Thom, Steve, and Roland, [F] 905.3.4 Stages. Stages greater than 1,000 square feet in area (93m2) shall be equipped with a Class III wet standpipe system with 1.5-inch and 2.5-inch (38mmand 64 mm) hose connections on each side of the stage.
Could this be a MANUAL wet standpipe? In other words if them there fire guys and girls are in the building, has the pumper truck hooked up to the FDC yet? I would hope so. I don't see the word AUTOMATIC in the IBC verbage. Might save the owner a fire pump perhaps? Ken -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Monday, March 26, 2007 12:20 PM To: [email protected] Subject: RE: Stage Hose Stations A combined system needs to be valved so that sprinklers and standpipe(s) can be independently controlled, whether it's two separate risers or a combination standpipe riser with sprinkler connections however it's zoned. And since it's a code thing regarding the hoses, can we take the exception from 14 for a fully sprinklered building, where you simply omit the hose in favor of a 2.5" x 1.5" reducer and cap? I think that the presence of hose stations on stages and in A-2 and A-3 occupancies is not congruent with the accepted practice of encouraging EVERYONE in the building to leave in case of a fire alarm or sign of fire. I would ask the serving fire dept. if they can live with points of connection and bring their hose for mop up. Steve L. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum