Re: Closets / cabinets

2008-11-05 Thread Myles Knebel
Good question. I would say,the closet is now a cabinet. I looked up
cabinets in the index however I could not find  8.9.4.1.3.3. in the 2007
addition (missing).
No references say anything about sprinklers inside cabinets so in my opinion
the cabiets don't need to be sprinklered.

Ergo

On Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:


 An office (light hazard) has several closets that have existing sprinklers.
 Part of the renovation is to remove the closet doors and provide built-in
 millwork recessed into the closet space. Essentially a storage cabinet made
 of wood with shelves at about every 2 feet and wooden doors. Is there any
 logical argument to provide or not provide sprinklers within this space? As
 a general rule we don't sprinkler furniture (although I don't think NFPA
 says it explicitly). Any comments?

 Tony

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: [EMAIL PROTECTED]

 To Unsubscribe, send an email to:[EMAIL PROTECTED][EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
It's furniture.  No sprinklers within.  Well, unless someone is going to occupy 
it.

NFPA 13, 2007, 8.1(7)

[cid:658182813@05112008-3391]





Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Myles Knebel
Sent: Wednesday, November 05, 2008 8:09 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

Good question. I would say,the closet is now a cabinet. I looked up cabinets 
in the index however I could not find  8.9.4.1.3.3. in the 2007 addition 
(missing).
No references say anything about sprinklers inside cabinets so in my opinion 
the cabiets don't need to be sprinklered.

Ergo

On Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:


 An office (light hazard) has several closets that have existing sprinklers.
 Part of the renovation is to remove the closet doors and provide
 built-in millwork recessed into the closet space. Essentially a
 storage cabinet made of wood with shelves at about every 2 feet and
 wooden doors. Is there any logical argument to provide or not provide
 sprinklers within this space? As a general rule we don't sprinkler
 furniture (although I don't think NFPA says it explicitly). Any comments?

 Tony

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to:
 [EMAIL PROTECTED]

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]to%3ASprinklerforum-reques
 [EMAIL PROTECTED] (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Re: Closets / cabinets

2008-11-05 Thread Allan Seidel
In situations like this the room's floor area now extends into the former
closet's footprint. Therefore the sprinkler coverage needs to account for
this recess in the wall. In other words if you call it furniture then it
must occupy a space as furniture would. As we all well know, the standard
cannot fit every situation, but there needs to be some accounting for these
conditions that would make sense for the AHJ. For an extreme example, I do
not think there would be an agreement to ignore former closets as such
(assume they were 36 deep) when EC sprinklers are used at their maximum
distance from the wall where the closets were.

Allan Seidel
St. Louis, MO

On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:

 It's furniture.  No sprinklers within.  Well, unless someone is going to
 occupy it.

 NFPA 13, 2007, 8.1(7)

 [cid:658182813@05112008-3391]





 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 [EMAIL PROTECTED]
 http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED] [mailto:
 [EMAIL PROTECTED] On Behalf Of Myles Knebel
 Sent: Wednesday, November 05, 2008 8:09 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 Good question. I would say,the closet is now a cabinet. I looked up
 cabinets in the index however I could not find  8.9.4.1.3.3. in the 2007
 addition (missing).
 No references say anything about sprinklers inside cabinets so in my
 opinion the cabiets don't need to be sprinklered.

 Ergo

 On Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:

 
  An office (light hazard) has several closets that have existing
 sprinklers.
  Part of the renovation is to remove the closet doors and provide
  built-in millwork recessed into the closet space. Essentially a
  storage cabinet made of wood with shelves at about every 2 feet and
  wooden doors. Is there any logical argument to provide or not provide
  sprinklers within this space? As a general rule we don't sprinkler
  furniture (although I don't think NFPA says it explicitly). Any comments?
 
  Tony
 
  ___
  Sprinklerforum mailing list
  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
  For Technical Assistance, send an email to:
  [EMAIL PROTECTED]
 
  To Unsubscribe, send an email
  to:[EMAIL PROTECTED][EMAIL PROTECTED]
 to%3ASprinklerforum-reques
  [EMAIL PROTECTED] (Put the word unsubscribe in the subject field)
 
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: [EMAIL PROTECTED]

 To Unsubscribe, send an email to:[EMAIL PROTECTED][EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: [EMAIL PROTECTED]

 To Unsubscribe, send an email to:[EMAIL PROTECTED][EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
So based on that would you provide a sprinkler below every shelf in order to 
adequately protect it?  If we're going to hold to code, then you need to look 
at shelf storage requirements.

If you read the description of the revision, I read it that the open floor area 
of the closet will now be part of the shelf system cabinet.  There is no floor 
open to the room, there are doors on the unit.

And protecting closet, well I can kind of accept, but a shelving unit with 
doors on the front, with no floor, well sorry but that just sounds silly.

At some point reason needs to prevail.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Allan Seidel
Sent: Wednesday, November 05, 2008 9:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

In situations like this the room's floor area now extends into the former 
closet's footprint. Therefore the sprinkler coverage needs to account for this 
recess in the wall. In other words if you call it furniture then it must occupy 
a space as furniture would. As we all well know, the standard cannot fit every 
situation, but there needs to be some accounting for these conditions that 
would make sense for the AHJ. For an extreme example, I do not think there 
would be an agreement to ignore former closets as such (assume they were 36 
deep) when EC sprinklers are used at their maximum distance from the wall where 
the closets were.

Allan Seidel
St. Louis, MO

On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:

 It's furniture.  No sprinklers within.  Well, unless someone is going
 to occupy it.

