A 960 square foot (footprint) house is being converted to offices and
a 13 system is to be installed. The top floor layout will not be
changed and there are several small closets, etc. which will require
sprinklers. The total number of sprinklers on that floor is 16.
Section 14.4.4.4.2 allows for the sprinklers in the closets to be
omitted if the design area is as stated in section 11.2.3.1.5 (1500
sqft). Since the building is smaller than the design area, would that
require the sprinklers in the closets to be included? Eliminating the
closet sprinklers would cut the number calculated in half.
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut