Re: [WISPA] Remote Powered Access Pont

2008-11-21 Thread Chuck McCown - 3
One source:
http://tnrbatteries.com/genesis.html

- Original Message - 
From: Chuck McCown - 3 [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Thursday, November 20, 2008 10:12 PM
Subject: Re: [WISPA] Remote Powered Access Pont


 http://www.enersysreservepower.com/documents/US-GPL-AM-003_0906.pdf

 Genesis pure lead EP or XE version will work down to -40.
 They are rated for 100% depth of discharge.  Repeatedly.  400 times.
 And can come back from 100% discharge at -40 to be fully charged.
 They are good for 2 years sitting on the shelf totally unused.
 I don't know of any other battery that can do that.

 They also have most of their energy available at super cold temperatures,
 where flooded cells lose most of their energy when cold.
 But you will pay 2 to 3 times more than for a Trojan.

 I figure everything by watt hour first.  So you need 5 watts * 24 hours * 
 30
 days = 3600 watt hours.
 At 30 cents per watt hour, you will end up paying more than $1000 for that
 battery.  Hopefully you can shop around and find them for less.  I used to
 pay 20 cents.  I don't know why they went up so much.

 Watt hours / system voltage = amp hours
 3600/12=300 amp hours.

 One of our supervisors recently found a good price (if you can call it 
 good)
 for the gates/hawker/enersys batteries.
 If I can find the source I will post it.

 - Original Message - 
 From: rabbtux rabbtux [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 8:27 PM
 Subject: Re: [WISPA] Remote Powered Access Pont


 Thanks for the great info Chuck!  Almost made the trojan battery mistake.
 what exactly is the battery technology and brand you suggest?  if I have 
 a
 5
 watt system you suggest a 120W  solar panel.  Also 30 days or 360AH of
 usable capacity at 12V?

 Thanks for  the clarification, and the pics that make your experience
 clear!

 On Wed, Nov 19, 2008 at 7:38 PM, Chuck McCown - 3 [EMAIL PROTECTED]
 wrote:

 At 60% depth of discharge they freeze at 0F.  Once frozen they are dead.
 Liquid electrolyte batteries need to be liquid to work.
 Not to mention the risk of a broken case. (You most likely mean you try
 to
 avoid taking them below 40% DOD, but 60% has a nice freezing point to
 exploit for purposes of rhetoric).

 Trojans were designed for the cabin with the fireplace and the
 intermittent
 use of the residential solar application.(Really, they were designed
 for
 golf carts).

 Constant load, constant nightly cycling, periods of no charging and deep
 discharge during the coldest days of the year is a different application
 and
 takes a different battery technology.

 Here is a good VLRA white paper on the temperature issue:
 http://www.cdtechno.com/custserv/pdf/7953.pdf

 We use VLRAs inside central offices where there is HVAC.  Not in the
 field.
 And they are much better than flooded cells like the T-105

 AGMs go in the field. And for solar only a few types of AGMs can be
 trusted.

 This app note is full of lots of good info.  It is on the batts we use
 that
 will still deliver 40% of their power at -40 degrees.
 http://www.enersysreservepower.com/documents/US-GPL-AM-003_0906.pdf

 But the only really important point is that in a solar situation, where
 you
 have weather and you have low temps, very few batteries will totally
 recover
 from an extreme deep discharge.  And that happens all the time when
 people
 scrimp on their battery capacity and solar panel capacity.

 20X watts 30 days autonomy = you will sleep all winter long.
   - Original Message -
  From: Blair Davis
  To: WISPA General List
   Sent: Wednesday, November 19, 2008 7:56 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  Ok.  our answer to that problem has always been to double up on our
 total
 battery size so we never discharge them below 60%

  Sounds like you are in a much more inaccessible environment than we 
 are!
  And in that kind of location, I'd likely be looking for the same thing.

  But, for us, inaccessibility won't last more than a week or so...

  Chuck McCown - 3 wrote:
 We buy batts that are rated to give you the energy down to -20F.
 Survive being at-20F while discharged to a stone cold state.
 And recover when the next available bit of sunlight hits the panel
 (perhaps
 days later).
 And last 2000 cycles.
 For that you pay 30 cents per watt hour.  And can sleep at night.
 (we used to get these for 20 cents, I don't know why they are so much
 more
 now)

 I just found a website selling a T-105 for $160\each
 6 volts, 225 aH  That comes to 11.8 cents per watt hour.

 The Trojan website says avoid locations where freezing temperatures are
 expected.
 It also says the must be kept fully charged when freezing.  Hard to do
 with
 solar on a mountain top.


 http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

 So, if you have a nice warm place to keep the trojans then they are a
 very
 good value.
 (assuming

Re: [WISPA] Remote Powered Access Pont

2008-11-21 Thread John Thomas
Depending on where this is, you may be able to mount a small wind generator.

http://www.solardyne.com/air403wingen.html

John



Chuck McCown - 3 wrote:
 I would use a 100 watt panel minimum.
 And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour 
 battery
 If you are running a 24 volt system then you need 3600/24=150 aH battery.
 If you are running a 12 volt system, you need a 300 aH battery.

 You will pay about 30 cents per watt hour for a battery.  So $1080 for the 
 battery.
 You will pay about $5/watt for the panel, so $500 for the panel.
 Charge controllers are about $100 or less.

 If you build it this way it will always work.  You can put in half the 
 battery for half the price.  But then you have only two weeks of insurance 
 against bad weather.

 Never ever go below 10X the load for the panel, that will just barely cut it 
 in the sunniest of climates.
 Even then you will probably have to put in a back up generator and you will 
 be cycling the crap out of your batts causing them to only last a couple of 
 years.

 If you want 99.999% reliability you have to use a panel 24X the size of the 
 load (unless you have a tracking mount, then you can reduce that).
 I try to always use 20X panels and no less than a 2 week battery.  But even 
 then, a week or two of snow on the panels and gray skies every day can cause 
 an outage.


 - Original Message - 
 From: Scott Parsons [EMAIL PROTECTED]
 To: 'WISPA General List' wireless@wispa.org
 Sent: Wednesday, November 19, 2008 5:33 PM
 Subject: [WISPA] Remote Powered Access Pont


   
 I'm looking into setting up a remote access point/repeater.
 Power requirements are 5W. No access to grid power.

 I was curious what you guys use for this type of thing?
 I figure I need a 30W solar panel, controller, battery and enclosure.
 How much should I expect to pay for a setup?
 Is there anything available off the shelf?

 Thanks for your help.
 Scott



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/

 



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/



   




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Randy Cosby
We recently visited a solar-powered site that had a supplementary 
wind-generation system.  Seemed to work well for them to have wind power 
when the weather is bad, solar when it is good.  Pretty windy place as well.

Chuck McCown - 3 wrote:
 Here is a note I posted several days ago on the Motorola list about solar 
 powering.

 From: Chuck McCown [mailto:[EMAIL PROTECTED]
 Sent: Friday, November 14, 2008 9:17 AM
 To: Dave Crim
 Subject: Re: solar



 Continuing on a bit, lets say you have 5 lousy days and one good sunny day 
 followed by 5 more lousy days.  That one sunny day needs to store enough to 
 charge the batts totally.  75 watts * 5 days * 24hours * 1.25 (batter 
 efficiency loss) + (75watts  * 24 hours) current day = 13050 watt hours.

 To make 13050 watt hours in one 10 hour day  you go:

 13050/.707*10=1845 watts.  You need 1845 watts of panel to do this.  That is 
 24 times the load.

 So, my rule of thumb of 20 times the load is still a little shy of being 
 conservative.



 The thing that saves you in a situation like this is a massive battery.  A 
 one month battery with 20 X panels will never fail due to a lack of sun 
 energy.

 A 2 week battery and 10X panels will fail now and then every single winter. 
 Sometimes for several days at a time.

   - Original Message - 

   From: Chuck McCown

   To: [EMAIL PROTECTED]

   Sent: Friday, November 14, 2008 9:09 AM

   Subject: solar



   Several thing you may not be including.

   Assuming this panel is somewhere in this neck of the woods, December 21 
 has 10 hours of time between runrise and sunset.

   But if you don't have tracking mounts (most don't) the amount of energy 
 you get out of a panel follows the first half of a sine wave.

   To estimate that energy, you integrate the area under the curve.  That 
 will equal .707 of what you thought you were going to get.



   So, let's say you put up a 500 watt panel, your daily sunny output will be 
 an average of 353 watts.  The sun shines for 10 hours solid and you store 
 3530 watt hours in your battery.  Now your load is on during the daytime, so 
 if you have a 75 watt load, you are now able to make 278 watts.  You are 
 down to 2780 watt hours.  You put in 2780 watt hours into a battery and you 
 get maybe 80% back out.  So you have 2224 watt hour available (if you drain 
 the batts which is not good for them).



   You have 14 hours of darkness and actually more like 16 hours before the 
 panel starts making any useful amount of energy.  16*75=1200 watt hours.

   But that next day is not sunny, there is frost and a light coating of 
 snow.  The whole works dies 16 hours later.  About 9 pm.



   One other note, you only want to draw your batteries down no more than 10% 
 each night or they won't last long.  That means a minimum of 12000 watt 
 hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24 volt 
 system, 500 amp hours.  And that is a minimum because here we get a week 
 with snow and ice and no sun easy, sometimes two weeks.



   You really need a generator, less load, or a whole bunch more batts and 
 panels.



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
   

-- 
Randy Cosby
Vice President
InfoWest, Inc

office: 435-773-6071





WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Chuck McCown
They must not be subject to ice storms.

- Original Message - 
From: Randy Cosby [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Thursday, November 20, 2008 10:22 AM
Subject: Re: [WISPA] Remote Powered Access Pont


 We recently visited a solar-powered site that had a supplementary
 wind-generation system.  Seemed to work well for them to have wind power
 when the weather is bad, solar when it is good.  Pretty windy place as 
 well.

 Chuck McCown - 3 wrote:
 Here is a note I posted several days ago on the Motorola list about solar
 powering.

 From: Chuck McCown [mailto:[EMAIL PROTECTED]
 Sent: Friday, November 14, 2008 9:17 AM
 To: Dave Crim
 Subject: Re: solar



 Continuing on a bit, lets say you have 5 lousy days and one good sunny 
 day
 followed by 5 more lousy days.  That one sunny day needs to store enough 
 to
 charge the batts totally.  75 watts * 5 days * 24hours * 1.25 (batter
 efficiency loss) + (75watts  * 24 hours) current day = 13050 watt hours.

 To make 13050 watt hours in one 10 hour day  you go:

 13050/.707*10=1845 watts.  You need 1845 watts of panel to do this.  That 
 is
 24 times the load.

 So, my rule of thumb of 20 times the load is still a little shy of being
 conservative.



 The thing that saves you in a situation like this is a massive battery. 
 A
 one month battery with 20 X panels will never fail due to a lack of sun
 energy.

 A 2 week battery and 10X panels will fail now and then every single 
 winter.
 Sometimes for several days at a time.

   - Original Message - 

   From: Chuck McCown

   To: [EMAIL PROTECTED]

   Sent: Friday, November 14, 2008 9:09 AM

   Subject: solar



   Several thing you may not be including.

   Assuming this panel is somewhere in this neck of the woods, December 21
 has 10 hours of time between runrise and sunset.

   But if you don't have tracking mounts (most don't) the amount of energy
 you get out of a panel follows the first half of a sine wave.

   To estimate that energy, you integrate the area under the curve.  That
 will equal .707 of what you thought you were going to get.



   So, let's say you put up a 500 watt panel, your daily sunny output will 
 be
 an average of 353 watts.  The sun shines for 10 hours solid and you store
 3530 watt hours in your battery.  Now your load is on during the daytime, 
 so
 if you have a 75 watt load, you are now able to make 278 watts.  You are
 down to 2780 watt hours.  You put in 2780 watt hours into a battery and 
 you
 get maybe 80% back out.  So you have 2224 watt hour available (if you 
 drain
 the batts which is not good for them).



   You have 14 hours of darkness and actually more like 16 hours before 
 the
 panel starts making any useful amount of energy.  16*75=1200 watt hours.

   But that next day is not sunny, there is frost and a light coating of
 snow.  The whole works dies 16 hours later.  About 9 pm.



   One other note, you only want to draw your batteries down no more than 
 10%
 each night or they won't last long.  That means a minimum of 12000 watt
 hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24 volt
 system, 500 amp hours.  And that is a minimum because here we get a week
 with snow and ice and no sun easy, sometimes two weeks.



   You really need a generator, less load, or a whole bunch more batts and
 panels.



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/


 -- 
 Randy Cosby
 Vice President
 InfoWest, Inc

 office: 435-773-6071




 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Randy Cosby
Good point :)  It's not too severe down here in So Utah.

Randy


Chuck McCown wrote:
 They must not be subject to ice storms.

 - Original Message - 
 From: Randy Cosby [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 10:22 AM
 Subject: Re: [WISPA] Remote Powered Access Pont


   
 We recently visited a solar-powered site that had a supplementary
 wind-generation system.  Seemed to work well for them to have wind power
 when the weather is bad, solar when it is good.  Pretty windy place as 
 well.

 Chuck McCown - 3 wrote:
 
 Here is a note I posted several days ago on the Motorola list about solar
 powering.

 From: Chuck McCown [mailto:[EMAIL PROTECTED]
 Sent: Friday, November 14, 2008 9:17 AM
 To: Dave Crim
 Subject: Re: solar



 Continuing on a bit, lets say you have 5 lousy days and one good sunny 
 day
 followed by 5 more lousy days.  That one sunny day needs to store enough 
 to
 charge the batts totally.  75 watts * 5 days * 24hours * 1.25 (batter
 efficiency loss) + (75watts  * 24 hours) current day = 13050 watt hours.

 To make 13050 watt hours in one 10 hour day  you go:

 13050/.707*10=1845 watts.  You need 1845 watts of panel to do this.  That 
 is
 24 times the load.

 So, my rule of thumb of 20 times the load is still a little shy of being
 conservative.



 The thing that saves you in a situation like this is a massive battery. 
 A
 one month battery with 20 X panels will never fail due to a lack of sun
 energy.

 A 2 week battery and 10X panels will fail now and then every single 
 winter.
 Sometimes for several days at a time.

   - Original Message - 

   From: Chuck McCown

   To: [EMAIL PROTECTED]

   Sent: Friday, November 14, 2008 9:09 AM

   Subject: solar



   Several thing you may not be including.

   Assuming this panel is somewhere in this neck of the woods, December 21
 has 10 hours of time between runrise and sunset.

   But if you don't have tracking mounts (most don't) the amount of energy
 you get out of a panel follows the first half of a sine wave.

   To estimate that energy, you integrate the area under the curve.  That
 will equal .707 of what you thought you were going to get.



   So, let's say you put up a 500 watt panel, your daily sunny output will 
 be
 an average of 353 watts.  The sun shines for 10 hours solid and you store
 3530 watt hours in your battery.  Now your load is on during the daytime, 
 so
 if you have a 75 watt load, you are now able to make 278 watts.  You are
 down to 2780 watt hours.  You put in 2780 watt hours into a battery and 
 you
 get maybe 80% back out.  So you have 2224 watt hour available (if you 
 drain
 the batts which is not good for them).



   You have 14 hours of darkness and actually more like 16 hours before 
 the
 panel starts making any useful amount of energy.  16*75=1200 watt hours.

   But that next day is not sunny, there is frost and a light coating of
 snow.  The whole works dies 16 hours later.  About 9 pm.



   One other note, you only want to draw your batteries down no more than 
 10%
 each night or they won't last long.  That means a minimum of 12000 watt
 hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24 volt
 system, 500 amp hours.  And that is a minimum because here we get a week
 with snow and ice and no sun easy, sometimes two weeks.



   You really need a generator, less load, or a whole bunch more batts and
 panels.



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/

   
 -- 
 Randy Cosby
 Vice President
 InfoWest, Inc

 office: 435-773-6071




 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/

 



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
   

-- 
Randy Cosby
Vice President
InfoWest, Inc

office: 435-773-6071





WISPA Wants You! Join today!
http://signup.wispa.org

Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Chuck McCown
Wind generators are good if you have plenty of wind and no ice.
Our problem has been that we need their power during the worst weather.
And that is when they fail.  They wear out or get loaded with ice and tear 
apart.

