AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* RE: QR Reduction - Question about wording of code Travis and Steve, That makes sense. I think I was kind of confusing the term “hydraulic design basis” with the hazard category. So, if you have a light hazard occupancy, with a

RE: QR Reduction - Question about wording of code

2019-02-28 Thread Steve Leyton
, February 28, 2019 8:47 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: QR Reduction - Question about wording of code Yeah, in simple terms, hydraulic design basis is the discharge criteria. So if you are using QR sprinklers in a portion of a building that has mixed uses – say

RE: QR Reduction - Question about wording of code

2019-02-28 Thread Cliff Whitfield
gt; www.fire-design.com From: Sprinklerforum On Behalf Of Kyle.Montgomery Sent: Thursday, February 28, 2019 11:07 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: QR Reduction - Question about wording of code Travis and Steve, That makes sense. I think I was kind of confusing the ter

RE: QR Reduction - Question about wording of code

2019-02-28 Thread Kyle . Montgomery
, 2019 8:47 AM To: sprinklerforum@lists.firesprinkler.org Subject: [EXTERNAL] RE: QR Reduction - Question about wording of code Yeah, in simple terms, hydraulic design basis is the discharge criteria. So if you are using QR sprinklers in a portion of a building that has mixed uses – say you’re

RE: QR Reduction - Question about wording of code

2019-02-28 Thread Steve Leyton
: QR Reduction - Question about wording of code For example, not mixing density/area and residential sprinkler calculations. [MFP_logo_F]<http://www.mfpdesign.com/> Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6

RE: QR Reduction - Question about wording of code

2019-02-28 Thread Travis Mack, SET, CFPS, CWBSP, RME-G
For example, not mixing density/area and residential sprinkler calculations. Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 tm...@mfpdesign.com Send la