Re: Residential sprinkler question
The section (16.2) in that chapter only applies to "Small Residential Board & Care Facilities." Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Mon, Feb 26, 2018 at 9:58 AM, Tom Duross <tduro...@comcast.net> wrote: > Also see Chapter 16 of 25. > > -Original Message- > From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] On Behalf Of Ron Greenman > Sent: Monday, February 26, 2018 12:56 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: Residential sprinkler question > > Below is the language in 13D/2016 regarding maintenance. It is > substantially, if not exactly the same as 2013. I left out section 12.3.5 > as that addresses anti-freeze only. I suppose if you wanted to add the > "test after twenty years" to the "what information SHOULD the contractor > provide" part, you could. > > > 12.1* General. The installer shall provide to the owner/occupant > instructions on inspecting, testing, and maintaining the system. > > 12.2* Inspections and Tests. The sprinkler system shall be inspected and > tested periodically to make sure the system is in good working condition. > > 12.3 Maintenance. > > 12.3.1 The sprinkler system shall be properly maintained in accordance > with this standard and the manufacturers’ instructions. > > 12.3.2 Any sprinkler that is operated, damaged, corroded, covered with > foreign materials, or showing signs of leakage shall be replaced with a new > listed sprinkler having the same performance characteristics as the > original equipment. > > 12.3.2.1* Where replacing residential sprinklers manufactured prior to > 2003 that are no longer available from the manufacturer and are installed > using a design density less than 0.05 gpm/ft2 (204 mm/min), a residential > sprinkler with an equivalent K-factor (± 5 percent) shall be permitted to > be used provided the currently listed coverage area for the replacement > sprinkler is not exceeded. > > 12.3.3 Painting Sprinklers. > > 12.3.3.1 Sprinklers shall not be painted unless applied by the > manufacturer. > > 12.3.3.2* Any sprinklers that have been painted outside of the factory > shall be replaced with a new listed sprinkler. > > 12.3.4* Wet Pipe Systems. A wet pipe system shall be maintained above > 40°F (4°C), including areas properly insulated to maintain 40°F (4°C). > > A.12.1 These instructions should include the following: > > (1) Information regarding the necessary system inspection, testing, and > maintenance as described in this standard > > (2) The manufacturers’ installation, care, and maintenance instructions > for the installed sprinkler system components > > (3) Name, address, and phone number of the installing contractor of the > fire sprinkler system > > (4) Name, address, and phone number of a fire sprinkler system service > company if different than the installing contractor > > > The occupants of a home with a sprinkler system should > > understand that maintaining a sprinkler system is mostly about > > common sense. Keeping the control valve open, not hanging > > items from the sprinklers, and making sure that the sprinklers > > do not get painted or obstructed are the most important items. > > It is also important to know the function of the main control > > valve and where the control valve is located. > > > A.12.2 The building owner or manager should understand the sprinkler > system operation and conduct periodic inspections and tests to make sure > that the system is in good working condition. A recommended inspection and > testing program includes the following: > > (1) Monthly inspection of all valves to ensure that they are open > > (2) Monthly inspection of tanks, if present, to confirm they are full > > (3) Monthly testing of pumps, if present, to make sure they operate > properly and do not trip circuit breakers when starting > > (4) Testing of all waterflow devices, when provided, every 6 months > including monitoring service (note that notification of the monitoring > service is essential to make sure that the fire department is not called > due to testing) > > (5) Ongoing visual inspection of all sprinklers to make sure they are not > obstructed, damaged, corroded, covered with foreign materials, field > painted, or showing signs of leakage, and that decorations are not attached > to them > > (6) Annually, fully open the test connection downstream of any > pressure-reducing or pressure-regulating valve, and make sure that the > pressure gauge reads a re
RE: Residential sprinkler question