 NFPA 13, 2007, 8.1(7)

 [cid:658182813@05112008-3391]





 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED] [mailto:
 [EMAIL PROTECTED] On Behalf Of Myles Knebel
 Sent: Wednesday, November 05, 2008 8:09 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 Good question. I would say,the closet is now a cabinet. I looked up
 cabinets in the index however I could not find  8.9.4.1.3.3. in the
 2007 addition (missing).
 No references say anything about sprinklers inside cabinets so in my
 opinion the cabiets don't need to be sprinklered.

 Ergo

 On Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:

 
  An office (light hazard) has several closets that have existing
 sprinklers.
  Part of the renovation is to remove the closet doors and provide
  built-in millwork recessed into the closet space. Essentially a
  storage cabinet made of wood with shelves at about every 2 feet and
  wooden doors. Is there any logical argument to provide or not
  provide sprinklers within this space? As a general rule we don't
  sprinkler furniture (although I don't think NFPA says it explicitly). Any 
  comments?
 
  Tony
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread GAYLE KNOWLES

did a job in White Plains, NY.  All the cabinets are sprinklered.  It is a 
3-story department store From: [EMAIL PROTECTED] To: 
sprinklerforum@firesprinkler.org Date: Wed, 5 Nov 2008 07:59:54 -0700 
Subject: RE: Closets / cabinets  So based on that would you provide a 
sprinkler below every shelf in order to adequately protect it? If we're going 
to hold to code, then you need to look at shelf storage requirements.  If you 
read the description of the revision, I read it that the open floor area of the 
closet will now be part of the shelf system cabinet. There is no floor open to 
the room, there are doors on the unit.  And protecting closet, well I can 
kind of accept, but a shelving unit with doors on the front, with no floor, 
well sorry but that just sounds silly.  At some point reason needs to 
prevail.  Craig L. Prahl, CET Fire Protection Specialist Mechanical 
Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, 
Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL 
PROTECTED] http://www.ch2m.com   -Original Message- From: [EMAIL 
PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Allan Seidel Sent: 
Wednesday, November 05, 2008 9:44 AM To: sprinklerforum@firesprinkler.org 
Subject: Re: Closets / cabinets  In situations like this the room's floor 
area now extends into the former closet's footprint. Therefore the sprinkler 
coverage needs to account for this recess in the wall. In other words if you 
call it furniture then it must occupy a space as furniture would. As we all 
well know, the standard cannot fit every situation, but there needs to be some 
accounting for these conditions that would make sense for the AHJ. For an 
extreme example, I do not think there would be an agreement to ignore former 
closets as such (assume they were 36 deep) when EC sprinklers are used at 
their maximum distance from the wall where the closets were.  Allan Seidel 
St. Louis, MO  On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:  
 It's furniture. No sprinklers within. Well, unless someone is going  to 
occupy it.   NFPA 13, 2007, 8.1(7)   [cid:658182813@05112008-3391]  
 Craig L. Prahl, CET  Fire Protection Specialist  Mechanical 
Department  CH2MHILL  Lockwood Greene  1500 International Drive  PO Box 
491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax -  864.599.8439 
[EMAIL PROTECTED] http://www.ch2m.com-Original Message-  
From: [EMAIL PROTECTED] [mailto:  [EMAIL PROTECTED] On Behalf Of Myles 
Knebel  Sent: Wednesday, November 05, 2008 8:09 AM  To: 
sprinklerforum@firesprinkler.org  Subject: Re: Closets / cabinets   Good 
question. I would say,the closet is now a cabinet. I looked up  cabinets in 
the index however I could not find 8.9.4.1.3.3. in the  2007 addition 
(missing).  No references say anything about sprinklers inside cabinets so in 
my  opinion the cabiets don't need to be sprinklered.   Ergo   On 
Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:  
An office (light hazard) has several closets that have existing  sprinklers. 
  Part of the renovation is to remove the closet doors and provide   
built-in millwork recessed into the closet space. Essentially a   storage 
cabinet made of wood with shelves at about every 2 feet and   wooden doors. 
Is there any logical argument to provide or not   provide sprinklers within 
this space? As a general rule we don't   sprinkler furniture (although I 
don't think NFPA says it explicitly). Any comments? Tony   
___ Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical 
Assistance, send an email to: [EMAIL PROTECTED]  To Unsubscribe, send an 
email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject 
field)___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Closets / cabinets

2008-11-05 Thread Ron Greenman
I tend to agree with Allen if I'm understanding his argument
correctly. And correct me if I'm misstating the thought but I don't
think he meant that the recess did not necessarily have to have
separate protection but that the floor area had to be accounted for by
some sprinkler. If I buy a free standing entertainment center I have a
potential fire hazard (lots of plugs and cords) and the area of the
building it occupies is protected by the overhead system. I am not
going to worry about a fire inside it until that fire breaches the
cabinet itself. By the same token if I have a built-in entertainment
center I have the same hazard and must consider the building area it
occupies if the fire breaches the cabinet. If that occurs then the
building must be protected (protecting the cabinet in both cases is my
concern, not society's, and could be addressed by a wonder gas if I so
desire). Now if I use a former closet for my cabinet, using a face
frame, with or without doors, and the former closet door lintel is an
obstruction, and the closet does not meet any of the closet exemption
rules then it would require a sprinkler on the closet side of the
lintel. The same issues would apply if I just put a free standing
cabinet in the closet opening. The cabinet parts are just a
distraction in this discussion. The issues are the lintel (i.e.:
obstruction) and sprinkler spacing rules.

