I don't disagree, but in thinking about Ron's comments and my own
previous response, I think we should look at it from an "intent"
standpoint.  Grain storage and silage is a HIGHLY combustible
environment and an explosion risk to boot.   It would seem that any
required water supply, i.e. standpipe system, should suitable for
primary streams and attack lines, which pretty much takes "small hose
stations" and Class II connections out of the equation.  This isn't the
classic mop up application ...

Steve Leyton
Protection Design & Consulting

The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems, nor serve as an interpretation
of NFPA 14.



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron
Greenman
Sent: Wednesday, December 05, 2007 1:55 PM
To: [email protected]
Subject: Re: Standpipes

I'd suggest that the two requirements are for the use of two different
 sets of folks: small hose stations for the owner/occupant and the
standpipe for the FD. I'd suspect that class II alone would not be an
option and that unless the local AHJ wanted the class II stations for
fast attack (in a sprinklered warehouse?) then a class I would the
one. Of course, as Steve says, the standpipe is for the FD and it's
their requirement that needs to be met.

On Dec 5, 2007 1:47 PM, Steve Leyton <[EMAIL PROTECTED]> wrote:
> In a word, no.  Methinks that you would go to the applicable building
> code to determine the class of service; if the code and referenced
> standards don't specify the requirement I would ask the serving
building
> and/or fire official.
>
> Steve Leyton
> Protection Design & Consulting
>
> The foregoing is my opinion only and is not intended to represent the
> Technical Committee on Standpipe Systems, nor serve as an
interpretation
> of NFPA 14.
>
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of David
> Autry
> Sent: Wednesday, December 05, 2007 11:10 AM
> To: [email protected]
> Subject: Standpipes
>
> I've got a large (over 12,000 sq. ft.) warehouse full of seed corn
> stacked
> 14' high.
>
>
> NFPA 61 2002 Edition - Prevention of Fires and Dust Explosions in
> Agricultural and Food Processing Facilities
> 12.4.3
> Wet or Dry standpipes shall be installed in warehouses and packing
areas
> with combustible contents.
>
> Exception: Bulk storage warehouses or warehouses used for other than
> agricultural or food product storage.
>
> NFPA 61 12.4.3 says I need a standpipe, 12.4.1 states if a standpipe
is
> installed it shall be in accordance with NFPA 14. It gives no guidance
> as to
> what class of standpipe. Class I, II or III.
>
>
>
> NFPA 13 2002 Edition
> 12.1.3
> Small hose connections shall be provided in accordance with 8.16.5 for
> first-aid fire-fighting and overhaul operations.
>
>
>
> Would the requirement in NFPA 13 satisfy NFPA 61? or vice a versa?
> Looking at a distance it appears that both are required, since 13 hose
> stations don't need to meet the requirements of 14 and 61 requires
them
> to
> meet 14.
>
> What say the Forum?
>
> I know the new 13 has some wording change about small hose stations,
but
> I'm
> working with 2002 in both cases.
>
>
> Thanks for helping out a confused AHJ,
>
>
>
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office
> 246 S. 14th Street
> Lincoln, NE 68508
> 402-471-9659
> 402-471-3118 fax
> www.sfm.ne.gov
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to