The wall between the offices and the storage area should go to the roof
and be rated per the building code since the storage area represents 70%
of the floor space unless it's less than 3,000 sf and is sprinkled.
Depending on these situations and what is being stored it should be
either a 2 or 3 hour barrier. The architect or GC should have this
figured out already.  

In either case if the space is completely inaccessible and is not
capable of supporting storage, and doesn't contain any combustibles or
equipment, I've never had an AHJ require sprinklers above the lay-in
ceiling.

If there is gas fired equipment or there is a platform or there are
objects which are combustible (piping/duct insulation, wiring, plastic
piping, etc) or it has some sort of access then yes, sprinkle it.

I assume the offices will be sprinkled, right?


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Saturday, June 16, 2007 1:29 PM
To: [email protected]
Subject: warehouse offices

I have seen this situation handled 3 ways and have my own opinion but
would like to see what you all think.

If you have an ordinary metal building warehouse with normal Ord Hazard
Group II storage with an office area you often end up with space above
the offices. In this case the offices will have lay in tile ceilings
with insulation on top of the ceiling and no structure above the
ceiling.
Therefore there will never be storage on top of the offices. There is
Approximately 14' of clear space above the offices of non combustible
construction with no separation between the space above the offices and
the warehouse.

The offices represent approx. 30% of the total area of the building.


Sprinklers will be installed under the ceiling of the offices.

Do you protect above the offices completely? 

Do you protect 15' of the space from the warehouse side?

Do you ignore it?

Thanks,
Greg


Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to