RE: mixed systems

2010-01-14 Thread Dewayne Martinez
Chris, I still think that if the hydraulically most demanding area falls either between 2 systems or branch lines off 2 separate cross mains, you still need to pick up the full remote area for the area/density method. The fire will not know what sprinklers are supplied from which pipe. You still

RE: mixed systems

2010-01-14 Thread George Church
On the other hand, there's a zillion SF of big boxes out there with multiple systems covering ONE area and with 40k SF system limit for high-piled storage, of course more than one system can cover an area. It would only be where different criteria apply and walls pop up that you start worrying

RE: mixed systems

2010-01-14 Thread Craig.Prahl
If you have adjacent systems and calc both are you anticipating flowing the entire remote areas of both systems? If statistics are correct and most fires are controlled or extinguished by less than 3 sprinklers even if the fire involved several sprinklers on adjacent systems, would calcing

Not a rumor, Arizona State Fire Marshals Office

2010-01-14 Thread Frank Herrick
http://www.dfbls.az.gov/UserFiles/file/ofm/budgetannouncement.pdf ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to:

RE: Arizona State Fire Marshal

2010-01-14 Thread Smith, David (VFD)
From another list. Division News from Arizona - Suspension of State Fire Marshal Programs By: Arizona Fire Chiefs Association http://www.dailydispatch.com/editorials.asp?authorid=30 Published: 1/8/2010 The Arizona Office of the State Fire Marshal has immediately suspended several

Re: mixed systems

2010-01-14 Thread Roland Huggins
Anyone want to venture a guess on whether water flowing through 2 systems is more or less hydraulically demanding than that flowing through one? Granted you could have a case where a higher hazard in a relatively small area is centered between systems that MIGHT be more demanding with two

RE: mixed systems

2010-01-14 Thread Dewayne Martinez
Thanks Roland, I guess I wasn't that clear in my statement but my thoughts were along the lines of the annex material you pointed out. Dewayne -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Roland Huggins

RE: mixed systems

2010-01-14 Thread Thom McMahon
If I'm remembering it correctly the statement was that someone had them calc. the area between two Deluge systems that were not separated by walls on the assumption that a fire in that area would set off both systems at the same time. This is similar to NAVFAC hangers with Deluge systems where

RE: mixed systems

2010-01-14 Thread Chris Cahill
Please note I am not arguing the big picture. One really, really should calc the most demanding area no matter how many systems it may or may not cross. My point was the standard was deficient in really small systems within the area of a larger system. Even if the area is bound by walls it

Re: mixed systems

2010-01-14 Thread Roland Huggins
agreed but that is a different animal and we're hunting wwwabbit Roland On Jan 14, 2010, at 9:09 AM, Thom McMahon wrote: If I'm remembering it correctly the statement was that someone had them calc. the area between two Deluge systems that were not separated by walls on the assumption

RE: mixed systems

2010-01-14 Thread Thom McMahon
This is the comment I was referring too! Yes it is a coyote and not a rabbit, but this started the whole multi system calc. stuff. (By the way I'm agreeing with you, in case that doesn't come thru) Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488

In-rack system zoning

2010-01-14 Thread Fletcher, Ron
We have 65,000 sqft of rack storage that requires in-rack sprinklers. The racks span an area that is protected by 4 roof systems. Can we use a single system to supply the in-rack and have all 65,000 sqft on a single valve? I thought that I read somewhere once upon a time that in-rack systems had

Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread å . . . . . . .
For jurisdictions facing budget cuts in their fire prevention departments, consider a document framed in 1995 by the US Fire Administration and conceived by Eric Schmidt, then FPE with Prince George's County Maryland. The 80 page document provides a method whereby residential sprinkler

RE: Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread Chris Cahill
Good to remind all of this. I was not part of the development but did review it around that time. I found it to be rather good. The math was sound for the time. What I mean is this was before the 0.05 and the modern crop of res heads so I can't swear the GPM and pressures are the same. Why

Re: In-rack system zoning

2010-01-14 Thread Jim Z
The way I understand it 40,000 sf is your limit. * 8.2.1 *The maximum floor area on any one floor to be protected by sprinklers supplied by any one sprinkler system riser or combined system riser shall be as follows: (3) Extra hazard (a) Pipe schedule — 25,000 ft2 (2323 m2) (b) Hydraulically

RE: In-rack system zoning

2010-01-14 Thread Fletcher, Ron
Would the 40,000 sqft limit apply to the area including the aisles? Of the 65,000 sqft of area the racks cover only about half is actually rack. So if there is only 32,500 sqft. of rack one system should do it? 13 doesn't address the issue (that I can find) and maybe that's why. I thought I read

