i may not be following your point,
but if you are concerned that the actual
C-factor of old UG pipe is less than the
idealized C-factor

what does it matter
as long as you take your source where ever
your gauge hydrant is?

the waterflow test will account for any aging
in the pipes, automatically.

it is another thing,
to extend this thinking,
downstream of the
guage hydrant though.
There you will need
professional judgement
to bring
value engineering.

scot deal
excelsior fire



On Feb 13, 2008 1:19 PM, danarbel <[EMAIL PROTECTED]> wrote:

>
>
> According to 22.4.4.7 Friction Loss, The C-Factor used for black steel
> pipe
> is 120.
>
> My question is:
>
> In case of using old pipe system Mains for water supply of sprinkler
> system,
>
>
> Is there in the code any requirement to find out by actual testing that
> the
> piping determined as adequate by the hydraulic calc procedure is indeed
> adequate?
>
> Thanks
>
>
> Dan Arbel
> Tel: 972-4-8243337
> Fax: 972-4-8243278
> M: 972-52-2810593
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.516 / Virus Database: 269.20.4/1275 - Release Date:
> 12/02/2008
> 15:20
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to