On Wed, Nov 5, 2008 at 6:59 AM,  [EMAIL PROTECTED] wrote:
 So based on that would you provide a sprinkler below every shelf in order to 
 adequately protect it?  If we're going to hold to code, then you need to look 
 at shelf storage requirements.

 If you read the description of the revision, I read it that the open floor 
 area of the closet will now be part of the shelf system cabinet.  There is no 
 floor open to the room, there are doors on the unit.

 And protecting closet, well I can kind of accept, but a shelving unit with 
 doors on the front, with no floor, well sorry but that just sounds silly.

 At some point reason needs to prevail.

 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 [EMAIL PROTECTED]
 http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Allan Seidel
 Sent: Wednesday, November 05, 2008 9:44 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 In situations like this the room's floor area now extends into the former 
 closet's footprint. Therefore the sprinkler coverage needs to account for 
 this recess in the wall. In other words if you call it furniture then it must 
 occupy a space as furniture would. As we all well know, the standard cannot 
 fit every situation, but there needs to be some accounting for these 
 conditions that would make sense for the AHJ. For an extreme example, I do 
 not think there would be an agreement to ignore former closets as such 
 (assume they were 36 deep) when EC sprinklers are used at their maximum 
 distance from the wall where the closets were.

 Allan Seidel
 St. Louis, MO

 On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:

 It's furniture.  No sprinklers within.  Well, unless someone is going
 to occupy it.

 NFPA 13, 2007, 8.1(7)

 [cid:658182813@05112008-3391]





 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED] [mailto:
 [EMAIL PROTECTED] On Behalf Of Myles Knebel
 Sent: Wednesday, November 05, 2008 8:09 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 Good question. I would say,the closet is now a cabinet. I looked up
 cabinets in the index however I could not find  8.9.4.1.3.3. in the
 2007 addition (missing).
 No references say anything about sprinklers inside cabinets so in my
 opinion the cabiets don't need to be sprinklered.

 Ergo

 On Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:

 
  An office (light hazard) has several closets that have existing
 sprinklers.
  Part of the renovation is to remove the closet doors and provide
  built-in millwork recessed into the closet space. Essentially a
  storage cabinet made of wood with shelves at about every 2 feet and
  wooden doors. Is there any logical argument to provide or not
  provide sprinklers within this space? As a general rule we don't
  sprinkler furniture (although I don't think NFPA says it explicitly). Any 
  comments?
 
  Tony
 
 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: [EMAIL PROTECTED]

 To Unsubscribe, send an email

RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
Somehow we've ventured far away from the original issue, a cabinet with shelves 
two feet apart.   Not a closet, not an entertainment center, more of something 
to put clothes or towels or linens or a portable meth lab into.  If the shelves 
are only two feet apart where is the sprinkler going to go?  If you put a 
sprinkler at the top of the cabinet what is the sprinkler going to do three 
levels down, probably nothing.  What good is a shelf with a 3-4 obstruction 
in it?  With even the most creative of arguments it would a struggle to 
convince anyone that protection would be required in light of what is so 
clearly spelled out in the Standard.

But there is always the exceptionally enlightened AHJ that might argue down 
some other path.  sigh


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Wednesday, November 05, 2008 10:27 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

I tend to agree with Allen if I'm understanding his argument correctly. And 
correct me if I'm misstating the thought but I don't think he meant that the 
recess did not necessarily have to have separate protection but that the floor 
area had to be accounted for by some sprinkler. If I buy a free standing 
entertainment center I have a potential fire hazard (lots of plugs and cords) 
and the area of the building it occupies is protected by the overhead system. I 
am not going to worry about a fire inside it until that fire breaches the 
cabinet itself. By the same token if I have a built-in entertainment center I 
have the same hazard and must consider the building area it occupies if the 
fire breaches the cabinet. If that occurs then the building must be protected 
(protecting the cabinet in both cases is my concern, not society's, and could 
be addressed by a wonder gas if I so desire). Now if I use a former closet for 
my cabinet, using a face frame, with or without doors, and the former closet 
door lintel is an obstruction, and the closet does not meet any of the closet 
exemption rules then it would require a sprinkler on the closet side of the 
lintel. The same issues would apply if I just put a free standing cabinet in 
the closet opening. The cabinet parts are just a distraction in this 
discussion. The issues are the lintel (i.e.:
obstruction) and sprinkler spacing rules.

On Wed, Nov 5, 2008 at 6:59 AM,  [EMAIL PROTECTED] wrote:
 So based on that would you provide a sprinkler below every shelf in order to 
 adequately protect it?  If we're going to hold to code, then you need to look 
 at shelf storage requirements.

 If you read the description of the revision, I read it that the open floor 
 area of the closet will now be part of the shelf system cabinet.  There is no 
 floor open to the room, there are doors on the unit.

 And protecting closet, well I can kind of accept, but a shelving unit with 
 doors on the front, with no floor, well sorry but that just sounds silly.

 At some point reason needs to prevail.

 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Allan
 Seidel
 Sent: Wednesday, November 05, 2008 9:44 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 In situations like this the room's floor area now extends into the former 
 closet's footprint. Therefore the sprinkler coverage needs to account for 
 this recess in the wall. In other words if you call it furniture then it must 
 occupy a space as furniture would. As we all well know, the standard cannot 
 fit every situation, but there needs to be some accounting for these 
 conditions that would make sense for the AHJ. For an extreme example, I do 
 not think there would be an agreement to ignore former closets as such 
 (assume they were 36 deep) when EC sprinklers are used at their maximum 
 distance from the wall where the closets were.