Also see Chapter 16 of 25. -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron Greenman Sent: Monday, February 26, 2018 12:56 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Residential sprinkler question Below is the language in 13D/2016 regarding maintenance. It is substantially, if not exactly the same as 2013. I left out section 12.3.5 as that addresses anti-freeze only. I suppose if you wanted to add the "test after twenty years" to the "what information SHOULD the contractor provide" part, you could. 12.1* General. The installer shall provide to the owner/occupant instructions on inspecting, testing, and maintaining the system. 12.2* Inspections and Tests. The sprinkler system shall be inspected and tested periodically to make sure the system is in good working condition. 12.3 Maintenance. 12.3.1 The sprinkler system shall be properly maintained in accordance with this standard and the manufacturers’ instructions. 12.3.2 Any sprinkler that is operated, damaged, corroded, covered with foreign materials, or showing signs of leakage shall be replaced with a new listed sprinkler having the same performance characteristics as the original equipment. 12.3.2.1* Where replacing residential sprinklers manufactured prior to 2003 that are no longer available from the manufacturer and are installed using a design density less than 0.05 gpm/ft2 (204 mm/min), a residential sprinkler with an equivalent K-factor (± 5 percent) shall be permitted to be used provided the currently listed coverage area for the replacement sprinkler is not exceeded. 12.3.3 Painting Sprinklers. 12.3.3.1 Sprinklers shall not be painted unless applied by the manufacturer. 12.3.3.2* Any sprinklers that have been painted outside of the factory shall be replaced with a new listed sprinkler. 12.3.4* Wet Pipe Systems. A wet pipe system shall be maintained above 40°F (4°C), including areas properly insulated to maintain 40°F (4°C). A.12.1 These instructions should include the following: (1) Information regarding the necessary system inspection, testing, and maintenance as described in this standard (2) The manufacturers’ installation, care, and maintenance instructions for the installed sprinkler system components (3) Name, address, and phone number of the installing contractor of the fire sprinkler system (4) Name, address, and phone number of a fire sprinkler system service company if different than the installing contractor The occupants of a home with a sprinkler system should understand that maintaining a sprinkler system is mostly about common sense. Keeping the control valve open, not hanging items from the sprinklers, and making sure that the sprinklers do not get painted or obstructed are the most important items. It is also important to know the function of the main control valve and where the control valve is located. A.12.2 The building owner or manager should understand the sprinkler system operation and conduct periodic inspections and tests to make sure that the system is in good working condition. A recommended inspection and testing program includes the following: (1) Monthly inspection of all valves to ensure that they are open (2) Monthly inspection of tanks, if present, to confirm they are full (3) Monthly testing of pumps, if present, to make sure they operate properly and do not trip circuit breakers when starting (4) Testing of all waterflow devices, when provided, every 6 months including monitoring service (note that notification of the monitoring service is essential to make sure that the fire department is not called due to testing) (5) Ongoing visual inspection of all sprinklers to make sure they are not obstructed, damaged, corroded, covered with foreign materials, field painted, or showing signs of leakage, and that decorations are not attached to them (6) Annually, fully open the test connection downstream of any pressure-reducing or pressure-regulating valve, and make sure that the pressure gauge reads a reasonable value (7) Inspect systems by individuals knowledgeable and trained in such systems when there is a change in ownership A.12.3.2.1 It is recognized that the flow and pressure available to the replacement sprinkler might be less than its current flow and pressure requirement. A.12.3.3.2 Whenever painting or home improvements are made in the dwelling unit, special attention should be paid to ensure that sprinklers are not painted or obstructed either at the time of installation or during subsequent redecoration. This is as important for the cover plates of concealed sprinklers as it is to the sprinklers themselves. Special paint is used for cover plates and can only be applied by the manufacturer. Applying paint to cover plates outside of the factory can cause the sprinkler to malfunction and possibly not operate during a
Re: Residential sprinkler question
