RE: Building Heights Requiring Standpipes

2018-08-09 Thread tstone52
: Sprinklerforum On Behalf Of Cesar Lira Sent: Thursday, August 9, 2018 1:53 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Building Heights Requiring Standpipes Hi. I have a doubt. NFPA13 request that all sprinklers system shall have a Retarding device. But in our sprinkler systems

RE: Building Heights Requiring Standpipes

2018-08-09 Thread Bob
] On Behalf Of Cesar Lira Sent: Thursday, August 09, 2018 11:53 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Building Heights Requiring Standpipes Hi. I have a doubt. NFPA13 request that all sprinklers system shall have a Retarding device. But in our sprinkler systems installed we

RE: Building Heights Requiring Standpipes

2018-08-09 Thread Cesar Lira
Hi. I have a doubt. NFPA13 request that all sprinklers system shall have a Retarding device. But in our sprinkler systems installed we are not using it. Because we have a water flow sensor above check alarm instead of an alarm pressure switch or water motor alarm. Is it correct as I have it?.

RE: Building Heights Requiring Standpipes

2018-08-09 Thread John Drucker
-904-6823 From: Sprinklerforum [sprinklerforum-boun...@lists.firesprinkler.org] on behalf of Taylor Schumacher [tay...@sfsprinkler.com] Sent: Thursday, August 09, 2018 8:39 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Building Heights Requiring Standpipes We had already walked

RE: Building Heights Requiring Standpipes

2018-08-09 Thread Taylor Schumacher
: Building Heights Requiring Standpipes Good example diagrams are in the ICC Fire /Bldg Code Commentary books. On Aug 8, 2018 18:01, Jim Davidson mailto:jdavid...@davidsonassociates.net>> wrote: Go to the Building Code for the definition of height above lowest level of FD Access, if ICC

RE: Building Heights Requiring Standpipes

2018-08-08 Thread Steele, Andrew
Good example diagrams are in the ICC Fire /Bldg Code Commentary books. On Aug 8, 2018 18:01, Jim Davidson wrote: Go to the Building Code for the definition of height above lowest level of FD Access, if ICC's IBC then call for a code interpretation and if needed ask for a written response. The

Re: Building Heights Requiring Standpipes

2018-08-08 Thread Mark Eckard
I think the code says if the highest floor elevation exceeds 30' above the lowest level of fire department access, stand pipes are required. Not quoting just remembering off the top of my head. On Wed, Aug 8, 2018, 5:55 PM Taylor Schumacher wrote: > I have an AHJ that is adamant that a 3-story

RE: Building Heights Requiring Standpipes

2018-08-08 Thread Steve Leyton
What Jim said. The measurement is from grade plane, so if there is a fire apparatus access at the lowest (basement) level, then standpipes in fact might be required. But if the ground (first of three) floor is the access grade plane, then the metrics are from that surface to the finished

RE: Building Heights Requiring Standpipes

2018-08-08 Thread Jim Davidson
Go to the Building Code for the definition of height above lowest level of FD Access, if ICC's IBC then call for a code interpretation and if needed ask for a written response. The ICC has been through this problem a few times. Some jurisdictions specifically define the height above the lowest