Re: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread Bruce Verhei
See Window Sprinklers in index. This line in the referenced sections is important: listed window sprinkler. Window sprinklers are installed per install sheet. Horizontal mullions. Last time I looked, no. And the other comment that always comes up, "it's only common sense that the

RE: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread David Williams
Scott (and others), I agree with you that this is not a matter of “actually” providing any equivalent fire protection to a 2 hr wall. This is checking the box on a Code requirement. That being said, I don’t see this provision significantly reducing the hazard of a fully sprinklered skywalk

RE: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread Craig.Prahl
Might want to also take a look at FM Global Data Sheet 1-20 “Protection Against Exterior Fire Exposure” which talks about this issue. Passive protection to accomplish required or desired separations are typically the preferred first choice such as fire rated partitions or walls but in cases

Re: 13R / 13D Water Duration

2016-11-07 Thread William Sparano
Thank you so much ! On Mon, Nov 7, 2016 at 2:11 PM, Ryan Labrie < rlab...@criticalsystemsolutions.com> wrote: > NFPA 13R 2010 9.2) 30 minutes > > NFPA 13D 2010 6.1.2 - 6.1.3) 10 or 7 minutes > > > > *Ryan Labrie* > > Fire Protection Designer > > > > > *Critical System Solutions, LLC*2830 Scherer

Re: 13R / 13D Water Duration

2016-11-07 Thread William Sparano
Awesome, Thanks guys!! On Mon, Nov 7, 2016 at 1:59 PM, Taylor Schumacher wrote: > NFPA 13R 2010 9.2 > > > > I believe this applies to 13D as well. > > > > *TAYLOR SCHUMACHER, CET* > > Security Fire Sprinkler > > *P* 320.656.0847 | *F* 320.656.0312 | *E*

RE: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread Scott Futrell
David, I’ll stand by what I wrote, to the best of my knowledge there hasn’t been testing to prove sprinklers as an effective strategy or an equivalency for rated construction. Window sprinklers for glazing are the exception, but to use a ‘water curtain’ in any manner in lieu of a required

RE: 13R / 13D Water Duration

2016-11-07 Thread Ryan Labrie
NFPA 13R 2010 9.2) 30 minutes NFPA 13D 2010 6.1.2 - 6.1.3) 10 or 7 minutes Ryan Labrie Fire Protection Designer Critical System Solutions, LLC 2830 Scherer Drive, Suite 300 St. Petersburg, FL 33716 Office: 727.209.5122 Fax: 727.209.5126 Cell: 813.394.3978 Email:

RE: 13R / 13D Water Duration

2016-11-07 Thread Taylor Schumacher
NFPA 13R 2010 9.2 I believe this applies to 13D as well. TAYLOR SCHUMACHER, CET Security Fire Sprinkler P 320.656.0847 | F 320.656.0312 | E tay...@sfsprinkler.com From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of William Sparano Sent: Monday,

RE: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread Scott Futrell
Bingo, but architects in general don’t care if it is ‘completely’ wetted, they are just looking at the method… I’ve argued until I’m blue in the face that they can’t wet the entire surface with standard sprinklers at the ceiling above… Scott Office: (763) 425-1001 x 2 Cell: (612) 759-5556

13R / 13D Water Duration

2016-11-07 Thread William Sparano
Someone please put me out of my misery. What is the water duration for 13R & 13D systems? Thanks in advanced ... Bill ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org

Re: 13D Porches

2016-11-07 Thread Roland Huggins
I suspect the equivalency would be valid but I have not actually opened the CFC for its exact wording, I’ll leave further comment on it to those applying it. Nonetheless, lets transition to the IBC and 13R. Unless the local adoption deletes the portions of chap 9 that exceeds 13R requirements

RE: 13D Porches

2016-11-07 Thread Jim Davidson
Roland, Great comment about building code trumps the standard, so may sprinkler contractors and engineers only think standard and never look at the building code. Which does lead to a beating. Have a fire safe day! Regards Jim Davidson Associates Fire Protection

Re: November 5th remarks

2016-11-07 Thread Brad Casterline
Uhhh, ya. That Stodgy Old TC Member comment came from left field. I couldn't believe I actually wrote it, when i read it the next morning. Consider me properly admonished, and pitifully ashamed of myself. I only drink whiskey a couple times a year-- and that was one of them. On Nov 7, 2016 11:56

November 5th remarks

2016-11-07 Thread Parsley Consulting
Brad, I took great offense at your rude statement regarding "stodgy old TC members" needing to be voted out. The 200+ or so men and women who serve on those committees are charged with a daunting task, for which they receive no pay. Indeed, in the 2016 code cycle the NFPA 13, 13R,

RE: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread Craig.Prahl
You’re dealing with exposure protection between and one bldg. being considered the “Exposed Bldg” and the other the “Exposing Bldg” using a water curtain. NFPA 13, 2013 7.8. These are sometimes designed as open head deluge systems to create the curtain effect to provide separation. Depending

