was the system ever tested with a water hammer produced by the pump so has to ensure everything was good and tight? Water hammer is a much bigger concern than static pressure. I certainly agree with checking it several times but when do you stop pounding things week in and week out?

The TC actually needs to do some work regarding compensating for water hammer. There are known cases where the uprights have rotated (believed to have been caused by continuous water hammers from the pump). Same thing for dry pipe and deluge systems and water impact. You only stand next to an elbow in the supply main ONCE when tripping deluge systems.

Roland

On Mar 8, 2007, at 3:50 PM, Joe Hankins wrote:

A real-world example:

Just a couple of years ago there was a situation at an auto parts warehouse. Fully sprinklered, adequate for the commodity and storage arrangement. Water supplied by a fire pump. Because of concerns that system might leak, even though it was relatively new with no sign of problems, the discharge valve was always shut before the weekly run of the fire pump.

You can guess what comes next. There was a fire, the pump starts up, and the system is subjected to pump pressure for the first time. A coupling in a large main let go and the water the sprinklers needed went out the open main instead, and the warehouse burned to the ground. The loss was in the 8 figure range.

The moral of the story is that if you are afraid to pressurize the system when there is no fire, you ought to be terrified of what could happen if there is a fire.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to