- Original Message - 
From: Randy Cosby [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Thursday, November 20, 2008 11:04 AM
Subject: Re: [WISPA] Remote Powered Access Pont


 Good point :)  It's not too severe down here in So Utah.

 Randy


 Chuck McCown wrote:
 They must not be subject to ice storms.

 - Original Message - 
 From: Randy Cosby [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 10:22 AM
 Subject: Re: [WISPA] Remote Powered Access Pont



 We recently visited a solar-powered site that had a supplementary
 wind-generation system.  Seemed to work well for them to have wind power
 when the weather is bad, solar when it is good.  Pretty windy place as
 well.

 Chuck McCown - 3 wrote:

 Here is a note I posted several days ago on the Motorola list about 
 solar
 powering.

 From: Chuck McCown [mailto:[EMAIL PROTECTED]
 Sent: Friday, November 14, 2008 9:17 AM
 To: Dave Crim
 Subject: Re: solar



 Continuing on a bit, lets say you have 5 lousy days and one good sunny
 day
 followed by 5 more lousy days.  That one sunny day needs to store 
 enough
 to
 charge the batts totally.  75 watts * 5 days * 24hours * 1.25 (batter
 efficiency loss) + (75watts  * 24 hours) current day = 13050 watt 
 hours.

 To make 13050 watt hours in one 10 hour day  you go:

 13050/.707*10=1845 watts.  You need 1845 watts of panel to do this. 
 That
 is
 24 times the load.

 So, my rule of thumb of 20 times the load is still a little shy of 
 being
 conservative.



 The thing that saves you in a situation like this is a massive battery.
 A
 one month battery with 20 X panels will never fail due to a lack of sun
 energy.

 A 2 week battery and 10X panels will fail now and then every single
 winter.
 Sometimes for several days at a time.

   - Original Message - 

   From: Chuck McCown

   To: [EMAIL PROTECTED]

   Sent: Friday, November 14, 2008 9:09 AM

   Subject: solar



   Several thing you may not be including.

   Assuming this panel is somewhere in this neck of the woods, December 
 21
 has 10 hours of time between runrise and sunset.

   But if you don't have tracking mounts (most don't) the amount of 
 energy
 you get out of a panel follows the first half of a sine wave.

   To estimate that energy, you integrate the area under the curve. 
 That
 will equal .707 of what you thought you were going to get.



   So, let's say you put up a 500 watt panel, your daily sunny output 
 will
 be
 an average of 353 watts.  The sun shines for 10 hours solid and you 
 store
 3530 watt hours in your battery.  Now your load is on during the 
 daytime,
 so
 if you have a 75 watt load, you are now able to make 278 watts.  You 
 are
 down to 2780 watt hours.  You put in 2780 watt hours into a battery and
 you
 get maybe 80% back out.  So you have 2224 watt hour available (if you
 drain
 the batts which is not good for them).



   You have 14 hours of darkness and actually more like 16 hours before
 the
 panel starts making any useful amount of energy.  16*75=1200 watt 
 hours.

   But that next day is not sunny, there is frost and a light coating of
 snow.  The whole works dies 16 hours later.  About 9 pm.



   One other note, you only want to draw your batteries down no more 
 than
 10%
 each night or they won't last long.  That means a minimum of 12000 watt
 hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24 
 volt
 system, 500 amp hours.  And that is a minimum because here we get a 
 week
 with snow and ice and no sun easy, sometimes two weeks.



   You really need a generator, less load, or a whole bunch more batts 
 and
 panels.



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/


 -- 
 Randy Cosby
 Vice President
 InfoWest, Inc

 office: 435-773-6071




 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/





 
 WISPA Wants You! Join today!
 http://signup.wispa.org

Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread reader
Your panel sizing is right on, but you don't need that much battery cost.

Golf Cart batteries, which are near 200 each, are more than enough for a 12 
volt system.





insert witty tagline here

- Original Message - 
From: Chuck McCown - 3 [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Wednesday, November 19, 2008 4:47 PM
Subject: Re: [WISPA] Remote Powered Access Pont


I would use a 100 watt panel minimum.
 And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour
 battery
 If you are running a 24 volt system then you need 3600/24=150 aH battery.
 If you are running a 12 volt system, you need a 300 aH battery.

 You will pay about 30 cents per watt hour for a battery.  So $1080 for the
 battery.
 You will pay about $5/watt for the panel, so $500 for the panel.
 Charge controllers are about $100 or less.

 If you build it this way it will always work.  You can put in half the
 battery for half the price.  But then you have only two weeks of insurance
 against bad weather.

 Never ever go below 10X the load for the panel, that will just barely cut 
 it
 in the sunniest of climates.
 Even then you will probably have to put in a back up generator and you 
 will
 be cycling the crap out of your batts causing them to only last a couple 
 of
 years.

 If you want 99.999% reliability you have to use a panel 24X the size of 
 the
 load (unless you have a tracking mount, then you can reduce that).
 I try to always use 20X panels and no less than a 2 week battery.  But 
 even
 then, a week or two of snow on the panels and gray skies every day can 
 cause
 an outage.


 - Original Message - 
 From: Scott Parsons [EMAIL PROTECTED]
 To: 'WISPA General List' wireless@wispa.org
 Sent: Wednesday, November 19, 2008 5:33 PM
 Subject: [WISPA] Remote Powered Access Pont


 I'm looking into setting up a remote access point/repeater.
 Power requirements are 5W. No access to grid power.

 I was curious what you guys use for this type of thing?
 I figure I need a 30W solar panel, controller, battery and enclosure.
 How much should I expect to pay for a setup?
 Is there anything available off the shelf?

 Thanks for your help.
 Scott



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/




 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/ 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread reader
Lead acid batteries won't freeze unless discharged more than 50%.

for winter, just insulate them well to shield them from severe temperature 
spikes and make sure you have more charging power than you need, and you're 
good to go.





insert witty tagline here

- Original Message - 
From: Chuck McCown - 3 [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Wednesday, November 19, 2008 6:48 PM
Subject: Re: [WISPA] Remote Powered Access Pont


 We buy batts that are rated to give you the energy down to -20F.
 Survive being at-20F while discharged to a stone cold state.
 And recover when the next available bit of sunlight hits the panel 
 (perhaps days later).
 And last 2000 cycles.
 For that you pay 30 cents per watt hour.  And can sleep at night.
 (we used to get these for 20 cents, I don't know why they are so much more 
 now)

 I just found a website selling a T-105 for $160\each
 6 volts, 225 aH  That comes to 11.8 cents per watt hour.

 The Trojan website says avoid locations where freezing temperatures are 
 expected.
 It also says the must be kept fully charged when freezing.  Hard to do 
 with solar on a mountain top.

 http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

 So, if you have a nice warm place to keep the trojans then they are a very 
 good value.
 (assuming they are in an air conditioned place in the summer too, else 
 they won't last too many summers)

 But most solar powered sites don't have a heater to keep them from 
 freezing and splitting.


  - Original Message - 
  From: Blair Davis
  To: WISPA General List
  Sent: Wednesday, November 19, 2008 7:25 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  What type of battery's are you using?  That price sounds very high.

  4x T-105 will provide 225Ah at 24V for a cost of about $500

  Chuck McCoy's - 3 wrote:
 I would use a 100 watt panel minimum.
 And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour
 battery
 If you are running a 24 volt system then you need 3600/24=150 aH battery.
 If you are running a 12 volt system, you need a 300 aH battery.

 You will pay about 30 cents per watt hour for a battery.  So $1080 for the
 battery.
 You will pay about $5/watt for the panel, so $500 for the panel.
 Charge controllers are about $100 or less.

 If you build it this way it will always work.  You can put in half the
 battery for half the price.  But then you have only two weeks of insurance
 against bad weather.

 Never ever go below 10X the load for the panel, that will just barely cut 
 it
 in the sunniest of climates.
 Even then you will probably have to put in a back up generator and you 
 will
 be cycling the crap out of your batts causing them to only last a couple 
 of
 years.

 If you want 99.999% reliability you have to use a panel 24X the size of 
 the
 load (unless you have a tracking mount, then you can reduce that).
 I try to always use 20X panels and no less than a 2 week battery.  But 
 even
 then, a week or two of snow on the panels and gray skies every day can 
 cause
 an outage.


