The section say's you can omit them from the calc (They still must be installed) when the design area exceeds the Minimum (1500 SF). You don't meet or exceed the Min. therefore you must include them in your calc as well as install them. You've been kicked back to 14.4.4.4.1
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, February 12, 2008 1:16 PM
Subject: omitting closets in small building


A 960 square foot (footprint) house is being converted to offices and a 13 system is to be installed. The top floor layout will not be changed and there are several small closets, etc. which will require sprinklers. The total number of sprinklers on that floor is 16. Section 14.4.4.4.2 allows for the sprinklers in the closets to be omitted if the design area is as stated in section 11.2.3.1.5 (1500 sqft). Since the building is smaller than the design area, would that require the sprinklers in the closets to be included? Eliminating the closet sprinklers would cut the number calculated in half.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to