Roland,

Just to make sure (for Thom's sake)


In reading the exception, if the building is sprinklered throughout that
only an 1 1/2" Hose Station in accordance with NFPA 13 Section 8.16.5 OR in
accordance with NFPA 14 for a Class II or III. If you go the NFPA 13 route,
then the water demands from NFPA 14 are not required. Just the hose
allowance at the point of connection.

I gotcha. 


Ken



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Monday, March 26, 2007 12:56 PM
To: [email protected]
Subject: Re: Stage Hose Stations

Look at this again.  It's required to be a Class III.  IN 2006 The exception
for fully sprinklered buildings is just a 1-1/2 outlet and it states it's
now a Class II or III.

As such, manual (being limited to a Class I in other than high-rise) is a
no-go.

Roland