 - Original Message - 
 From: Scott Parsons [EMAIL PROTECTED]
 To: 'WISPA General List' wireless@wispa.org
 Sent: Wednesday, November 19, 2008 5:33 PM
 Subject: [WISPA] Remote Powered Access Pont


  I'm looking into setting up a remote access point/repeater.
 Power requirements are 5W. No access to grid power.

 I was curious what you guys use for this type of thing?
 I figure I need a 30W solar panel, controller, battery and enclosure.
 How much should I expect to pay for a setup?
 Is there anything available off the shelf?

 Thanks for your help.
 Scott



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/




 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/




 --




  
 
  WISPA Wants You! Join today!
  http://signup.wispa.org/
  
 

  WISPA Wireless List: wireless@wispa.org

  Subscribe/Unsubscribe:
  http://lists.wispa.org/mailman/listinfo/wireless

  Archives: http://lists.wispa.org/pipermail/wireless

Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread reader
I have used a AIR-X for 4 years now.   The blades are a composite plastic 
and the ice WILL NOT stick to them.   I've been there when the pole 
supporting the generator had nearly an inch of ice on it and the antennas 
were all coated too thick to break off, and the genset blades were ice free.

Mark




insert witty tagline here

- Original Message - 
From: Chuck McCown [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Thursday, November 20, 2008 10:13 AM
Subject: Re: [WISPA] Remote Powered Access Pont


 Wind generators are good if you have plenty of wind and no ice.
 Our problem has been that we need their power during the worst weather.
 And that is when they fail.  They wear out or get loaded with ice and tear
 apart.

 - Original Message - 
 From: Randy Cosby [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 11:04 AM
 Subject: Re: [WISPA] Remote Powered Access Pont


 Good point :)  It's not too severe down here in So Utah.

 Randy


 Chuck McCown wrote:
 They must not be subject to ice storms.

 - Original Message - 
 From: Randy Cosby [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 10:22 AM
 Subject: Re: [WISPA] Remote Powered Access Pont



 We recently visited a solar-powered site that had a supplementary
 wind-generation system.  Seemed to work well for them to have wind 
 power
 when the weather is bad, solar when it is good.  Pretty windy place as
 well.

 Chuck McCown - 3 wrote:

 Here is a note I posted several days ago on the Motorola list about
 solar
 powering.

 From: Chuck McCown [mailto:[EMAIL PROTECTED]
 Sent: Friday, November 14, 2008 9:17 AM
 To: Dave Crim
 Subject: Re: solar



 Continuing on a bit, lets say you have 5 lousy days and one good sunny
 day
 followed by 5 more lousy days.  That one sunny day needs to store
 enough
 to
 charge the batts totally.  75 watts * 5 days * 24hours * 1.25 (batter
 efficiency loss) + (75watts  * 24 hours) current day = 13050 watt
 hours.

 To make 13050 watt hours in one 10 hour day  you go:

 13050/.707*10=1845 watts.  You need 1845 watts of panel to do this.
 That
 is
 24 times the load.

 So, my rule of thumb of 20 times the load is still a little shy of
 being
 conservative.



 The thing that saves you in a situation like this is a massive 
 battery.
 A
 one month battery with 20 X panels will never fail due to a lack of 
 sun
 energy.

 A 2 week battery and 10X panels will fail now and then every single
 winter.
 Sometimes for several days at a time.

   - Original Message - 

   From: Chuck McCown

   To: [EMAIL PROTECTED]

   Sent: Friday, November 14, 2008 9:09 AM

   Subject: solar



   Several thing you may not be including.

   Assuming this panel is somewhere in this neck of the woods, December
 21
 has 10 hours of time between runrise and sunset.

   But if you don't have tracking mounts (most don't) the amount of
 energy
 you get out of a panel follows the first half of a sine wave.

   To estimate that energy, you integrate the area under the curve.
 That
 will equal .707 of what you thought you were going to get.



   So, let's say you put up a 500 watt panel, your daily sunny output
 will
 be
 an average of 353 watts.  The sun shines for 10 hours solid and you
 store
 3530 watt hours in your battery.  Now your load is on during the
 daytime,
 so
 if you have a 75 watt load, you are now able to make 278 watts.  You
 are
 down to 2780 watt hours.  You put in 2780 watt hours into a battery 
 and
 you
 get maybe 80% back out.  So you have 2224 watt hour available (if you
 drain
 the batts which is not good for them).



   You have 14 hours of darkness and actually more like 16 hours before
 the
 panel starts making any useful amount of energy.  16*75=1200 watt
 hours.

   But that next day is not sunny, there is frost and a light coating 
 of
 snow.  The whole works dies 16 hours later.  About 9 pm.



   One other note, you only want to draw your batteries down no more
 than
 10%
 each night or they won't last long.  That means a minimum of 12000 
 watt
 hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24
 volt
 system, 500 amp hours.  And that is a minimum because here we get a
 week
 with snow and ice and no sun easy, sometimes two weeks.



   You really need a generator, less load, or a whole bunch more batts
 and
 panels.



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/


 -- 
 Randy Cosby
 Vice President
 InfoWest, Inc

 office: 435-773-6071

Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Mike Hammett
You're special, Chuck.  :-p


-
Mike Hammett
Intelligent Computing Solutions
http://www.ics-il.com



--
From: Chuck McCown [EMAIL PROTECTED]
Sent: Thursday, November 20, 2008 2:07 PM
To: WISPA General List wireless@wispa.org
Subject: Re: [WISPA] Remote Powered Access Pont

 Oh, ice will indeed stick to an air-x.
 Can you spot it in these photos...
 I have been doing wind and solar for 30 years.
 There are those with frozen batts...
 And then there is me.

 - Original Message - 
 From: [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 1:01 PM
 Subject: Re: [WISPA] Remote Powered Access Pont


I have used a AIR-X for 4 years now.   The blades are a composite plastic
 and the ice WILL NOT stick to them.   I've been there when the pole
 supporting the generator had nearly an inch of ice on it and the antennas
 were all coated too thick to break off, and the genset blades were ice
 free.

 Mark



 
 insert witty tagline here

 - Original Message - 
 From: Chuck McCown [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 10:13 AM
 Subject: Re: [WISPA] Remote Powered Access Pont


 Wind generators are good if you have plenty of wind and no ice.
 Our problem has been that we need their power during the worst weather.
 And that is when they fail.  They wear out or get loaded with ice and
 tear
 apart.

 - Original Message - 
 From: Randy Cosby [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 11:04 AM
 Subject: Re: [WISPA] Remote Powered Access Pont


 Good point :)  It's not too severe down here in So Utah.

 Randy


 Chuck McCown wrote:
 They must not be subject to ice storms.

 - Original Message - 
 From: Randy Cosby [EMAIL PROTECTED]
 To: WISPA General List wireless@wispa.org
 Sent: Thursday, November 20, 2008 10:22 AM
 Subject: Re: [WISPA] Remote Powered Access Pont



 We recently visited a solar-powered site that had a supplementary
 wind-generation system.  Seemed to work well for them to have wind
 power
 when the weather is bad, solar when it is good.  Pretty windy place 
 as
 well.

 Chuck McCown - 3 wrote:

 Here is a note I posted several days ago on the Motorola list about
 solar
 powering.

 From: Chuck McCown [mailto:[EMAIL PROTECTED]
 Sent: Friday, November 14, 2008 9:17 AM
 To: Dave Crim
 Subject: Re: solar



 Continuing on a bit, lets say you have 5 lousy days and one good
 sunny
 day
 followed by 5 more lousy days.  That one sunny day needs to store
 enough
 to
 charge the batts totally.  75 watts * 5 days * 24hours * 1.25 
 (batter
 efficiency loss) + (75watts  * 24 hours) current day = 13050 watt
 hours.

 To make 13050 watt hours in one 10 hour day  you go:

 13050/.707*10=1845 watts.  You need 1845 watts of panel to do this.
 That
 is
 24 times the load.

 So, my rule of thumb of 20 times the load is still a little shy of
 being
 conservative.



 The thing that saves you in a situation like this is a massive
 battery.
 A
 one month battery with 20 X panels will never fail due to a lack of
 sun
 energy.

 A 2 week battery and 10X panels will fail now and then every single
 winter.
 Sometimes for several days at a time.

