#x27;s upstream Gus. I'm just trying to help Craig get out of the (if Mr.
> Greenman will pardon my French) Remote Area with the calc software he has.
>
> :)
>
> Brad
>
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
> On Behal
@lists.firesprinkler.org
Subject: Re: spray bar versus deluge heads for opening protection [EXTERNAL]
Why not a large orifice sidewall at each side of each trailer?
Going back to objectives, and what is not objective. Writing it out helps, at
least me.
1. Goal is not to protect trailer or
f the (if Mr.
> Greenman will pardon my French) Remote Area with the calc software he has.
>
> :)
>
> Brad
>
> -Original Message-
> From: Sprinklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler.
> org]
>
> On Behalf Of Gus Olson
> Sent: Monday, September 19, 2016 1
rum-boun...@lists.firesprinkler.org]
> On Behalf Of rongreenman .
> Sent: Monday, September 19, 2016 8:50 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Re: spray bar versus deluge heads for opening protection
>
> Why not just put a barrel of water on top of keg of black p
...@lists.firesprinkler.org] On
Behalf Of rongreenman .
Sent: Monday, September 19, 2016 11:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: spray bar versus deluge heads for opening protection [EXTERNAL]
Why not just put a barrel of water on top of keg of black powder with a fuse
going into the
, 2016 8:50 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: spray bar versus deluge heads for opening protection
Why not just put a barrel of water on top of keg of black powder with a fuse
going into the trailer?
On Mon, Sep 19, 2016 at 8:47 AM, Brad Casterline
mailto:bcasterl
] On
Behalf Of Gus Olson
Sent: Monday, September 19, 2016 11:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: spray bar versus deluge heads for opening protection [EXTERNAL]
Brad,
Don't forget to add a strainer
Gus Olson
-Original Message-
From: Sprinkler
alf Of Brad Casterline
> Sent: Monday, September 19, 2016 11:30 AM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: RE: spray bar versus deluge heads for opening protection
>
> P = 40 PSI
> K = 1.55
> Q = 9.8 GPM
>
> 36 GPM / 9.8 = 3.67 holes per nozzle
>
> call i
Olson
Sent: Monday, September 19, 2016 10:37 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: spray bar versus deluge heads for opening protection
Brad,
Don't forget to add a strainer
Gus Olson
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesp
016 9:57 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: spray bar versus deluge heads for opening protection
Dude, you need serious help. HAHA
Now how many average sprinkler designers could have figured that out?
But it has to equal the discharge of spray nozzles which are requir
@lists.firesprinkler.org
Subject: RE: spray bar versus deluge heads for opening protection
Dude, you need serious help. HAHA
Now how many average sprinkler designers could have figured that out?
But it has to equal the discharge of spray nozzles which are required to
provide a minimum of 36 gpm at 40
nsion 77540
craig.pr...@ch2m.com
-Original Message-
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of mphe...@aerofire.com
Sent: Monday, September 19, 2016 10:52 AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: spray bar versus deluge head
AM
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: spray bar versus deluge heads for opening protection [EXTERNAL]
(.25/24)^2 * PI = .000314 ft^2
assume coefficient of discharge of .9
.000314 *.9 = .000283
'imply' 7 PSI
7 / .433 = 16.167 (h)
v = (2gh)^.5 = 32.266 ft/sec
32.
Why wouldn't you just install a one hour rated door at the opening held open by
a fusible link. When they have a fire in the pallet trailer, it would probably
take 10 minutes to pick it with a dolly and move it to a safe location away
from the dock. Or 20 minutes to become a smoldering pile of a
(.25/24)^2 * PI = .000314 ft^2
assume coefficient of discharge of .9
.000314 *.9 = .000283
'imply' 7 PSI
7 / .433 = 16.167 (h)
v = (2gh)^.5 = 32.266 ft/sec
32.266 ft/sec * .000283 ft^3 = .00913 ft^3/sec, * 7.48 * 60 = 4.1 GPM
Q = 4.1
P = 7.0
K = 1.55
Brad
-Original Message-
From: Sprin
I would ask them how that is a listed discharge device required per NFPA.
If you can get past that, I would just ask what is the minimum flow and
pressure they require at the point of connection to that pipe. It sounds like
they have done this before.
Travis Mack, SET