Re: In-rack system zoning

2010-01-14 Thread Travis Mack, SET
Ron: i remember reading the same thing and it did include the rack aisles. I will try to find it. T On 1/14/2010 1:10 PM, Fletcher, Ron wrote: Would the 40,000 sqft limit apply to the area including the aisles? Of the 65,000 sqft of area the racks cover only about half is actually rack. So

RE: In-rack system zoning

2010-01-14 Thread Craig.Prahl
8.13 In-Rack Sprinklers. 8.13.1 System Size. The area protected by a single system of sprinklers in racks shall not exceed 40,000 ft2 (3716 m2) of floor area occupied by the racks, including aisles, regardless of the number of levels of in-rack sprinklers. Craig L. Prahl, CET Fire

Re: In-rack system zoning

2010-01-14 Thread Jim Z
craig, Good find. I just found that and almost hit send -Jim On Thu, Jan 14, 2010 at 2:18 PM, craig.pr...@ch2m.com wrote: 8.13 In-Rack Sprinklers. 8.13.1 System Size. The area protected by a single system of sprinklers in racks shall not exceed 40,000 ft2 (3716 m2) of floor area occupied

RE: In-rack system zoning

2010-01-14 Thread Fletcher, Ron
Thanks Craig. I must have read right past that two or three times this morning. I need a vacation. Ron -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Thursday, January 14, 2010

RE: In-rack system zoning

2010-01-14 Thread Craig.Prahl
When I've had multiple roof zones with extensive racking I'll feed the racks in roof area A off of the adjacent roof area B's riser. Then serve B's racks off of A's roof system riser. Reasoning for this is that if you had an impairment in system A you only impact one system, either the roof

RE: In-rack system zoning

2010-01-14 Thread Fletcher, Ron
That's a good idea. If it doesn't cost too much in the way of bulk pipe I may give it a try. Ron F -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of craig.pr...@ch2m.com Sent: Thursday, January 14, 2010 1:25

Definition

2010-01-14 Thread Karen Purvis
Can anyone give me a definition of indicating shut-off valve. My guess is that it is an OS Y but don't know. Karen Purvis Senior Designer Facility Systems Consultants 713 South Central Street, Suite 101 Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084

RE: Definition

2010-01-14 Thread Craig.Prahl
Not necessarily. Ball Valves and butterfly valves can be considered indicating valves due to the fact that either by the position of the handle or the flag on the actuator, their position can be determined. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL

RE: Definition

2010-01-14 Thread Rod DiBona
Any valve that has an indicating device where you can tell if it is open or closed by looking. OSY would be one as with others. Rod DiBona Rapid Fire -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Karen

RE: Definition

2010-01-14 Thread Jim Kettler
An OSY is one type of indicating valve. A Post Indicating Valve (PIV) would also fall into that category. It wouldn't HAVE to specifically be an Outside Stem/Screw and Yoke valve. The indicating portion would be signage as part of the valve showing OPEN or SHUT/CLOSED or some other means to

RE: Definition

2010-01-14 Thread Karen Purvis
Yes this answered the question, which of course was the answer I thought but was prompted to ask anyway. Thanks all. Karen Purvis Senior Designer Facility Systems Consultants 713 South Central Street, Suite 101 Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084 -Original Message- From:

Sidewall with a 12 throwback?

2010-01-14 Thread Carrol Glimstad
Does anyone know of a sidewall sprinkler that is listed for LH with an extended throwback? Needs to cover at least 10 inches behind... Thanks, Carrol A. Glimstad Fire Sprinkler Systems Designer Cosco Fire Protection, Inc. 500 Menlo Drive, Suite 150 Rocklin, CA 95765 Ph: 916.652.1306 Fax:

RE: Definition

2010-01-14 Thread Ken Holsopple (forum)
Mr. Cahill wrote: A ball valve may very well indicate its position but I don't think they are any Listed as a fire sprinkler control valve. I think the 5 second rule is what eliminates them from the Listed variety of a generic indicating valve. For the most part you are correct, but Victaulic

RE: Definition

2010-01-14 Thread Chris Cahill
Good to know, thanks. Chris -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ken Holsopple (forum) Sent: Thursday, January 14, 2010 3:17 PM To: sprinklerforum@firesprinkler.org Subject: RE: Definition Mr.