   - Original Message - 

   From: Chuck McCown

   To: [EMAIL PROTECTED]

   Sent: Friday, November 14, 2008 9:09 AM

   Subject: solar



   Several thing you may not be including.

   Assuming this panel is somewhere in this neck of the woods,
 December
 21
 has 10 hours of time between runrise and sunset.

   But if you don't have tracking mounts (most don't) the amount of
 energy
 you get out of a panel follows the first half of a sine wave.

   To estimate that energy, you integrate the area under the curve.
 That
 will equal .707 of what you thought you were going to get.



   So, let's say you put up a 500 watt panel, your daily sunny output
 will
 be
 an average of 353 watts.  The sun shines for 10 hours solid and you
 store
 3530 watt hours in your battery.  Now your load is on during the
 daytime,
 so
 if you have a 75 watt load, you are now able to make 278 watts.  You
 are
 down to 2780 watt hours.  You put in 2780 watt hours into a battery
 and
 you
 get maybe 80% back out.  So you have 2224 watt hour available (if 
 you
 drain
 the batts which is not good for them).



   You have 14 hours of darkness and actually more like 16 hours
 before
 the
 panel starts making any useful amount of energy.  16*75=1200 watt
 hours.

   But that next day is not sunny, there is frost and a light coating
 of
 snow.  The whole works dies 16 hours later.  About 9 pm.



   One other note, you only want to draw your batteries down no more
 than
 10%
 each night or they won't last long.  That means a minimum of 12000
 watt
 hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24
 volt
 system, 500 amp hours

Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Chuck McCown
feelin' da luv today

(As some might suspect, I do have a passion for mountain-top solar and wind 
power, having had to risk human life on more than one occasion to keep 
things alive or restore service.  $2000 helicopter rides after the storm 
blows through is also a good reason to get it right.  I have quite a few 
sites and I  think I have made every possible mistake you can make.  Just 
one helicopter ride more than pays for the batts that will not freeze.)


 You're special, Chuck.  :-p


 -
 Mike Hammett




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Scott Parsons
Thanks so much for the insight and great information. You just saved me
having to make all those mistakes all over again. I was definitely
undersizing the system and I'd bet most folks would tend to do that, trying
to save costs.

One more question: I read that solar panels will still output on cloudy
days, maybe 75% of sunny day capacity. Have you any experience with this?

Regards,
Scott

-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
Behalf Of Chuck McCown
Sent: Thursday, November 20, 2008 1:42 PM
To: WISPA General List
Subject: Re: [WISPA] Remote Powered Access Pont

feelin' da luv today

(As some might suspect, I do have a passion for mountain-top solar and wind 
power, having had to risk human life on more than one occasion to keep 
things alive or restore service.  $2000 helicopter rides after the storm 
blows through is also a good reason to get it right.  I have quite a few 
sites and I  think I have made every possible mistake you can make.  Just 
one helicopter ride more than pays for the batts that will not freeze.)


 You're special, Chuck.  :-p


 -
 Mike Hammett





WISPA Wants You! Join today!
http://signup.wispa.org/


 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Chuck McCown
We can even detect a little charge due to moonlight.

Clouds are such variable density it is hard to give a meaningful answer.
Plus there are days that are scattered, broken and overcast cloud 
conditions.
We typically see a 50% reduction of current when clouds pass over on the 
telemetry.

If you are trying to scrape together a system and feel you are falling 
short, cheap insurance is a small generator (assuming you can access the 
site).
Don't neglect the telemetry.  The RMS - BND system is ideal.  Packetflux 
just came out with a new system too.  With telemetry at least you can watch 
it die and not be surprised.

- Original Message - 
From: Scott Parsons [EMAIL PROTECTED]
To: 'WISPA General List' wireless@wispa.org
Sent: Thursday, November 20, 2008 2:15 PM
Subject: Re: [WISPA] Remote Powered Access Pont


 Thanks so much for the insight and great information. You just saved me
 having to make all those mistakes all over again. I was definitely
 undersizing the system and I'd bet most folks would tend to do that, 
 trying
 to save costs.

 One more question: I read that solar panels will still output on cloudy
 days, maybe 75% of sunny day capacity. Have you any experience with this?

 Regards,
 Scott

 -Original Message-
 From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
 Behalf Of Chuck McCown
 Sent: Thursday, November 20, 2008 1:42 PM
 To: WISPA General List
 Subject: Re: [WISPA] Remote Powered Access Pont

 feelin' da luv today

 (As some might suspect, I do have a passion for mountain-top solar and 
 wind
 power, having had to risk human life on more than one occasion to keep
 things alive or restore service.  $2000 helicopter rides after the storm
 blows through is also a good reason to get it right.  I have quite a few
 sites and I  think I have made every possible mistake you can make.  Just
 one helicopter ride more than pays for the batts that will not freeze.)


 You're special, Chuck.  :-p


 -
 Mike Hammett



 
 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Randy Cosby
I appreciate the fact that you not only have made the mistakes for us, 
but that you are willing to share the experiences instead of sitting 
back an snickering.

Randy


Chuck McCown wrote:
 feelin' da luv today

 (As some might suspect, I do have a passion for mountain-top solar and wind 
 power, having had to risk human life on more than one occasion to keep 
 things alive or restore service.  $2000 helicopter rides after the storm 
 blows through is also a good reason to get it right.  I have quite a few 
 sites and I  think I have made every possible mistake you can make.  Just 
 one helicopter ride more than pays for the batts that will not freeze.)


   
 You're special, Chuck.  :-p


 -
 Mike Hammett
 



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 
  
 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
   

-- 
Randy Cosby
Vice President
InfoWest, Inc

office: 435-773-6071





WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread rabbtux rabbtux
Thanks for the great info Chuck!  Almost made the trojan battery mistake.
what exactly is the battery technology and brand you suggest?  if I have a 5
watt system you suggest a 120W  solar panel.  Also 30 days or 360AH of
usable capacity at 12V?

Thanks for  the clarification, and the pics that make your experience clear!

On Wed, Nov 19, 2008 at 7:38 PM, Chuck McCown - 3 [EMAIL PROTECTED] wrote:

 At 60% depth of discharge they freeze at 0F.  Once frozen they are dead.
 Liquid electrolyte batteries need to be liquid to work.
 Not to mention the risk of a broken case. (You most likely mean you try to
 avoid taking them below 40% DOD, but 60% has a nice freezing point to
 exploit for purposes of rhetoric).

 Trojans were designed for the cabin with the fireplace and the intermittent
 use of the residential solar application.(Really, they were designed for
 golf carts).

 Constant load, constant nightly cycling, periods of no charging and deep
 discharge during the coldest days of the year is a different application and
 takes a different battery technology.

 Here is a good VLRA white paper on the temperature issue:
 http://www.cdtechno.com/custserv/pdf/7953.pdf

 We use VLRAs inside central offices where there is HVAC.  Not in the field.
 And they are much better than flooded cells like the T-105

 AGMs go in the field. And for solar only a few types of AGMs can be
 trusted.

 This app note is full of lots of good info.  It is on the batts we use that
 will still deliver 40% of their power at -40 degrees.
 http://www.enersysreservepower.com/documents/US-GPL-AM-003_0906.pdf

 But the only really important point is that in a solar situation, where you
 have weather and you have low temps, very few batteries will totally recover
 from an extreme deep discharge.  And that happens all the time when people
 scrimp on their battery capacity and solar panel capacity.

 20X watts 30 days autonomy = you will sleep all winter long.
   - Original Message -
  From: Blair Davis
  To: WISPA General List
   Sent: Wednesday, November 19, 2008 7:56 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  Ok.  our answer to that problem has always been to double up on our total
 battery size so we never discharge them below 60%

  Sounds like you are in a much more inaccessible environment than we are!
  And in that kind of location, I'd likely be looking for the same thing.

  But, for us, inaccessibility won't last more than a week or so...

  Chuck McCown - 3 wrote:
 We buy batts that are rated to give you the energy down to -20F.
 Survive being at-20F while discharged to a stone cold state.
 And recover when the next available bit of sunlight hits the panel (perhaps
 days later).
 And last 2000 cycles.
 For that you pay 30 cents per watt hour.  And can sleep at night.
 (we used to get these for 20 cents, I don't know why they are so much more
 now)

 I just found a website selling a T-105 for $160\each
 6 volts, 225 aH  That comes to 11.8 cents per watt hour.