Re: 13D Porches

2016-11-07 Thread Parsley Consulting
I'm a little confused by that too, Mark, since the CFC (California has to have their own, you see), clearly makes reference to NFPA 13D being an acceptable equivalent to the guidelines presented in the CFC. It would seem the design could follow 13D, and still be in conformance with the CRC (or

RE: 13D Porches

2016-11-07 Thread MPhelps
Just for my benefit, if the building is a single family residence, and 13D is the design standard, wouldn’t the locally adopted building code need to recognize some form of the IRC, and not so much the IBC for this application? Mark at Aero 602 820-7894 From: Sprinklerforum

RE: 13D Porches

2016-11-07 Thread Cliff Whitfield
We need a ‘like’ button on here but since we don’t have one – Well said Roland. And besides, Steve is always ‘gruff’ this early in the morning :) Cliff Whitfield From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Monday,

Re: 13D Porches

2016-11-07 Thread Roland Huggins
Slow down Amigo. Before withdrawing from the fun, consider the following: A - we will never all agree B - just because something is said with enthusiasm, it doesn’t make it right (otherwise I’d never be wrong) C - the building code trumps the standard so knowing what it says (when it’s

RE: 13D Porches

2016-11-07 Thread Steve Leyton
No, no that's not the spirit of my comment. I just chose yours for response because it was the most recent but the implication was that this is being over thought. The question perhaps should be, "Is a screen porch a room?"Is "Porch" a defined term in the IRC or the sprinkler standard?

RE: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread David Williams
I will note we don’t even have glazing in the walls in question. On a previous job at a community college for an after the install wall upgrade, we used Firelite in the entry doors where we couldn’t get sprinklers to work, window sprinklers where we have glazing and “closely spaced” sprinklers

Re: velocity in pipes

2016-11-07 Thread Brad Casterline
You're getting there Grasshopper. The Truth lies in the Relative Roughness. Meaning slightly corroded small pipe suffers far more friction loss relative to the square of the velocity than slightly corroded big pipe. Come and get me Roland. You are the King of the Hill now. I'm ready for whatever

RE: 13D Porches

2016-11-07 Thread Trillium Fire Sprinkler Design Inc.
I was just wanting to help out. Since I have designed to 13R and 13D and once submitted they rejected saying that although it met 13R or 13D but not IBC. Sorry for trying to help. I'll just read what the experts post and keep my opinion to myself. From: Sprinklerforum

Re: Wall Wetting per IBC - 2012, Chapter 31, 3104.5 Exception 1

2016-11-07 Thread Roland Huggins
look at NFPA 13:8.15.26 - Sprinkler Protected Glazing. The wetting of the entire surface is rather important (in order to avoid failure of the glazing (barrier) from thermal shock. It, I believe, originated in the Life Safety Code (which long ago allowed an exception using sprinklers with

RE: 13D Porches

2016-11-07 Thread Steve Leyton
What am I missing here?The question is whether 13D (that's "Thirteen Dee") requires sprinklers in porches and we've got a thread that's turning toward the IBC. If the dwelling(s) in question are being built per the IBC then I don't think 13D would be the correct standard in the first

Re: velocity in pipes

2016-11-07 Thread Roland Huggins
actually it is not a fixed velocity where results diverge. It differs based on diameter and type of material (coefficient of roughness). Sometimes HW shows a greater loss and others DW. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers

RE: 13D Porches

2016-11-07 Thread Trillium Fire Sprinkler Design Inc.
CHECK IBC. I THINK IT WILL REQUIRE THEM. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: November-07-16 11:10 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: 13D Porches I would say OPEN is to the temperature, not

Re: 13D Porches

2016-11-07 Thread firstin
Great answer Roland. Owen Evans. Sent from my iPhone > On Nov 7, 2016, at 8:09 AM, Roland Huggins wrote: > > I would say OPEN is to the temperature, not the bugs. Also look at it from > the potential to flash-over. The screen will not hold in the heat. Now

Re: 13D Porches

2016-11-07 Thread Roland Huggins
I would say OPEN is to the temperature, not the bugs. Also look at it from the potential to flash-over. The screen will not hold in the heat. Now have that discussion with the AHJ. The TC member caveat - Not to be considered a formal interpretation of NFPA Roland Roland Huggins, PE - VP

RE: Fire Code for Transformers

2016-11-07 Thread Craig.Prahl
NFPA 13, NFPA 15 and NFPA 70. Are you talking indoor or outdoor, dry or liquid filled? Also don’t confused when someone uses the term “Less Flammable” when it comes to oil cooled units. It is an FM Global term but the oil is still a combustible. Craig L. Prahl Fire Protection Group Lead/SME

Fire Code for Transformers

2016-11-07 Thread Laleh Zargarinejad
What is the associated NFPA code for suppression system for substations and transformers? Thanks, Laleh Zargarinejad, PE ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org