protected underneath from paint and overspray with a bag. After the painting is finished, the bags should be removed from the sprinklers and the cover plates should be replaced. A.12.3.4 See Figure A.9.1.1(a) through Figure A.9.1.1(d) for possible methods used by the installer to insulate sprinkler piping in unheated areas. It is important that this insulation not be disturbed or removed. Disturbing or removing this insulation could result in sprinkler pipes being frozen during winter months that would not only block water flow to the sprinklers but could cause broken pipes and fittings. Ron Greenman rongreen...@gmail.com 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-) On Sat, Feb 24, 2018 at 6:43 AM, Scott Futrell <sco...@ffcdi.com> wrote: > I talked to the FD. They will do a yearly inspection, test the waterflow > switch, no charge and look at sprinklers for corrosion and obstruction. No > other testing recommendations to the owners. I specifically ask about > twenty year testing. > > So, if NFPA 25 isn't in play, how does a homeowner know they have a twenty > year sprinkler test required? Agree with Ron G. > > Scott > > Office: (763) 425-1001 x2 > Cell: (612) 759-5556 > > -Original Message- > From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] On Behalf Of Bruce Verhei > Sent: Friday, February 23, 2018 10:34 PM > To: sprinklerforum@lists.firesprinkler.org > Subject: Re: Residential sprinkler question > > From Scottsdale FP’s website: > > http://www.scottsdaleaz.gov/fire/residential-sprinkler > > Sounds as if you may schedule a visit from the fire department. > > Best. > > Bruce Verhei > > > On Feb 23, 2018, at 17:51, John Irwin <john.ir...@dynafire.com> wrote: > >> I understand the inspection is not required, but the sprinkler doesn't > know it's in a house and not a highrise. If asked I would reccomend they > get tested as they would in an NFPA 13 occupancy. > > > > John Irwin > > > > On Feb 23, 2018, 8:41 PM, at 8:41 PM, Ron Greenman < > rongreen...@gmail.com> wrote: > >> John. It’s different because the requirement is in 25 and 13d systems > >> are exempt from 25. It would need to be a jurisdiction amendment to > >> 25 or a stand alone requirement. > >> > >> On Fri, Feb 23, 2018 at 4:29 PM John Irwin <john.ir...@dynafire.com> > >> wrote: > >> > >>> Why would it be any different than a Residential sprinkler installed > >> in a > >>> dwelling unit in an NFPA 13 system? > >>> > >>> John Irwin > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > -- next part -- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180226/56c3a85b/attachment.html> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Residential sprinkler question
I talked to the FD. They will do a yearly inspection, test the waterflow switch, no charge and look at sprinklers for corrosion and obstruction. No other testing recommendations to the owners. I specifically ask about twenty year testing. So, if NFPA 25 isn't in play, how does a homeowner know they have a twenty year sprinkler test required? Agree with Ron G. Scott Office: (763) 425-1001 x2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bruce Verhei Sent: Friday, February 23, 2018 10:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Residential sprinkler question From Scottsdale FP’s website: http://www.scottsdaleaz.gov/fire/residential-sprinkler Sounds as if you may schedule a visit from the fire department. Best. Bruce Verhei > On Feb 23, 2018, at 17:51, John Irwin <john.ir...@dynafire.com> wrote: >> I understand the inspection is not required, but the sprinkler doesn't know >> it's in a house and not a highrise. If asked I would reccomend they get >> tested as they would in an NFPA 13 occupancy. > > John Irwin > > On Feb 23, 2018, 8:41 PM, at 8:41 PM, Ron Greenman <rongreen...@gmail.com> > wrote: >> John. It’s different because the requirement is in 25 and 13d systems >> are exempt from 25. It would need to be a jurisdiction amendment to >> 25 or a stand alone requirement. >> >> On Fri, Feb 23, 2018 at 4:29 PM John Irwin <john.ir...@dynafire.com> >> wrote: >> >>> Why would it be any different than a Residential sprinkler installed >> in a >>> dwelling unit in an NFPA 13 system? >>> >>> John Irwin ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: Residential sprinkler question
