Dan,
Flow through the pipe and accurate measurement of the loss is the only way
to understand what you have to work with. Adjusting the C factor to
compensate for aging is definitely a guessing process. You may look at
tables that attempt to predict the C of older rough pipes but I would be
suspicious of the information without some backup. At best this
information would be an average of many tested samples. This still does
not predict your specific losses. Please the see the following information
concerning the Hazen-Williams equation and the C factor.
The Hazen-Williams equation is used widely in water supply and sanitary
engineering and almost exclusively in fire protection sprinkler systems.
This equation uses a constant, the Hazen-Williams C, to indicate the
roughness of a pipe interior. Because of the empirical nature of the
equation, its range of applicability is limited. Many textbooks and
software manuals give C values based on pipe type, condition, and age but
do not give the range of applicability. Historic experimental data has
demonstrated that C is a function of Reynolds number, relative roughness
(absolute roughness divided by the pipe diameter) and pipe size. The
Hazen-Williams equation is not dimensionally homogeneous and has narrow
applicable ranges for Reynolds numbers and pipe sizes. The level of error
when the Hazen-Williams equation is used outside its data ranges can be
significant.
The original work performed by Allen Hazen and Gardner Williams in their
book “Hydraulic Tables – The Elements of Gagings and the Friction of Water
Flowing in Pipes, Aqueducts, Sewers, etc. 1920” was directed mainly at
smooth new pipes larger than 2 inches. In this original work, several
items should be noted per the following quotes:
The constant, 4.52, that we use in the Hazen-Williams equation today has a
very interesting history. It is derived from the number .001 to the -.04
power (1.318). Hazen-Williams added this constant to their original
equation to “simply equalize the value of C with the Chezy formula and
other exponential formulas which may be used at a slope of .001 instead of
at a slope of 1.”
In the book, Hazen and Williams discuss the exponents used in their formula
and the value of C. “If exponents could be selected agreeing perfectly
with the facts, the value of C would depend upon the roughness only, and
for any given degree of roughness, C would then be a constant. It is not
possible to reach this actually because the values of the exponents vary
with different surfaces and also their values may not be exactly the same
for large diameters and for small ones, nor for steep slopes and for flat
ones.”
When speaking about deterioration of the interior of pipe when using the
formula, the authors state “It is a difficult matter to handle adequately,
for no two pieces of iron pipe deteriorate at the same rate, and any
figures given are therefore at best only approximations to averages, which
averages may be very far from individual cases.
On the subject of the exponent of the slope ‘s’ (Hf / L, feet of head per
foot of pipe length), The authors state the following: “This exponent
shows the rate at which friction increases with velocity. Experiments with
seventeen pipes have been selected as being helpful in reaching a
representative value for this exponent. Each of these pipes were very
smooth. The value of the coefficient actually found in the experiments is
taken as the best evidence of smoothness. Many older data have been
excluded, because the value of C show that the pipes that they represent
were not really smooth. Data for pipes less than two inches in diameter
are not included. Such data are numerous and accurate; but viscosity is a
greater element in the flow of water in small pipes.
Further the authors state: For rough pipes the value of the exponent s is
lower, but seldom or never lower than 0.50(1/.5 = exponent of 2 versus
1.85). Perhaps 0.52 would be a representative value for old pipe.
In conclusion it is worth noting that tests were made at a velocity of 5
feet per second or less; many at 3.25 feet per second. It is also
important to note that the authors were considering correction of the
exponents rather than changing the C value for rough pipe.
Therefore, the question of what is the C value needed for rough pipe is
simply a guess or assumption as the Hazen-Williams equation was predicated
on smooth pipes. It is important to remember that the C value assumed for
a large rough pipe is very different than the C value for a small pipe.
There will be only one C value for each condition. There is no one size
fitting all. The only absolute way to determine the correct C value is to
accurately measure the losses with a known flow through the pipe in
question.
Thank You
Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102
"danarbel"
<[EMAIL PROTECTED] To
.com> [email protected]
Sent by: cc
sprinklerforum-bo
[EMAIL PROTECTED] Subject
er.org C-Factor for old piping
02/13/2008 07:19
AM
Please respond to
[EMAIL PROTECTED]
resprinkler.org
According to 22.4.4.7 Friction Loss, The C-Factor used for black steel pipe
is 120.
My question is:
In case of using old pipe system Mains for water supply of sprinkler
system,
Is there in the code any requirement to find out by actual testing that the
piping determined as adequate by the hydraulic calc procedure is indeed
adequate?
Thanks
Dan Arbel
Tel: 972-4-8243337
Fax: 972-4-8243278
M: 972-52-2810593
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.516 / Virus Database: 269.20.4/1275 - Release Date: 12/02/2008
15:20
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)