 The Trojan website says avoid locations where freezing temperatures are
 expected.
 It also says the must be kept fully charged when freezing.  Hard to do with
 solar on a mountain top.


 http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

 So, if you have a nice warm place to keep the trojans then they are a very
 good value.
 (assuming they are in an air conditioned place in the summer too, else they
 won't last too many summers)

 But most solar powered sites don't have a heater to keep them from freezing
 and splitting.


  - Original Message -
  From: Blair Davis
  To: WISPA General List
  Sent: Wednesday, November 19, 2008 7:25 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  What type of battery's are you using?  That price sounds very high.

  4x T-105 will provide 225Ah at 24V for a cost of about $500

  Chuck McCoy's - 3 wrote:
 I would use a 100 watt panel minimum.
 And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour
 battery
 If you are running a 24 volt system then you need 3600/24=150 aH battery.
 If you are running a 12 volt system, you need a 300 aH battery.

 You will pay about 30 cents per watt hour for a battery.  So $1080 for the
 battery.
 You will pay about $5/watt for the panel, so $500 for the panel.
 Charge controllers are about $100 or less.

 If you build it this way it will always work.  You can put in half the
 battery for half the price.  But then you have only two weeks of insurance
 against bad weather.

 Never ever go below 10X the load for the panel, that will just barely cut
 it
 in the sunniest of climates.
 Even then you will probably have to put in a back up generator and you will
 be cycling the crap out of your batts causing them to only last a couple of
 years.

 If you want 99.999% reliability you have to use a panel 24X the size of the
 load (unless you have a tracking mount, then you can reduce that).
 I try to always use 20X panels

Re: [WISPA] Remote Powered Access Pont

2008-11-20 Thread Chuck McCown - 3
http://www.enersysreservepower.com/documents/US-GPL-AM-003_0906.pdf

Genesis pure lead EP or XE version will work down to -40.
They are rated for 100% depth of discharge.  Repeatedly.  400 times.
And can come back from 100% discharge at -40 to be fully charged.
They are good for 2 years sitting on the shelf totally unused.
I don't know of any other battery that can do that.

They also have most of their energy available at super cold temperatures, 
where flooded cells lose most of their energy when cold.
But you will pay 2 to 3 times more than for a Trojan.

I figure everything by watt hour first.  So you need 5 watts * 24 hours * 30 
days = 3600 watt hours.
At 30 cents per watt hour, you will end up paying more than $1000 for that 
battery.  Hopefully you can shop around and find them for less.  I used to 
pay 20 cents.  I don't know why they went up so much.

Watt hours / system voltage = amp hours
3600/12=300 amp hours.

One of our supervisors recently found a good price (if you can call it good) 
for the gates/hawker/enersys batteries.
If I can find the source I will post it.

- Original Message - 
From: rabbtux rabbtux [EMAIL PROTECTED]
To: WISPA General List wireless@wispa.org
Sent: Thursday, November 20, 2008 8:27 PM
Subject: Re: [WISPA] Remote Powered Access Pont


 Thanks for the great info Chuck!  Almost made the trojan battery mistake.
 what exactly is the battery technology and brand you suggest?  if I have a 
 5
 watt system you suggest a 120W  solar panel.  Also 30 days or 360AH of
 usable capacity at 12V?

 Thanks for  the clarification, and the pics that make your experience 
 clear!

 On Wed, Nov 19, 2008 at 7:38 PM, Chuck McCown - 3 [EMAIL PROTECTED] 
 wrote:

 At 60% depth of discharge they freeze at 0F.  Once frozen they are dead.
 Liquid electrolyte batteries need to be liquid to work.
 Not to mention the risk of a broken case. (You most likely mean you try 
 to
 avoid taking them below 40% DOD, but 60% has a nice freezing point to
 exploit for purposes of rhetoric).

 Trojans were designed for the cabin with the fireplace and the 
 intermittent
 use of the residential solar application.(Really, they were designed 
 for
 golf carts).

 Constant load, constant nightly cycling, periods of no charging and deep
 discharge during the coldest days of the year is a different application 
 and
 takes a different battery technology.

 Here is a good VLRA white paper on the temperature issue:
 http://www.cdtechno.com/custserv/pdf/7953.pdf

 We use VLRAs inside central offices where there is HVAC.  Not in the 
 field.
 And they are much better than flooded cells like the T-105

 AGMs go in the field. And for solar only a few types of AGMs can be
 trusted.

 This app note is full of lots of good info.  It is on the batts we use 
 that
 will still deliver 40% of their power at -40 degrees.
 http://www.enersysreservepower.com/documents/US-GPL-AM-003_0906.pdf

 But the only really important point is that in a solar situation, where 
 you
 have weather and you have low temps, very few batteries will totally 
 recover
 from an extreme deep discharge.  And that happens all the time when 
 people
 scrimp on their battery capacity and solar panel capacity.

 20X watts 30 days autonomy = you will sleep all winter long.
   - Original Message -
  From: Blair Davis
  To: WISPA General List
   Sent: Wednesday, November 19, 2008 7:56 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  Ok.  our answer to that problem has always been to double up on our 
 total
 battery size so we never discharge them below 60%

  Sounds like you are in a much more inaccessible environment than we are!
  And in that kind of location, I'd likely be looking for the same thing.

  But, for us, inaccessibility won't last more than a week or so...

  Chuck McCown - 3 wrote:
 We buy batts that are rated to give you the energy down to -20F.
 Survive being at-20F while discharged to a stone cold state.
 And recover when the next available bit of sunlight hits the panel 
 (perhaps
 days later).
 And last 2000 cycles.
 For that you pay 30 cents per watt hour.  And can sleep at night.
 (we used to get these for 20 cents, I don't know why they are so much 
 more
 now)

 I just found a website selling a T-105 for $160\each
 6 volts, 225 aH  That comes to 11.8 cents per watt hour.

 The Trojan website says avoid locations where freezing temperatures are
 expected.
 It also says the must be kept fully charged when freezing.  Hard to do 
 with
 solar on a mountain top.


 http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

 So, if you have a nice warm place to keep the trojans then they are a 
 very
 good value.
 (assuming they are in an air conditioned place in the summer too, else 
 they
 won't last too many summers)

 But most solar powered sites don't have a heater to keep them from 
 freezing
 and splitting.


  - Original Message -
  From: Blair Davis
  To: WISPA General

[WISPA] Remote Powered Access Pont

2008-11-19 Thread Scott Parsons
I'm looking into setting up a remote access point/repeater.
Power requirements are 5W. No access to grid power.

I was curious what you guys use for this type of thing?
I figure I need a 30W solar panel, controller, battery and enclosure.
How much should I expect to pay for a setup? 
Is there anything available off the shelf?

Thanks for your help.
Scott




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-19 Thread Chuck McCown - 3
I would use a 100 watt panel minimum.
And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour 
battery
If you are running a 24 volt system then you need 3600/24=150 aH battery.
If you are running a 12 volt system, you need a 300 aH battery.

You will pay about 30 cents per watt hour for a battery.  So $1080 for the 
battery.
You will pay about $5/watt for the panel, so $500 for the panel.
Charge controllers are about $100 or less.

If you build it this way it will always work.  You can put in half the 
battery for half the price.  But then you have only two weeks of insurance 
against bad weather.

Never ever go below 10X the load for the panel, that will just barely cut it 
in the sunniest of climates.
Even then you will probably have to put in a back up generator and you will 
be cycling the crap out of your batts causing them to only last a couple of 
years.

If you want 99.999% reliability you have to use a panel 24X the size of the 
load (unless you have a tracking mount, then you can reduce that).
I try to always use 20X panels and no less than a 2 week battery.  But even 
then, a week or two of snow on the panels and gray skies every day can cause 
an outage.


- Original Message - 
From: Scott Parsons [EMAIL PROTECTED]
To: 'WISPA General List' wireless@wispa.org
Sent: Wednesday, November 19, 2008 5:33 PM
Subject: [WISPA] Remote Powered Access Pont


 I'm looking into setting up a remote access point/repeater.
 Power requirements are 5W. No access to grid power.

