Look at this again. It's required to be a Class III. IN 2006 The
exception for fully sprinklered buildings is just a 1-1/2 outlet and
it states it's now a Class II or III.
As such, manual (being limited to a Class I in other than high-rise)
is a no-go.
Roland
On Mar 26, 2007, at 9:33 AM, Steve Leyton wrote:
It can most certainly be manual.
Steve
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Ken
Holsopple
Sent: Monday, March 26, 2007 8:28 AM
To: [email protected]
Subject: RE: Stage Hose Stations
Thom, Steve, and Roland,
[F] 905.3.4 Stages.
Stages greater than 1,000 square feet in area (93m2) shall be
equipped with
a Class III wet standpipe system with 1.5-inch and 2.5-inch
(38mmand 64 mm)
hose connections on each side of the stage.
Could this be a MANUAL wet standpipe? In other words if them there
fire guys
and girls are in the building, has the pumper truck hooked up to
the FDC
yet? I would hope so.
I don't see the word AUTOMATIC in the IBC verbage. Might save the
owner a
fire pump perhaps?
Ken
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
Steve Leyton
Sent: Monday, March 26, 2007 12:20 PM
To: [email protected]
Subject: RE: Stage Hose Stations
A combined system needs to be valved so that sprinklers and
standpipe(s) can
be independently controlled, whether it's two separate risers or a
combination standpipe riser with sprinkler connections however it's
zoned.
And since it's a code thing regarding the hoses, can we take the
exception
from 14 for a fully sprinklered building, where you simply omit the
hose in
favor of a 2.5" x 1.5" reducer and cap?
I think that the presence of hose stations on stages and in A-2 and
A-3
occupancies is not congruent with the accepted practice of encouraging
EVERYONE in the building to leave in case of a fire alarm or sign
of fire.
I would ask the serving fire dept. if they can live with points of
connection and bring their hose for mop up.
Steve L.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum