You need to know how the facility was classified as far as Occupancy.
Depending on what kind of facility it is, it could be a Class I-1 or R-4
and depending on the construction type and other factors, it could even
be a standard NFPA 13 system.  But I wouldn't agree to it being a 13D,
that is specifically titled for ONE AND TWO FAMILY DWELLINGS.  What
you've described doesn't fit that definition,  more likely 13R but I
wouldn't design it using  13D.

You need more info.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
On Jun 13, 2007, at 11:21 AM, Mike Cabral wrote:

>
> Looking at a Goverment Owned Group Home located in Eastern Canada.3 
> stories 1615 sq ft each floor for a total of 4845 sq ft total. 3 
> bedrooms in the basement, 3 bedrooms on the second floor 7 bedrooms on

> the third floor for a total of 13 bedrooms. One small kitchen,
> 3.5 bathrooms. 1 large living room 1 small sitting area and a dinning 
> room.
> One stair way to each level. I'ts one dwelling unit I guess. . .  
> AHJ says it's 13D is he correct. Any thing above the minimum 
> reccomended here?
>
> Mike Cabral
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to