Date:04/05/2019 02:31 PM
Subject:EC HSW Under Garage Doors
Sent by:"Sprinklerforum"
mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
BE ADVISED - This email originated
nkler.org
Subject: RE: EC HSW Under Garage Doors
Just think how your dad feels ☹
Cliff Whitfield, SET
President
Fire Design, Inc.
184 Comfort Place
Burnsville, NC 28714
Ph: 828-284-4772
[Description: New FDI Logo-4.jpg]
cl...@fire-design.com<mailto:cl...@fire-design.com>
www.f
n Behalf
Of Skyler Bilbo
Sent: Friday, April 5, 2019 2:52 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: EC HSW Under Garage Doors
Thanks! I need to buy the 2019 version... I feel like one of those old guys,
from when I started in the industry, that quotes older versions becaus
nity Drive • Fort Wayne, IN • 46825
> *direct *260.487.7824* / cell *260.417.0625* / fax *260.487.7991
> * email *mmo...@shambaugh.com
>
>
>
>
>
>
>
> From:Skyler Bilbo
> To:sprinklerforum@lists.firesprinkler.org
> Date:04/05/2019 02
ayne, IN • 46825
direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991
email mmo...@shambaugh.com
From: Skyler Bilbo
To: sprinklerforum@lists.firesprinkler.org
Date: 04/05/2019 02:31 PM
Subject:EC HSW Under Garage Doors
Sent by:"Sprinklerforum"
Is anyone installing EC HSW heads under garage doors? I keep running into
16 ft wide doors (queue jokes: "just open the door"). It would be cheaper
to install one EC head rather than a standard spray HSW on each side.
I'm looking in the 2013 version of NFPA 13, and I see in
boun...@lists.firesprinkler.org] On Behalf Of Bob
Sent: Friday, March 07, 2014 2:30 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: sprinklers under sloped garage doors
Good point. Is it possible to come at the door from the side instead?
Thank You,
Bob Knight, CET III
208-318-
-
Work
Sent: Friday, March 07, 2014 1:27 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: sprinklers under sloped garage doors
Sort of planning on that, but if I angle it down the slope the sprinkelr
will be the low point
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
07, 2014 12:34 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: sprinklers under sloped garage doors
>
> This is sort of the same question I asked a while back, but I will try to
> re-phrase it. We have a 14x14 garage door that when opened, follows the
> contour of the pitched roof
r.org
Subject: sprinklers under sloped garage doors
This is sort of the same question I asked a while back, but I will try to
re-phrase it. We have a 14x14 garage door that when opened, follows the
contour of the pitched roof. We need to install a sprinkler beneath it. My
initial thought was to
This is sort of the same question I asked a while back, but I will try to
re-phrase it. We have a 14x14 garage door that when opened, follows the contour
of the pitched roof. We need to install a sprinkler beneath it. My initial
thought was to put a sidewall at the high point pointing down the s
Inc.
>> Ph: 719-488-3479
>>
>>
>>
>> cl...@fire-design.com
>> www.fire-design.com
>>
>> -Original Message-
>> From: sprinklerforum-boun...@lists.firesprinkler.org
>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
lf Of Todd
Williams
Sent: Tuesday, February 11, 2014 7:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sidewalls under garage doors
Do we have to follow the requirement to discharge down the slope for heads
under garage doors?
Todd G Williams, PE
Fire Protection Design/Consulting
Stoningt
sday, February 11, 2014 7:48 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Sidewalls under garage doors
>
> Do we have to follow the requirement to discharge down the slope for heads
> under garage doors?
>
> Todd G Williams, PE
> Fire Protection Design/Consulti
forum-boun...@lists.firesprinkler.org] On Behalf Of Todd
Williams
Sent: Tuesday, February 11, 2014 7:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sidewalls under garage doors
Do we have to follow the requirement to discharge down the slope for heads
under garage doors?
Todd G Williams, PE
Fire
Williams
Sent: Tuesday, February 11, 2014 8:48 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Sidewalls under garage doors
Do we have to follow the requirement to discharge down the slope for heads
under garage doors?
Todd G Williams, PE
Fire Protection Design/Consulting
Stoni
Do we have to follow the requirement to discharge down the slope for heads
under garage doors?
Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com
___
Sprinklerforum mailing list
Sprinklerforum
We space them for Light Hazard.
Greg
On Sat, Sep 24, 2011 at 6:48 PM, Thomas Watt <
firesprinklerssaveli...@gmail.com> wrote:
> September 20, 2011|By Anika Myers Palm, Orlando Sentinel
>
> A malfunctioning Orange County fire truck was at the center of a fire at a
> county-owned garage this mornin
September 20, 2011|By Anika Myers Palm, Orlando Sentinel
A malfunctioning Orange County fire truck was at the center of a fire at a
county-owned garage this morning, Orange County Fire Rescue has confirmed.