 Allan Seidel
 St. Louis, MO

 On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:

 It's furniture.  No sprinklers within.  Well, unless someone is going
 to occupy it.

 NFPA 13, 2007, 8.1(7)

 [cid:658182813@05112008-3391]





 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED] [mailto:
 [EMAIL PROTECTED] On Behalf Of Myles Knebel

RE: Closets / cabinets

2008-11-05 Thread Chris Cahill
I'm with Allan.  You can call it furniture if the floor is covered to code
from the overhead system.  Furniture normally sits on a floor already
covered by sprinkler.  The code on furniture gets you out of the second head
covering the area, not the first.  Soffits, lintels, etc. may get in the
way.  If the floor isn't covered then you have a head under the soffit for
example and not in the furniture below the soffit.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
  Waverly, MN 55390

-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, November 05, 2008 9:00 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

So based on that would you provide a sprinkler below every shelf in order to
adequately protect it?  If we're going to hold to code, then you need to
look at shelf storage requirements.

If you read the description of the revision, I read it that the open floor
area of the closet will now be part of the shelf system cabinet.  There is
no floor open to the room, there are doors on the unit.

And protecting closet, well I can kind of accept, but a shelving unit with
doors on the front, with no floor, well sorry but that just sounds silly.

At some point reason needs to prevail.

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Allan Seidel
Sent: Wednesday, November 05, 2008 9:44 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

In situations like this the room's floor area now extends into the former
closet's footprint. Therefore the sprinkler coverage needs to account for
this recess in the wall. In other words if you call it furniture then it
must occupy a space as furniture would. As we all well know, the standard
cannot fit every situation, but there needs to be some accounting for these
conditions that would make sense for the AHJ. For an extreme example, I do
not think there would be an agreement to ignore former closets as such
(assume they were 36 deep) when EC sprinklers are used at their maximum
distance from the wall where the closets were.

Allan Seidel
St. Louis, MO

On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:

 It's furniture.  No sprinklers within.  Well, unless someone is going
 to occupy it.

 NFPA 13, 2007, 8.1(7)

 [cid:658182813@05112008-3391]





 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED] [mailto:
 [EMAIL PROTECTED] On Behalf Of Myles Knebel
 Sent: Wednesday, November 05, 2008 8:09 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 Good question. I would say,the closet is now a cabinet. I looked up
 cabinets in the index however I could not find  8.9.4.1.3.3. in the
 2007 addition (missing).
 No references say anything about sprinklers inside cabinets so in my
 opinion the cabiets don't need to be sprinklered.

 Ergo

 On Tue, Nov 4, 2008 at 12:21 PM, A.P.Silva [EMAIL PROTECTED] wrote:

 
  An office (light hazard) has several closets that have existing
 sprinklers.
  Part of the renovation is to remove the closet doors and provide
  built-in millwork recessed into the closet space. Essentially a
  storage cabinet made of wood with shelves at about every 2 feet and
  wooden doors. Is there any logical argument to provide or not
  provide sprinklers within this space? As a general rule we don't
  sprinkler furniture (although I don't think NFPA says it explicitly).
Any comments?
 
  Tony
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Closets / cabinets

2008-11-05 Thread Roland Huggins
I go with what Ron said.  Also note that obstructions (shelves) are  
not an issue in a closet.  Also it is A.8.15.8.2 that states that  
sprinklers are not required within furniture is the old text and it  
was expanded in 07 (and put within the standard ) at 8.1.1(7).  That  
section also states you can attach the furniture to the structure.  It  
doesn't say you can put it within a closet.


Roland


On Nov 5, 2008, at 7:27 AM, Ron Greenman wrote:


I tend to agree with Allen if I'm understanding his argument
correctly. And correct me if I'm misstating the thought but I don't
think he meant that the recess did not necessarily have to have
separate protection but that the floor area had to be accounted for by
some sprinkler. If I buy a free standing entertainment center I have a
potential fire hazard (lots of plugs and cords) and the area of the
building it occupies is protected by the overhead system. I am not
going to worry about a fire inside it until that fire breaches the
cabinet itself. By the same token if I have a built-in entertainment
center I have the same hazard and must consider the building area it
occupies if the fire breaches the cabinet. If that occurs then the
building must be protected (protecting the cabinet in both cases is my
concern, not society's, and could be addressed by a wonder gas if I so
desire). Now if I use a former closet for my cabinet, using a face
frame, with or without doors, and the former closet door lintel is an
obstruction, and the closet does not meet any of the closet exemption
rules then it would require a sprinkler on the closet side of the
lintel. The same issues would apply if I just put a free standing
cabinet in the closet opening. The cabinet parts are just a
distraction in this discussion. The issues are the lintel (i.e.:
obstruction) and sprinkler spacing rules.


___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Craig Leadbetter
Come to the State of Michigan. The head would be required in this
closet. 

Craig Leadbetter
Safeguard of Marquette
(P)906-475-9955 Ext 101
(F) 906-475-5474
(C) 906-362-5393


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, November 05, 2008 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

Somehow we've ventured far away from the original issue, a cabinet with
shelves two feet apart.   Not a closet, not an entertainment center,
more of something to put clothes or towels or linens or a portable meth
lab into.  If the shelves are only two feet apart where is the sprinkler
going to go?  If you put a sprinkler at the top of the cabinet what is
the sprinkler going to do three levels down, probably nothing.  What
good is a shelf with a 3-4 obstruction in it?  With even the most
creative of arguments it would a struggle to convince anyone that
protection would be required in light of what is so clearly spelled out
in the Standard.

