Cliff, I gotta admit I've never heard a formal definition of what a
communicating space is, but I've interpreted that to mean any adjacent room
that heat from a fire could travel into and activate sprinklers.  By calcing
up to 2 sprinkles in each of these spaces, the sprinkler system shouldn't
get overpowered.

I've been known to be wrong.
Ed Kramer
Littleton, CO

 
> I understood the whole idea regarding communicating spaces was to escape
> the
> fire.  Who is going to leave a larger office and hide in a closet to get
> away from a fire?
> 
> I guess I misunderstood the reasoning on this.
> 
> Cliff
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Roland
> Huggins
> Sent: Tuesday, February 12, 2008 4:17 PM
> To: [email protected]
> Subject: Re: omitting closets in small building
> 
> If you have an adjacent compartment with an unprotected opening, how
> can you justify ignoring it just because it is small?
> 
> Put a closer on the doors, then exclude them.
> 
> Roland
> 
> On Feb 12, 2008, at 1:01 PM, Cliff Whitfield wrote:
> 
> > Todd,
> >
> > Could you not use the Room Design method for your calcs?  That should
> > eliminate the need to include those heads in the closets.  I don't
> > think a
> > closet is considered a "communicating space" in this instance.
> >
> > Cliff