From Scottsdale FP’s website: http://www.scottsdaleaz.gov/fire/residential-sprinkler Sounds as if you may schedule a visit from the fire department. Best. Bruce Verhei > On Feb 23, 2018, at 17:51, John Irwin <john.ir...@dynafire.com> wrote: > > I understand the inspection is not required, but the sprinkler doesn't know > it's in a house and not a highrise. If asked I would reccomend they get > tested as they would in an NFPA 13 occupancy. > > John Irwin > DynaFire Inc. > Tampa Fire Sprinkler Division > 727-282-9243 > > This email was sent from a mobile device. Please forgive brevity, > typographical errors, and grammatical gaffes. > >> On Feb 23, 2018, 8:41 PM, at 8:41 PM, Ron Greenman <rongreen...@gmail.com> >> wrote: >> John. It’s different because the requirement is in 25 and 13d systems >> are >> exempt from 25. It would need to be a jurisdiction amendment to 25 or a >> stand alone requirement. >> >> On Fri, Feb 23, 2018 at 4:29 PM John Irwin <john.ir...@dynafire.com> >> wrote: >> >>> Why would it be any different than a Residential sprinkler installed >> in a >>> dwelling unit in an NFPA 13 system? >>> >>> John Irwin >>> DynaFire Inc. >>> Tampa Fire Sprinkler Division >>> 727-282-9243 >>> >>> This email was sent from a mobile device. Please forgive brevity, >>> typographical errors, and grammatical gaffes. >>> >>> On Feb 23, 2018, 7:25 PM, at 7:25 PM, Scott Futrell >> <sco...@ffcdi.com> >>> wrote: >>>> Nothing in the original data sheet or the next generation about any >>>> testing... >>>> >>>> Scott >>>> >>>> Office: (763) 425-1001 x2 >>>> Cell: (612) 759-5556 >>>> >>>> >>>> -Original Message- >>>> From: Sprinklerforum >>>> [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of >>>> Bruce Verhei >>>> Sent: Friday, February 23, 2018 6:19 PM >>>> To: sprinklerforum@lists.firesprinkler.org >>>> Subject: Re: Residential sprinkler question >>>> >>>> [This message was identified as a phishing scam. Learn about >> phishing >>>> at http://aka.ms/LearnAboutPhishing] >>>> >>>> What did the installation manual for the heads say? It’s part of the >>>> listing. >>>> >>>> Best. >>>> >>>> Bruce Verhei >>>> >>>>> On Feb 23, 2018, at 16:05, Scott Futrell <sco...@ffcdi.com> wrote: >>>>> >>>>> Forumites: >>>>> >>>>> Scottsdale has required residential sprinklers since 1985 and >> those >>>> residential sprinklers are now more than twenty years old. Is >> anyone >>>> performing or recommending twenty year inspections of these >> sprinklers? >>>> Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if >> you >>>> have to test fast response after twenty years, why wouldn't it apply >> to >>>> residential systems? >>>>> >>>>> Comments, thoughts? >>>>> >>>>> Thanks! >>>>> >>>>> Scott Futrell >>>>> Futrell Fire Consulty & Design, Inc. >>>>> >>>>> Office: (763) 425-1001 x2 >>>>> Cell: (612) 759-5556 >>>>> >>>>> >>>>> ___ >>>>> Sprinklerforum mailing list >>>>> Sprinklerforum@lists.firesprinkler.org >>>>> >>>> >>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>>> >>>> ___ >>>> Sprinklerforum mailing list >>>> Sprinklerforum@lists.firesprinkler.org >>>> >>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>>> ___ >>>> Sprinklerforum mailing list >>>> Sprinklerforum@lists.firesprinkler.org >>>> >>> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>> -- next part -- >>> An HTML attachment was scrubbed... >>> URL: < >>> >> http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachme
Re: Residential sprinkler question
I understand the inspection is not required, but the sprinkler doesn't know it's in a house and not a highrise. If asked I would reccomend they get tested as they would in an NFPA 13 occupancy. John Irwin DynaFire Inc. Tampa Fire Sprinkler Division 727-282-9243 This email was sent from a mobile device. Please forgive brevity, typographical errors, and grammatical gaffes. On Feb 23, 2018, 8:41 PM, at 8:41 PM, Ron Greenman <rongreen...@gmail.com> wrote: >John. It’s different because the requirement is in 25 and 13d systems >are >exempt from 25. It would need to be a jurisdiction amendment to 25 or a >stand alone requirement. > >On Fri, Feb 23, 2018 at 4:29 PM John Irwin <john.ir...@dynafire.com> >wrote: > >> Why would it be any different than a Residential sprinkler installed >in a >> dwelling unit in an NFPA 13 system? >> >> John Irwin >> DynaFire Inc. >> Tampa Fire Sprinkler Division >> 727-282-9243 >> >> This email was sent from a mobile device. Please forgive brevity, >> typographical errors, and grammatical gaffes. >> >> On Feb 23, 2018, 7:25 PM, at 7:25 PM, Scott Futrell ><sco...@ffcdi.com> >> wrote: >> >Nothing in the original data sheet or the next generation about any >> >testing... >> > >> >Scott >> > >> >Office: (763) 425-1001 x2 >> >Cell: (612) 759-5556 >> > >> > >> >-Original Message- >> >From: Sprinklerforum >> >[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of >> >Bruce Verhei >> >Sent: Friday, February 23, 2018 6:19 PM >> >To: sprinklerforum@lists.firesprinkler.org >> >Subject: Re: Residential sprinkler question >> > >> >[This message was identified as a phishing scam. Learn about >phishing >> >at http://aka.ms/LearnAboutPhishing] >> > >> >What did the installation manual for the heads say? It’s part of the >> >listing. >> > >> >Best. >> > >> >Bruce Verhei >> > >> >> On Feb 23, 2018, at 16:05, Scott Futrell <sco...