But there is always the exceptionally enlightened AHJ that might argue
down some other path.  sigh


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Wednesday, November 05, 2008 10:27 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

I tend to agree with Allen if I'm understanding his argument correctly.
And correct me if I'm misstating the thought but I don't think he meant
that the recess did not necessarily have to have separate protection but
that the floor area had to be accounted for by some sprinkler. If I buy
a free standing entertainment center I have a potential fire hazard
(lots of plugs and cords) and the area of the building it occupies is
protected by the overhead system. I am not going to worry about a fire
inside it until that fire breaches the cabinet itself. By the same token
if I have a built-in entertainment center I have the same hazard and
must consider the building area it occupies if the fire breaches the
cabinet. If that occurs then the building must be protected (protecting
the cabinet in both cases is my concern, not society's, and could be
addressed by a wonder gas if I so desire). Now if I use a former closet
for my cabinet, using a face frame, with or without doors, and the
former closet door lintel is an obstruction, and the closet does not
meet any of the closet exemption rules then it would require a sprinkler
on the closet side of the lintel. The same issues would apply if I just
put a free standing cabinet in the closet opening. The cabinet parts are
just a distraction in this discussion. The issues are the lintel (i.e.:
obstruction) and sprinkler spacing rules.

On Wed, Nov 5, 2008 at 6:59 AM,  [EMAIL PROTECTED] wrote:
 So based on that would you provide a sprinkler below every shelf in
order to adequately protect it?  If we're going to hold to code, then
you need to look at shelf storage requirements.

 If you read the description of the revision, I read it that the open
floor area of the closet will now be part of the shelf system cabinet.
There is no floor open to the room, there are doors on the unit.

 And protecting closet, well I can kind of accept, but a shelving unit
with doors on the front, with no floor, well sorry but that just sounds
silly.

 At some point reason needs to prevail.

 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com


 -Original Message-
 From: [EMAIL PROTECTED]
 [mailto:[EMAIL PROTECTED] On Behalf Of Allan
 Seidel
 Sent: Wednesday, November 05, 2008 9:44 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: Closets / cabinets

 In situations like this the room's floor area now extends into the
former closet's footprint. Therefore the sprinkler coverage needs to
account for this recess in the wall. In other words if you call it
furniture then it must occupy a space as furniture would. As we all well
know, the standard cannot fit every situation, but there needs to be
some accounting for these conditions that would make sense for the AHJ.
For an extreme example, I do not think there would be an agreement to
ignore former closets as such (assume they were 36 deep) when EC
sprinklers are used at their maximum distance from the wall where the
closets were.

 Allan Seidel
 St. Louis, MO

 On Wed, Nov 5, 2008 at 7:29 AM, [EMAIL PROTECTED] wrote:

 It's furniture.  No sprinklers within.  Well, unless someone is going
 to occupy it.

 NFPA 13, 2007, 8.1(7)

 [cid:658182813@05112008-3391]





 Craig L

RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
But it's not being described as a closet.  Maybe if we had pictures or drawings 
it would be clearer.  What I've seen is often called a built-in.  It is an area 
of the wall, recessed to accept a piece of furniture such as for linen storage 
or for a stereo systems or other such uses.  But they are not a clothes closet, 
you can't walk into them.

I still want someone to describe how a sprinkler would function in a SHELF unit 
with shelves 2ft apart and someone stacking towels or shoes or other such 
objects in that 24 space.

If we were to sprinkle the built-in linen shelves why not put one in the 
built-in refrigerator?


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Craig Leadbetter
Sent: Wednesday, November 05, 2008 11:37 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

Come to the State of Michigan. The head would be required in this closet.

Craig Leadbetter
Safeguard of Marquette
(P)906-475-9955 Ext 101
(F) 906-475-5474
(C) 906-362-5393


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Wednesday, November 05, 2008 10:47 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

Somehow we've ventured far away from the original issue, a cabinet with
shelves two feet apart.   Not a closet, not an entertainment center,
more of something to put clothes or towels or linens or a portable meth lab 
into.  If the shelves are only two feet apart where is the sprinkler going to 
go?  If you put a sprinkler at the top of the cabinet what is the sprinkler 
going to do three levels down, probably nothing.  What good is a shelf with a 
3-4 obstruction in it?  With even the most creative of arguments it would a 
struggle to convince anyone that protection would be required in light of what 
is so clearly spelled out in the Standard.

But there is always the exceptionally enlightened AHJ that might argue down 
some other path.  sigh


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Wednesday, November 05, 2008 10:27 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

I tend to agree with Allen if I'm understanding his argument correctly.
And correct me if I'm misstating the thought but I don't think he meant that 
the recess did not necessarily have to have separate protection but that the 
floor area had to be accounted for by some sprinkler. If I buy a free standing 
entertainment center I have a potential fire hazard (lots of plugs and cords) 
and the area of the building it occupies is protected by the overhead system. I 
am not going to worry about a fire inside it until that fire breaches the 
cabinet itself. By the same token if I have a built-in entertainment center I 
have the same hazard and must consider the building area it occupies if the 
fire breaches the cabinet. If that occurs then the building must be protected 
(protecting the cabinet in both cases is my concern, not society's, and could 
be addressed by a wonder gas if I so desire). Now if I use a former closet for 
my cabinet, using a face frame, with or without doors, and the former closet 
door lintel is an obstruction, and the closet does not meet any of the closet 
exemption rules then it would require a sprinkler on the closet side of the 
lintel. The same issues would apply if I just put a free standing cabinet in 
the closet opening. The cabinet parts are just a distraction in this 
discussion. The issues are the lintel (i.e.:
obstruction) and sprinkler spacing rules.

