I don't think the closet sprinklers can be omitted if the design area is less than 1500 sq.ft. Can you use the room design method to omit a few heads, instead?
Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: February 12, 2008 1:17 PM To: [email protected] Subject: omitting closets in small building A 960 square foot (footprint) house is being converted to offices and a 13 system is to be installed. The top floor layout will not be changed and there are several small closets, etc. which will require sprinklers. The total number of sprinklers on that floor is 16. Section 14.4.4.4.2 allows for the sprinklers in the closets to be omitted if the design area is as stated in section 11.2.3.1.5 (1500 sqft). Since the building is smaller than the design area, would that require the sprinklers in the closets to be included? Eliminating the closet sprinklers would cut the number calculated in half. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)