 I was curious what you guys use for this type of thing?
 I figure I need a 30W solar panel, controller, battery and enclosure.
 How much should I expect to pay for a setup?
 Is there anything available off the shelf?

 Thanks for your help.
 Scott



 
 WISPA Wants You! Join today!
 http://signup.wispa.org/
 

 WISPA Wireless List: wireless@wispa.org

 Subscribe/Unsubscribe:
 http://lists.wispa.org/mailman/listinfo/wireless

 Archives: http://lists.wispa.org/pipermail/wireless/
 




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-19 Thread Chuck McCown - 3
Here is a note I posted several days ago on the Motorola list about solar 
powering.

From: Chuck McCown [mailto:[EMAIL PROTECTED]
Sent: Friday, November 14, 2008 9:17 AM
To: Dave Crim
Subject: Re: solar



Continuing on a bit, lets say you have 5 lousy days and one good sunny day 
followed by 5 more lousy days.  That one sunny day needs to store enough to 
charge the batts totally.  75 watts * 5 days * 24hours * 1.25 (batter 
efficiency loss) + (75watts  * 24 hours) current day = 13050 watt hours.

To make 13050 watt hours in one 10 hour day  you go:

13050/.707*10=1845 watts.  You need 1845 watts of panel to do this.  That is 
24 times the load.

So, my rule of thumb of 20 times the load is still a little shy of being 
conservative.



The thing that saves you in a situation like this is a massive battery.  A 
one month battery with 20 X panels will never fail due to a lack of sun 
energy.

A 2 week battery and 10X panels will fail now and then every single winter. 
Sometimes for several days at a time.

  - Original Message - 

  From: Chuck McCown

  To: [EMAIL PROTECTED]

  Sent: Friday, November 14, 2008 9:09 AM

  Subject: solar



  Several thing you may not be including.

  Assuming this panel is somewhere in this neck of the woods, December 21 
has 10 hours of time between runrise and sunset.

  But if you don't have tracking mounts (most don't) the amount of energy 
you get out of a panel follows the first half of a sine wave.

  To estimate that energy, you integrate the area under the curve.  That 
will equal .707 of what you thought you were going to get.



  So, let's say you put up a 500 watt panel, your daily sunny output will be 
an average of 353 watts.  The sun shines for 10 hours solid and you store 
3530 watt hours in your battery.  Now your load is on during the daytime, so 
if you have a 75 watt load, you are now able to make 278 watts.  You are 
down to 2780 watt hours.  You put in 2780 watt hours into a battery and you 
get maybe 80% back out.  So you have 2224 watt hour available (if you drain 
the batts which is not good for them).



  You have 14 hours of darkness and actually more like 16 hours before the 
panel starts making any useful amount of energy.  16*75=1200 watt hours.

  But that next day is not sunny, there is frost and a light coating of 
snow.  The whole works dies 16 hours later.  About 9 pm.



  One other note, you only want to draw your batteries down no more than 10% 
each night or they won't last long.  That means a minimum of 12000 watt 
hours.  If that is a 12 volt system, 1000 amp hours.  If it is a 24 volt 
system, 500 amp hours.  And that is a minimum because here we get a week 
with snow and ice and no sun easy, sometimes two weeks.



  You really need a generator, less load, or a whole bunch more batts and 
panels.




WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-19 Thread Blair Davis




What type of battery's are you using? That price sounds very high.

4x T-105 will provide 225Ah at 24V for a cost of about $500

Chuck McCoy's - 3 wrote:

  I would use a 100 watt panel minimum.
And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour 
battery
If you are running a 24 volt system then you need 3600/24=150 aH battery.
If you are running a 12 volt system, you need a 300 aH battery.

You will pay about 30 cents per watt hour for a battery.  So $1080 for the 
battery.
You will pay about $5/watt for the panel, so $500 for the panel.
Charge controllers are about $100 or less.

If you build it this way it will always work.  You can put in half the 
battery for half the price.  But then you have only two weeks of insurance 
against bad weather.

Never ever go below 10X the load for the panel, that will just barely cut it 
in the sunniest of climates.
Even then you will probably have to put in a back up generator and you will 
be cycling the crap out of your batts causing them to only last a couple of 
years.

If you want 99.999% reliability you have to use a panel 24X the size of the 
load (unless you have a tracking mount, then you can reduce that).
I try to always use 20X panels and no less than a 2 week battery.  But even 
then, a week or two of snow on the panels and gray skies every day can cause 
an outage.


- Original Message - 
From: "Scott Parsons" [EMAIL PROTECTED]
To: "'WISPA General List'" wireless@wispa.org
Sent: Wednesday, November 19, 2008 5:33 PM
Subject: [WISPA] Remote Powered Access Pont


  
  
I'm looking into setting up a remote access point/repeater.
Power requirements are 5W. No access to grid power.

I was curious what you guys use for this type of thing?
I figure I need a 30W solar panel, controller, battery and enclosure.
How much should I expect to pay for a setup?
Is there anything available off the shelf?

Thanks for your help.
Scott




WISPA Wants You! Join today!
http://signup.wispa.org/


WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


  
  



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/
  







WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/

Re: [WISPA] Remote Powered Access Pont

2008-11-19 Thread Chuck McCown - 3
We buy batts that are rated to give you the energy down to -20F.  
Survive being at-20F while discharged to a stone cold state.
And recover when the next available bit of sunlight hits the panel (perhaps 
days later).
And last 2000 cycles.
For that you pay 30 cents per watt hour.  And can sleep at night.
(we used to get these for 20 cents, I don't know why they are so much more now)

I just found a website selling a T-105 for $160\each
6 volts, 225 aH  That comes to 11.8 cents per watt hour.

The Trojan website says avoid locations where freezing temperatures are 
expected.
It also says the must be kept fully charged when freezing.  Hard to do with 
solar on a mountain top.

http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

So, if you have a nice warm place to keep the trojans then they are a very good 
value.
(assuming they are in an air conditioned place in the summer too, else they 
won't last too many summers)

But most solar powered sites don't have a heater to keep them from freezing and 
splitting.


  - Original Message - 
  From: Blair Davis 
  To: WISPA General List 
  Sent: Wednesday, November 19, 2008 7:25 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  What type of battery's are you using?  That price sounds very high.

  4x T-105 will provide 225Ah at 24V for a cost of about $500

  Chuck McCoy's - 3 wrote: 
I would use a 100 watt panel minimum.
And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour 
battery
If you are running a 24 volt system then you need 3600/24=150 aH battery.
If you are running a 12 volt system, you need a 300 aH battery.

You will pay about 30 cents per watt hour for a battery.  So $1080 for the 
battery.
You will pay about $5/watt for the panel, so $500 for the panel.
Charge controllers are about $100 or less.

If you build it this way it will always work.  You can put in half the 
battery for half the price.  But then you have only two weeks of insurance 
against bad weather.

Never ever go below 10X the load for the panel, that will just barely cut it 
in the sunniest of climates.
Even then you will probably have to put in a back up generator and you will 
be cycling the crap out of your batts causing them to only last a couple of 
years.

If you want 99.999% reliability you have to use a panel 24X the size of the 
load (unless you have a tracking mount, then you can reduce that).
I try to always use 20X panels and no less than a 2 week battery.  But even 
then, a week or two of snow on the panels and gray skies every day can cause 
an outage.


- Original Message - 
From: Scott Parsons [EMAIL PROTECTED]
To: 'WISPA General List' wireless@wispa.org
Sent: Wednesday, November 19, 2008 5:33 PM
Subject: [WISPA] Remote Powered Access Pont


  I'm looking into setting up a remote access point/repeater.
Power requirements are 5W. No access to grid power.

I was curious what you guys use for this type of thing?
I figure I need a 30W solar panel, controller, battery and enclosure.
How much should I expect to pay for a setup?
Is there anything available off the shelf?

Thanks for your help.
Scott




WISPA Wants You! Join today!
http://signup.wispa.org/


WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/





WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/
  



--




  

  WISPA Wants You! Join today!
  http://signup.wispa.org/
  

   
  WISPA Wireless List: wireless@wispa.org

  Subscribe/Unsubscribe:
  http://lists.wispa.org/mailman/listinfo/wireless

  Archives: http://lists.wispa.org/pipermail/wireless/



WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/


Re: [WISPA] Remote Powered Access Pont

2008-11-19 Thread Blair Davis




Ok. our answer to that problem has always been to double up on our
total battery size so we never discharge them below 60%

Sounds like you are in a much more inaccessible environment than we
are! And in that kind of location, I'd likely be looking for the same
thing.