On Wed, Nov 5, 2008 at 6:59 AM,  [EMAIL PROTECTED] wrote:
 So based on that would you provide a sprinkler below every shelf in
order to adequately protect it?  If we're going to hold to code, then you need 
to look at shelf storage requirements.

 If you read the description of the revision, I read it that the open
floor area of the closet will now be part of the shelf system cabinet.
There is no floor open to the room, there are doors on the unit.

 And protecting closet, well I can kind of accept, but a shelving unit
with doors on the front, with no floor, well sorry but that just sounds silly.

 At some point reason needs to prevail.

 Craig L. Prahl, CET
 Fire Protection Specialist
 Mechanical Department
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
 864.599.8439 [EMAIL PROTECTED] http

RE: Closets / cabinets

2008-11-05 Thread Thom McMahon
Generally Furniture would not extend up to the ceiling, and so not be
blocking the spray pattern, that developed for the room. A converted closet
will since there is a lintel over what used to be the door that extends to
the ceiling. The secondary issue is if the area was included in the area of
protection provided by the sprinklers in the room, formerly the Adjoining
room? If not some method of protection should be supplied, unless a
specific exception can be met.

A single head at the top of the closet/linen cabinet should suffice. If you
add 14-15 Gpm to a 3x3 space, that cooling effect will be huge, and while
water may not directly contact the burning materials, the normally loose
fitting shelves of a cabinet, will allow the water to wet the interior
surfaces of the cabinet all the way to the floor.

So unless this is a Suppression mode system, I would say containment was
the likely result, if a fire occurred in the cabinet/closet with a single
sprinkler head at the top.

My two peso's, and well worth it, Se?


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, November 05, 2008 9:08 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

I go with what Ron said.  Also note that obstructions (shelves) are not an
issue in a closet.  Also it is A.8.15.8.2 that states that sprinklers are
not required within furniture is the old text and it was expanded in 07 (and
put within the standard ) at 8.1.1(7).  That section also states you can
attach the furniture to the structure.  It doesn't say you can put it within
a closet.

Roland


On Nov 5, 2008, at 7:27 AM, Ron Greenman wrote:

 I tend to agree with Allen if I'm understanding his argument 
 correctly. And correct me if I'm misstating the thought but I don't 
 think he meant that the recess did not necessarily have to have 
 separate protection but that the floor area had to be accounted for by 
 some sprinkler. If I buy a free standing entertainment center I have a 
 potential fire hazard (lots of plugs and cords) and the area of the 
 building it occupies is protected by the overhead system. I am not 
 going to worry about a fire inside it until that fire breaches the 
 cabinet itself. By the same token if I have a built-in entertainment 
 center I have the same hazard and must consider the building area it 
 occupies if the fire breaches the cabinet. If that occurs then the 
 building must be protected (protecting the cabinet in both cases is my 
 concern, not society's, and could be addressed by a wonder gas if I so 
 desire). Now if I use a former closet for my cabinet, using a face 
 frame, with or without doors, and the former closet door lintel is an 
 obstruction, and the closet does not meet any of the closet exemption 
 rules then it would require a sprinkler on the closet side of the 
 lintel. The same issues would apply if I just put a free standing 
 cabinet in the closet opening. The cabinet parts are just a 
 distraction in this discussion. The issues are the lintel (i.e.:
 obstruction) and sprinkler spacing rules.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Autry, David

Yeah I know! The Tri angle of fire is OLD School, and someday it will be
the Obelisk of fire, but I hope by then to have been put to the flame for
the last time.

Actually it's a Tetrahedron.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
Yeah, yeah, now you had to go ruin the fun with all that techno-jargon stuff.


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Wednesday, November 05, 2008 12:44 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

We would not need to Sprinkler a Residential Refrigerator, because we rely on 
the magnetic seal to keep air out and food fresh, hence the old fire tri angle 
wouldn't work until you open the door, and exposed the fire hazard to the air 
as well as the room sprinkler. Does the room sprinkler put out or contain the 
fire in the fridge? Hell no! When you jump back from that burst of flame as you 
opened the door, the inclined plane hinges will close it for you, returning the 
situation to the lop sided triangle again as soon as the air is used up. You 
might want to swear off that 8 alarm chili, or call Tom D. cause he'll want to 
get some before it's all gone. But that's another story.

As far as commercial refrigerator's go, we do sprinkler them when we can 
actually walk inside it. Otherwise we once again rely on the Automatically 
closing doors to break the tri angle of fire on the smaller ones.

Yeah I know! The Tri angle of fire is OLD School, and someday it will be the 
Obelisk of fire, but I hope by then to have been put to the flame for the 
last time.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



If we were to sprinkle the built-in linen shelves why not put one in the 
built-in refrigerator?


Craig L. Prahl, CET

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Thom McMahon
We would not need to Sprinkler a Residential Refrigerator, because we rely
on the magnetic seal to keep air out and food fresh, hence the old fire tri
angle wouldn't work until you open the door, and exposed the fire hazard to
the air as well as the room sprinkler. Does the room sprinkler put out or
contain the fire in the fridge? Hell no! When you jump back from that burst
of flame as you opened the door, the inclined plane hinges will close it for
you, returning the situation to the lop sided triangle again as soon as the
air is used up. You might want to swear off that 8 alarm chili, or call Tom
D. cause he'll want to get some before it's all gone. But that's another
story.

