-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Greg
McGahan
Sent: Wednesday, May 01, 2013 10:01 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: check valves on dry standpipes
Message -
From: John Denhardt jdenha...@stricklandfire.com
To: sprinklerforum@lists.firesprinkler.org
sprinklerforum@lists.firesprinkler.org
Sent: Wednesday, May 1, 2013 6:45:40 PM
Subject: Re: check valves on dry standpipes
Agree with you. No check valves required.
Fire sprinklers save
: check valves on dry standpipes
We did a manual dry in a parking garage a few years ago, I asked this
question to the local AHJ and he did require one. NFPA 14 (2013) - 6.4.2
requires one.
Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office (731) 424-9285 fax
(731
: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John
Denhardt
Sent: Thursday, May 02, 2013 7:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: check valves on dry standpipes
That is very interesting. I wonder what
@lists.firesprinkler.org
Subject: RE: check valves on dry standpipes
My only thought is when the fire department disconnects their hoses the water
can come back through the FDC - some people may still install single clapper
FDC's not thinking ahead or the clappers could stick or malfunction as well.
Greg - in your
Gillett
Sent: Thursday, May 02, 2013 7:54 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: check valves on dry standpipes
My only thought is when the fire department disconnects their hoses the water
can come back through the FDC - some people may still install single clapper
FDC's
: Thursday, May 02, 2013 7:54 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: check valves on dry standpipes
My only thought is when the fire department disconnects their hoses the
water can come back through the FDC - some people may still install single
clapper FDC's not thinking ahead
@lists.firesprinkler.org
Cc: Steve Leyton
Subject: RE: check valves on dry standpipes
That is very interesting. I wonder what is the reason one is required?
Steve?
John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number
@lists.firesprinkler.org
Subject: Re: check valves on dry standpipes
In this case, the local FD would be familiar with the SP - it is also
visible and free standing. I know we did one other similar dock without
the check valve in the same county.
Thanks,
Greg
On Thu, May 2, 2013 at 8:46 AM, George
[mailto:jdenha...@stricklandfire.com]
Sent: Thursday, May 02, 2013 8:40 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: check valves on dry standpipes
That is very interesting. I wonder what is the reason one is required?
Steve?
John August Denhardt, P.E., FSFPE
Strickland Fire
, 2013 1:15 PM
To: 'sprinklerforum@lists.firesprinkler.org'
Subject: RE: check valves on dry standpipes
Wow, is this the second time in your illustrious career that you were not
correct? LOL
Maybe it's time to switch over to fire alarm systems, like me. I still can't
believe I have been
AM
Subject: Re: check valves on dry standpipes
This is a Manual Dry Standpipe with one 2-1/2 hose valve on a dock. I do
not see a purpose for the check valve persoanlly.
On Thu, May 2, 2013 at 12:38 AM, bver...@comcast.net wrote:
Did you mean dry sprinkler system, or standpipe, ie, built
...@keyfireprotection.com
To: sprinklerforum@lists.firesprinkler.org
Sent: Thursday, May 2, 2013 5:54:24 AM
Subject: RE: check valves on dry standpipes
My only thought is when the fire department disconnects their hoses the
water can come back through the FDC - some people may still install
Are you required to put check valves on FDC's supplyign dry standpipe
systems such as on docks etc?
Thanks,
--
Greg McGahan
Living Water Fire Protection, LLC http://www.livingwaterfp.com
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
Hello Greg,
Is it a Manual Dry system? If so we do not and the AHJs in the area see no
reason to.
Wednesday, May 1, 2013, 9:38:18 PM, you wrote:
Are you required to put check valves on FDC's supplyign dry standpipe
systems such as on docks etc?
Thanks,
--
Best regards,
Charles
Agree with you. No check valves required.
Fire sprinklers save lives
Sent from my iPad
On May 1, 2013, at 9:44 PM, Charles Thurston charl...@mbfsg.com wrote:
Hello Greg,
Is it a Manual Dry system? If so we do not and the AHJs in the area see no
reason to.
Wednesday, May 1, 2013,
T
hanks - that makes three!~!
On Wed, May 1, 2013 at 8:45 PM, John Denhardt
jdenha...@stricklandfire.comwrote:
Agree with you. No check valves required.
Fire sprinklers save lives
Sent from my iPad
On May 1, 2013, at 9:44 PM, Charles Thurston charl...@mbfsg.com wrote:
Hello Greg,
Subject: Re: check valves on dry standpipes
Agree with you. No check valves required.
Fire sprinklers save lives
Sent from my iPad
On May 1, 2013, at 9:44 PM, Charles Thurston charl...@mbfsg.com wrote:
Hello Greg,
Is it a Manual Dry system? If so we do not and the AHJs in the area see