I've got a large (over 12,000 sq. ft.) warehouse full of seed corn stacked
14' high.


NFPA 61 2002 Edition - Prevention of Fires and Dust Explosions in
Agricultural and Food Processing Facilities 
12.4.3
Wet or Dry standpipes shall be installed in warehouses and packing areas
with combustible contents.

Exception: Bulk storage warehouses or warehouses used for other than
agricultural or food product storage.

NFPA 61 12.4.3 says I need a standpipe, 12.4.1 states if a standpipe is
installed it shall be in accordance with NFPA 14. It gives no guidance as to
what class of standpipe. Class I, II or III.



NFPA 13 2002 Edition
12.1.3
Small hose connections shall be provided in accordance with 8.16.5 for
first-aid fire-fighting and overhaul operations.



Would the requirement in NFPA 13 satisfy NFPA 61? or vice a versa?
Looking at a distance it appears that both are required, since 13 hose
stations don't need to meet the requirements of 14 and 61 requires them to
meet 14.

What say the Forum?

I know the new 13 has some wording change about small hose stations, but I'm
working with 2002 in both cases.


Thanks for helping out a confused AHJ,

   


David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 