@ffcdi.com> wrote: >> >> >> >> Forumites: >> >> >> >> Scottsdale has required residential sprinklers since 1985 and >those >> >residential sprinklers are now more than twenty years old. Is >anyone >> >performing or recommending twenty year inspections of these >sprinklers? >> >Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if >you >> >have to test fast response after twenty years, why wouldn't it apply >to >> >residential systems? >> >> >> >> Comments, thoughts? >> >> >> >> Thanks! >> >> >> >> Scott Futrell >> >> Futrell Fire Consulty & Design, Inc. >> >> >> >> Office: (763) 425-1001 x2 >> >> Cell: (612) 759-5556 >> >> >> >> >> >> ___ >> >> Sprinklerforum mailing list >> >> Sprinklerforum@lists.firesprinkler.org >> >> >> > >> >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> > >> >___ >> >Sprinklerforum mailing list >> >Sprinklerforum@lists.firesprinkler.org >> > >> >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> >___ >> >Sprinklerforum mailing list >> >Sprinklerforum@lists.firesprinkler.org >> > >> >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> -- next part -- >> An HTML attachment was scrubbed... >> URL: < >> >http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180223/6f791d2a/attachment.html >> > >> ___ >> Sprinklerforum mailing list >> Sprinklerforum@lists.firesprinkler.org >> >> >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> >-- >Sent from Gmail Mobile >-- next part -- >An HTML attachment was scrubbed... >URL: ><http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180224/f88eaa68/attachment.html> >___ >Sprinklerforum mailing list >Sprinklerforum@lists.firesprinkler.org >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- next part -- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180223/0e863dbf/attachment.html> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: Residential sprinkler question
John. It’s different because the requirement is in 25 and 13d systems are exempt from 25. It would need to be a jurisdiction amendment to 25 or a stand alone requirement. On Fri, Feb 23, 2018 at 4:29 PM John Irwin <john.ir...@dynafire.com> wrote: > Why would it be any different than a Residential sprinkler installed in a > dwelling unit in an NFPA 13 system? > > John Irwin > DynaFire Inc. > Tampa Fire Sprinkler Division > 727-282-9243 > > This email was sent from a mobile device. Please forgive brevity, > typographical errors, and grammatical gaffes. > > On Feb 23, 2018, 7:25 PM, at 7:25 PM, Scott Futrell <sco...@ffcdi.com> > wrote: > >Nothing in the original data sheet or the next generation about any > >testing... > > > >Scott > > > >Office: (763) 425-1001 x2 > >Cell: (612) 759-5556 > > > > > >-Original Message- > >From: Sprinklerforum > >[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of > >Bruce Verhei > >Sent: Friday, February 23, 2018 6:19 PM > >To: sprinklerforum@lists.firesprinkler.org > >Subject: Re: Residential sprinkler question > > > >[This message was identified as a phishing scam. Learn about phishing > >at http://aka.ms/LearnAboutPhishing] > > > >What did the installation manual for the heads say? It’s part of the > >listing. > > > >Best. > > > >Bruce Verhei > > > >> On Feb 23, 2018, at 16:05, Scott Futrell <sco...@ffcdi.com> wrote: > >> > >> Forumites: > >> > >> Scottsdale has required residential sprinklers since 1985 and those > >residential sprinklers are now more than twenty years old. Is anyone > >performing or recommending twenty year inspections of these sprinklers? > >Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if you > >have to test fast response after twenty years, why wouldn't it apply to > >residential systems? > >> > >> Comments, thoughts? > >> > >> Thanks! > >> > >> Scott Futrell > >> Futrell Fire Consulty & Design, Inc. > >> > >> Office: (763) 425-1001 x2 > >> Cell: (612) 759-5556 > >> > >> > >> ___ > >> Sprinklerforum mailing list > >> Sprinklerforum@lists.firesprinkler.org > >> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > >___ > >Sprinklerforum mailing list > >Sprinklerforum@lists.firesprinkler.org > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > >___ > >Sprinklerforum mailing list > >Sprinklerforum@lists.firesprinkler.org > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- next part -- > An HTML attachment was scrubbed... > URL: < > http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180223/6f791d2a/attachment.html > > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > -- Sent from Gmail Mobile -- next part -- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180224/f88eaa68/attachment.html> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Residential sprinkler question