RE: Definition

2010-01-14 Thread George Church
Or the Milwaukee butterball dating back to the 80's -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris Cahill Sent: Thursday, January 14, 2010 4:13 PM To: sprinklerforum@firesprinkler.org Subject: RE:

RE: Definition

2010-01-14 Thread John Drucker
What does Turkey have to do with it ? -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Thursday, January 14, 2010 4:45 PM To: sprinklerforum@firesprinkler.org Subject: RE: Definition Or

RE: Definition

2010-01-14 Thread Chris Cahill
Ok let me clarify my original statements. I was referring to a lever handled ball valve not being Listed but an indicating valve. I did indeed forget about the ball inside the hybrid butterballs and now see the clone in Victaulic's. (We use plenty of M. BB's so a swift KITA is warranted.) Hey

RE: Definition

2010-01-14 Thread Ken Holsopple (forum)
Yep...but the Butterball has a disc. It's not a ball valve, but is a listed indicating control valve. What do I win? Best Regards, Ken Holsopple -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George

Re: Definition

2010-01-14 Thread Charles Thurston
Hello Ken, You WON Left over Christmas fruit cake. Thursday, January 14, 2010, 5:00:11 PM, you wrote: Yep...but the Butterball has a disc. It's not a ball valve, but is a listed indicating control valve. What do I win? Best Regards, Ken Holsopple -Original Message-

RE: Definition

2010-01-14 Thread Craig.Prahl
I was referring to the ball valves such as the Vic 728's with the indicator flag. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439

RE: Definition

2010-01-14 Thread George Church
Move East where its warmer and yes it IS time to go home now and Ken will provide SKITA at no charge to the employee. We could use a nice PE to kick around ;) I checked my iPhone to see if it WAS warmer here tan there today (figured you're about same as Fargo) and indeed, we're 39*F now.

Re: Definition

2010-01-14 Thread Ron Greenman
It's been unseasonably warm here at the latitude 1 degree north of Fargo getting into the fifties each day and staying in the mid --forties at night. Turkey, by the way, since Craig asked, is a country that occupies all of the Anatolian Peninsula, sometimes known as Asia Minor but I don't know

Re: Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread Ron Greenman
I reviewed this about ten years ago and I found the concept to be good but there were many anomalies in the execution that put me off. I don't recall what the exact issues were but the taste they left in my mouth drove me back to 13D exclusively. On the other hand the rule of thumb or schedule

Re: Definition

2010-01-14 Thread Todd Williams
You can't all leave yet, I just got here! The Butterball is an indicating turkey that pops up when done. If ignored, it could potentially set off the residential sprinkler system (in PA). At 05:43 PM 1/14/2010, you wrote: It's been unseasonably warm here at the latitude 1 degree north of

Re: Definition

2010-01-14 Thread Ron Greenman
Only if it gets smokey. On Thu, Jan 14, 2010 at 3:04 PM, Todd Williams t...@fpdc.com wrote: You can't all leave yet, I just got here! The Butterball is an indicating turkey that pops up when done. If ignored, it could potentially set off the residential sprinkler system (in PA). At 05:43

RE: Definition

2010-01-14 Thread Thom McMahon
Speaking OF residential sprinkler systems in PA or anywhere else for that matter, the 5 sec. slow close is code specific. You won't find it in 13D because a ball valve is not required to be listed for 13D, but still can indicate. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box

RE: Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread Jim Johnston
We had this very discussion at work yesterday. If Washington State were actually successful in adopting the IRC as it reads I personally don't believe there are enough sprinkler companies to do the work as conventional (bid, design, permit, then install and test). We discussed how electricians

Re: Definition

2010-01-14 Thread Ron Greenman
And a ball valve that's part of a listed assembly, even if you would otherwise need a slow close valve like for a main drain, is OK. On Thu, Jan 14, 2010 at 3:23 PM, Thom McMahon tmcma...@firetechinc.com wrote: Speaking OF residential sprinkler systems in PA or anywhere else for that matter,

Re: Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread Ron Greenman
Or sadly, one of their children. On Thu, Jan 14, 2010 at 3:40 PM, Jim Johnston j...@inlandfireprotection.com wrote: We had this very discussion at work yesterday.  If Washington State were actually successful in adopting the IRC as it reads I personally don't believe there are enough sprinkler

Re: Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread bverhei
All: Was this guide written to before or after the 13-D committee added the min gpm/sf requirement? Yours, Bruce Verhei - Original Message - From: Ron Greenman rongreen...@gmail.com To: sprinklerforum@firesprinkler.org Sent: Thursday, January 14, 2010 3:49:02 PM GMT -08:00

Re: Fire Departments - Inspection of residential systems faster, but just as sure...

2010-01-14 Thread Ron Greenman
As far as I know this was written before there were any residential heads except Omegas and the calcs are based on the 0.04 density. On Thu, Jan 14, 2010 at 5:04 PM, bver...@comcast.net wrote: All: Was this guide written to before or after the 13-D committee added the min gpm/sf