As far as commercial refrigerator's go, we do sprinkler them when we can
actually walk inside it. Otherwise we once again rely on the Automatically
closing doors to break the tri angle of fire on the smaller ones.

Yeah I know! The Tri angle of fire is OLD School, and someday it will be
the Obelisk of fire, but I hope by then to have been put to the flame for
the last time.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



If we were to sprinkle the built-in linen shelves why not put one in the
built-in refrigerator?


Craig L. Prahl, CET

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Craig Leadbetter
Below is a copy of the rule for the State of Michigan on any Office of
Fire Safety reviewed project. We were also directed to protect built in
shelving unit similar to the ones describe even though they were just
being used to store adult diaper and sheets. 


Bureau of Fire Services Informational Interpretation PR 07-01, Sprinkler
Coverage in Closets and Wardrobes for all Fully Sprinklered
Facilities, in accordance with National Fire Protection Association
standards 13, 13R or 13D, regulated by the Bureau of Fire
Services.
1. Built - in closets shall be protected by placing a sprinkler head
inside.
2. Wardrobes over 36 cubic feet shall be protected by placing a
sprinkler head in side.
3. Wardrobes 36 cubic feet and under shall be protected by placing a
sprinkler head inside or placing a sprinkler head
within 3 feet directly in front of the wardrobe.

Craig Leadbetter
Safeguard of Marquette
(P)906-475-9955 Ext 101
(F) 906-475-5474
(C) 906-362-5393


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Wednesday, November 05, 2008 12:19 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

Generally Furniture would not extend up to the ceiling, and so not be
blocking the spray pattern, that developed for the room. A converted
closet
will since there is a lintel over what used to be the door that extends
to
the ceiling. The secondary issue is if the area was included in the area
of
protection provided by the sprinklers in the room, formerly the
Adjoining
room? If not some method of protection should be supplied, unless a
specific exception can be met.

A single head at the top of the closet/linen cabinet should suffice. If
you
add 14-15 Gpm to a 3x3 space, that cooling effect will be huge, and
while
water may not directly contact the burning materials, the normally loose
fitting shelves of a cabinet, will allow the water to wet the interior
surfaces of the cabinet all the way to the floor.

So unless this is a Suppression mode system, I would say containment
was
the likely result, if a fire occurred in the cabinet/closet with a
single
sprinkler head at the top.

My two peso's, and well worth it, Se?


Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, November 05, 2008 9:08 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

I go with what Ron said.  Also note that obstructions (shelves) are not
an
issue in a closet.  Also it is A.8.15.8.2 that states that sprinklers
are
not required within furniture is the old text and it was expanded in 07
(and
put within the standard ) at 8.1.1(7).  That section also states you can
attach the furniture to the structure.  It doesn't say you can put it
within
a closet.

Roland


On Nov 5, 2008, at 7:27 AM, Ron Greenman wrote:

 I tend to agree with Allen if I'm understanding his argument 
 correctly. And correct me if I'm misstating the thought but I don't 
 think he meant that the recess did not necessarily have to have 
 separate protection but that the floor area had to be accounted for by

 some sprinkler. If I buy a free standing entertainment center I have a

 potential fire hazard (lots of plugs and cords) and the area of the 
 building it occupies is protected by the overhead system. I am not 
 going to worry about a fire inside it until that fire breaches the 
 cabinet itself. By the same token if I have a built-in entertainment 
 center I have the same hazard and must consider the building area it 
 occupies if the fire breaches the cabinet. If that occurs then the 
 building must be protected (protecting the cabinet in both cases is my

 concern, not society's, and could be addressed by a wonder gas if I so

 desire). Now if I use a former closet for my cabinet, using a face 
 frame, with or without doors, and the former closet door lintel is an 
 obstruction, and the closet does not meet any of the closet exemption 
 rules then it would require a sprinkler on the closet side of the 
 lintel. The same issues would apply if I just put a free standing 
 cabinet in the closet opening. The cabinet parts are just a 
 distraction in this discussion. The issues are the lintel (i.e.:
 obstruction) and sprinkler spacing rules.

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED

RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
Actually it's a Tetrahedron.



Gee I thought those things were extinct?

I learn so much here..  ;)


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Autry, David
Sent: Wednesday, November 05, 2008 12:53 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets


Yeah I know! The Tri angle of fire is OLD School, and someday it will be the 
Obelisk of fire, but I hope by then to have been put to the flame for the 
last time.

Actually it's a Tetrahedron.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Steve Leyton
Does anyone know exactly when the Fire Triangle went 3D??   Can I just
read it with Navis or do I need a drafting engine?

I'm so confused ...

Steve Leyton
Protection Design  Consulting
San Diego, CA


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, November 05, 2008 10:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets

Actually it's a Tetrahedron.



Gee I thought those things were extinct?

I learn so much here..  ;)


Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Autry,
David
Sent: Wednesday, November 05, 2008 12:53 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Closets / cabinets


Yeah I know! The Tri angle of fire is OLD School, and someday it will
be the Obelisk of fire, but I hope by then to have been put to the
flame for the last time.

Actually it's a Tetrahedron.


