Garth,

You originally asked if this arrangement was code compliant or not.
There were some qualified yeas but  mostly a lot of "it depends." I
doubt if anyone on the forum thinks it's a good arrangement but we all
have different reads on whether it's a legal arrangement. That said
I'll reiterate that the call here is by someone higher on the decision
ladder than you. But a precarious spot  for you though since if all
goes well it doesn't matter but if all does not go well you then
become at least a target high on the potential liability ladder. If
this were my job I wouldn't be questioning the forum members I'd be
writing a letter to the architect describing the arrangement, stating
my concerns, proposing my alternatives, and asking for a decision, yea
or nay on the original arrangement and on the alternative, or for
another arrangement. I'd want this reply in writing. To the AHJ I'd
merely write saying I had concerns and whether or not he has accepted
the current layout. I'd also want this answer in writing. I would by
now have done my due diligence by bringing a might have been
overlooked (from MY point of view) deficiency to the attention of the
powers that be and allowed them to decide. I might later end up having
to defend myself in a liability issue but I bet I'd have a couple of
really big bullets to bring to the gunfight when I have documentation
that I thought the arrangement to be bogus but the two biggest guns in
town said it was OK.

On 9/13/07, Garth W. Warren <[EMAIL PROTECTED]> wrote:
> Craig - The underground vales are not supervised, the location of some are
> not even known.  Yes, the underground is ductile, not sure if the lead-ins
> are ductile or copper as the individual risers are 2".  I agree the
> underground set-up is typical.  Plans show each floor of each system, a
> single set of calculation results has been provided for the entire project.
> I do not know the type of alarm system but can not imagine it not notifying
> a central station.  Neither do I know if an alarm from one of the individual
> risers causes an alarm in all of the structures.
>
>  I have just never run into a site where control valves are not present and
> accessible or where there are no checks between the fdc and the hydrant.
> All ten of these building parts will be out-of-service if there is a fire,
> freeze-up or accidental discharge in any of the individual structures....at
> least until the underground valve is located, a t-wrench found, and the
> valve closed or the individual riser is disconnected and plugged.
>
> Garth
>
>
> ----- Original Message -----
> From: <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Wednesday, September 12, 2007 9:41 AM
> Subject: RE: what makes a "building"
>
>
> This doesn't sound like anything much different than a site with
> multiple buildings served by a private fire main.  However there are a
> few things that don't sound like they are what we would consider good
> engineering practice and maybe even to the point of not being compliant
> but again, without seeing it first hand or having more info that's hard
> to tell.
>
> It's not uncommon to come into an industrial park or campus and bring
> the underground into a building or pit, enter the backflow then out to
> the rest of the buildings on the site.  Is the underground piping
> ductile with run-ins into the buildings?  I'd question the buried gate
> valves in the roadway boxes, they are probably not monitored or secured,
> but that wasn't stated specifically.  The shot-gun type riser assembly
> with no check valve or control valve isn't that uncommon either, but
> again not necessarily best practice but a cheap installation, probably
> how the installer got the job in the first place.
>
> The problems I can see is that the control valve in the yard (when able
> to be found) could be closed and no one would know it.  So that's not
> code compliant,  (no supervision), hopefully the flow switch is actually
> connected to an NFPA 72 compliant fire alarm system which reports to
> some sort of monitoring service?
>
> The fact that there are FDC's on each "riser" yet no check valve makes
> no sense.  On private loops often there is a single FDC tied into the
> loop on the private side of the fire main at or near the Backflow
> location and near a municipal hydrant.  When that's the case there are
> often no FDC's at the individual buildings.  I've seen this
> configuration accepted by various jurisdictions and Underwriters.
>
> What a concoction of a sprinkler system.  Were there any riser placards,
> proof of any hydraulic calcs?  Any inspection tags or reports?
>
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [EMAIL PROTECTED]
> http://www.lg.com
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to