Eric,

The Fire Protection Research Foundation is currently working on a
project to develop fire sprinkler design criteria for compact mobile
storage units. A first report summarizing prior fire testing is
available on the NFPA web site. Additional fire testing is planned to
happen over the next year but is limited to tightly packed file storage
like you'd see in a doctor's office.

The easy answer to your question is that this is an active area of
research and there is no published sprinkler criteria that I know of at
this time. A handful of historical fire tests are covered in the
Research Foundation report, but they deal with archival record storage
almost exclusively and provide little help in developing criteria for
other configurations such as yours. During the 2007 cycle, the NFPA 13
technical committee attempted to develop criteria for the standard (see
the ROP/ROC), but this was voted down on the floor at the annual
meeting.

Now for the whole story - here are the challenges you face:
*       This configuration can't simply be treated as shelf, rack or
narrow aisle storage following the criteria in NFPA 13 - it won't work.
*       These fires can burn or smolder for a very long time due to
limited oxygen reaching the center of the array. Tests conducted in the
last few months resulted in over 60+ minutes for the sprinklers to
activate after ignition, with another 60+ minutes of water flow before
the fire stopped spreading due to shielding. 
*       When the shelves are closed, it is very difficult for water to
penetrate into the storage array, thus allowing the fire to spread in
multiple directions. Simply dumping more water on the fire didn't help -
some tests conducted up in the 0.7 gpm/ft2 range still didn't touch the
fire.
*       Any fire will result in a significant loss to the entire array
including most items consumed by fire, or with heavy smoke/water damage.
It will be important to tell the client that the fire protection may
save the building, but will not be controlling the fire with the first
few sprinklers open. Basically everything stored in the array will be
lost...
*       Your configuration is unique with excess ceiling clearance,
further delaying sprinkler activation. The array size is also a concern
and if located in a larger space may open a significant number of
sprinklers.

Remember what Joe has said here many times before - there are just some
storage configurations that are not addressed by NFPA 13 and can't be
protected with sprinklers only. At this time, if the client is really
interested in limited damage to what is stored in the array, it might be
best to lower the ceiling, build an enclosure around it, and use a clean
agent gaseous fire suppression agent (backed up by sprinklers, of
course).

Rich Pehrson
Futrell Fire Consult & Design


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Eric
Shelton
Sent: Friday, July 27, 2007 3:53 PM
To: [email protected]
Subject: High Density Art Storage

I have a museum with a system of high density storage units used for
storing small paintings and sculptures, some of which is crated.  It is
similar to the units used for records storage, being about 8'6" high
with 24" deep shelves, with two back-to-back shelves per unit.  The
units are manual; there are no motors.  The footprint of the units is
about 2000 square feet, and the ceiling height is about 30 feet.
 
Does anyone have any experience with this sort of storage, and could
suggest a density?
 
Eric J. Shelton, PE
Senior Fire Protection Engineer

Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
 
v: (804) 285.4171 f: (804) 217.8520
http://www.haengineers.com <http://www.haengineers.com/> 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to