was the system ever tested with a water hammer produced by the pump
so has to ensure everything was good and tight? Water hammer is a
much bigger concern than static pressure. I certainly agree with
checking it several times but when do you stop pounding things week
in and week out?
The TC actually needs to do some work regarding compensating for
water hammer. There are known cases where the uprights have rotated
(believed to have been caused by continuous water hammers from the
pump). Same thing for dry pipe and deluge systems and water impact.
You only stand next to an elbow in the supply main ONCE when tripping
deluge systems.
Roland
On Mar 8, 2007, at 3:50 PM, Joe Hankins wrote:
A real-world example:
Just a couple of years ago there was a situation at an auto parts
warehouse. Fully sprinklered, adequate for the commodity and
storage arrangement. Water supplied by a fire pump. Because of
concerns that system might leak, even though it was relatively new
with no sign of problems, the discharge valve was always shut
before the weekly run of the fire pump.
You can guess what comes next. There was a fire, the pump starts
up, and the system is subjected to pump pressure for the first
time. A coupling in a large main let go and the water the
sprinklers needed went out the open main instead, and the warehouse
burned to the ground. The loss was in the 8 figure range.
The moral of the story is that if you are afraid to pressurize the
system when there is no fire, you ought to be terrified of what
could happen if there is a fire.