RE: RTI

2012-06-10 Thread Brad Casterline
Yes Russell, it is of great interest to me, thank you. On Friday lunch break I found NZS4541:2007. It is not free. I also refreshed my memory on RTI. Since it is based on temperature AND velocity of the heat, given RTI=36, without knowing the rated temp, one does not know if the length unit is

RE: RTI

2012-06-09 Thread Russell Carol Gregory
Of Brad Casterline Sent: Saturday, 9 June 2012 12:27 AM To: sprinklerforum@firesprinkler.org Subject: RE: RTI Thanks Russell! I thought I had answered my own question using 'pure reasoning' alone :), especially since the original question dealt with needing to differentiate RTI, and 30 must be a UL

RE: RTI

2012-06-08 Thread Brad Casterline
: RE: RTI In our NZ Standard NZS541 a sprinkler with RTI between 50 and 80 is designated a Special Response Sprinkler. These usually have a 4mm bulb. Std Response has a 5mm or larger bulb and the Fast Response has a 3mm bulb. Russell Gregory Ph 03 338 4853 e-mail rcgreg...@snap.net.nz -Original

RE: RTI

2012-06-07 Thread Brad Casterline
never mind (coffee worked), it's called 'nobody makes them because they would not be UL Listed', and it points out the amazing (to me) tolerances sprinklers are manufactured to. -Original Message- From: bcasterl...@fsc-inc.com [mailto:bcasterl...@fsc-inc.com] Sent: Thursday, June 07,

RE: RTI

2012-06-07 Thread George Church
: Thursday, June 07, 2012 7:37 AM To: sprinklerforum@firesprinkler.org Subject: RE: RTI never mind (coffee worked), it's called 'nobody makes them because they would not be UL Listed', and it points out the amazing (to me) tolerances sprinklers are manufactured to. -Original Message- From

RE: RTI Cloud Deluge

2012-06-07 Thread Bill Brooks
N. Brooks, P.E. Brooks Fire Protection Engineering Inc. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Hairfield Sent: Wednesday, June 06, 2012 3:36 PM To: AFSA SprinklerFORUM Subject: RE: RTI You

RE: RTI Cloud Deluge

2012-06-07 Thread Fairchild, Jack
@firesprinkler.org Subject: RE: RTI Cloud Deluge Yes we have a rulebook instead of an engineering approach (thank goodness), and yes we have been fumbling around for many years about this cloud thing, but in the name of common sense (which I hope we still have a little of) this design approach must

RE: RTI

2012-06-07 Thread RFletcher
Of George Church Sent: Thursday, June 07, 2012 5:27 AM To: sprinklerforum@firesprinkler.org Subject: RE: RTI The amount of significant digits we work to in various aspects is quite varied. Some folks believe calc programs down to the .001 level when it all comes down to a gauge bouncing around

RE: RTI

2012-06-07 Thread Russell Carol Gregory
In our NZ Standard NZS541 a sprinkler with RTI between 50 and 80 is designated a Special Response Sprinkler. These usually have a 4mm bulb. Std Response has a 5mm or larger bulb and the Fast Response has a 3mm bulb. Russell Gregory Ph 03 338 4853 e-mail rcgreg...@snap.net.nz -Original

Re: RTI

2012-06-07 Thread Charles Thurston
Hello Well the alarm guys that put the heat detector in the elevator shaft need to consider the RTI of the sprinkler head in comparison to the RTI of the Heat Detector they put within 24 of the sprinkler head also. Going to be a Pain when the the requirement that anything within 48 of the

RE: RTI

2012-06-06 Thread Craig.Prahl
Call Tyco. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SCĀ  29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 craig.pr...@ch2m.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: RTI

2012-06-06 Thread Mike Hairfield
Thanks, They told me it was 36. Mike From: craig.pr...@ch2m.com To: sprinklerforum@firesprinkler.org Subject: RE: RTI Date: Wed, 6 Jun 2012 17:21:17 + Call Tyco. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC

RE: RTI

2012-06-06 Thread Cahill, Christopher
To: AFSA SprinklerFORUM Subject: RE: RTI Thanks, They told me it was 36. Mike From: craig.pr...@ch2m.com To: sprinklerforum@firesprinkler.org Subject: RE: RTI Date: Wed, 6 Jun 2012 17:21:17 + Call Tyco. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500