But, for us, inaccessibility won't last more than a week or so...

Chuck McCown - 3 wrote:

  We buy batts that are rated to give you the energy down to -20F.  
Survive being at-20F while discharged to a stone cold state.
And recover when the next available bit of sunlight hits the panel (perhaps days later).
And last 2000 cycles.
For that you pay 30 cents per watt hour.  And can sleep at night.
(we used to get these for 20 cents, I don't know why they are so much more now)

I just found a website selling a T-105 for $160\each
6 volts, 225 aH  That comes to 11.8 cents per watt hour.

The Trojan website says "avoid locations where freezing temperatures are expected".
It also says the must be kept fully charged when freezing.  Hard to do with solar on a mountain top.

http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

So, if you have a nice warm place to keep the trojans then they are a very good value.
(assuming they are in an air conditioned place in the summer too, else they won't last too many summers)

But most solar powered sites don't have a heater to keep them from freezing and splitting.


  - Original Message - 
  From: Blair Davis 
  To: WISPA General List 
  Sent: Wednesday, November 19, 2008 7:25 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  What type of battery's are you using?  That price sounds very high.

  4x T-105 will provide 225Ah at 24V for a cost of about $500

  Chuck McCoy's - 3 wrote: 
I would use a 100 watt panel minimum.
And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour 
battery
If you are running a 24 volt system then you need 3600/24=150 aH battery.
If you are running a 12 volt system, you need a 300 aH battery.

You will pay about 30 cents per watt hour for a battery.  So $1080 for the 
battery.
You will pay about $5/watt for the panel, so $500 for the panel.
Charge controllers are about $100 or less.

If you build it this way it will always work.  You can put in half the 
battery for half the price.  But then you have only two weeks of insurance 
against bad weather.

Never ever go below 10X the load for the panel, that will just barely cut it 
in the sunniest of climates.
Even then you will probably have to put in a back up generator and you will 
be cycling the crap out of your batts causing them to only last a couple of 
years.

If you want 99.999% reliability you have to use a panel 24X the size of the 
load (unless you have a tracking mount, then you can reduce that).
I try to always use 20X panels and no less than a 2 week battery.  But even 
then, a week or two of snow on the panels and gray skies every day can cause 
an outage.


- Original Message - 
From: "Scott Parsons" [EMAIL PROTECTED]
To: "'WISPA General List'" wireless@wispa.org
Sent: Wednesday, November 19, 2008 5:33 PM
Subject: [WISPA] Remote Powered Access Pont


  I'm looking into setting up a remote access point/repeater.
Power requirements are 5W. No access to grid power.

I was curious what you guys use for this type of thing?
I figure I need a 30W solar panel, controller, battery and enclosure.
How much should I expect to pay for a setup?
Is there anything available off the shelf?

Thanks for your help.
Scott




WISPA Wants You! Join today!
http://signup.wispa.org/


WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/





WISPA Wants You! Join today!
http://signup.wispa.org/

 
WISPA Wireless List: wireless@wispa.org

Subscribe/Unsubscribe:
http://lists.wispa.org/mailman/listinfo/wireless

Archives: http://lists.wispa.org/pipermail/wireless/
  



--




  
  WISPA Wants You! Join today!
  http://signup.wispa.org/
  
   
  WISPA Wireless List: wireless@wispa.org

  Subscribe/Unsubscribe:
  http://lists.wispa.org/mailman/listinfo/wireless

  Archives: http://lists.wispa.org/pipermail/wireless/



WISPA Wants You! Join 

Re: [WISPA] Remote Powered Access Pont

2008-11-19 Thread Chuck McCown - 3
At 60% depth of discharge they freeze at 0F.  Once frozen they are dead. Liquid 
electrolyte batteries need to be liquid to work.
Not to mention the risk of a broken case. (You most likely mean you try to 
avoid taking them below 40% DOD, but 60% has a nice freezing point to exploit 
for purposes of rhetoric).

Trojans were designed for the cabin with the fireplace and the intermittent use 
of the residential solar application.(Really, they were designed for golf 
carts).

Constant load, constant nightly cycling, periods of no charging and deep 
discharge during the coldest days of the year is a different application and 
takes a different battery technology.

Here is a good VLRA white paper on the temperature issue: 
http://www.cdtechno.com/custserv/pdf/7953.pdf

We use VLRAs inside central offices where there is HVAC.  Not in the field.  
And they are much better than flooded cells like the T-105

AGMs go in the field. And for solar only a few types of AGMs can be trusted.

This app note is full of lots of good info.  It is on the batts we use that 
will still deliver 40% of their power at -40 degrees.  
http://www.enersysreservepower.com/documents/US-GPL-AM-003_0906.pdf

But the only really important point is that in a solar situation, where you 
have weather and you have low temps, very few batteries will totally recover 
from an extreme deep discharge.  And that happens all the time when people 
scrimp on their battery capacity and solar panel capacity.  

20X watts 30 days autonomy = you will sleep all winter long.
  - Original Message - 
  From: Blair Davis 
  To: WISPA General List 
  Sent: Wednesday, November 19, 2008 7:56 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  Ok.  our answer to that problem has always been to double up on our total 
battery size so we never discharge them below 60%

  Sounds like you are in a much more inaccessible environment than we are!  And 
in that kind of location, I'd likely be looking for the same thing.

  But, for us, inaccessibility won't last more than a week or so...

  Chuck McCown - 3 wrote: 
We buy batts that are rated to give you the energy down to -20F.  
Survive being at-20F while discharged to a stone cold state.
And recover when the next available bit of sunlight hits the panel (perhaps 
days later).
And last 2000 cycles.
For that you pay 30 cents per watt hour.  And can sleep at night.
(we used to get these for 20 cents, I don't know why they are so much more now)

I just found a website selling a T-105 for $160\each
6 volts, 225 aH  That comes to 11.8 cents per watt hour.

The Trojan website says avoid locations where freezing temperatures are 
expected.
It also says the must be kept fully charged when freezing.  Hard to do with 
solar on a mountain top.

http://www.trojan-battery.com/Tech-Support/documents/UsersGuide_0708_English_003.pdf

So, if you have a nice warm place to keep the trojans then they are a very good 
value.
(assuming they are in an air conditioned place in the summer too, else they 
won't last too many summers)

But most solar powered sites don't have a heater to keep them from freezing and 
splitting.


  - Original Message - 
  From: Blair Davis 
  To: WISPA General List 
  Sent: Wednesday, November 19, 2008 7:25 PM
  Subject: Re: [WISPA] Remote Powered Access Pont


  What type of battery's are you using?  That price sounds very high.

  4x T-105 will provide 225Ah at 24V for a cost of about $500

  Chuck McCoy's - 3 wrote: 
I would use a 100 watt panel minimum.
And a one month battery.  5watts * 24hours * 30 days = 3600 watt hour 
battery
If you are running a 24 volt system then you need 3600/24=150 aH battery.
If you are running a 12 volt system, you need a 300 aH battery.

You will pay about 30 cents per watt hour for a battery.  So $1080 for the 
battery.
You will pay about $5/watt for the panel, so $500 for the panel.
Charge controllers are about $100 or less.

If you build it this way it will always work.  You can put in half the 
battery for half the price.  But then you have only two weeks of insurance 
against bad weather.

Never ever go below 10X the load for the panel, that will just barely cut it 
in the sunniest of climates.
Even then you will probably have to put in a back up generator and you will 
be cycling the crap out of your batts causing them to only last a couple of 
years.

If you want 99.999% reliability you have to use a panel 24X the size of the 
load (unless you have a tracking mount, then you can reduce that).
I try to always use 20X panels and no less than a 2 week battery.  But even 
then, a week or two of snow on the panels and gray skies every day can cause 
an outage.


- Original Message - 
From: Scott Parsons [EMAIL PROTECTED]
To: 'WISPA General List' wireless@wispa.org
Sent: Wednesday, November 19, 2008 5:33 PM
Subject: [WISPA] Remote Powered Access Pont


  I'm looking into setting up a remote access point/repeater.
Power requirements are 5W. No access