Why would it be any different than a Residential sprinkler installed in a dwelling unit in an NFPA 13 system? John Irwin DynaFire Inc. Tampa Fire Sprinkler Division 727-282-9243 This email was sent from a mobile device. Please forgive brevity, typographical errors, and grammatical gaffes. On Feb 23, 2018, 7:25 PM, at 7:25 PM, Scott Futrell <sco...@ffcdi.com> wrote: >Nothing in the original data sheet or the next generation about any >testing... > >Scott > >Office: (763) 425-1001 x2 >Cell: (612) 759-5556 > > >-Original Message- >From: Sprinklerforum >[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of >Bruce Verhei >Sent: Friday, February 23, 2018 6:19 PM >To: sprinklerforum@lists.firesprinkler.org >Subject: Re: Residential sprinkler question > >[This message was identified as a phishing scam. Learn about phishing >at http://aka.ms/LearnAboutPhishing] > >What did the installation manual for the heads say? It’s part of the >listing. > >Best. > >Bruce Verhei > >> On Feb 23, 2018, at 16:05, Scott Futrell <sco...@ffcdi.com> wrote: >> >> Forumites: >> >> Scottsdale has required residential sprinklers since 1985 and those >residential sprinklers are now more than twenty years old. Is anyone >performing or recommending twenty year inspections of these sprinklers? >Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if you >have to test fast response after twenty years, why wouldn't it apply to >residential systems? >> >> Comments, thoughts? >> >> Thanks! >> >> Scott Futrell >> Futrell Fire Consulty & Design, Inc. >> >> Office: (763) 425-1001 x2 >> Cell: (612) 759-5556 >> >> >> ___ >> Sprinklerforum mailing list >> Sprinklerforum@lists.firesprinkler.org >> >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > >___ >Sprinklerforum mailing list >Sprinklerforum@lists.firesprinkler.org >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >___ >Sprinklerforum mailing list >Sprinklerforum@lists.firesprinkler.org >http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org -- next part -- An HTML attachment was scrubbed... URL: <http://lists.firesprinkler.org/private.cgi/sprinklerforum-firesprinkler.org/attachments/20180223/6f791d2a/attachment.html> ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
RE: Residential sprinkler question
Nothing in the original data sheet or the next generation about any testing... Scott Office: (763) 425-1001 x2 Cell: (612) 759-5556 -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bruce Verhei Sent: Friday, February 23, 2018 6:19 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Residential sprinkler question [This message was identified as a phishing scam. Learn about phishing at http://aka.ms/LearnAboutPhishing] What did the installation manual for the heads say? It’s part of the listing. Best. Bruce Verhei > On Feb 23, 2018, at 16:05, Scott Futrell <sco...@ffcdi.com> wrote: > > Forumites: > > Scottsdale has required residential sprinklers since 1985 and those > residential sprinklers are now more than twenty years old. Is anyone > performing or recommending twenty year inspections of these sprinklers? > Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if you have > to test fast response after twenty years, why wouldn't it apply to > residential systems? > > Comments, thoughts? > > Thanks! > > Scott Futrell > Futrell Fire Consulty & Design, Inc. > > Office: (763) 425-1001 x2 > Cell: (612) 759-5556 > > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Re: Residential sprinkler question
What did the installation manual for the heads say? It’s part of the listing. Best. Bruce Verhei > On Feb 23, 2018, at 16:05, Scott Futrellwrote: > > Forumites: > > Scottsdale has required residential sprinklers since 1985 and those > residential sprinklers are now more than twenty years old. Is anyone > performing or recommending twenty year inspections of these sprinklers? > Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if you have > to test fast response after twenty years, why wouldn't it apply to > residential systems? > > Comments, thoughts? > > Thanks! > > Scott Futrell > Futrell Fire Consulty & Design, Inc. > > Office: (763) 425-1001 x2 > Cell: (612) 759-5556 > > > ___ > Sprinklerforum mailing list > Sprinklerforum@lists.firesprinkler.org > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Residential sprinkler question
Forumites: Scottsdale has required residential sprinklers since 1985 and those residential sprinklers are now more than twenty years old. Is anyone performing or recommending twenty year inspections of these sprinklers? Obviously NFPA 25 doesn't apply to 13D systems, I know that, but if you have to test fast response after twenty years, why wouldn't it apply to residential systems? Comments, thoughts? Thanks! Scott Futrell Futrell Fire Consulty & Design, Inc. Office: (763) 425-1001 x2 Cell: (612) 759-5556 ___ Sprinklerforum mailing list Sprinklerforum@lists.firesprinkler.org http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org