RE: RTI

2012-06-06 Thread Bob
Mike, I had an AHJ ask that once. Thing was he was clueless about sprinklers and what we were doing, but he had apparently done some reading and came across the RTI. He thought he had found the nail for our coffin. Tried to hold up the project because of it. This in spite of FM approval. Once

RE: RTI

2012-06-06 Thread Brad Casterline
, June 06, 2012 12:26 PM To: AFSA SprinklerFORUM Subject: RE: RTI Thanks, They told me it was 36. Mike From: craig.pr...@ch2m.com To: sprinklerforum@firesprinkler.org Subject: RE: RTI Date: Wed, 6 Jun 2012 17:21:17 + Call Tyco. Craig L. Prahl, CET Fire Protection CH2MHILL

RE: RTI

2012-06-06 Thread Mike Hairfield
There are QR Sprinklers in the same room that has a deluge system with open heads in it, they want to make sure that the detectors do not trip the deluge system first. From: ccah...@burnsmcd.com To: sprinklerforum@firesprinkler.org Date: Wed, 6 Jun 2012 12:31:18 -0500 Subject: RE: RTI

RE: RTI

2012-06-06 Thread Craig.Prahl
SprinklerFORUM Subject: RE: RTI There are QR Sprinklers in the same room that has a deluge system with open heads in it, they want to make sure that the detectors do not trip the deluge system first. From: ccah...@burnsmcd.com To: sprinklerforum@firesprinkler.org Date: Wed, 6 Jun 2012

RE: RTI

2012-06-06 Thread Mike Hairfield
big DA came up with this idea. It's a tiered classroom with a sloping floor, I suggested they install some life preservers for the students so they won't drown when the system trips. Mike From: craig.pr...@ch2m.com To: sprinklerforum@firesprinkler.org Subject: RE: RTI Date: Wed, 6

RE: RTI

2012-06-06 Thread Craig.Prahl
Subject: RE: RTI You won't believe this! Armstrong ceiling clouds that are arched, architect doesn't want to penetrate the clouds like the Armstrong data sheet shows so we have QR sprinklers above the clouds and a deluge system of sidewall sprinklers feed from the soffits throwing water under

RE: RTI

2012-06-06 Thread Cahill, Christopher
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Hairfield Sent: Wednesday, June 06, 2012 2:36 PM To: AFSA SprinklerFORUM Subject: RE: RTI You won't believe this! Armstrong ceiling clouds that are arched, architect doesn't want to penetrate the clouds like the Armstrong

RE: RTI

2012-06-06 Thread George Church
:36 PM To: AFSA SprinklerFORUM Subject: RE: RTI You won't believe this! Armstrong ceiling clouds that are arched, architect doesn't want to penetrate the clouds like the Armstrong data sheet shows so we have QR sprinklers above the clouds and a deluge system of sidewall sprinklers feed from

Re: RTI

2012-06-06 Thread Ron Greenman
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto: sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Hairfield Sent: Wednesday, June 06, 2012 3:36 PM To: AFSA SprinklerFORUM Subject: RE: RTI You won't believe this! Armstrong ceiling clouds

Re: RTI Times

2007-05-14 Thread Roland Huggins
Try contacting Peter Larrimer (FPE for the VA verses just one of their hospitals). He pops up on occasion on the Forum. Roland On May 14, 2007, at 9:06 AM, Jay Stough wrote: We have a customer, a VA Hospital, that is trying to justify changing from Standard response to quick response

RE: RTI Times

2007-05-14 Thread Rich Pehrson
NIST ran a number of full scale fire tests in hospital patient rooms looking at different sprinkler heads, locations, activation times, etc. The report is located here: http://fire.nist.gov/bfrlpubs/fire79/PDF/f79004.pdf Rich Pehrson Futrell Fire -Original Message- From: [EMAIL

Re: RTI Times

2007-05-14 Thread Michael M. Fitz
The actual sprinkler operation time is a function of the fire size and growth because the heat transfer to the element is related to the temperature and velocity of gasses passing the link/bulb, plus other factors. I use a program to calculate the difference in time, there are several

RE: RTI Times

2007-05-14 Thread Sal Izzo
, and ESFR). Regards, Salvatore Izzo, P.E. SFPE Manager - Reliable Technical Services From: [EMAIL PROTECTED] on behalf of Rich Pehrson Sent: Mon 5/14/2007 12:30 To: sprinklerforum@firesprinkler.org Subject: RE: RTI Times NIST ran a number of full scale fire