative Roughness.
Meaning slightly corroded small pipe suffers far more friction loss
relative to the square of the velocity than slightly corroded big pipe.
Come and get me Roland. You are the King of the Hill now.
I'm ready for whatever
I was just wanting to help out. Since I have designed to 13R and 13D and
once submitted they rejected saying that although it met 13R or 13D but not
IBC.
Sorry for trying to help. I'll just read what the experts post and keep my
opinion to myself.
From: Sprinklerforum
look at NFPA 13:8.15.26 - Sprinkler Protected Glazing. The wetting of the
entire surface is rather important (in order to avoid failure of the glazing
(barrier) from thermal shock. It, I believe, originated in the Life Safety
Code (which long ago allowed an exception using sprinklers with
What am I missing here?The question is whether 13D (that's "Thirteen Dee")
requires sprinklers in porches and we've got a thread that's turning toward the
IBC. If the dwelling(s) in question are being built per the IBC then I don't
think 13D would be the correct standard in the first
actually it is not a fixed velocity where results diverge. It differs based
on diameter and type of material (coefficient of roughness). Sometimes HW
shows a greater loss and others DW.
Roland
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn. --- Fire Sprinklers
CHECK IBC. I THINK IT WILL REQUIRE THEM.
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Roland Huggins
Sent: November-07-16 11:10 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: 13D Porches
I would say OPEN is to the temperature, not
Great answer Roland.
Owen Evans.
Sent from my iPhone
> On Nov 7, 2016, at 8:09 AM, Roland Huggins wrote:
>
> I would say OPEN is to the temperature, not the bugs. Also look at it from
> the potential to flash-over. The screen will not hold in the heat. Now
I would say OPEN is to the temperature, not the bugs. Also look at it from the
potential to flash-over. The screen will not hold in the heat. Now have that
discussion with the AHJ.
The TC member caveat - Not to be considered a formal interpretation of NFPA
Roland
Roland Huggins, PE - VP
NFPA 13, NFPA 15 and NFPA 70.
Are you talking indoor or outdoor, dry or liquid filled?
Also don’t confused when someone uses the term “Less Flammable” when it comes
to oil cooled units. It is an FM Global term but the oil is still a
combustible.
Craig L. Prahl
Fire Protection Group Lead/SME
What is the associated NFPA code for suppression system for substations and
transformers?
Thanks,
Laleh Zargarinejad, PE