Todd,

Could you not use the Room Design method for your calcs?  That should
eliminate the need to include those heads in the closets.  I don't think a
closet is considered a "communicating space" in this instance.

Cliff

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Tuesday, February 12, 2008 2:17 PM
To: [email protected]
Subject: omitting closets in small building

A 960 square foot (footprint) house is being converted to offices and 
a 13 system is to be installed. The top floor layout will not be 
changed and there are several small closets, etc. which will require 
sprinklers. The total number of sprinklers on that floor is 16. 
Section 14.4.4.4.2 allows for the sprinklers in the closets to be 
omitted if the design area is as stated in section 11.2.3.1.5 (1500 
sqft). Since the building is smaller than the design area, would that 
require the sprinklers in the closets to be included? Eliminating the 
closet sprinklers would cut the number calculated in half.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to