10" pipe with 1.0 CRR

2017-08-11 Thread Dewayne Martinez
Anyone know of 10in non-sch40 pipe that has a CRR of 1? Have a project where the EOR is insisting on this. They also have a 100lb maximum point load per hanger…..but that is a conversation for another day! Thanks, Dewayne Martinez Fire Protection Design Manager *TOTAL** Mechanical* *Buil

RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Mike Stossel
It has always been my understanding that the corrosion resistance ratio benchmark of (1) is based on threaded schedule 40 steel, so I believe any other pipe type would have a better or worse ratio, but not the same. Mike Stossel SET [400dpiLogoCropped] 36 Barren Road East Stroudsburg, PA 18302 O

Re: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Mark . Phelps
Isn't the CRR based on the actual remaining wall thickness at the root of the first exposed thread outside of a fitting? So if you're not threading it, it should theoretically have a CRR greater than 1.0. Also, I believe the term Standard wall pipe in 10" diameter refers to schedule 30. Mark at

RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Richard Carr
I thought that as a manufacturing standard all steel pipe regardless of schedule had to have a CRR of 1 or greater. Richard Carr, SET Branch Manager Cox Fire Protection, Inc 6555 Grace Lane. Jacksonville, Fl. 32205 rc...@coxfire.com 904-781-8227 From: Sprinklerforum [mailto:sprinklerforum-boun..

Obstructed construction

2017-08-11 Thread Zachary Siegrist
I thought I was clear on this definition but I have an FPE and a technical representative from a fire sprinkler manufacturer stating they are not concerned with the opening of cross section area in regards to the 70 % stipulation in the definitions. They have stated they are only concerned about t

Heat trace power

2017-08-11 Thread fpdcdesign
Anything special needed for monitoring power to heat trace? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell) ___ Sprinklerforum mailing list Sp

Re: Obstructed construction

2017-08-11 Thread Roland Huggins
You are both right (but you are molter right). BOTH conditions determine the classification. The 70% is in the definition (3.7.2) and the depth the solid portion of the structure; member protrudes down from the ceiling is in the annex. Roland Huggins, PE - Senior VP Engineering American Fi

RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Dewayne Martinez
We can only find cut sheets for 10” sch 40 that show a CRR of 1.0 We have reached out to our suppliers and they have nothing either and the EOR wants a cut sheet…. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Richard Carr *Sent:* Friday, August

RE: [EXTERNAL] RE: 10" pipe with 1.0 CRR

2017-08-11 Thread Kyle . Montgomery
The CRR (corrosion resistance ratio) is solely based on wall thickness: CRR = (X / Y)^3 Where: X is the thickness of the pipe in question at the first exposed thread OR THINNEST WALL SECTION FOR UNTHREADED PIPE. And Y is the thickness of schedule 40 pipe under the first exposed thread. So if

Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Dewayne Martinez
I had a AHJ question recently why we didn’t have hangers on our branch lines coming off the backside of the main. They are 2 ½” supplying one sprinkler and are 36” long. I was taught to use the lengths specified in 9.2.3.4.1 (unsupported lengths) and consider my main pipe as the “hanger” required

Re: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Mark Phillips
With that size I'm guessing you have a pump Then unsupported can't be more than 12". Sent from my Verizon 4G LTE Droid On Aug 11, 2017 12:13 PM, Dewayne Martinez wrote: I had a AHJ question recently why we didn’t have hangers on our branch lines coming off the backside of the main. They are 2 ½

RE: [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Kyle . Montgomery
Well, if they are only supplying one head, then “technically” they are an armover, right? Are they attached directly to the main, or on a tee at the top of a riser nipple? -Kyle M From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Dewayne Martinez Sent: F

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Kyle . Montgomery
Not true. The "over 100 psi" issue is only a factor when you have pipe above the ceiling feeding sprinklers below a ceiling. If it is an exposed condition with uprights or pendents on the line, then the presence of a pump is not relevant. -Original Message- From: Sprinklerforum [mailto:

RE: [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Dewayne Martinez
It’s comes off the tee on a RN. The sprinkler is a upright. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of * Kyle.Montgomery *Sent:* Friday, August 11, 2017 11:17 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* RE: [EXTERNAL] Outrigger B

Re: Heat trace power

2017-08-11 Thread Charles Thurston
Hello Fpdcdesign, The one time I did heat trace, the controller had trouble contacts for remote monitoring. Friday, August 11, 2017, 10:07:21 AM, you wrote: Anything special needed for monitoring power to heat trace? Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-53

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Steve Leyton
What I’ve always tried to do in that situation was put the main on the “in” side of the truss or beam it was hanging from, pass the tail-backs under the same member and catch a hanger on the “out” side. If the pipe to the last sprinkler had to be longer, just increase the pipe size. Steve L F

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Dewayne Martinez
Makes perfect sense Steve, thanks. *From:* Sprinklerforum [mailto: sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Steve Leyton *Sent:* Friday, August 11, 2017 11:33 AM *To:* sprinklerforum@lists.firesprinkler.org *Subject:* RE: Outrigger BL off mains - NFPA 13 (07ed) What I’ve

Re: Obstructed construction

2017-08-11 Thread Zachary Siegrist
Thank you. Further clarification...the manufacturer is stating in conjunction with an FPE that since its a special listed head, the 70 percent open cross section is irrelevant ( and therefore ignored) since it's listing allows it to throw within a six inch open space. I have never heard this befo

RE: [EXTERNAL] Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Kyle . Montgomery
Then I think you should be able to use the section you are referring to and have a maximum unsupported length of 60”. Is it a welded branch line? That make it a little bit easier sell than if it’s threaded with individual segments. From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.fires

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Bob
I have always considered those to be armovers. Technically, 13 says armovers are off of branch lines, but it seems a stretch to me not to include a short branch line off of the main with a single sprinkler not to be an armover. Bob Knight, CET III 208-318-3057 From: Sprinklerforum [mail

Fabric ventilation ducts

2017-08-11 Thread David Bitton
Can someone provide me with insight regarding the applicable obstruction rules for ventilation ducts made of fabric? It seems that the issues are not the same as metal ducts but I cannot find any reference in NFPA 13 that addresses these ducts as being different. Thanks, David Bitton, in

RE: Outrigger BL off mains - NFPA 13 (07ed)

2017-08-11 Thread Bob
To further muddy the waters, the Annex shows examples of armovers and uses the wording “branch line or cross main”. Thank you, Bob Knight, CET III 208-318-3057 From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Bob Sent: Friday, August 11, 2017

RE: Fabric ventilation ducts

2017-08-11 Thread Byron Weisz
Our experience with fabric - retraceable ducts is that the same obstruction rules apply as hard duct, especially when dealing with ESFR sprinklers [ccfs_LOGO (2)] Byron Weisz Cen-Cal Fire Systems, Inc. P.O. Box 1284 Lodi, CA 95241 Phone (209) 334-9119 Fax (209) 334-2923 by...@cen-calf

Sammy vs CSR

2017-08-11 Thread Bob
When using Sammy screws (or similar product) is it the intent of NFPA 13 to have the sammy screw follow the same guidelines as a CSR? Thank you, Bob Knight, CET III 208-318-3057 FBK-LOGO-SMALL ___ Sprinklerforum mailing list Sprinklerforum@l

RE: Sammy vs CSR

2017-08-11 Thread John Denhardt
I do not believe so. I would follow the LISTED products installation literature which should replace the requirements of NFPA 13. John August Denhardt, P.E. Strickland Fire Protection Incorporated 4011 Penn Belt Place Forestville, Maryland 20747-4737 301.474.1136 - Office 301.343.1457 - Mobile