just food for thought... I have never seen a "spec" warehouse stay the way
the owner/developer described it. After the job is done, many liberties will
be taken, of which YOU did not make them aware, (height, location, type,
etc..) Be sure you document well.....

R/


Matt 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom L
Sent: Tuesday, February 06, 2007 3:40 PM
To: [email protected]
Subject: Re: Determining a Warehouse Commodity Classification

Rich,

"belts, hoses"

"There are filters, including fuel, oil, air, water, and hydraulic types,
all sizes and shapes."

Any plastic filters??

How much of the above? Remember NFPA 13, 2002, section  5.6.1.2.3, mixed
commodities u are allowed 10 pallet loads in a 40K whse, u half this amount
so u are now at 4-5 pallet loads. More then 5 and u have to protect the
ENTIRE whse at the higher commodity. IF u design for a class 2 commodity,
now u are allowed 2 pallet loads! see (3) in the NFPA section above.
This material could be classified as a Grp A Plastic.

Regards

Tom LaCorte

Chubb Insurance

Check out our web site for hands- on fire protection training.
http://www.chubb.com/businesses/service/chubb5999.html



>From: "Jeff Hewitt" <[EMAIL PROTECTED]>
>Reply-To: [email protected]
>To: <[email protected]>
>Subject: Re: Determining a Warehouse Commodity Classification
>Date: Tue, 6 Feb 2007 13:56:56 -0600
>
>You mentioned wood crates.  You did not mention if there are any 
>pallets involved.  If there are any plastic pallets involved you may 
>have to increase the commodity class.
>
>
>
>Jeff Hewitt, PE, SET, SFPE (Prof. Member) Corporate Engineer Bi-State 
>Fire Protection Corporation
>636-946-0011
>636-946-5172 (FAX)
>
>This e-mail and any attachments are CONFIDENTIAL and may be protected 
>by one or more legal privileges.  It is intended solely for the use of 
>the addressee identified above.  If you are not the intended recipient, 
>any use, disclosure, copying or distribution of this e-mail is
unauthorized.
>If you received this e-mail in error, please notify the sender 
>immediately at the above captioned address.
>
>----- Original Message ----- From: "Lindner, Richard" 
><[EMAIL PROTECTED]>
>To: <[email protected]>
>Sent: Tuesday, February 06, 2007 11:42 AM
>Subject: Determining a Warehouse Commodity Classification
>
>
>(I seem to have lost access to the archives, so I can't research 
>this..)
>
>I am involved in an initial design (performance spec) for a warehouse 
>type project consisting of a butler building approx. 300'x60' and 35' 
>high in size (18,000 sq. ft.).  Approx 7000 sq. ft. of floor area will 
>consist of 25' high rack storage that is 42" deep with a 12" space and 
>then another 42" deep rack.  There are 5 racks of this arrangement with 
>an aisle at minimum 9'-6" width between them.  The shelving itself is wire
decking.
>
>The center part of the building has some administrative area offices 
>and other storage areas (no shelving shown).  The other end of the 
>building is a maintenance garage for repairs of vehicles.
>
>We have asked about what they intend to store on the shelving and have 
>been told that primarily they are storing spare machinery parts, some 
>of which are in wood crates; these are small, medium, large and very 
>large.  These include hydraulic cylinders, engines, transmissions, 
>radiators, air chambers, pumps, belts, hoses, fittings, nuts, bolts 
>(small items are in cardboard boxes in most cases), and tools (both power
and non-power tools).
>Aerosol cans include brake cleaner, starting fluid, lubricant (WD-40), 
>window cleaner, and paint.  They carry no more than two cases (24 cans) 
>of each item in stock.  There are filters, including fuel, oil, air, 
>water, and hydraulic types, all sizes and shapes.  They also store 
>spare pre-charged batteries. These are heavy equipment batteries; (2) 
>large, (2) medium and (4) small are typically all they have on hand.
>
>We feel the rack storage area is our most demanding area.  We have 
>reviewed our options and feel that Commodity Class II would be 
>appropriate based on the above information.  Does anyone see something 
>that might reflect using a different classification?
>
>Appreciate any response.
>
>Richard
>
>Richard K. Lindner
>Plumbing Senior Designer
>Morris, Johnson & Associates, Inc.
>
>611 Industrial Way West
>Eatontown, New Jersey  07724
>P:  732-380-1100 ext. 4186  |  F:  732-380-1111 
>[EMAIL PROTECTED] www.morrisjohnson.com
>
>
>
>
>--------------------------------------------------------
>
>This message contains confidential information and is intended only for 
>the individual named. If you are not the named addressee you should not 
>disseminate, distribute or copy this e-mail. Please notify the sender 
>immediately by e-mail if you have received this e-mail by mistake and 
>delete this e-mail from your system. E-mail transmission cannot be 
>guaranteed to be secure or error-free as information could be 
>intercepted, corrupted, lost, destroyed, arrive late or incomplete, or
contain viruses.
>The sender therefore does not accept liability for any errors or 
>omissions in the contents of this message, which arise as a result of 
>e-mail transmission. If verification is required please request a 
>hard-copy version.
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_________________________________________________________________
Laugh, share and connect with Windows Live Messenger
http://clk.atdmt.com/MSN/go/msnnkwme0020000001msn/direct/01/?href=http://ima
gine-msn.com/messenger/launch80/default.aspx?locale=en-us&source=hmtagline

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to