Greg,

We do that up here a lot. We have always been required to protect the area
over the offices, since the wall does not go all the way up. A lot of times
they may even put a light dust cover over it, still inaccessible for
storage.    

Bobby Gillett
Designer
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Saturday, June 16, 2007 12:29 PM
To: [email protected]
Subject: warehouse offices

I have seen this situation handled 3 ways and have my own opinion but would
like to see what you all think.

If you have an ordinary metal building warehouse with normal Ord Hazard
Group II storage with an office area you often end up with space above the
offices. In this case the offices will have lay in tile ceilings with
insulation on top of the ceiling and no structure above the ceiling.
Therefore there will never be storage on top of the offices. There is
Approximately 14' of clear space above the offices of non combustible
construction with no separation between the space above the offices and the
warehouse.

The offices represent approx. 30% of the total area of the building.


Sprinklers will be installed under the ceiling of the offices.

Do you protect above the offices completely? 

Do you protect 15' of the space from the warehouse side?

Do you ignore it?

Thanks,
Greg


Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to