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3587 (20081105) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__ Information from ESET NOD32 Antivirus, version of virus
signature database 3587 (20081105) __

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


Re: Closets / cabinets

2008-11-05 Thread Ron Greenman
Thom,

Tetrahedron. We are getting off but this is an important line of
discussion relative to what we are protecting. I'd say that the best
way to look at this is that if you removed all the stuff we put in a
building that isn't really part of the building, including built-in
furniture (cabinets, appliances, etc.) then the question is, is
everything left covered by the sprinklers? Is there sheetrock behind
the cabinet, no lintel or other obstruction, and does the room
sprinkler cover the alcove (closet) per spacing rules? If the answer
is yes to all these questions then no sprinkler would be necessary
inside the alcove (closet), but if the answer is no to any of those
questions I'd say the area enclosed by cabinet needs to be covered
regardless of shelving or other contents. Essentially we're taking
about a combustible concealed space when the doors are closed, or,
when a lintel is present, an obstructed space, or, when the space is
beyond the spacing rules of the room sprinkler, an unprotected area
within a sprinklered structure.

On Wed, Nov 5, 2008 at 9:43 AM, Thom McMahon [EMAIL PROTECTED] wrote:
 We would not need to Sprinkler a Residential Refrigerator, because we rely
 on the magnetic seal to keep air out and food fresh, hence the old fire tri
 angle wouldn't work until you open the door, and exposed the fire hazard to
 the air as well as the room sprinkler. Does the room sprinkler put out or
 contain the fire in the fridge? Hell no! When you jump back from that burst
 of flame as you opened the door, the inclined plane hinges will close it for
 you, returning the situation to the lop sided triangle again as soon as the
 air is used up. You might want to swear off that 8 alarm chili, or call Tom
 D. cause he'll want to get some before it's all gone. But that's another
 story.

 As far as commercial refrigerator's go, we do sprinkler them when we can
 actually walk inside it. Otherwise we once again rely on the Automatically
 closing doors to break the tri angle of fire on the smaller ones.

 Yeah I know! The Tri angle of fire is OLD School, and someday it will be
 the Obelisk of fire, but I hope by then to have been put to the flame for
 the last time.

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926



 If we were to sprinkle the built-in linen shelves why not put one in the
 built-in refrigerator?


 Craig L. Prahl, CET

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to: [EMAIL PROTECTED]

 To Unsubscribe, send an email to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)




-- 
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Thom McMahon
Yeah! For Now!

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Actually it's a Tetrahedron.


David Autry

___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


RE: Closets / cabinets

2008-11-05 Thread Craig.Prahl
Then do you put sprinklers in kitchen cabinets or pantries or bathroom 
cabinets?  To what point is this taken?

I guess my point in all this is that sprinkler protection is that sprinklers 
are not an accessory most people put at the top of their home décor list.  If 
we don't have clear Code direction and we're just wingin' it on places we feel 
should have sprinklers, it makes us look a bit ridiculous and dilutes our cause.

Should I put sprinklers behind and overhead of my entertainment center?

Anyone have any statistics on fires beginning in residential pantry or linen 
closets?


Sometimes we can be a bit overzealous to the point of being nonsensical.




Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Wednesday, November 05, 2008 1:21 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Closets / cabinets

Thom,

Tetrahedron. We are getting off but this is an important line of discussion 
relative to what we are protecting. I'd say that the best way to look at this 
is that if you removed all the stuff we put in a building that isn't really 
part of the building, including built-in furniture (cabinets, appliances, etc.) 
then the question is, is everything left covered by the sprinklers? Is there 
sheetrock behind the cabinet, no lintel or other obstruction, and does the room 
sprinkler cover the alcove (closet) per spacing rules? If the answer is yes to 
all these questions then no sprinkler would be necessary inside the alcove 
(closet), but if the answer is no to any of those questions I'd say the area 
enclosed by cabinet needs to be covered regardless of shelving or other 
contents. Essentially we're taking about a combustible concealed space when the 
doors are closed, or, when a lintel is present, an obstructed space, or, when 
the space is beyond the spacing rules of the room sprinkler, an unprotected 
area within a sprinklered structure.

On Wed, Nov 5, 2008 at 9:43 AM, Thom McMahon [EMAIL PROTECTED] wrote:
 We would not need to Sprinkler a Residential Refrigerator, because
 we rely on the magnetic seal to keep air out and food fresh, hence the
 old fire tri angle wouldn't work until you open the door, and exposed
 the fire hazard to the air as well as the room sprinkler. Does the
 room sprinkler put out or contain the fire in the fridge? Hell no!
 When you jump back from that burst of flame as you opened the door,
 the inclined plane hinges will close it for you, returning the
 situation to the lop sided triangle again as soon as the air is used
 up. You might want to swear off that 8 alarm chili, or call Tom D.
 cause he'll want to get some before it's all gone. But that's another story.

 As far as commercial refrigerator's go, we do sprinkler them when we
 can actually walk inside it. Otherwise we once again rely on the
 Automatically closing doors to break the tri angle of fire on the smaller 
 ones.

 Yeah I know! The Tri angle of fire is OLD School, and someday it
 will be the Obelisk of fire, but I hope by then to have been put to
 the flame for the last time.

 Thom McMahon, SET
 Firetech, Inc.
 2560 Copper Ridge Dr
 P.O. Box 882136
 Steamboat Springs, CO 80488
 Tel:  970-879-7952
 Fax: 970-879-7926



 If we were to sprinkle the built-in linen shelves why not put one in
 the built-in refrigerator?


 Craig L. Prahl, CET

 ___
 Sprinklerforum mailing list
 http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
 For Technical Assistance, send an email to:
 [EMAIL PROTECTED]

 To Unsubscribe, send an email
 to:[EMAIL PROTECTED]
 (Put the word unsubscribe in the subject field)




--
Ron Greenman
at home
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)