RE: Barrier / Partition Definition

2007-08-20 Thread Ray Vance
Bob, The language is such that the standard clarifies the PURPOSE of the barrier, ie barrier or partition capable of trapping heat in its requirement to provide such a barrier or partition. If you go further into this type of requirement in the NFPA standards, you could also correlate it to the

Seismic ZOI

2007-08-20 Thread Brian Harris
I'm having a brain cramp this morning so your help would be greatly appreciated. I haven't done seismic in a while and I can't remember the criteria to determine the Zone Of Influence, help a brother out.. ___ Sprinklerforum mailing

RE: Barrier / Partition Definition

2007-08-20 Thread Craig.Prahl
The definition of fire wall, fire partition, fire barrier comes from the building code. If using the IBC see Chapter 7. Depending on the occupancies and the level of sprinkler protection you may or may not be required to provide one of the three. Each one has slightly different characteristics

RE: Seismic ZOI

2007-08-20 Thread G. Tim Stone
Brian, Refer to 2002 ed NFPA 13, Chapt. A9.3.5.6, (3,a,b). This should help. G. Tim Stone NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 TEL: (802) 434-2968 Fax: (802) 434-4343

RE: Barrier / Partition Definition

2007-08-20 Thread Bob Knight
Vance, Thank you. When I spoke to this friend, Jerry, the EFSR example is the very same one that we both mentioned. Also, all of your talking points are the same ones that we spoke about. I appreciate the input, and as well the validation as to what we had spoken about. Bob Knight

RE: Barrier / Partition Definition

2007-08-20 Thread Bob Knight
Craig, I think that you are over analyzing this situation. There is no mention in 13 for this to be a fire rated anything. This barrier / partition is merely for heat containment for the purpose of sprinkler activation or lack thereof, not the spread of fire. Thank you, Bob Knight

large single family houses

2007-08-20 Thread Todd Williams - work
What's the latest poop on protecting large single-family residences? It doesn't seem that 13D would be appropriate for the structure, but I don't see anything in any of my Codes that would modify it. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080

RE: Barrier / Partition Definition

2007-08-20 Thread Craig.Prahl
Bob, It comes down to the way the AHJ is interpreting this section of NFPA 13 and what was type of wall actually constructed versus what may have been or is required. If the wall is 8 block floor to ceiling but there are two openings in it that are unprotected then the wall does not provide for

RE: large single family houses

2007-08-20 Thread A.P.Silva
I had this question when designing a 32,000 sq.ft. home. The mech. consultant specified 13D. I recommended 13 or at least 13R. They settled for 13R. But by this time a 2 underground was already installed. They wouldn't give me the 4 underground I needed for designing to 13R. Finally it was

RE: large single family houses

2007-08-20 Thread John Drucker
Todd, New Jersey addresses this issue. The NJ Uniform Construction Code, N.J.A.C. 5:23, specifically N.J.A.C. 5:23-3.21(c)3.i. limits R-5 (One and Two Family Dwellings or Single Family Townhouses not more than three stories in height) Buildings of Type VB unprotected wood frame construction to

RE: large single family houses

2007-08-20 Thread Steve Leyton
Why do you need a 4 UG for 13R? We do them on 2 and 2-1/2 UG's all the time, including combined services with a domestic allowance taken for fixture count at the common supply point. Is this to be a dedicated 2 fire service or a combined line? Steve Leyton Protection Design Consulting

RE: large single family houses

2007-08-20 Thread Paul Sincaglia
I have done a fairly large number of these jumbo homes and the real issue for any of them is quality of water supply. (As if that is not true in any sprinkler design). The problems with Jumbo homes are varied but all work against the sprinkler designers and installers. First, our experience has

RE: large single family houses

2007-08-20 Thread Jim Kettler
Call me naive, but what exactly are the concerns over using 13D for a larger house? A fire in a single room should still be contained/confined by the 13D system. Does an NFPA 13 system readily translate to a dwelling unit? Would you also adjust the required water supply for the NFPA 13 system? I

RE: large single family houses

2007-08-20 Thread Jim Kettler
We struggled with this issue and the exact definition of attic. We use the following: If it has full headroom and walk-up stairs - it is not an attic. This has worked very well. Jim Kettler And last but not least or us...the design team will say The attic will not be used and doesn't need

RE: large single family houses

2007-08-20 Thread Steve Leyton
Jim: What if that single room is 4,000 s.f. with ceilings that peak at 30' and have pockets, beams, suspended obstructions, catwalks, lofts, etc., etc., etc.? I agree that some measure of additional protection is appropriate for these mega-homes, as both the fire load and volume of space in

RE: large single family houses

2007-08-20 Thread Jim Kettler
I guess that was the point I was trying to make. Is the problem the size of the home or the very specific hazard we are trying to protect? We haven't done any homes that large, but we've done 15k s.f. houses with attached greenhouses, indoor swimming pools, and one with indoor basketball court

Re: And I'll huff and I'll puff, what straw houses?

2007-08-20 Thread Todd Williams - work
Interesting they were doing the Hayes residence. At 04:09 PM 8/20/2007, you wrote: Yeah just when you thought you've been dealt the ultimate challenge, there's always something new. http://www.designforward.net/hayes.shtm And they are not limited to residential either. Check out some of the

Annual Fire Pump testing

2007-08-20 Thread Forestfwl
The other day, I ran across an FMG Inspector at a Big Box Store. He was testing fire pumps. To measure flow, he used 2 Pollard Hydrant Diffusers with built in Pitot Gauges and screwed them onto the Pump test header. He then walks back and forth as he opens the valve, checks readings, etc.

RE: Annual Fire Pump testing

2007-08-20 Thread Tom Duross
I have tested many fire pumps all by my lonesome before, I prefer a helper but in a pinch have done it alone. He should have been modulating with the OSY or BV and not with those straight gates, they do walk and are not supposed to be used for anything but full open or full closed, imho. So he's

pitotless

2007-08-20 Thread Todd Williams - work
OK, Tom. You've been pushing these pitotless nozzles. It looks like a great toy, but what justifies the $495 dollar cost? (I know, this should be on Sprinkler Chat, but it is a segue from a technical Q, so I figured it was OK.) At 06:07 PM 8/20/2007, you wrote: I have tested many fire

RE: pitotless

2007-08-20 Thread Tom Duross
Nothing to break, no pitots to buy again. Much more efficient too. -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Todd Williams - work Sent: Monday, August 20, 2007 6:31 PM To: sprinklerforum@firesprinkler.org Subject: pitotless OK, Tom. You've been

RE: pitotless

2007-08-20 Thread George Church
I've never missed a chance to avoid staying as dry as possible during pump tests, so we use the monsters with built-in pitots and occasionally use the remote reader extensions. But we didn't hesitate to buy 3 more once 2500's approached routine. After 7 or 8 years I think we've replaced 2 or 3