.the sprinkler system had helped to contain most of the blaze,
http://articles.orlan
Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Friday, September 23, 2011 5:17 PM
To: b...@firebyknight.com; sprinklerforum@firesprinkler.org
Subject: RE: Sidewall below garage doors
Ah ha! The old later
11 3:17 PM
> To: b...@firebyknight.com; sprinklerforum@firesprinkler.org
> Subject: RE: Sidewall below garage doors
>
> Ah ha! The old later edition trick. Thanks
>
>
> At 04:16 PM 9/23/2011, you wrote:
> >LH spacing per 13 8.7.3.1.7 2010 ed. Can you apply this even though
>
r.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: September 23, 2011 3:17 PM
To: b...@firebyknight.com; sprinklerforum@firesprinkler.org
Subject: RE: Sidewall below garage doors
Ah ha! The old later edition trick. Thanks
At 04:16 PM 9/23/2011, you wrote:
>LH spacing per 13 8
Message-
>From: sprinklerforum-boun...@firesprinkler.org
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
>Sent: Friday, September 23, 2011 2:08 PM
>To: sprinklerforum@firesprinkler.org
>Subject: Sidewall below garage doors
>
>When sidewall sp
I usually go with a Tyco SW-20. They're listed for up to around 16x18 at OH1.
Jimmy Waite
Sent from my HTC smartphone on the Now Network from Sprint!
- Reply message -
From: "Todd Williams"
To:
Subject: Sidewall below garage doors
Date: Fri, Sep 23, 2011 4:08 pm
lf Of Todd Williams
Sent: Friday, September 23, 2011 2:08 PM
To: sprinklerforum@firesprinkler.org
Subject: Sidewall below garage doors
When sidewall sprinklers are to be installed under a garage door, do you
have to meet the spacing requirements of Table 8.7.2.2.1 (NFPA 13 - 2002)?
I am working on a pr
When sidewall sprinklers are to be installed under a garage door, do you have
to meet the spacing requirements of Table 8.7.2.2.1 (NFPA 13 - 2002)? I am
working on a project where we have 12 ft wide by 14 ft high (approx -
confirming exact dimensions, but over 10 ft) overhead doors in a fire
d
s. Then in a recent issue NFPA 13, included
balconies. I consider it a clarification, not a "new" requirement.
Tony
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of douglas hicks
Sent: April 12, 2008 8:32 AM
To: sprinkler board
Subject:
the other answer is also confirmed by 8.4.2(3) (Sidewalls) To protect
areas below overhead doors Which was needed sine it was common
practice (AND a good idea) but outside the listing
Roland
On Apr 12, 2008, at 7:31 AM, douglas hicks wrote:
What issue of NFPA 13 requires overhead doors to
pic.
Bill Brooks
William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell
Original Message
Subject: Garage Doors
From: " douglas hicks" <[EMAIL PROTECTED]>
Date: Sat
"Overhead Doors" in the index.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of douglas hicks
Sent: Saturday, April 12, 2008 9:32 AM
To: sprinkler board
Subject: Garage D
the one that deals with obstructions over 4' wide.
Garth
- Original Message -
From: " douglas hicks" <[EMAIL PROTECTED]>
To: "sprinkler board"
Sent: Saturday, April 12, 2008 9:31 AM
Subject: Garage Doors
What issue of NFPA 13 requires overhead doors to
What issue of NFPA 13 requires overhead doors to have sprinklers under the open
door?
Douglas Hicks
General Fire Equipment Co of Eastern Oregon, Inc
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/
07 8:25 AM
Subject: Garage doors
I am designing an apartment complex and using CPVC. I have convinced myself
that somewhere I have ran across a code or standard that overrides the
exception in NFPA13R that allows the omission of sprinklers beneath garage
doors. Is anyone familiar with such a
forum@firesprinkler.org
Subject: RE: Garage doors
Maybe the bell was for combustible balconies. Though 13R allows them to
not be sprinklered, the IBC requires it.
Ed Kramer
Littleton, CO
>I am designing an apartment complex and using CPVC. I have convinced
>myself
>that somewhere I have ran
rides the
>exception in NFPA13R that allows the omission of sprinklers beneath garage
>doors. Is anyone familiar with such a document?
>
>
>
>Thanks,
>
>Ron
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.f
NFPA 13R, 2007 - 6.8.3.2
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Wednesday, October 24, 2007 8:26 AM
To: AFSA
Subject: Garage doors
I am designing an apartment complex and using CPVC. I have convinced
myself that somewhere I have
ECTED] On
- >Behalf Of Russell
- >Sent: Wednesday, October 24, 2007 8:26 AM
- >To: AFSA
- >Subject: Garage doors
- >
- >I am designing an apartment complex and using CPVC. I
- >have convinced myself that somewhere I have ran across a
- >code or stan
I am designing an apartment complex and using CPVC. I have convinced myself
that somewhere I have ran across a code or standard that overrides the
exception in NFPA13R that allows the omission of sprinklers beneath garage
doors. Is anyone familiar with such a document?
Thanks,
Ron